View Single Post
  #3   Report Post  
Posted to uk.d-i-y
Tuthledeen Tuthledeen is offline
external usenet poster
 
Posts: 3
Default Strange electrical problem


"Tuthledeen" wrote in message
...

"Mano" wrote in message
...
OK open to ideas here with this one :-

we have a mcb style mains board (crabtree from memory) which has an RCD
device built in. Normally when when for an example a bulb goes the trip
for that lighting circuit goes bit of a pain but we can live with it.
However yesterday and today has been a nightmare with the main breaker
tripping on average every two hours! No individual circuit goes and
throwing the break brings everything back to normal (apart from having to
reset the times on the cooker microwave stero etc!).

At a loss for any ideas. Nothing has changed regarding load no new
devices etc and its happened day and night so its not something we are
manually turning on or off.

any ideas where to start ?

Switch off individual breakers and see when/ if the problem goes away.
After determining the circuit at fault you can then isolate individual
appliances on that circuit until you isolate one that causes the problem
to go away. You then attend to that appliance. If you can identify an
individual circuit that has problems but no appliance has a problem, then
you have wiring/ wiring fitting problems.

If the problem doesn't go away at all using any of the checks above you
then, most probably, have a defective MCB.

I think you may have some confusion between the function of an mcb and
that of an rcd. The mcb will trip if the circuit current exceeds the value
quoted on the mcb, whereas the rcd will trip if the difference in the
current flowing in the live and neutral conductors exceeds a minimal
value, normally 30 mA (30 thousandths of an ampere). The two devices are
intended to protect you against rather different circuit faults and may
well be protecting you against fire at this very moment.

Call in a qualified electrician and get it sorted! Don't do any nasty
desperate bodges!
Sorry, end of paragraph 2 should read................, have a defective RCD