View Single Post
  #7   Report Post  
Posted to alt.home.repair
RBM[_2_] RBM[_2_] is offline
external usenet poster
 
Posts: 1,563
Default Installing a subpanel


"Kevin Ricks" wrote in message
...
Wayne Whitney wrote:
On 2008-12-21, Kevin Ricks wrote:

In my area sub-panel disconnects are required.


That seems odd--shutting off the main breaker in a subpanel doesn't
render it safe to work on, as the incoming feeder conductors are still
energized. To deenergize the panel, you have to kill the feeder itself.


I was told the local inspector would require the disconnects where there
are 2 columns of breakers in the panel? With one column you can turn
everything off in one sweeping hand motion...with 2 columns your all
confused in a panic emergency ..... It was just a store employee that said
that... , but it may be that the NEC would require disconnect anyway in my
situation. It's an 8 slot sub in a detached shop building. I believe NEC
requires disconnects for subs in detached buildings.
Actually, I am not sure if my shop is classified as attached or detached?
It's separated from the house by a breezeway but attached at the roof. I
treated it as detached.


OR what I did was to back feed the sub-panel through a standard
breaker (60A in my case). Much cheaper than the main breaker kit,
but it uses up 2 slots in the sub-panel.


This configuration requires an additional holddown bracket on the
backfed breaker.


Thanks I didn't know that.
Kevin




Cheers, Wayne


The NEC does require a disconnect in a sub panel in a detached building, but
it also allows up to 6 disconnects in the panel, which is probably where the
single column of breakers comes from