I have 3 noisy TRVs as they are fitted on the return instead of the flow.
The instructions suggest this should be okay but they buzz as they close.
Rather than change ends (requiring 4 joints to be disturbed on each rad) is
there any disadvantage in rotating the valve to a horizontal plane - thus
putting the flow onto the 'base' of the valve?
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 11,175
Default Noisy TRV

In article 6,
DerbyBorn writes:
I have 3 noisy TRVs as they are fitted on the return instead of the flow.
The instructions suggest this should be okay but they buzz as they close.
Rather than change ends (requiring 4 joints to be disturbed on each rad) is
there any disadvantage in rotating the valve to a horizontal plane - thus
putting the flow onto the 'base' of the valve?


Should be fine.
Actually, it's a better mounting position for anyone who is going to
struggle to bend down to read the setting on the front - I recently
installed some in this position for an elderly relative for this
reason, so they can read the setting from above.

Make sure it's not sticking out somewhere where it's likely to get
knocked or walked into though.

--
Andrew Gabriel
[email address is not usable -- followup in the newsgroup]
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 569
Default Noisy TRV

In article , Andrew Gabriel wrote:
In article 6,
DerbyBorn writes:
I have 3 noisy TRVs as they are fitted on the return instead of the flow.
The instructions suggest this should be okay but they buzz as they close.
Rather than change ends (requiring 4 joints to be disturbed on each rad) is
there any disadvantage in rotating the valve to a horizontal plane - thus
putting the flow onto the 'base' of the valve?


Should be fine.
Actually, it's a better mounting position for anyone who is going to
struggle to bend down to read the setting on the front - I recently
installed some in this position for an elderly relative for this
reason, so they can read the setting from above.


Some installation instructions also say it's a better position for the sensor:
http://danfoss-randall.co.uk/xxNewsx...8ab022edb.html
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 10,998
Default Noisy TRV

Noisy valves seem to be an issue a lot. a place where I go has one in a
studio, and this means it has to be shut off during recordings. We call it
Hissing Sid, well we are little children at heart...
Brian

--
From the Sofa of Brian Gaff Reply address is active
"Alan Braggins" wrote in message
...
In article , Andrew Gabriel wrote:
In article 6,
DerbyBorn writes:
I have 3 noisy TRVs as they are fitted on the return instead of the
flow.
The instructions suggest this should be okay but they buzz as they
close.
Rather than change ends (requiring 4 joints to be disturbed on each rad)
is
there any disadvantage in rotating the valve to a horizontal plane -
thus
putting the flow onto the 'base' of the valve?


Should be fine.
Actually, it's a better mounting position for anyone who is going to
struggle to bend down to read the setting on the front - I recently
installed some in this position for an elderly relative for this
reason, so they can read the setting from above.


Some installation instructions also say it's a better position for the
sensor:
http://danfoss-randall.co.uk/xxNewsx...8ab022edb.html



  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 633
Default Noisy TRV

On 01/10/2012 09:14, DerbyBorn wrote:
I have 3 noisy TRVs as they are fitted on the return instead of the flow.
The instructions suggest this should be okay but they buzz as they close.
Rather than change ends (requiring 4 joints to be disturbed on each rad) is
there any disadvantage in rotating the valve to a horizontal plane - thus
putting the flow onto the 'base' of the valve?


Beware they can't be wacked by a vacuum cleaner being enthusiastically
wizzed around.


  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 11,175
Default Noisy TRV

In article 6,
DerbyBorn writes:
I have 3 noisy TRVs as they are fitted on the return instead of the flow.
The instructions suggest this should be okay but they buzz as they close.
Rather than change ends (requiring 4 joints to be disturbed on each rad) is
there any disadvantage in rotating the valve to a horizontal plane - thus
putting the flow onto the 'base' of the valve?


Another thought - have the TRVs been fitted without ensuring the boiler
has a bypass route for when they all shut off?
Is there a radiator which doesn't have a TRV and can't be turned off
(lockshield at both ends)?

