Andrew Thelwell wrote:

Hi all, I'm the OP,

First off thanks for all the replies -- great to get so much feedback.

Let me clarify a few points... this should help with the discussion:

1) The house is newly-purchased, not a new build. It's a 1930's
semi-detached

2) I may have misled when I referred to RCDs (sorry!). We have two
large rotary switch type things on our consumer unit labelled
"Earth-Leakage Circuit Breaker".


Ohhhhhhhhhhhhhhhh. Those. In that case we know a couple of things
straight away. This is oldish wiring, and uses TT earthing, meaning a
local earth rod with high earth impedance.


There is apparently one on each 'loop'
of the house.


Big house then?

It is these that have tripped


ELCBs rarely trip in error. I think I know whats going on now.

3) The problem with the meter when the guy came to change it was that
he was as follows: He had one of those 'mains tester' screwdrivers with
the LEDs in the end that should only light up on when touched to a live
terminal. However, he got it to light up on ALL FOUR terminals attached
to our meter (+ in, - in, + out, - out, yes?). I don't think there was
an suggestion as to the 'size' of the current though. He also got it to
light up when he pressed it to the big grey block (neutral block) in
the meter box, which apparently it shouldn't do. This happenend both
with our consumer unit main isolator turned ON and OFF. It stopped,
however, when he pulled the main fuse out of the meter box.


OK, then we can safely ignore anything he says


Two mains engineers from Central Networks came out that night and
tested thoroughly for almost 2 hours in our meter box and around our
roof (we have overhead supply). They found nothing out of place at all.


And we can safely conclude nothing is out of place at all with your
supply as far as the CU or fusebox.


They asked if we'd experienced any oddities inside the house, which we
hadn't. However, since then we have seen our Earth-Leakage Circuit
Breakers (not RCDs, sorry!) trip three times. Two of these times have
been due to turning on the one socket in the spare room. One other time
the other ELCB tripped when my girlfriend turned on the microwave. All
sockets in the house test out fine using a normal B&Q socket tester,
except the one in the spare room, which shows only one light,
supposedly "L/N Reverse".


OK, I think I see the problem clearly. An ELCB will trip when it sees
large earth currents (unlike RCDs which trip on small earth currents).
This means you have a major fault in whatever appliance caused it to
trip when the socket was switched on. So the microwave and whatever was
plugged into the spare room socket should be taken out of service now,
and some checks done on them later to confirm or deny theyre the
problem.

From everything you say, the only problem with the installation itself

is the swapped wires behind a socket, which is a trivial matter easily
fixed in 2 minutes.

Your 2 faulty appliances would not have tripped anything at your last
house, which I can conclude had low impedance earthing and no RCD.
However on a high impedance earth, which you have here, such faulty
appliances are not safe to use at all.


NT