(a slight followup first for those of you who were reading my subpanel
thread a few days ago)

I decided not to use the 100amp box. I found a proper 12 postion
subpanel at the borg. I've already started the install. I'm using
3/4" emt with #6 wire, 60 amp breaker in the main box, a 75' run, all
indoors.

Originally, I was going to run four wires through the 3/4" pipe (red,
white, black, and green). The electrical guy at home depot said that
if you're using emt, you don't need the separate ground wire since the
boxes are grounded together through the emt. Does this sound right?
So far, I've run the other three. It's a bit of a long run so I'd
rather not do the fourth wire.

brian

  #2   Report Post  
Art Greenberg
 
Posts: n/a
Default

On 6 Jun 2005 09:03:43 -0700, brianlanning wrote:
(a slight followup first for those of you who were reading my subpanel
thread a few days ago)

I decided not to use the 100amp box. I found a proper 12 postion
subpanel at the borg. I've already started the install. I'm using
3/4" emt with #6 wire, 60 amp breaker in the main box, a 75' run, all
indoors.


Are you certain you won't exceed the fill limit (or need to derate the
conductors) on the conduit with three current-carrying #6 conductors?

Originally, I was going to run four wires through the 3/4" pipe (red,
white, black, and green). The electrical guy at home depot said that
if you're using emt, you don't need the separate ground wire since the
boxes are grounded together through the emt. Does this sound right?
So far, I've run the other three. It's a bit of a long run so I'd
rather not do the fourth wire.


Check the NEC. I think you need the ground wire. And bonding at both ends of
the conduit.

--
Art Greenberg
artg AT eclipse DOT net
  #3   Report Post  
Jim
 
Posts: n/a
Default


"brianlanning" wrote in message
oups.com...
(a slight followup first for those of you who were reading my subpanel
thread a few days ago)

I decided not to use the 100amp box. I found a proper 12 postion
subpanel at the borg. I've already started the install. I'm using
3/4" emt with #6 wire, 60 amp breaker in the main box, a 75' run, all
indoors.

Originally, I was going to run four wires through the 3/4" pipe (red,
white, black, and green). The electrical guy at home depot said that
if you're using emt, you don't need the separate ground wire since the
boxes are grounded together through the emt. Does this sound right?

No, but it does sound like you should let someone who knows what he is doing
(such as an electrician) do the job.
Jim


  #4   Report Post  
Doug Miller
 
Posts: n/a
Default

In article .com, "brianlanning" wrote:
(a slight followup first for those of you who were reading my subpanel
thread a few days ago)

I decided not to use the 100amp box. I found a proper 12 postion
subpanel at the borg. I've already started the install. I'm using
3/4" emt with #6 wire, 60 amp breaker in the main box, a 75' run, all
indoors.


If you're using THHN or THWN conductors, that's ok. If TW, THW, RHW, or RHH,
you have a code violation already. They're probably THHN, but you oughta check
just to make sure. It's stamped on the insulation.

Originally, I was going to run four wires through the 3/4" pipe (red,
white, black, and green). The electrical guy at home depot said that
if you're using emt, you don't need the separate ground wire since the
boxes are grounded together through the emt. Does this sound right?


The NEC _explicitly_permits_ the use of EMT as an equipment grounding
conductor. [Article 250-91(b)]

So far, I've run the other three. It's a bit of a long run so I'd
rather not do the fourth wire.



--
Regards,
Doug Miller (alphageek at milmac dot com)

Nobody ever left footprints in the sands of time by sitting on his butt.
And who wants to leave buttprints in the sands of time?
  #5   Report Post  
 
Posts: n/a
Default

Even if the EMT is allowed to be the grounding conductor, I'd run a
copper wire anyway, especially for a circuit feeding a subpanel.



  #6   Report Post  
brianlanning
 
Posts: n/a
Default

If you're using THHN or THWN conductors, that's ok. If TW, THW, RHW, or RHH,
you have a code violation already. They're probably THHN, but you oughta check
just to make sure. It's stamped on the insulation.


I believe it's THHN. He had a code book there and looked up the types,
gauge, and conduit sizes on the spot.


The NEC _explicitly_permits_ the use of EMT as an equipment grounding
conductor. [Article 250-91(b)]


Thanks, this is what I was looking for.

brian

  #7   Report Post  
brianlanning
 
Posts: n/a
Default

Are you certain you won't exceed the fill limit (or need to derate the
conductors) on the conduit with three current-carrying #6 conductors?


Those sizes came from a NEC code book they had there in the store.

brian

  #8   Report Post  
LRod
 
Posts: n/a
Default

On 6 Jun 2005 13:49:20 -0700, "brianlanning"
wrote:

If you're using THHN or THWN conductors, that's ok. If TW, THW, RHW, or RHH,
you have a code violation already. They're probably THHN, but you oughta check
just to make sure. It's stamped on the insulation.


I believe it's THHN. He had a code book there and looked up the types,
gauge, and conduit sizes on the spot.


The NEC _explicitly_permits_ the use of EMT as an equipment grounding
conductor. [Article 250-91(b)]


Thanks, this is what I was looking for.


There is one other thing to consider and that is three 6s in 3/4"
conduit, even thought permitted, can be a tough pull (especially over
75'. Can it hurt you to put in 1" instead? You'll probably have to use
preformed elbows.

--
LRod

Master Woodbutcher and seasoned termite

Shamelessly whoring my website since 1999

http://www.woodbutcher.net

Proud participant of rec.woodworking since February, 1997
  #9   Report Post  
Lew Hodgett
 
Posts: n/a
Default

brianlanning wrote:

The electrical guy at home depot said that
if you're using emt, you don't need the separate ground wire since the
boxes are grounded together through the emt. Does this sound right?



