Hello,

I went away for a couple of weeks and I didn't know how cold the house
would get so rather than turn off the heating, I left it set low for
frost protection so I didn't come back to burst pipes. When I got
back, the house was very cold and the boiler was dead. I investigated
with a volt stick and found that current was going to the boiler from
the FCU but no further. I looked on the PCB and there is a 1.6A fuse
that had blown. I didn't have any replacements: the best I had was a
couple of 1A fuses from a shaver socket adaptor. The boiler tries to
start but there is a funny noise and then the fuse blows. It doesn't
help that I was using 1A fuses rather than 1.6A.

I only got a second or two before the fuse blew, but I think the noise
came from the pump. Would that make sense? I've read that pumps can
seize. If it was seized, would it stall a draw a higer current than
usual and blow the fuse? I read that you can unscrew the large screw
onthe shaft of the pump and try to move the pump spindle. The boiler
is an ancient Seme and I know I need to save up and replace it with a
modern condensing boiler. The pump has a bolt head in the centre of
the shaft which I managed to loosen and I could feel the shaft
rotating but some black water came out.

I am waiting for some replacement fuses to arrive. I'm wondering
whether the pump was seized and whether I have managed to loosen it.
Do you think it is worth taking the pump off to give it a rinse? I was
surprised the water that came out was so dark as I added inhibitor and
a magnetic filter.

Do you think I should get a new pump just in case? The one fitted is
probably the original and very old.

I read that sometimes valves stick when you go on holiday but as this
is a combi boiler and the heating is on one zone, the only valve is
the diverter that switches between CH and HW and since I get neither
CH nor HW, I'm sure the problem lies somewhere else.

Thanks in advance!
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,066
Default central heating fault: fuse blown - pump?

On Tuesday, 3 March 2020 06:35:26 UTC, Stephen wrote:
Hello,

I went away for a couple of weeks and I didn't know how cold the house
would get so rather than turn off the heating, I left it set low for
frost protection so I didn't come back to burst pipes. When I got
back, the house was very cold and the boiler was dead. I investigated
with a volt stick and found that current was going to the boiler from
the FCU but no further. I looked on the PCB and there is a 1.6A fuse
that had blown. I didn't have any replacements: the best I had was a
couple of 1A fuses from a shaver socket adaptor. The boiler tries to
start but there is a funny noise and then the fuse blows. It doesn't
help that I was using 1A fuses rather than 1.6A.

I only got a second or two before the fuse blew, but I think the noise
came from the pump. Would that make sense? I've read that pumps can
seize. If it was seized, would it stall a draw a higer current than
usual and blow the fuse? I read that you can unscrew the large screw
onthe shaft of the pump and try to move the pump spindle. The boiler
is an ancient Seme and I know I need to save up and replace it with a
modern condensing boiler. The pump has a bolt head in the centre of
the shaft which I managed to loosen and I could feel the shaft
rotating but some black water came out.

I am waiting for some replacement fuses to arrive. I'm wondering
whether the pump was seized and whether I have managed to loosen it.
Do you think it is worth taking the pump off to give it a rinse? I was
surprised the water that came out was so dark as I added inhibitor and
a magnetic filter.

Do you think I should get a new pump just in case? The one fitted is
probably the original and very old.

I read that sometimes valves stick when you go on holiday but as this
is a combi boiler and the heating is on one zone, the only valve is
the diverter that switches between CH and HW and since I get neither
CH nor HW, I'm sure the problem lies somewhere else.

Thanks in advance!


Look on the motor end of the pump.
In the centre of the motor there may be a cap with a screw slot to remove/unscrew it. (There may be a little water gets out when taken off)

This gives access to the motor shaft which has another screwdriver slot which enables you to twiddle the shaft to free it up if it has seized.

  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 39,563
Default central heating fault: fuse blown - pump?

On 03/03/2020 06:35, Stephen wrote:
I only got a second or two before the fuse blew, but I think the noise
came from the pump. Would that make sense? I've read that pumps can
seize. If it was seized, would it stall a draw a higer current than
usual and blow the fuse?


The answer is yes. Most pumps have a central place where you can remove
a cover with a slotted screwdriver and rotate the spindle by hand or
using a tool. That can free up any crud enough to get the pump working
again. Until you can source a new pump and go through the faff of
draining down refitting adding the fernox and then trying to get all the
air out of the CH. I wish you luck.



