  #1   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 574
Default Honeywell Sundial wiring centre

I'm about to wire up an extra CH zone, the thermostat will call the
valve, and the valve's auxiliary switch will call the heating system.

However I find that the system is wired using an Honeywell 42005748-001
wiring centre. This appears to have no provision for a second (third
etc) zone.

http://www.uk-plumbing.com/brochure/...Centre4200.pdf

Does anyone know how to wire the zone into such a wiring centre? This
photo shows how it is currently wired:

http://bit.ly/6Iv5Lg

If I just connect it to the roomstat terminals in parallel with the
existing roomstat this will also call the main S plan zone valve.

If this is too complicated, I may just replace the wiring centre with a
10-way junction strip. I'll want to add more zones as I go through the
renovations.

I was planning to place the new zone valve in parallel with the
existing CH zone valve, so either one or both could be open. So the
new one would be tee-ed in at the same point that the DHW feed leaves
the pumped feed from the boiler. Bottom of is photo, near the
broomstick top:

http://bit.ly/54spPu

The zone return just joins the main return wherever convenient.

I hope that's right?

Thanks,
R.
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,688
Default Honeywell Sundial wiring centre


"TheOldFellow" wrote in message
. ..
I'm about to wire up an extra CH zone, the thermostat will call the
valve, and the valve's auxiliary switch will call the heating system.

However I find that the system is wired using an Honeywell 42005748-001
wiring centre. This appears to have no provision for a second (third
etc) zone.

http://www.uk-plumbing.com/brochure/...Centre4200.pdf

Does anyone know how to wire the zone into such a wiring centre? This
photo shows how it is currently wired:

http://bit.ly/6Iv5Lg

If I just connect it to the roomstat terminals in parallel with the
existing roomstat this will also call the main S plan zone valve.

If this is too complicated, I may just replace the wiring centre with a
10-way junction strip. I'll want to add more zones as I go through the
renovations.


If you are not adding an extra programmer and are just zoning the heating
using room stats then wire up the new 2 port valve and the new room stat in
parallel with the existing CH 2 port valve and roomstat with just one small
alteration.

The alteration is. The return/call from the new room stat should be
connected to the BROWN wire on the new 2 port valve and these two wires
should not be connected to anything else. A piece of strip connector should
be fine for this connection

Adam

Adam

  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 574
Default Honeywell Sundial wiring centre

On Sun, 29 Nov 2009 15:52:20 GMT
"ARWadsworth" wrote:


"TheOldFellow" wrote in message
. ..
I'm about to wire up an extra CH zone, the thermostat will call the
valve, and the valve's auxiliary switch will call the heating system.

However I find that the system is wired using an Honeywell 42005748-001
wiring centre. This appears to have no provision for a second (third
etc) zone.

http://www.uk-plumbing.com/brochure/...Centre4200.pdf

Does anyone know how to wire the zone into such a wiring centre? This
photo shows how it is currently wired:

http://bit.ly/6Iv5Lg

If I just connect it to the roomstat terminals in parallel with the
existing roomstat this will also call the main S plan zone valve.

If this is too complicated, I may just replace the wiring centre with a
10-way junction strip. I'll want to add more zones as I go through the
renovations.


If you are not adding an extra programmer and are just zoning the heating
using room stats then wire up the new 2 port valve and the new room stat in
parallel with the existing CH 2 port valve and roomstat with just one small
alteration.

The alteration is. The return/call from the new room stat should be
connected to the BROWN wire on the new 2 port valve and these two wires
should not be connected to anything else. A piece of strip connector should
be fine for this connection

Adam

Adam


The new room stat is a programmable, two wire. I take your term
Programmer to mean Programmable Time Switch, a Honeywell ST699 in my
case. So to check by paraphrase:

Connect the Grey (Switch 1 - live), Blue (Neutral), G/Yellow (Earth),
Orange (Switch 2 - Boiler/Pump call) of the new zone valve into the same
connectors as the Current zone valve. Connect the new stat between
live and the new Zone Valve Brown (Motor Live).

Yes, I understand that and see how it works. Thanks, saved me from
rewiring the lot although I might just do it anyway, as I find the
wiring much easier to understand when I can see it all!

  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 574
Default Honeywell Sundial wiring centre

Correction: where I said the new stat should be between live and
valve-BROWN, I meant the ON-HW terminal of the Programmer and
valve-BROWN.

Otherwise the zone can call the boiler even when the timer is off.

R.

