Problems with hot water since fitting shower mixer valve.
 
Hi, have a Worcester 35CDi II combi, and everything was fine until plumbed
up shower mixer valve. Now, whilst the heating works fine, the hot water
only cycles between lukewarm and cold (with the boiler switching the
heating off soon after it goes on).

Now there was some vague blurb in the mixer tap fitting instructions about
the water pressures. We have very high water pressure here ~5Bar, and I
a quick Google has brought up a single mention of someone seeing something
similar, that the pressure of the cold water is going through the valve
and back down the hot output.

Can someone elaborate on this? What are my options on how to fix this?
Fit a pressure reducer to the cold feed? What sort of pressure will my
combi hot side have? I always thought it was the same as the mains
pressure when you had a combi....


Mixer PDF:
http://www.roperrhodes.co.uk/wp-cont...TRUCTIONS7.pdf

"Unbalanced Water Supply
Valves must always be operated within either the range for BS 1287 OR
BS1111 as described in the table below. Valves cannot operate effectively
where a hot or cold pressure system crosses the boundaries of the two
ranges. In addition the maximum ratio of unbalanced hot and cold water
pressures for the valves to operate effectively is 5:1. Hot or cold
pressure must be reduced or boosted so as to work within the required
range.

Maximum Water Pressure
Concealed Dual and Triple Control shower valves are suitable for use with
all water supply systems up to a maximum of 5.0 Bar. Operating pressures
above 5.0 Bar will require the installation of pressure reducing valves."


--
Using Opera's revolutionary email client: http://www.opera.com/mail/

Toby October 1st 12 12:19 PM

Problems with hot water since fitting shower mixer valve.
 
On 01/10/2012 10:00, MarkG wrote:
Hi, have a Worcester 35CDi II combi, and everything was fine until
plumbed up shower mixer valve. Now, whilst the heating works fine, the
hot water only cycles between lukewarm and cold (with the boiler
switching the heating off soon after it goes on).

Now there was some vague blurb in the mixer tap fitting instructions
about the water pressures. We have very high water pressure here
~5Bar, and I a quick Google has brought up a single mention of someone
seeing something similar, that the pressure of the cold water is going
through the valve and back down the hot output.

Can someone elaborate on this? What are my options on how to fix this?
Fit a pressure reducer to the cold feed? What sort of pressure will my
combi hot side have? I always thought it was the same as the mains
pressure when you had a combi....


Mixer PDF:
http://www.roperrhodes.co.uk/wp-cont...TRUCTIONS7.pdf


"Unbalanced Water Supply
Valves must always be operated within either the range for BS 1287 OR
BS1111 as described in the table below. Valves cannot operate
effectively where a hot or cold pressure system crosses the boundaries
of the two ranges. In addition the maximum ratio of unbalanced hot and
cold water pressures for the valves to operate effectively is 5:1. Hot
or cold pressure must be reduced or boosted so as to work within the
required range.

Maximum Water Pressure
Concealed Dual and Triple Control shower valves are suitable for use
with all water supply systems up to a maximum of 5.0 Bar. Operating
pressures above 5.0 Bar will require the installation of pressure
reducing valves."


Can you isolate the hot or cold to the shower mixer valve?
If so, do that (either of them or both) and if that solves the problem,
simply fit two non return valves to the hot and cold feed to the mixer.

If you cant isolate the shower, put the mixer to coldest setting and see
if that solves it, if so, fit the non return valves.

--
Toby...
Remove pants to reply

MarkG October 1st 12 03:15 PM

Problems with hot water since fitting shower mixer valve.
 
On Mon, 01 Oct 2012 12:19:11 +0100, Toby wrote:

On 01/10/2012 10:00, MarkG wrote:
Hi, have a Worcester 35CDi II combi, and everything was fine until
plumbed up shower mixer valve. Now, whilst the heating works fine, the
hot water only cycles between lukewarm and cold (with the boiler
switching the heating off soon after it goes on).

Now there was some vague blurb in the mixer tap fitting instructions
about the water pressures. We have very high water pressure here
~5Bar, and I a quick Google has brought up a single mention of someone
seeing something similar, that the pressure of the cold water is going
through the valve and back down the hot output.

Can someone elaborate on this? What are my options on how to fix this?
Fit a pressure reducer to the cold feed? What sort of pressure will my
combi hot side have? I always thought it was the same as the mains
pressure when you had a combi....


