Which receptacle ?
"Brian Elfert" wrote in message
...
"Jim" writes:
It isn't overdesigned if you use a 3HP saw. It is underdesigned if you
use
a 5 HP single phase saw.
A 3HP saw only requires a 20 amp circuit and I believe a 5HP saw will be
fine on a 30 amp circuit.
Brian Elfert
Delta's catalog says 40 amp slow blow fuse for the 5 hp saw. I am not sure
what the equivalent circuit breaker would be, The starting current for a
single phase motor is quite a bit more than the rated amperes for the motor,
but of course that peak only lasts for a very short time.
They don't say what the circuit breaker or fuse size should be for a 3 hp
motor.
No matter what, the OP should consult an electrician for this kind of
question rather than the mighty mass of misinformation that is called the
internet.
Jim
|