4.5 HP Needs a 30 Amp Breaker?
In article , Tom B wrote:
Flameproof suit on.
Laguna says 30 Amp breaker on 220 Volt service is needed for the
LT16HD (4.5 HP Baldor motor).
My quick calc shows 4.5 HP on 220V is ~3375 Watts or about 15.3 Amp.
That's assuming 100% efficiency, which you're not going to get. Figure
*at*least* 20A, probably more.
Is the start-up draw 30% higher than the run draw?
No, it's even worse than that.
I have 220V 20A service and 10-3 wiring installed over about a 20'
span and wonder if I need to go up to a 30 Amp breaker.
The manufacturer recommends a 30A circuit.
10-3 wire will support a 30A circuit.
A 30A double pole breaker will cost about ten bucks, and take you fifteen
minutes, tops, to swap in.
Doesn't sound like a difficult decision to me.
I could just plug it in, crank it up, and see if the breaker pops :-).
Yes, you could. Or you could spend the ten bucks and fifteen minutes, and
put in the correct breaker.
Your choice. :-)
--