--
In a Time of Universal Deceit, Telling the Truth Is a Revolutionary Act.

- George Orwell
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 5,774
Default central heating fault: fuse blown - pump?

On 03/03/2020 06:35, Stephen wrote:


Do you think I should get a new pump just in case? The one fitted is
probably the original and very old.


Pumps usually seize only if they have been left unused for a period of
time such as in a system where the pump is only used for central heating
and the heating has been turned off during the summer. A friend who was
in the plumbing business used to get a lot of pump failure calls in
Autumn when people tried their heating for the first time in 6 months.

Was your heating running OK before you went away. If so then maybe the
fault is elsewhere - although a faulty pump cannot be ruled out.

The noise you are hearing may just be the normal pump noise on starting
as the boiler fires up and you haven't noticed it before because the
noise is normally of short duration before the burners fire up. If as
you say the shaft is turning then it is no longer seized (if it had been
in the first place). A small amount of water with the pump screw cover
removed is normal and its colour is more of a indication of the sludge
etc. in the system (or had been in the system) but probably at this time
not the cause of your failure.


If you have the necessary competence disconnect the pump wiring and
apply mains voltage to the pump from another source and if you feel it
running and/or see the shaft turning then the pump is possibly OK.
Google also for central heating pump starting capacitor. Do not attempt
to fire up the boiler during this test.

Do you have an installation manual for your boiler, or is there one on
the internet (installation manual rather than a user guide). It may have
a circuit showing what the fuse is protecting and/or a fault finding
step by step flow chart.



--
mailto : news {at} admac {dot} myzen {dot} co {dot} uk
  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 12,364
Default central heating fault: fuse blown - pump?

On Tuesday, 3 March 2020 06:35:26 UTC, Stephen wrote:
Hello,

I went away for a couple of weeks and I didn't know how cold the house
would get so rather than turn off the heating, I left it set low for
frost protection so I didn't come back to burst pipes. When I got
back, the house was very cold and the boiler was dead. I investigated
with a volt stick and found that current was going to the boiler from
the FCU but no further. I looked on the PCB and there is a 1.6A fuse
that had blown. I didn't have any replacements: the best I had was a
couple of 1A fuses from a shaver socket adaptor. The boiler tries to
start but there is a funny noise and then the fuse blows. It doesn't
help that I was using 1A fuses rather than 1.6A.

I only got a second or two before the fuse blew, but I think the noise
came from the pump. Would that make sense? I've read that pumps can
seize. If it was seized, would it stall a draw a higer current than
usual and blow the fuse? I read that you can unscrew the large screw
onthe shaft of the pump and try to move the pump spindle. The boiler
is an ancient Seme and I know I need to save up and replace it with a
modern condensing boiler. The pump has a bolt head in the centre of
the shaft which I managed to loosen and I could feel the shaft
rotating but some black water came out.

I am waiting for some replacement fuses to arrive. I'm wondering
whether the pump was seized and whether I have managed to loosen it.
Do you think it is worth taking the pump off to give it a rinse? I was
surprised the water that came out was so dark as I added inhibitor and
a magnetic filter.

Do you think I should get a new pump just in case? The one fitted is
probably the original and very old.

I read that sometimes valves stick when you go on holiday but as this
is a combi boiler and the heating is on one zone, the only valve is
the diverter that switches between CH and HW and since I get neither
CH nor HW, I'm sure the problem lies somewhere else.

Thanks in advance!


Pumps can seize, and yes undoing the centre screw is sometimes enough to free them. Gunky water is normal. I'd disconnect the pump & fire the system up, but only for several seconds as the boiler will get no flow & overheat very quickly. Then you'll know if the pump is the problem.


NT


  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,048
Default central heating fault: fuse blown - pump?

On Tue, 03 Mar 2020 06:35:16 +0000, Stephen wrote:

I only got a second or two before the fuse blew, but I think the noise
came from the pump. Would that make sense?

Yes...

I've read that pumps can
seize. If it was seized, would it stall a draw a higer current than
usual and blow the fuse?


Possibly.

I read that you can unscrew the large screw
onthe shaft of the pump and try to move the pump spindle.


Yes.

