When the mfr specifies the max. # of breaker poles, are the 2 poles on
the main breaker considered in the total?


Is it kosher to wirenut 2 wires together and pigtail to a breaker


within a panelboard?


wire nuts in the panel are a no-no......I would wager that, that
prohibtion is nearly universal


that's why I usually install a LARGE box near any main or *sub I
install......gives a place to do this sort of thing and still be code
compliant


cheers
Bob


That is not true at all. You are allowed to splice in a panelboard
enclosure. The issue is "fill" and a wirenut has a fill adder of zero.


could you explain further?

tia
Bob