Like the other post said, you don't have an imbalance until something or
someone creates the bridge to ground. Then the device trips




"Jeff Wisnia" wrote in message
...
RBM wrote:

The ground fault device and anything plugged into any outlets connected
to the load side of it, will cause the GFCI to trip if any leak of
current to ground occurs, regardless if the outlets are grounded. The
GFCI does not need a ground connected to it to function


Of course, but that's NOT what I asked.

I was talking about (internal fault) leakage to the safety ground lead
(chassis) oF an appliance with a three wire cord and plug. And, that
faulty appliance is plugged into a GFCI outlet which does not have a
ground wire run to it. i.e. an outlet which would require the little label
stuck on it warning that there was no safety ground there.

Take a look at Sam Goldwasser's diagrams and explain please how the GFCI
can sense internal leakage to the safety ground lead of the appliance if
the ground pin hole in the outlet isn't connected to anything.

http://www.codecheck.com/gfci_principal.htm

Jeff




"Jeff Wisnia" wrote in message
...

PipeDown wrote:


Use of a single GFCI or a GFCI breaker does not solve the problem of not
having a ground wire in the first place. If you use a GFCI receptacle
and connect several receptacles downsteam, you will get some GFCI
protection but not from current into ground (the ground tab on those
will still be open). Only at the GFCI receptacle itself do you get
virtual safety ground protection.

I think I understand you. But just to be sure, are you saying that even
without a ground wire connected to it the first GFCI receptacle would
trip if an appliance plugged into it equipped with a three wire cord and
plug developed internal leakage between hot and ground (or on the fancier
GFCIs also between neutral and ground.), but that you don't get that
level of protection on the downstream ones?

I'd assume you wouldn't get that protection on the first receptical
either if there was no ground wire connected to it. I can't see where a
leakage current to ground would flow if there was no ground wire for it
to flow through.

If what you said assumed there WAS a ground wire to connect to the GFCI
receptical then I agree with your statement, but that's prolly not what
the OP has, unless he's lucky and the wall boxes are grounded, perhaps
via the bare ground wire used in some of the old BX cables.