Christian McArdle wrote:
1. For efficient heating of the space overall I should stick with
radiators since these are running on gas anyway, therefore I'm
producing less carbon if I run uninsulated on rads rather than pretty
well insulated on the electric UFH.
---This is OK and what I plan to do anyway


Indeed.

2. If I stick with putting in the UFH for comfort heating then I am
wasting my money with the 6mm insulation, since most heat comes from
the rads so payback on the insulation is somewhere well over the
horizon, probably beyond the lifetime of the installation.
---This is OK since I don't have the money or the headroom.


What is the intended finished floor surface? If carpet or wood based, I
wouldn't use UFH at all.

3. For control of the UFH I should use the floor temperature sensor and
set it as low as possible (say 20C) to keep the duy cycle to minimum so
it just does the job of keeping the floor at a comfortable temperature.


Certainly. Personally, if I really wanted UFH heating in there and there
really was only a choice between 6mm and 0mm insulation, I would still go
for the 6mm. Note that 10mm boards are the same price and the additional 4mm
is worthwhile.

don't seal the joint then any condensation which forms on the inside of
the wall membrane should (on the whole) run down the gap between the
wall and floor membrane and so end up in the drainage system rather
than on the floor or at the base of dry-lining.


What you haven't considered is that if the insulation is adequete, then the
wall temperature will be much higher. Provided the ventilation is up to
spec, which seems to be very much the case with heat recovery ventilation
mentioned, then the relative humidity at the vapour barrier will be much
less than 100% and no condensation at all will occur. As the temperature
drops through the insulation, what little air (with closed cell insulation)
that gets through will be very low in absolute humidity due to the vapour
barrier, so no interstitial condensation will occur there either.

Christian.


Thanks again, I'm signing it off now. I would put the 6mm in if it
weren't so damn expensive but 10mm is really pushing the headroom issue
(partly because the guys who poured the floor were worried about not
having enough concrete so ordered the extra 0.5m3 which meant the slab
ended up about 10mm thicker than planned so I had less to play with
than I thought. BCO is very understanding about stair headroom and
stuff like that but I don't want to push him too hard. The problem with
the condensation is that the ventilation is inside the room (for the
occupants) and doesn't ventilate as well the space behind the
insulation and in front of the membrane. Essentially there is likely to
be a humidity gradient through the wall.

Anyway the arrangement of the membrane should ensure that condensation
on that interface isn't an issue so I will be insulating between the
studs for the dry-lining. Before anyone comments on bridging by the
studs and using over stud insulation, I know, I know but I don't want
to keep bringing the walls in. Anyway U-value for the wall construction
even accounting for the bridging is pretty good (I'm going for ~0.3
although heat-loss calculation was based on 0.6). I'm really not going
to notice this room on the heating bill.

Thankyou to everyone.