UK diy (uk.d-i-y) For the discussion of all topics related to diy (do-it-yourself) in the UK. All levels of experience and proficency are welcome to join in to ask questions or offer solutions.

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
David Hearn
 
Posts: n/a
Default Case of the unknown circuit

A while back I asked people to aid me in working out what my electric
circuits were. Well, I've now done some further investigation and things
are a little more strange.

I have 6 circuits:

32A - electric shower
32A - downstairs ring including a FCU off to the garage and a single socket
radial off the same MCB.
32A - upstairs ring (including a spur somewhere off it to feed a socket
which the immersion heater comes off.
6A - downstairs lighting
16A - upstairs lighting and loft lighting
6A - unknown.

People had suggested that someone had wired up the wrong MCB to the upstairs
lighting and the unknown 6A MCB thinking the 16A should be for the immersion
heater. However, upon further investigation, I've found that the immersion
heater socket is a spur from the upstairs ring. We don't actually use it,
and the plug/socket is slightly scorched!

I've also found that the unknown 6A circuit goes somewhere upstairs via the
cavity (in the same direction as the shower cable - straight up) - where it
ends up, I've no idea. Also that 6A MCB is dead. I noticed that it would
turn off very easily at almost the slightest touch when the others took a
little more force. I checked with a multimeter and the MCB makes contact at
about 2/3 on, but when fully on its disconnected. As a result, this circuit
has never been on for the 6 months we've lived here and there's nothing
electrical that we know of that isn't working - so we've no idea where it
goes.

Any ideas what the unknown circuit is going, what it may be connected to? I
can only assume that it was for something which isn't used any more - but
you'd have expected them to have disconnected it at the CU! It does mean
that I have a spare slot in my CU - which may be useful for something in the
future.

Incidentally, both the upstairs lighting circuit (I think 2.5mm T&E) and the
unknown circuit (possibly 1mm T&E) appears to be in grey T&E where the rest
is in 100% white T&E. It may have had white on it at some point as it is
clearly grey, but around the curved edges looks almost like white paint was
on it as some is still there with an almost flaky appearance (the flat part
is grey). For the lighting circuit, this is both at the CU end, and the
loft end where the lighting comes off it. It looks the same sort of stuff
as the white T&E and is marked with the Henley trade name (250V specced).

Thanks

D

--
To send email to me - remove references to NoSpam, and Spammer from my email
address.


  #2   Report Post  
David W.E. Roberts
 
Posts: n/a
Default Case of the unknown circuit

Quick top posted guess :-)

The spare 6A breaker was for the upstairs lighting - looks the correct
rating and cable.
The 16A breaker was for the immersion - again the correct rating and cable.

The 6a breaker failed.
Some North American horse rider with big hat and spurs decided that the
easiest way to fix things was to connect (upstairs) the immersion feed to
the lighting circuit, and connect the immersion heater to a 13A socket.

If you look hard upstairs you may find where this was done.
If so, you might be able to undo it.
i.e. replace the breaker with a new one, reconnect the lighting, reconnect
the immersion to the 16A direct feed.

As I say, this is only a guess.

Cheers
Dave R


"David Hearn" wrote in message
...
A while back I asked people to aid me in working out what my electric
circuits were. Well, I've now done some further investigation and things
are a little more strange.

I have 6 circuits:

32A - electric shower
32A - downstairs ring including a FCU off to the garage and a single

socket
radial off the same MCB.
32A - upstairs ring (including a spur somewhere off it to feed a socket
which the immersion heater comes off.
6A - downstairs lighting
16A - upstairs lighting and loft lighting
6A - unknown.

People had suggested that someone had wired up the wrong MCB to the

upstairs
lighting and the unknown 6A MCB thinking the 16A should be for the

immersion
heater. However, upon further investigation, I've found that the

immersion
heater socket is a spur from the upstairs ring. We don't actually use it,
and the plug/socket is slightly scorched!

I've also found that the unknown 6A circuit goes somewhere upstairs via

the
cavity (in the same direction as the shower cable - straight up) - where

it
ends up, I've no idea. Also that 6A MCB is dead. I noticed that it would
turn off very easily at almost the slightest touch when the others took a
little more force. I checked with a multimeter and the MCB makes contact

at
about 2/3 on, but when fully on its disconnected. As a result, this

circuit
has never been on for the 6 months we've lived here and there's nothing
electrical that we know of that isn't working - so we've no idea where it
goes.

Any ideas what the unknown circuit is going, what it may be connected to?

I
can only assume that it was for something which isn't used any more - but
you'd have expected them to have disconnected it at the CU! It does mean
that I have a spare slot in my CU - which may be useful for something in

the
future.

Incidentally, both the upstairs lighting circuit (I think 2.5mm T&E) and

the
unknown circuit (possibly 1mm T&E) appears to be in grey T&E where the

rest
is in 100% white T&E. It may have had white on it at some point as it is
clearly grey, but around the curved edges looks almost like white paint

was
on it as some is still there with an almost flaky appearance (the flat

part
is grey). For the lighting circuit, this is both at the CU end, and the
loft end where the lighting comes off it. It looks the same sort of stuff
as the white T&E and is marked with the Henley trade name (250V specced).

