Thread
:
Wire size for 40A welder
View Single Post
#
8
Posted to alt.home.repair
Doug Miller
external usenet poster
Posts: 6,375
Wire size for 40A welder
In article ,
wrote:
On Sun, 17 Dec 2006 01:17:49 GMT,
(Doug Miller)
wrote:
In article ,
wrote:
To connect a welder about 15 feet from breaker box. The welder says
primary amps 40. A wire chart on a website shows #6 as 37.5 amps.
Wow, I wonder where they came up with that. The National Electrical Code shows
#6 copper at 55 amps.
Here's the site: I thought it shoul be higher than that....
http://www.interfacebus.com/Copper_Wire_AWG_SIze.html
Below the table, it does say "The National Electrical Code [NEC] requires
their own cable sizing for premises wiring. Refer to the NEC rules to
determine building wiring, as this page relates to electronic equipment
wiring."
This is then followed by a sample list of wire guages and supposedly
NEC-permissible ampacities, which I will *not* reproduce here because it's
wrong.
It seems to me like the old cable type service entrances for 60A
service were #6-3 plus ground (wrapped around the bundle).
Sounds about right.
Will #6 be close enough or should I use #4?
Neither -- #8 copper is quite sufficient for 40 amps. If you're using
aluminum, then you need #6. But in no case do you need #4 for a load of only
40 amps.
Thanks
Good luck, and stay safe.
--
Regards,
Doug Miller (alphageek at milmac dot com)
It's time to throw all their damned tea in the harbor again.
Reply With Quote
Doug Miller
View Public Profile
Find all posts by Doug Miller