On Jun 19, 12:16 am, "Steve Wolfe" wrote:
Your description does not constitute that the batteries are good. If they
have become very hot, then they are most likely damaged. You will have to
try new batteries to test.


If they're that hot, I would think that the charging circuit is
overcharging them. Before spending the money on new batteries, I'd measure
the voltage presented by the charging circuit while the batteries are
connected, then disconnect the batteries and measure them each individually.

If the charger was giving them more than a float voltage (27.8, within
about .1), but both batteries were at (or above) 13.9 individually, then the
charging circuit has either lost regulation on the float-charging stage, or
is failing to switch from a bulk to a float stage.

On the other hand, if one (or both) of the batteries measure significantly
below 13.9, you have one or more shorted cells. If the charger was still
presenting the 27.8-ish volts to them, then it hasn't recognized the shorted
cells. The charger *might* be bad, or it may have just been battery
failure.

Those voltages are for dual 12V batteries in series. Half them if your
unit uses 6V batteries.

As for a 3-year rule on SLAs, if they're properly cared for, that's the
*minimum* you should get. We replace our batteries at 3 years just as a
precaution, but I have yet to see one fail before that time - *if* it's been
properly cared for. Occasionally, someone will unplug their UPS, ignore the
beeping until the battery is completely dead, and let the UPS sit like that
for a month or two. That's not the battery's fault, it's the user's fault.
The batteries that have failed on us have all been in units that were 4+
years old, often 5-6 years.

steve


thanks for clarification,