Conduit required in a garage.
ejluhn720 via HomeKB.com wrote:
Wayne, Others,
Thanks for the help. It looks as if all types of NM cable (NM, NMC, NMS)
are out as per the "dwelling" issue of a detached garage as per 334.10 . Then
conduit or metallic cable it is!
Interesting what one learns on newsgroups.
You could also ask the inspector if they allow NM.
Wayne Whitney wrote:
Is conduit required for wiring in a detached garage, or can the wire be run
to the outlet boxes in NM cable? I have exposed 2x4's with no drywall. Can
[quoted text clipped - 3 lines]
Anybody help me out?
Take a look at http://forums.mikeholt.com/showthread.php?t=99016.
I agree with those who say that since a detached garage is not a
dwelling unit, the use of NM cable is subject to the requirements of
NEC 334.10(3). That means NM can only be used if covered by a 15
minute fire-rated finish, i.e. drywall. You could use MC instead.
Cheers, Wayne
|