Thanks

D

--
To send email to me - remove references to NoSpam, and Spammer from my

email
address.




  #3   Report Post  
Christian McArdle
 
Posts: n/a
Default Case of the unknown circuit

6A - unknown.

TV booster? Disused lighting circuit?

Possibly maybe it had some lights on it once. When a persistent short meant
it could no longer be used and the short could not be located, those lights
were transferred to the other lighting circuit.

Christian.

P.S. Your immersion shouldn't be off the ring main, although you'll get away
with it if you don't actually use it much. Unfortunately, as a back up it is
the worst possible situation, as you'd probably need that ring main for fan
heaters if your boiler goes t-u.

P.P.S. 16A is normally considered too much for a lighting circuit. Many
fittings are required to be fused at 10A (or even 6A).



  #4   Report Post  
David Hearn
 
Posts: n/a
Default Case of the unknown circuit


"Christian McArdle" wrote in message
t...
6A - unknown.


TV booster? Disused lighting circuit?

Possibly maybe it had some lights on it once. When a persistent short

meant
it could no longer be used and the short could not be located, those

lights
were transferred to the other lighting circuit.

Christian.

P.S. Your immersion shouldn't be off the ring main, although you'll get

away
with it if you don't actually use it much. Unfortunately, as a back up it

is
the worst possible situation, as you'd probably need that ring main for

fan
heaters if your boiler goes t-u.

P.P.S. 16A is normally considered too much for a lighting circuit. Many
fittings are required to be fused at 10A (or even 6A).


What I may do (if I can't find an obvious reason for the circuit needing to
be there) is to move the lighting across to a new 6A MCB and whilst I'm at
it, rejiggle the whole CU such that the 32A feeds are at the switch end
(currently they're at the far end!).

We've been in the house for 6 months and we've never yet used the immersion
heater (mainly because the socket it was plugged into had been pulled off
the wall and there were two screws rattling around inside it!). Personally
I can't see there being any need to use it unless there's a major problem
(ie. boiler death) - but as you say, may well need to use the ring for
heating...

Incidentally, how do people get cables up through a cavity once the house is
used? I'm amazed that someone managed to get the shower cable from the CU
to the loft via the cavity. Straight up is one thing (which this is) - but
I can't imagine how someone would start to try doing it horizontally or
diagonally. Annoyingly, the bathroom is directly above the CU. Not exactly
easy to lift floorboards when there's a toilet and bath spanning them (plus
its fitted on top of lino, so we can't take that up without cutting round
everything... I doubt I'll ever get to see what wiring goes under there.

When I added some sockets, I assumed that 2 2.5mm T&E cables coming up from
above the boiler was the ring for upstairs. Certainly one went to a socket,
and the other disappeared somewhere. I fitted all the sockets I wanted in
the room, cut into the ring only to find it was 3 core + earth! Wasn't
2.5mm - but the 3rd core had made the 1mm look like the size of 2.5mm
(heating control I guess). The other wire was the ring, and I can only
assume, that the in and out of the ring don't actually come via the same
point from downstairs. 50-50 chance of me picking the wrong wire. Had I
picked the right wire, I'd be none the wiser. Typical though that I didn't
have a 4 connector junction box around and it was only an hour or so off
starting to go dark! I've now made a map of the wiring in that room and put
it under the floorboards. Shame people didn't do that at time of
installation!

Thanks

D


  #5   Report Post  
Bob Mannix
 
Posts: n/a
Default Case of the unknown circuit


"David W.E. Roberts" wrote in message
...
Quick top posted guess :-)

The spare 6A breaker was for the upstairs lighting - looks the correct
rating and cable.
The 16A breaker was for the immersion - again the correct rating and

cable.

The 6a breaker failed.
Some North American horse rider with big hat and spurs decided that the
easiest way to fix things was to connect (upstairs) the immersion feed to
the lighting circuit, and connect the immersion heater to a 13A socket.

If you look hard upstairs you may find where this was done.
If so, you might be able to undo it.
i.e. replace the breaker with a new one, reconnect the lighting, reconnect
the immersion to the 16A direct feed.

As I say, this is only a guess.


That would be my *very strong* suspicion also.


--
Bob Mannix
(anti-spam is as easy as 1-2-3 - not)


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Longish query - circuit breakers in consumer units David W.E. Roberts UK diy 9 November 9th 03 01:33 PM
using 30A cable to supply 5A lighting circuit: good idea? dave L UK diy 3 October 7th 03 11:08 PM
How do you solder pipework which is at the lowest point of the circuit? PoP UK diy 12 October 2nd 03 08:17 AM
RCD trips while working on dead circuit Bob Mannix UK diy 4 September 9th 03 10:31 AM
Is it a radial or ring circuit? Paul UK diy 14 September 4th 03 05:48 PM


All times are GMT +1. The time now is 07:38 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"