tvmo wrote:

OK, probably worth noting that all these faults are probably unrelated.

1)What happens when you try to run the hair dryer?


On one of the sockets it doesn't work, on another socket the hair
dryer blows air in pulses, on the majority of sockets it blows air
evenly


This could be a number of things. The most likely being loose
connections on the sockets - causing sparking and intermittent supply to
the dryer. The lower power requirements of the lamp may mean less local
heating and hence less movement of the wires.

Alternatively it may be you have a serious voltage drop issue. Either a
section of seriously undersized cable in a circuit, or a high resistance
connection. These options would fit the symptom better if the dryer was
a type with soft touch controls (i.e. electronic rather than mechanical
switching), where the low voltage might cause it to behave incorrectly.

*** in either case, this fault is serious and needs investigating as a
matter of urgency ***

High resistance or arcing connections are a fire risk. I would suggest
not using the sockets (and probably the circuit) in question until this
is fixed.

Some more background he

http://wiki.diyfaq.org.uk/index.php?...Circuit_Faults


2) Switching on the dish washer, which is on a separate ring to the
majority of the sockets in my house, causes frequency issues on my TV

You mean you get a noise pattern on the screen - say lines with bright
speckles on them?


Yes, exactly - sorry about the poor description


I would expect the mains input filter on the dishwasher, or possibly the
noise suppression caps on the motor have failed. Probably not a house
wiring fault - although it is possible it could be related to a bad
connection on part of a ring circuit.

3) The washer dryer frequently trips the electric.

Trips what exactly? The circuit breaker for the individual circuit, or
the RCD protecting a group of circuits or possibly even the whole house?

The whole house trips.


The washer dryer is probably faulty. It may be the heating element is
leaking current to earth (not uncommon as they age), or water has got
into parts of the machine they should not have.

The other possibility is that you have just have too many circuits on
the same RCD and it is as a result pre-sensitised. In these cases the
switching transients of things like thermostatically controlled heaters
cutting in and out may be enough to cause a trip.

See the nuisance trips section of the RCD FAQ:

http://wiki.diyfaq.org.uk/index.php?...Nuisance_trips

The problem is compounded by you having a single RCD protecting all of
the circuits in the house. This no longer considered and acceptable way
of wiring, but there was a time where this was common. A consumer unit
upgrade would separate the protection for the circuits into groups such
that you don't loose all at once, and also reduce the likelihood of
trips in the first place as a result of the cumulative leakage being
excessive for a single RCD.


--