On Wed, 08 Aug 2007 15:03:21 -0700, ransley
wrote Re Is this acceptable HVAC performance?:

On Aug 8, 2:56 pm, "Moe Jones" wrote:
wrote:
I just had a new HVAC system installed in a new house and have not
paid for it yet. Today the temperature is 100 outside. I have my
thermostat set to 77 and the actual temperature is 81. (This is
upstairs, downstairs a separate system is maintaining the selected
temperature.)


I am getting about a 20 degree drop. Is that acceptable or should the
system be doing better?


Thanks for any help!


If you realy have the question if the upstairs unit has been properly charge
is have a heat load done to your home.

Also have your system checked to make sure ther is no problems.

--
Moe Jones
HVAC Service Technician
Energy Equalizers Inc.
Houston, Texaswww.EnergyEqualizers.com


Its set to 77 and its 81 , maybe the thermostat is not calibrated if
its cycling, turn it to 70, how hot was everything when you started
it, wait a few days and let it run continously, keep the thermostat
temp set low so it runs. My installer gave a guarnteed temp drop in
writing.


Here's a way to measure performance:

1) With the house warm, turn the thermostat down so the a/c will turn
on and run for at least 10 minutes.

2) After running for ten minutes, and while still running, measure the
temp of warm air going into the a/c unit as close as you can get to
it. At the same time, measure the cool air coming out of the vent
nearest to the a/c unit.

3) A 20 - 25F temp drop is very good. More than 30F and you may have
an over sized unit.
--