I am in the process of fitting a complete new kitchen, and would like the
advice of the experts in this NG regarding some electrical regulations.



I have Googled about a bit and found some answers, but not all the info I
need.



So here goes, four topics really.



1.. My understanding is that electrical outlet, 13A sockets, must be at
least 300mm from a sink. Is this correct?


2.. I want to put some mains halogen downlighters in a sloping ceiling
which will have insulation behind the plasterboard. Am I right in assuming
that I should create a box around the downlighters, say 100mm around the
light to keep the insulation away from the heat of the lights. The ceiling
is yet to be put up, so this would be easy, but the builder wants to plaster
the ceiling next week.


3.. Are there any regulations concerning placing junction boxes behind a
plastered ceiling? What are the regulations regarding accessibility to the
junction box? I have a lighting junction box connecting three external
lights to an external PIR.


4.. We are fitting a built under double oven and ceramic halogen hob. My
question here is how to wire this in. The Oven is rated at 5.18 kW (22A @
230V) and the hob at 5.4kW (23A @ 230V). Currently the MCB for the slot in
cooker is 32A. I will upgrade this to 45A. My idea is to run 10mm cable from
the MCB to the Cooker switch above the counter top, and then run two 6mm
cables from the cooker switch to cooker outlet plates below the counter top.
Is this OK?




Thanks for taking the time to read this, any advice / guidance gratefully
received



Duncan


  #2   Report Post  
BigWallop
 
Posts: n/a
Default Kitchen Electrical Wiring Regulations Advice Please


"DeeBee" wrote in message
...
snipped

1.. My understanding is that electrical outlet, 13A sockets, must be at
least 300mm from a sink. Is this correct?


It can be directly over the sink if you wish, just as long as it doesn't get splashed with water when your
hands are in it doing the dishes. So YES, it is best to keep live electrical outlets away from where
you're working with water.


2.. I want to put some mains halogen downlighters in a sloping ceiling
which will have insulation behind the plasterboard. Am I right in assuming
that I should create a box around the downlighters, say 100mm around the
light to keep the insulation away from the heat of the lights. The ceiling
is yet to be put up, so this would be easy, but the builder wants to plaster
the ceiling next week.


The only thing that you need to watch out for, is that you don't have anything that will combust if it
reaches a certain temperature close to the fittings. This includes any timber frame, any combustible
paper insulation or linings, Etc.

Any heat building up around the light fittings will also greatly decrease the lamps life expectancy, so
try to keep an air flow around the fittings to keep them as cool as possible. The best way to do this, is
cut holes through the insulation after it has been laid, then allow the heat from the light fittings to
escape into the gap above them. This helps to keep the fittings cool but the rest of the ceiling
insulated.


3.. Are there any regulations concerning placing junction boxes behind a
plastered ceiling? What are the regulations regarding accessibility to the
junction box? I have a lighting junction box connecting three external
lights to an external PIR.


Any electrical fitting with screw terminal (compression type connections) must be allowed access for
maintenance reasons. After a short period of time these types of junction boxes work the connections
loose through heating and cooling, so if they eventually come loose and break the conenction, you're in
the doo doo if have to make repair to them.

Best leave access to the junction box, even if it is sited above a hole for the new light fittings where
it can pulled out and worked on.


4.. We are fitting a built under double oven and ceramic halogen hob. My
question here is how to wire this in. The Oven is rated at 5.18 kW (22A @
230V) and the hob at 5.4kW (23A @ 230V). Currently the MCB for the slot in
cooker is 32A. I will upgrade this to 45A. My idea is to run 10mm cable from
the MCB to the Cooker switch above the counter top, and then run two 6mm
cables from the cooker switch to cooker outlet plates below the counter top.
Is this OK?


One 10 millimeter csa' (cross sectional area) cable is the best for total load you're going to take. The
diversity rule that says, all the hob rings should not all be on at the same time because of their
thermostat controls, and the fact that you're very unlikely to be running both ovens at the same time, all
the time, would, I think, come into play here. So you should be able to use just one 10mm cable fused at
45amps for this type of situation. But if you do want to run more than one cable for this, then take into
consideration the cable grouping rules as well.


Thanks for taking the time to read this, any advice / guidance gratefully
received

Duncan




---
http://www.basecuritysystems.no-ip.com

Outgoing mail is certified Virus Free.
Checked by AVG anti-virus system (http://www.grisoft.com).
Version: 6.0.557 / Virus Database: 349 - Release Date: 30/12/03


  #3   Report Post  
Christian McArdle
 
Posts: n/a
Default Kitchen Electrical Wiring Regulations Advice Please

1.. My understanding is that electrical outlet, 13A sockets, must be
at least 300mm from a sink. Is this correct?