The boiler
is an ancient Seme and I know I need to save up and replace it with a
modern condensing boiler. The pump has a bolt head in the centre of
the shaft which I managed to loosen and I could feel the shaft
rotating but some black water came out.


If it was stuck, it isn't now...

I am waiting for some replacement fuses to arrive. I'm wondering
whether the pump was seized and whether I have managed to loosen it.


If it was, it isn't now...

Do you think it is worth taking the pump off to give it a rinse?


No.

I was
surprised the water that came out was so dark as I added inhibitor and
a magnetic filter.

Do you think I should get a new pump just in case? The one fitted is
probably the original and very old.


Depends -- on when you replace the boiler, and the risk of another pump failure.
If the pipes freeze, that's bad, if the house goes a bit cold and you need to
use electric heaters or a woodburner for a while, it's not.


Thomas Prufer
  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4
Default central heating fault: fuse blown - pump?

On Tue, 3 Mar 2020 09:58:57 +0000, alan_m
wrote:



Pumps usually seize only if they have been left unused for a period of
time such as in a system where the pump is only used for central heating



Hello,

Thanks for all the replies.

The pump is only used for CH. I had the CH thermostat turned dwen low
for frost protection, so I don't know how often the boiler fired up
while I was away. I must have fired at least once to blow the fuse.

I never thought to power the pump independently, thyatnks for that,
I'll try that if there is ever a next time.

What limited me on the day was that I didn't have any 20mm fuses,
other than a 1A one from a shaver adaptor and they are not very easy
to find. I'm surprised at this because you would think they would be
very popular in shaver adaptors, especially now everyone has electric
toothbrushes, as well as shavers. I think office clocks still use
BS646 fuses too.

I've managed to order some 1.6A fuses, so it's a maytter of trying
them when they arrive.

The pump does not have the central screw. Instead it has a hex head
bolt. I'm not sure if that's how it came or whether that's an "after
market modification" by a previous owner/plumber, but it seems to do
the same job. I couldn't remove it completely, but once I had loosed
it, the shaft seemed to turn rather than the screw.

I suppose it wouldn't hurt to drain it and top it up with fresh
inhibitor. I'm just not sure whether this was a warning that the pump
is on its way out and whether to replace that at the same time.
  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,048
Default central heating fault: fuse blown - pump?

On Thu, 05 Mar 2020 08:27:18 +0000, Stephen wrote:

I'm just not sure whether this was a warning that the pump
is on its way out and whether to replace that at the same time.


They do last multiple decades...


Thomas Prufer
  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 643
Default central heating fault: fuse blown - pump?

On Thursday, 5 March 2020 08:27:28 UTC, Stephen wrote:
On Tue, 3 Mar 2020 09:58:57 +0000, alan_m
wrote:



Pumps usually seize only if they have been left unused for a period of
time such as in a system where the pump is only used for central heating



Hello,

Thanks for all the replies.

The pump is only used for CH. I had the CH thermostat turned dwen low
for frost protection, so I don't know how often the boiler fired up
while I was away. I must have fired at least once to blow the fuse.

I never thought to power the pump independently, thyatnks for that,
I'll try that if there is ever a next time.

What limited me on the day was that I didn't have any 20mm fuses,
other than a 1A one from a shaver adaptor and they are not very easy
to find. I'm surprised at this because you would think they would be
very popular in shaver adaptors, especially now everyone has electric
toothbrushes, as well as shavers. I think office clocks still use
BS646 fuses too.

I've managed to order some 1.6A fuses, so it's a maytter of trying
them when they arrive.

The pump does not have the central screw. Instead it has a hex head
bolt. I'm not sure if that's how it came or whether that's an "after
market modification" by a previous owner/plumber, but it seems to do
the same job. I couldn't remove it completely, but once I had loosed
it, the shaft seemed to turn rather than the screw.

I suppose it wouldn't hurt to drain it and top it up with fresh
inhibitor. I'm just not sure whether this was a warning that the pump
is on its way out and whether to replace that at the same time.


I was once advised by a plumber's wife (to save the call out charge) to hit a seized pump with a hammer a few times. Did the job and it carried on working.

Jonathan
  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 39,563
Default central heating fault: fuse blown - pump?

