On Tue, 27 Jul 2004 16:23:58 GMT, "William" wrote:
"Gary Coffman" wrote in message
.. .
208 wye is common, but falling out of favor. Higher voltages are preferred
now almost everywhere because they allow smaller wires to carry more
power (higher voltage, same current, more power). Lots of 480 3 ph wye
and 277 volt 1 ph. That means transformers are required to get 120 or 240,
but spotting dry transformers around the facility where low voltage 1 ph
is required while distributing power to them at a higher voltage saves a
*lot* of copper (lot of money in any building bigger than a bread box).

Gary


Well that is true you can run smaller wire, but as I found out there is a
dirty little secrete in the above plan. It's the transformers!!! I set up
my shop that way and was going to run 480 volt to my house and step it down
there ( smaller wire less cost, lower % voltage drop etc...) sounds GREAT
on paper, well reality is that it's not cheaper at all! at the shop I have
a 225 amp panel for 208 3phase that I use to feed the 5 ton air unit (
single phase) and lots of wall outlets. To run that panel NEC says min 75
kva transformer. Problem?? that transformer burns 600 watts at idle!! just
keeping it warm! The house is even worse, planed to send 150 amps of 480
up to it, to feed a 300 amp panel. so ole NEC says I need a 112.5 kva
transformer. I have a nice 800lb copper wound K13 rated transformer, and
it burns 1200 watts !!!! IF you could run a smaller transformer you
wouldn't have so much loss, but unlike the power co that will feed 5-6,
200amp houses with a single 50kva can, I have to follow the NEC:-(


Lets put this in perspective. Our plant's power bills average $20,000
a month. At 4 cents a kWh, we don't even notice the transformer
magnetization current losses. But we certainly noticed the $600,000
savings in wiring the plant by using 480/277 instead of 220.

Gary