Default 26.5A on a 20A circuit?

On Nov 27, 8:06*am, Art Todesco wrote:
wrote:
On Nov 27, 2:15 am, "Kevin" wrote:
I just finished wiring in two 220V circuits to the shop -- 1 for the dust
collector (5.5A), and the other for the tablesaw (14.5A), jointer (6.5A),
and tbd.


Just for grins I put all of them onto the one circuit. *So 5.5+14.5+6.5 =
26.5A. *The 20A breaker did not trip. *I even tried starting up the tablesaw
while the others were running.


Now in practice, I will keep my dust collector (5.5A, 1.5HP) on it's own
circuit, but apparently I could concurrently run both the tablesaw (14..5A)
and the jointer (6.5A) and possibly even a 3rd TBD on that other circuit.
How is that? *The real load must be under 20A, or the 20A breaker allows
more like 28A.


I first tried the TS and Jointer, and when they did not trip the breaker
(total 21A), I added the DC. *I was surprised all three did not trip the
breaker. *But I guess each was running with no load, so that is surely
another reason.


Curious,


Those ratings are for machines with a maximum work load. * In other
words, a saw just spinning doesn't pull as many amps as one ripping a
big piece of wood. *If you put them to work instead of just spinning
them up, your results would be different.


Also, breakers don't trip instantly.
They can take quite a long time for
a marginal overload. *BTW, for a big
overload, like a short, they trip
pretty fast.


I was on the scene when a "smart" electrician (also young) said he
could find the breaker by shorting the two 220V wires.(on a
conveyor)
He kept getting these huge arcs...and after numerous tries...gave up
red-faced!