It's more of a guideline than a rule.

4.. We are fitting a built under double oven and ceramic halogen hob. My
question here is how to wire this in. The Oven is rated at 5.18 kW (22A @
230V) and the hob at 5.4kW (23A @ 230V). Currently the MCB for the slot

in
cooker is 32A. I will upgrade this to 45A. My idea is to run 10mm cable

from
the MCB to the Cooker switch above the counter top, and then run two 6mm
cables from the cooker switch to cooker outlet plates below the counter

top.
Is this OK?


32A would be fine. There is no need to upgrade to 45A. I would keep the 32A
for increased short circuit protection, particularly if the cable runs are
long.

You may have difficulty getting two lots of 6mm cable into the 45A DP
switch. If so, you can probably use 4mm cable for the runs to the cable
outlets. Although 4mm can't take the full 45A, I believe you are permitted
to take advantage of the fact that a heating device is unlikely to produce
an overload situation beyond the total sum of its heating elements as there
are no failure modes for a heating element to do this. 4mm (even 2.5mm)
cable is quite capable of carrying the 23A that each appliance needs.

This assumes that the runs between the DP switch and cooker outlets are
short (they should be, as the outlets must be close to the switch). If not,
you may have trouble using the MCB for short circuit and earth fault
protection, as the earth loop impedence may be too high.

Christian.



  #4   Report Post  
The Natural Philosopher
 
Posts: n/a
Default Kitchen Electrical Wiring Regulations Advice Please

DeeBee wrote:

I am in the process of fitting a complete new kitchen, and would like the
advice of the experts in this NG regarding some electrical regulations.



I have Googled about a bit and found some answers, but not all the info I
need.



So here goes, four topics really.



1.. My understanding is that electrical outlet, 13A sockets, must be at
least 300mm from a sink. Is this correct?



I believe so.



2.. I want to put some mains halogen downlighters in a sloping ceiling
which will have insulation behind the plasterboard. Am I right in assuming
that I should create a box around the downlighters, say 100mm around the
light to keep the insulation away from the heat of the lights. The ceiling
is yet to be put up, so this would be easy, but the builder wants to plaster
the ceiling next week.



Two points. My sister in law, having just spent 60 quid on new halogen
blsb inher kitchen, is now disappinted to find that 50% have gone
withong 4 months.

I am delighted that only two of my LV spots have gine in two years.

LV pays for itself quite quickly....AND the bulbs are cheaper too.

Secondly, unless the insulation is flammable don't worry about the
lights getting it hot. Plasterboard doesn't burn either. But DO worry
about nearby woodwork, and if you use LV, about overheating transformers.

If the insulatin is a wool type you can generally make a void by pushing
it back. If its celotex you need to cut around teh area - about a square
foot I'd say to mount the lights in a void if LV, a little less for mains.




3.. Are there any regulations concerning placing junction boxes behind a
plastered ceiling? What are the regulations regarding accessibility to the
junction box? I have a lighting junction box connecting three external
lights to an external PIR.



Junction boxes are supposed to be accessible. strictly, you should use
crimps for a 'permanent' buried connection. In practice, if the building
inspector doesn't see it, and you feel confident in making a good
connection with a box and burying it - who cares?



4.. We are fitting a built under double oven and ceramic halogen hob. My
question here is how to wire this in. The Oven is rated at 5.18 kW (22A @
230V) and the hob at 5.4kW (23A @ 230V). Currently the MCB for the slot in
cooker is 32A. I will upgrade this to 45A. My idea is to run 10mm cable from
the MCB to the Cooker switch above the counter top, and then run two 6mm
cables from the cooker switch to cooker outlet plates below the counter top.
Is this OK?



Pass. Can't remember cable ratings, but it sounds fine to me...





Thanks for taking the time to read this, any advice / guidance gratefully
received



Duncan





Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electrical wiring inspector? phil UK diy 14 November 25th 03 01:54 AM
advice require about wiring of fitted electric oven Davey P UK diy 7 October 31st 03 02:48 PM
Saniflow, regulations and pipe through kitchen Scott UK diy 1 October 23rd 03 01:05 PM
Proposed Part P Building Regulations (Electrical Wiring) Andy Hall UK diy 5 September 10th 03 03:07 AM
New Electrical Regs PoP UK diy 22 September 1st 03 09:41 PM


All times are GMT +1. The time now is 03:31 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"