Mixer PDF:
http://www.roperrhodes.co.uk/wp-cont...TRUCTIONS7.pdf


"Unbalanced Water Supply
Valves must always be operated within either the range for BS 1287 OR
BS1111 as described in the table below. Valves cannot operate
effectively where a hot or cold pressure system crosses the boundaries
of the two ranges. In addition the maximum ratio of unbalanced hot and
cold water pressures for the valves to operate effectively is 5:1. Hot
or cold pressure must be reduced or boosted so as to work within the
required range.

Maximum Water Pressure
Concealed Dual and Triple Control shower valves are suitable for use
with all water supply systems up to a maximum of 5.0 Bar. Operating
pressures above 5.0 Bar will require the installation of pressure
reducing valves."


Can you isolate the hot or cold to the shower mixer valve?
If so, do that (either of them or both) and if that solves the problem,
simply fit two non return valves to the hot and cold feed to the mixer.

If you cant isolate the shower, put the mixer to coldest setting and see
if that solves it, if so, fit the non return valves.



Well, spoke to my bathroom fitter, and whilst the mixer has been plumbed
up for a while, he only turned the isolators on last night, which was
exactly the time the other problem cropped up, so pretty sure it's related.

Will the non-return valves limit flow in any way? Is there a specific
type? Going to pop down plumbase and pick a couple up in a mo....




--
Using Opera's revolutionary email client: http://www.opera.com/mail/

Roger Mills[_2_] October 1st 12 04:39 PM

Problems with hot water since fitting shower mixer valve.
 
On 01/10/2012 10:00, MarkG wrote:


Can someone elaborate on this? What are my options on how to fix this?
Fit a pressure reducer to the cold feed? What sort of pressure will my
combi hot side have? I always thought it was the same as the mains
pressure when you had a combi....


Chances are that the combi needs to throttle the water going through it
in order to heat it sufficiently. [Otherwise you might have a very high
flow of luke warm water].

What flow rate do you get at (say) the kitchen hot tap? How does this
compare with the rate at the kitchen cold tap. If the cold rate is much
higher than the hot, throttle it so that they are more or less equal.
The shower mixer should then work better.
--
Cheers,
Roger
____________
Please reply to Newsgroup. Whilst email address is valid, it is seldom
checked.

Toby October 1st 12 05:22 PM

Problems with hot water since fitting shower mixer valve.
 
On 01/10/2012 15:15, MarkG wrote:
On Mon, 01 Oct 2012 12:19:11 +0100, Toby wrote:

On 01/10/2012 10:00, MarkG wrote:
Hi, have a Worcester 35CDi II combi, and everything was fine until
plumbed up shower mixer valve. Now, whilst the heating works fine, the
hot water only cycles between lukewarm and cold (with the boiler
switching the heating off soon after it goes on).

Now there was some vague blurb in the mixer tap fitting instructions
about the water pressures. We have very high water pressure here
~5Bar, and I a quick Google has brought up a single mention of someone
seeing something similar, that the pressure of the cold water is going
through the valve and back down the hot output.

Can someone elaborate on this? What are my options on how to fix this?
Fit a pressure reducer to the cold feed? What sort of pressure will my
combi hot side have? I always thought it was the same as the mains
pressure when you had a combi....


Mixer PDF:
http://www.roperrhodes.co.uk/wp-cont...TRUCTIONS7.pdf



"Unbalanced Water Supply
Valves must always be operated within either the range for BS 1287 OR
BS1111 as described in the table below. Valves cannot operate
effectively where a hot or cold pressure system crosses the boundaries
of the two ranges. In addition the maximum ratio of unbalanced hot and
cold water pressures for the valves to operate effectively is 5:1. Hot
or cold pressure must be reduced or boosted so as to work within the
required range.

Maximum Water Pressure
Concealed Dual and Triple Control shower valves are suitable for use
with all water supply systems up to a maximum of 5.0 Bar. Operating
pressures above 5.0 Bar will require the installation of pressure
reducing valves."


Can you isolate the hot or cold to the shower mixer valve?
If so, do that (either of them or both) and if that solves the
problem, simply fit two non return valves to the hot and cold feed to
the mixer.

If you cant isolate the shower, put the mixer to coldest setting and
see if that solves it, if so, fit the non return valves.



Well, spoke to my bathroom fitter, and whilst the mixer has been plumbed
up for a while, he only turned the isolators on last night, which was
exactly the time the other problem cropped up, so pretty sure it's related.

Will the non-return valves limit flow in any way? Is there a specific
type? Going to pop down plumbase and pick a couple up in a mo....


With your high water pressure and it only supplying the shower, I am
sure it won't be a problem.


