Thread
:
Electrical wiring
View Single Post
#
48
Posted to rec.woodworking
Doug Miller
external usenet poster
Posts: 6,375
Electrical wiring
In article ,
wrote:
10 or 12 is the wire size, 2 or 3 the number of conductors. All Romex type
cable has a ground which is not referenced as an "official: conductor. 10/3
cable has 3 10awg power carrying conductors and a ground. The 3 conductors
are white (neutral) Black and Red (hots) and is used in balanced 240/120
volt circuits (120 from each hot to neutral, 240 across the hots)
All correct up to this point, but now you go astray:
10/2 has a white and black and is used in 120volt circuits only.
Completely incorrect. Since a 240V circuit has no neutral conductor, only
two hots and a ground, 10/2 with ground is perfectly fine for use in 240V
circuits up to 30A. Three-conductor cable (such as 10/3) is needed for a 240V
circuit only if there are also 120V loads on the circuit; an example of this
would be an electric dryer, which has 240V heating elements and (typically) a
120V motor. The 240V motors which are typically found in woodworking tools
have no neutral, only two hots, and will get along just fine on circuits wired
with two-conductor cable.
--
Regards,
Doug Miller (alphageek at milmac dot com)
It's time to throw all their damned tea in the harbor again.
Reply With Quote
Doug Miller
View Public Profile
Find all posts by Doug Miller