Only posting to point out the point of testing and keeping proper
records for additions to electrical circuits.

Today's first job was to sort the low ME reading.

A work colleague had already identified the cause as the "twinkly
lights" above the bath (just to point out that these are lots of very
small fibre optic lights in some boxing above a bath in a children's
hospice) so permission and an agreed time to was needed to forcibly
remove the side panels of the boxing in for further investigation.

And the cause was that the PSUs of the fibre optic lights were plugged
into an RCD socket behind the boxing in. The RCD socket was the cause of
the low NE reading.

The lights were fitted by volunteers a few years ago.

However then came my second job.

High Zs on drive lights (same place). Yep but only high because they
were not designed correctly in the first place (and a pro designed that
11 years ago). The Zs reading of 1.8 ohms was lower than my guess of
20.0 to 2.5 ohms based on pacing out the length of the driveway.

Now the lights have been changed from sodium to LED and so rather than
checking the tightness of every earth terminal (which IMHO would do
nothing) I just swapped the MCB from a C type to a B type.




--
Adam

Bill Wright[_3_] May 29th 19 03:47 AM

Low NE reading lighting circuit on an EICR
 
On 28/05/2019 19:10, ARW wrote:
Only posting to point out the point of testing and keeping proper
records for additions to electrical circuits.

Today's first job was to sort the low ME reading.

A work colleague had already identified the cause as the "twinkly
lights" above the bath (just to point out that these are lots of very
small fibre optic lights in some boxing above a bath in a children's
hospice) so permission and an agreed time to was needed to forcibly
remove the side panels of the boxing in for further investigation.

And the cause was that the PSUs of the fibre optic lights were plugged
into an RCD socket behind the boxing in. The RCD socket was the cause of
the low NE reading.

The lights were fitted by volunteers a few years ago.

However then came my second job.

High Zs on drive lights (same place). Yep but only high because they
were not designed correctly in the first place (and a pro designed that
11 years ago). The Zs reading of 1.8 ohms was lower than my guess of
20.0 to 2.5 ohms based on pacing out the length of the driveway.

Now the lights have been changed from sodium to LED and so rather than
checking the tightness of every earth terminal (which IMHO would do
nothing) I just swapped the MCB from a C type to a B type.


Interesting.

Bill

Jim K.. May 29th 19 09:41 PM

Low NE reading lighting circuit on an EICR
 
ARW Wrote in message:
Only posting to point out the point of testing and keeping proper
records for additions to electrical circuits.

Today's first job was to sort the low ME reading.

A work colleague had already identified the cause as the "twinkly
lights" above the bath (just to point out that these are lots of very
small fibre optic lights in some boxing above a bath in a children's
hospice) so permission and an agreed time to was needed to forcibly
remove the side panels of the boxing in for further investigation.

And the cause was that the PSUs of the fibre optic lights were plugged
into an RCD socket behind the boxing in. The RCD socket was the cause of
the low NE reading.

The lights were fitted by volunteers a few years ago.

However then came my second job.

High Zs on drive lights (same place). Yep but only high because they
were not designed correctly in the first place (and a pro designed that
11 years ago). The Zs reading of 1.8 ohms was lower than my guess of
20.0 to 2.5 ohms based on pacing out the length of the driveway.

Now the lights have been changed from sodium to LED and so rather than
checking the tightness of every earth terminal (which IMHO would do
nothing) I just swapped the MCB from a C type to a B type.





Did you mean to email Owain with that too?
--
Jim K


----Android NewsGroup Reader----
http://usenet.sinaapp.com/

Andrew[_22_] May 30th 19 04:11 PM

Low NE reading lighting circuit on an EICR
 
On 28/05/2019 19:10, ARW wrote:
The Zs reading of 1.8 ohms was lower than my guess of 20.0 to 2.5 ohms
based on pacing out the length of the driveway.


Couldn't the apprentice have measured the distance properly :-)