--
Toby...
Remove pants to reply

Phil Addison October 1st 12 05:49 PM

Problems with hot water since fitting shower mixer valve.
 
On Mon, 01 Oct 2012 16:39:37 +0100, Roger Mills wrote:

On 01/10/2012 10:00, MarkG wrote:


Can someone elaborate on this? What are my options on how to fix this?
Fit a pressure reducer to the cold feed? What sort of pressure will my
combi hot side have? I always thought it was the same as the mains
pressure when you had a combi....


Chances are that the combi needs to throttle the water going through it
in order to heat it sufficiently. [Otherwise you might have a very high
flow of luke warm water].

What flow rate do you get at (say) the kitchen hot tap? How does this
compare with the rate at the kitchen cold tap. If the cold rate is much
higher than the hot, throttle it so that they are more or less equal.
The shower mixer should then work better.


You seem to have been to posh bathroom supplier, at least by the look of their website.
Would it not be their responsibility to have installed a shower suitable for your
pre-existing boiler?

--
Phil Addison

MarkG October 1st 12 06:26 PM

Problems with hot water since fitting shower mixer valve.
 
On Mon, 01 Oct 2012 17:49:25 +0100, Phil Addison
wrote:

On Mon, 01 Oct 2012 16:39:37 +0100, Roger Mills
wrote:

On 01/10/2012 10:00, MarkG wrote:


Can someone elaborate on this? What are my options on how to fix this?
Fit a pressure reducer to the cold feed? What sort of pressure will my
combi hot side have? I always thought it was the same as the mains
pressure when you had a combi....


Chances are that the combi needs to throttle the water going through it
in order to heat it sufficiently. [Otherwise you might have a very high
flow of luke warm water].

What flow rate do you get at (say) the kitchen hot tap? How does this
compare with the rate at the kitchen cold tap. If the cold rate is much
higher than the hot, throttle it so that they are more or less equal.
The shower mixer should then work better.


You seem to have been to posh bathroom supplier, at least by the look of
their website.
Would it not be their responsibility to have installed a shower suitable
for your
pre-existing boiler?

--
Phil Addison



Well it's suitable for both hi and low pressure systems, but clearly can
get freaked out by large differentials in pressure. They didn't install
it, they just supplied the valve, and it's not even theirs, it's a stock
concealed thermostatic triple valve that every man and his dog seems to
use these days, they just do their own knobs and faceplates to suit...


Been on a trip to Plumbase and picked up a 15mm pressure reducing valve on
the cold side.

http://www.ebay.co.uk/itm/Honeywell-...item3ccade1b3c

or a check valve on the hot side to stop the cold going back down.

http://www.ebay.co.uk/itm/BRASS-SING...item3a5e3438e2

Not sure what's going to be best (opinions???), but have both options
available.. The other option I have considered is that my boiler might
not be pressursing the hot side correctly, and it's only become a problem
now, so I guess I need to pressure check both sides to see what I have...

--
Using Opera's revolutionary email client: http://www.opera.com/mail/

fred October 1st 12 07:47 PM

Problems with hot water since fitting shower mixer valve.
 
In article op.wlif25ksxafqef@desktop, MarkG writes

Well it's suitable for both hi and low pressure systems, but clearly can
get freaked out by large differentials in pressure. They didn't install
it, they just supplied the valve, and it's not even theirs, it's a stock
concealed thermostatic triple valve that every man and his dog seems to
use these days, they just do their own knobs and faceplates to suit...


Been on a trip to Plumbase and picked up a 15mm pressure reducing valve on
the cold side.

http://www.ebay.co.uk/itm/Honeywell-...Valve-PRV-for-
15mm-or-22mm-1-5bar-6bar-/261101591356?pt=UK_Home_Garden_Hearing_Coolin
g_Air&hash=item3ccade1b3c

or a check valve on the hot side to stop the cold going back down.

http://www.ebay.co.uk/itm/BRASS-SING...MM-NON-RETURN-
COMPRESSION-/250688583906?pt=UK_DIY_Materials_Plumbing_MJ&hash= item
3a5e3438e2

Not sure what's going to be best (opinions???), but have both options
available.. The other option I have considered is that my boiler might
not be pressursing the hot side correctly, and it's only become a problem
now, so I guess I need to pressure check both sides to see what I have...

I am a bit surprised by your problems. One of the main benefits of combi
boilers is that you get balanced pressure of both hot and cold water
(the hot water comes from the mains too, it just passes thro a heat
exchanger).