On 06/03/2020 11:38, Jonathan wrote:
On Thursday, 5 March 2020 08:27:28 UTC, Stephen wrote:
On Tue, 3 Mar 2020 09:58:57 +0000, alan_m
wrote:



Pumps usually seize only if they have been left unused for a
period of time such as in a system where the pump is only used
for central heating



Hello,

Thanks for all the replies.

The pump is only used for CH. I had the CH thermostat turned dwen
low for frost protection, so I don't know how often the boiler
fired up while I was away. I must have fired at least once to blow
the fuse.

I never thought to power the pump independently, thyatnks for
that, I'll try that if there is ever a next time.

What limited me on the day was that I didn't have any 20mm fuses,
other than a 1A one from a shaver adaptor and they are not very
easy to find. I'm surprised at this because you would think they
would be very popular in shaver adaptors, especially now everyone
has electric toothbrushes, as well as shavers. I think office
clocks still use BS646 fuses too.

I've managed to order some 1.6A fuses, so it's a maytter of trying
them when they arrive.

The pump does not have the central screw. Instead it has a hex
head bolt. I'm not sure if that's how it came or whether that's an
"after market modification" by a previous owner/plumber, but it
seems to do the same job. I couldn't remove it completely, but once
I had loosed it, the shaft seemed to turn rather than the screw.

I suppose it wouldn't hurt to drain it and top it up with fresh
inhibitor. I'm just not sure whether this was a warning that the
pump is on its way out and whether to replace that at the same
time.


I was once advised by a plumber's wife (to save the call out charge)
to hit a seized pump with a hammer a few times. Did the job and it
carried on working.

Jonathan


Ah. The old joke.

Customer objects to $100 bill for hitting the water pump with a spanner,
so the bill is re-presented

"To hitting the water pump with a hammer -$1
"For coming out, knowing where to find it, and how hard and where to hit
it - $99

TOTAL $100


--
The theory of Communism may be summed up in one sentence: Abolish all
private property.

Karl Marx



  #11   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,556
Default central heating fault: fuse blown - pump?

In article ,
Jonathan writes
On Thursday, 5 March 2020 08:27:28 UTC, Stephen wrote:
On Tue, 3 Mar 2020 09:58:57 +0000, alan_m
wrote:



Pumps usually seize only if they have been left unused for a period of
time such as in a system where the pump is only used for central heating



Hello,

Thanks for all the replies.

The pump is only used for CH. I had the CH thermostat turned dwen low
for frost protection, so I don't know how often the boiler fired up
while I was away. I must have fired at least once to blow the fuse.

I never thought to power the pump independently, thyatnks for that,
I'll try that if there is ever a next time.

What limited me on the day was that I didn't have any 20mm fuses,
other than a 1A one from a shaver adaptor and they are not very easy
to find. I'm surprised at this because you would think they would be
very popular in shaver adaptors, especially now everyone has electric
toothbrushes, as well as shavers. I think office clocks still use
BS646 fuses too.

I've managed to order some 1.6A fuses, so it's a maytter of trying
them when they arrive.

The pump does not have the central screw. Instead it has a hex head
bolt. I'm not sure if that's how it came or whether that's an "after
market modification" by a previous owner/plumber, but it seems to do
the same job. I couldn't remove it completely, but once I had loosed
it, the shaft seemed to turn rather than the screw.

I suppose it wouldn't hurt to drain it and top it up with fresh
inhibitor. I'm just not sure whether this was a warning that the pump
is on its way out and whether to replace that at the same time.


I was once advised by a plumber's wife (to save the call out charge) to
hit a seized pump with a hammer a few times. Did the job and it carried
on working.

Jonathan

Preferably a rubber one.
--
bert
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Fuse: fast blown vs slow blown Man-wai Chang Electronics Repair 66 June 4th 11 08:46 PM
URGENT Help needed please - Blown heating fuse... Richard Marx UK diy 25 January 11th 06 02:56 AM
Several things wrong with new flat - no central heating, low hot water pressure even with water pump, noisey pump kiich UK diy 69 July 13th 05 07:36 PM
Pioneer CLD-870 -Blown Fuse ED Electronics 2 March 27th 04 07:20 AM
blown fuse in sub-woofer heckubiss Electronics Repair 8 August 20th 03 01:44 AM


All times are GMT +1. The time now is 11:44 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"