--
Andrew Gabriel
[email address is not usable -- followup in the newsgroup]
  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 137
Default Noisy TRV

?

Another thought - have the TRVs been fitted without ensuring the
boiler has a bypass route for when they all shut off?
Is there a radiator which doesn't have a TRV and can't be turned off
(lockshield at both ends)?


There is one rad with no TRV and whilst it doens;t have lockshields both
ends, it will not get turned off as it is the important hall radiator.
  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 11,175
Default Noisy TRV

In article 6,
DerbyBorn writes:
?

Another thought - have the TRVs been fitted without ensuring the
boiler has a bypass route for when they all shut off?
Is there a radiator which doesn't have a TRV and can't be turned off
(lockshield at both ends)?


There is one rad with no TRV and whilst it doens;t have lockshields both
ends, it will not get turned off as it is the important hall radiator.


Is it a large radiator (which is likely to be set with a good flow
through it), or a tiny radiator which might have the lock shield
only open a crack (assuming the system has been balanced)?

When the TRVs start making a noise, I would try opening the hall
radiator's lockshield, and see if that stops it. Note exactly how
far you opened it, so you can set it back to where it was again.

When you have a radiator as the bypass loop, particularly a small
radiator, it may be that you have to increase the flow in it above
what is ideal for balancing, in order for it to cope with the flow
needed to maintain the bypass.

Is there a thermostat in the hall, to prevent the boiler firing
when the house is up to temperature?

--
Andrew Gabriel
[email address is not usable -- followup in the newsgroup]
  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 66
Default Noisy TRV

On Mon, 1 Oct 2012, "DerbyBorn" writ:

?

Another thought - have the TRVs been fitted without ensuring the
boiler has a bypass route for when they all shut off?
Is there a radiator which doesn't have a TRV and can't be turned off
(lockshield at both ends)?


There is one rad with no TRV and whilst it doens;t have lockshields both
ends, it will not get turned off as it is the important hall radiator.


Where is the thermostat? Are there TRVs on the rads in the room with the
thermostat?
--
P
  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 137
Default Noisy TRV

Percy wrote in :

On Mon, 1 Oct 2012, "DerbyBorn" writ:

?

Another thought - have the TRVs been fitted without ensuring the
boiler has a bypass route for when they all shut off?
Is there a radiator which doesn't have a TRV and can't be turned off
(lockshield at both ends)?


There is one rad with no TRV and whilst it doens;t have lockshields both
ends, it will not get turned off as it is the important hall radiator.


Where is the thermostat? Are there TRVs on the rads in the room with the
thermostat?


In the hall - across from the non-TRV radiator. Valves on the flow end are
quiet.
The noisy ones are in 2 bedrooms and these are usually the only ones to
normally close.


  #11   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 66
Default Noisy TRV

On Tue, 2 Oct 2012, "DerbyBorn" writ:

Percy wrote in :

On Mon, 1 Oct 2012, "DerbyBorn" writ:

?

Another thought - have the TRVs been fitted without ensuring the
boiler has a bypass route for when they all shut off?
Is there a radiator which doesn't have a TRV and can't be turned off
(lockshield at both ends)?


There is one rad with no TRV and whilst it doens;t have lockshields both
ends, it will not get turned off as it is the important hall radiator.


Where is the thermostat? Are there TRVs on the rads in the room with the
thermostat?


In the hall - across from the non-TRV radiator. Valves on the flow end are
quiet.
The noisy ones are in 2 bedrooms and these are usually the only ones to
normally close.


OK, I only asked because there should not be TRVs in the room with the
thermostat.
--
P
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Noisy TRV. [email protected] UK diy 6 December 17th 10 11:43 AM
Noisy AC Augustine Home Repair 4 June 14th 06 09:54 PM
Noisy Tap not available UK diy 1 February 22nd 06 07:04 AM
noisy DIY Steve UK diy 34 July 15th 05 05:49 PM
Noisy TV Barry Electronics 3 July 19th 04 08:16 PM


All times are GMT +1. The time now is 12:05 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"