A quick look at the installation manual for the boiler shows that it is
suitable for use on mains supply of up to 10bar without the use of a
pressure reducing valve so I wouldn't expect one to be fitted to yours
(it would be on the cold feed to the boiler).

That said, the symptoms you describe do suggest back pressure on the hot
side, reducing or stopping flow and causing the boiler to shut off.

Have a look to see if you can see a pressure reducing valve before the
boiler as that could be an explanation. The manual I looked at did not
show an internal pressure reducing valve.

You also say the mixing valve has a maximum pressure of 5bar so there
may be an issue there too but the bad news is that if you have over 5bar
on both hot and cold then you may need to pressure reduce both.

I don't think a check valve on the hot side will be of benefit as if the
fault is a cold to hot pressure differential then the valve will be held
closed by the pressure diff, no water will flow end the boiler wont
fire.

As an experiment, try opening a hot tap in the bathroom a bit then turn
on the shower valve. If the flow from the hot tap increases then you
have back flow cold to hot.

HTH
--
fred
it's a ba-na-na . . . .

MarkG October 1st 12 07:57 PM

Problems with hot water since fitting shower mixer valve.
 
On Mon, 01 Oct 2012 19:47:25 +0100, fred wrote:

In article op.wlif25ksxafqef@desktop, MarkG writes



You also say the mixing valve has a maximum pressure of 5bar so there
may be an issue there too but the bad news is that if you have over 5bar
on both hot and cold then you may need to pressure reduce both.



Well it states a maximum "static" pressure of 10bar and a maximumk "flow"
pressure of 5 bar.

What's the difference? - please no wise asses saying 5 bar :-)



Using Opera's revolutionary email client: http://www.opera.com/mail/

Toby October 1st 12 08:00 PM

Problems with hot water since fitting shower mixer valve.
 
On 01/10/2012 18:26, MarkG wrote:
On Mon, 01 Oct 2012 17:49:25 +0100, Phil Addison
wrote:

On Mon, 01 Oct 2012 16:39:37 +0100, Roger Mills
wrote:

On 01/10/2012 10:00, MarkG wrote:


Can someone elaborate on this? What are my options on how to fix this?
Fit a pressure reducer to the cold feed? What sort of pressure will my
combi hot side have? I always thought it was the same as the mains
pressure when you had a combi....


Chances are that the combi needs to throttle the water going through it
in order to heat it sufficiently. [Otherwise you might have a very high
flow of luke warm water].

What flow rate do you get at (say) the kitchen hot tap? How does this
compare with the rate at the kitchen cold tap. If the cold rate is much
higher than the hot, throttle it so that they are more or less equal.
The shower mixer should then work better.


You seem to have been to posh bathroom supplier, at least by the look
of their website.
Would it not be their responsibility to have installed a shower
suitable for your
pre-existing boiler?

--
Phil Addison



Well it's suitable for both hi and low pressure systems, but clearly can
get freaked out by large differentials in pressure. They didn't
install it, they just supplied the valve, and it's not even theirs, it's
a stock concealed thermostatic triple valve that every man and his dog
seems to use these days, they just do their own knobs and faceplates to
suit...


Been on a trip to Plumbase and picked up a 15mm pressure reducing valve
on the cold side.

http://www.ebay.co.uk/itm/Honeywell-...item3ccade1b3c


or a check valve on the hot side to stop the cold going back down.

http://www.ebay.co.uk/itm/BRASS-SING...item3a5e3438e2


Not sure what's going to be best (opinions???), but have both options
available.. The other option I have considered is that my boiler might
not be pressursing the hot side correctly, and it's only become a
problem now, so I guess I need to pressure check both sides to see what
I have...

You want to use the non return valve on both hot sides!

What is happening is this...

Your shower comprises of a mixer then a simple on/off valve, so when the
valve is off, this is just stopping the mixed water from exiting through
the shower head, it should already have a check valve, the PDF you
linked to shows it does, but this doesn't seem to be working, or the
shower only has one on the cold, or it has one on the hot, but has been
connected the wrong way around (do you get hot water out the shower when
you ask it to deliver hot!?)

Fitting a non return valve to the hot feed to the shower will prevent
cold water passing through the valve when you open a hot tap, and the
boiler restricts the flow to get the temperature you have asked of it,
if the boiler didn't restrict the flow, then too much water would pass,
and the boiler would not be able to raise the temperature enough, so
when the boiler is restricting the flow, water then passes through the
shower mixer, as it is an easier path.

