View Single Post
  #7   Report Post  
Posted to uk.d-i-y
Mano Mano is offline
external usenet poster
 
Posts: 5
Default Strange electrical problem

Andy Wade wrote:
Tuthledeen wrote:
"Mano" wrote in message
...
OK open to ideas here with this one :-


Switch off individual breakers and see when/ if the problem goes away.
[...]

If the problem doesn't go away at all using any of the checks above
you then, most probably, have a defective MCB.


Not necessarily true. A neutral-earth short anywhere in the
installation (or an appliance) could cause the reported symptoms.
Isolating individual final circuits would not help in this case, unless
the OP has double-pole MCBs (unlikely).

I think you may have some confusion between the function of an mcb and
that of an rcd.


So do you, judging by your reply above. Anyway it's fairly rare for
RCDs to become defective and when they do fail they tend to become
insensitive, or won't trip at all, rather then becoming over-sensitive.

A faulty appliance is the most likely cause. Start with washing
machine, dishwasher, fridge & freezer (esp. if frost-free type),
immersion heater, toaster. Unplug or isolate these completely, such
that the neutral is disconnected too.

Ok all thanks for the ideas is switching of a circuit at the MCB enough
to issoloate everything on that leg or not I am suspicious of a freezer
in the garage but having turned off the seperate consumer panel there
had discounted that are we now saying I should have unplugged the
freezer to test this idea?