Nice try but no cigar.

Not in my world anyway.

Lew
  #10   Report Post  
Scott Lurndal
 
Posts: n/a
Default

Lew Hodgett writes:
brianlanning wrote:

The electrical guy at home depot said that
if you're using emt, you don't need the separate ground wire since the
boxes are grounded together through the emt. Does this sound right?



Nice try but no cigar.

Not in my world anyway.


And what world is that? See the NEC. EMT is explicitly
allowed as the grounding conductor. BX and armoured cable
are explicitly disallowed (as of 1999?).

If I were doing it, using the EMT as the grounding
means, I'd use compression fittings rather than setscrew.

scott

Lew



  #11   Report Post  
brianlanning
 
Posts: n/a
Default

It was tough. I finished it last night. I used 90 degree fittings
also which made it that much worse. Half way through the project, I
started threading sections of emt as I assembled them. That made the
job a lot easier. I didn't look at the price for 1" conduit. I know
the 1 1/4" conduit I would have used for the #3 100amp wire was $15 for
an 8' segment. That was three times more than the $5 for the 3/4". So
I went with the 60 amp parts. If I had to do it again, I would buy the
pipe bender. That tool would probably have been cheaper than the cost
of all the fittings and it would have made pulling the wire easier.

brian


LRod wrote:
On 6 Jun 2005 13:49:20 -0700, "brianlanning"
wrote:
There is one other thing to consider and that is three 6s in 3/4"
conduit, even thought permitted, can be a tough pull (especially over
75'. Can it hurt you to put in 1" instead? You'll probably have to use
preformed elbows.


  #12   Report Post  
Doug Miller
 
Posts: n/a
Default

In article .com, "brianlanning" wrote:
It was tough. I finished it last night. I used 90 degree fittings
also which made it that much worse. Half way through the project, I
started threading sections of emt as I assembled them.


Threading EMT is _explicitly_forbidden_ by the NEC.


--
Regards,
Doug Miller (alphageek at milmac dot com)

Nobody ever left footprints in the sands of time by sitting on his butt.
And who wants to leave buttprints in the sands of time?
  #13   Report Post  
Dave Hinz
 
Posts: n/a
Default

On Tue, 07 Jun 2005 18:15:58 GMT, Doug Miller wrote:
In article .com, "brianlanning" wrote:
It was tough. I finished it last night. I used 90 degree fittings
also which made it that much worse. Half way through the project, I
started threading sections of emt as I assembled them.


Threading EMT is _explicitly_forbidden_ by the NEC.


I didn't know you _could_ thread EMT, even if not forbidden from doing
so?

(side note: just how many groups do we cross paths in, Doug?)

  #14   Report Post  
Doug Miller
 
Posts: n/a
Default

In article , Dave Hinz wrote:
On Tue, 07 Jun 2005 18:15:58 GMT, Doug Miller wrote:
In article .com,

"brianlanning" wrote:
It was tough. I finished it last night. I used 90 degree fittings
also which made it that much worse. Half way through the project, I
started threading sections of emt as I assembled them.


Threading EMT is _explicitly_forbidden_ by the NEC.


I didn't know you _could_ thread EMT, even if not forbidden from doing
so?


I didn't either, actually.... not sure why anyone would try, since the walls
are so thin. But it's there in the Code.

(side note: just how many groups do we cross paths in, Doug?)


At least two besides this one, I think. :-)

--
Regards,
Doug Miller (alphageek at milmac dot com)

Nobody ever left footprints in the sands of time by sitting on his butt.
And who wants to leave buttprints in the sands of time?
  #15   Report Post  
Art Greenberg
 
Posts: n/a
Default

On Tue, 07 Jun 2005 18:15:58 GMT, Doug Miller wrote:
In article .com, "brianlanning" wrote:
It was tough. I finished it last night. I used 90 degree fittings
also which made it that much worse. Half way through the project, I
started threading sections of emt as I assembled them.


Threading EMT is _explicitly_forbidden_ by the NEC.


I *think* he meant as in "threading a needle". Rather than pull the wires
through a fully assembled conduit run, he's pushing the conduit sections onto
the cable, one at a time.

At least, that's what I think he meant.

--
Art Greenberg
artg AT eclipse DOT net


  #16   Report Post  
LRod
 
Posts: n/a
Default

On Tue, 07 Jun 2005 19:35:47 GMT, Art Greenberg
wrote:

On Tue, 07 Jun 2005 18:15:58 GMT, Doug Miller wrote:
In article .com, "brianlanning" wrote:
It was tough. I finished it last night. I used 90 degree fittings
also which made it that much worse. Half way through the project, I
started threading sections of emt as I assembled them.


Threading EMT is _explicitly_forbidden_ by the NEC.


I *think* he meant as in "threading a needle". Rather than pull the wires
through a fully assembled conduit run, he's pushing the conduit sections onto
the cable, one at a time.

At least, that's what I think he meant.


I took it that way, too.

--
LRod

Master Woodbutcher and seasoned termite

Shamelessly whoring my website since 1999

http://www.woodbutcher.net

Proud participant of rec.woodworking since February, 1997
  #17   Report Post  
brianlanning
 
Posts: n/a
Default

oops, I mean pushing wire throught he conduit, not cutting threads in
the ends.

brian

  #19   Report Post  
ATP*
 
Posts: n/a
Default


"brianlanning" wrote in message
oups.com...
Are you certain you won't exceed the fill limit (or need to derate the
conductors) on the conduit with three current-carrying #6 conductors?


Those sizes came from a NEC code book they had there in the store.

brian


Never use the minimum conduit size allowed by the NEC. It's not worth it.
Also consider using boxes as pull points when you change direction and at
reasonable intervals.


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT +1. The time now is 05:33 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"