If you are just taking cold water at a high rate (bath tap, or multiple
taps open on cold possibly), then I expect you may end up with water
flowing the other way through the shower valve, this is why I suggested
having two non-return valves on the shower, one on each feed.

--
Toby...
Remove pants to reply

MarkG October 1st 12 08:05 PM

Problems with hot water since fitting shower mixer valve.
 
On Mon, 01 Oct 2012 19:57:58 +0100, MarkG wrote:

On Mon, 01 Oct 2012 19:47:25 +0100, fred wrote:

In article op.wlif25ksxafqef@desktop, MarkG writes



You also say the mixing valve has a maximum pressure of 5bar so there
may be an issue there too but the bad news is that if you have over
5bar on both hot and cold then you may need to pressure reduce both.



Well it states a maximum "static" pressure of 10bar and a maximumk
"flow" pressure of 5 bar.

What's the difference? - please no wise asses saying 5 bar :-)



Using Opera's revolutionary email client: http://www.opera.com/mail/



I did the test, and the hot flows correctly out of other taps when the
shower valve is on....




--
Using Opera's revolutionary email client: http://www.opera.com/mail/

fred October 1st 12 08:10 PM

Problems with hot water since fitting shower mixer valve.
 
In article op.wlikawzlxafqef@desktop, MarkG writes
On Mon, 01 Oct 2012 19:47:25 +0100, fred wrote:

In article op.wlif25ksxafqef@desktop, MarkG writes


You also say the mixing valve has a maximum pressure of 5bar so there
may be an issue there too but the bad news is that if you have over 5bar
on both hot and cold then you may need to pressure reduce both.

Well it states a maximum "static" pressure of 10bar and a maximumk "flow"
pressure of 5 bar.

What's the difference? - please no wise asses saying 5 bar :-)

This means that when it is off it wont leak or burst at a pressure up to
10 bar, when it is operating (on) however the pressure limit is lower,
5bar.

No idea what the reason for this is, it may be a pressure balance issue
or it may be that post valve sealing is not proof to higher levels.
--
fred
it's a ba-na-na . . . .

Roger Mills[_2_] October 2nd 12 03:22 PM

Problems with hot water since fitting shower mixer valve.
 
On 01/10/2012 19:57, MarkG wrote:


Well it states a maximum "static" pressure of 10bar and a maximumk
"flow" pressure of 5 bar.

What's the difference? - please no wise asses saying 5 bar :-)


Are you asking why static and flow pressure are different, or why this
device has different limits for the two? Someone else has addressed the
second possibility, so I will address the first.

Static pressure is what you get when there is no flow, so the full
pressure generated by the pump - or whatever is driving it - is seen at
the point of application. Flow pressure is what you get when liquid is
flowing, and is lower than static pressure because some of the pressure
is lost along the way, overcoming flow resistance.

The electrical analogy is to consider the difference of measuring first
the Open Circuit voltage at a point in an electrical circuit, and then
the voltage when current is flowing. The second measurement is lower due
to the internal resistance of the power supply and the resistance of the
cables etc.
--
Cheers,
Roger
____________
Please reply to Newsgroup. Whilst email address is valid, it is seldom
checked.

MarkG October 2nd 12 07:08 PM

Problems with hot water since fitting shower mixer valve.
 
OK, picked up a pressure gauge from PlumbCentre, measured 4Bar on cold
side and 3.3Bar on the hot side.

So it's below the 5Bar limit, which is good, so the question is, would a
0.7bar difference in pressure cause this sort of problem? Seems like a
VERY picky thermostatic mixer, or is this perfectly normal?

Toby October 2nd 12 09:37 PM

Problems with hot water since fitting shower mixer valve.
 
On 02/10/2012 19:08, MarkG wrote:
OK, picked up a pressure gauge from PlumbCentre, measured 4Bar on cold
side and 3.3Bar on the hot side.

So it's below the 5Bar limit, which is good, so the question is, would a
0.7bar difference in pressure cause this sort of problem? Seems like a
VERY picky thermostatic mixer, or is this perfectly normal?


That's strange, with all the taps off, I would expect the static
pressure to be the same on both the hot and the cold if they are both
"powered" by the incoming mains supply.

In the PDF you linked to, it shows a non return valve, are you able to
see if this is actually present on the unit you have?

I asked earlier if the pipes were connected the correct way around, are
they (do you get hot water from the shower if the mixer is set to hot only?)

--
Toby...
Remove pants to reply


All times are GMT +1. The time now is 12:03 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004 - 2014 DIYbanter