  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,688
Default Honeywell Sundial wiring centre


"TheOldFellow" wrote in message
. ..
On Sun, 29 Nov 2009 15:52:20 GMT
"ARWadsworth" wrote:


"TheOldFellow" wrote in message
. ..
I'm about to wire up an extra CH zone, the thermostat will call the
valve, and the valve's auxiliary switch will call the heating system.

However I find that the system is wired using an Honeywell 42005748-001
wiring centre. This appears to have no provision for a second (third
etc) zone.

http://www.uk-plumbing.com/brochure/...Centre4200.pdf

Does anyone know how to wire the zone into such a wiring centre? This
photo shows how it is currently wired:

http://bit.ly/6Iv5Lg

If I just connect it to the roomstat terminals in parallel with the
existing roomstat this will also call the main S plan zone valve.

If this is too complicated, I may just replace the wiring centre with a
10-way junction strip. I'll want to add more zones as I go through the
renovations.


If you are not adding an extra programmer and are just zoning the heating
using room stats then wire up the new 2 port valve and the new room stat
in
parallel with the existing CH 2 port valve and roomstat with just one
small
alteration.

The alteration is. The return/call from the new room stat should be
connected to the BROWN wire on the new 2 port valve and these two wires
should not be connected to anything else. A piece of strip connector
should
be fine for this connection

Adam

Adam


The new room stat is a programmable, two wire. I take your term
Programmer to mean Programmable Time Switch, a Honeywell ST699 in my
case. So to check by paraphrase:

Connect the Grey (Switch 1 - live), Blue (Neutral), G/Yellow (Earth),
Orange (Switch 2 - Boiler/Pump call) of the new zone valve into the same
connectors as the Current zone valve. Connect the new stat between
live and the new Zone Valve Brown (Motor Live).

Yes, I understand that and see how it works. Thanks, saved me from
rewiring the lot although I might just do it anyway, as I find the
wiring much easier to understand when I can see it all!



As long as you connect the new programmable stat to a permanent live (the
grey wire from the 2 port valve is fine) and then put its return only to the
brown cable in the new 2 port valve you will have two independant CH zones.

Do not wire the new stat up to the old stat as I first suggested as the new
zone will only work when the "old" zone is calling for heat via the old 699
programmer.

HTH

Adam






  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,688
Default Honeywell Sundial wiring centre


"TheOldFellow" wrote in message
. ..
Correction: where I said the new stat should be between live and
valve-BROWN, I meant the ON-HW terminal of the Programmer and
valve-BROWN.

Otherwise the zone can call the boiler even when the timer is off.

R.



Do you want to have two separate time controlled CH zones or two CH zones
that are controlled by one master time control programmer and then uses two
stats (one a programmable one) for each of the zones?

Adam








  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 574
Default Honeywell Sundial wiring centre

On Sun, 29 Nov 2009 18:22:38 GMT
"ARWadsworth" wrote:


"TheOldFellow" wrote in message
. ..
Correction: where I said the new stat should be between live and
valve-BROWN, I meant the ON-HW terminal of the Programmer and
valve-BROWN.

Otherwise the zone can call the boiler even when the timer is off.

R.



Do you want to have two separate time controlled CH zones or two CH zones
that are controlled by one master time control programmer and then uses two
stats (one a programmable one) for each of the zones?

Adam


I really don't need the 699 for the CH, I use the time-switch for the
HW so that it gives the boiler a long run rather than topping up the
cylinder (OSO unvented) temp.

I see why you ask the question, if the new zone is to be completely
independent of the other zones, then the time-switching should be part
of the zone controls. If we want a whole-house time-switch then the
Stat should be fed from the common time-switch.

In fact I'm going to use a Programmable Stat (Hostmann Centaurstat), so
I don't really need the 699 in the feed.

As you say in the other thread on wring diagrams (good thread BTW)
there are a lot of ways that a fully zoned system can be done. And
this is why I may trash the Sundial Wiring Centre and put in a big
choc-block!

Thanks for the inputs. I feel quite confident about it now I've got
the logic of the thing worked out.

R.

  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,688
Default Honeywell Sundial wiring centre


"TheOldFellow" wrote in message
. ..
On Sun, 29 Nov 2009 18:22:38 GMT
"ARWadsworth" wrote:


"TheOldFellow" wrote in message
. ..
Correction: where I said the new stat should be between live and
valve-BROWN, I meant the ON-HW terminal of the Programmer and
valve-BROWN.

Otherwise the zone can call the boiler even when the timer is off.

R.



Do you want to have two separate time controlled CH zones or two CH zones
that are controlled by one master time control programmer and then uses
two
stats (one a programmable one) for each of the zones?

Adam


I really don't need the 699 for the CH, I use the time-switch for the
HW so that it gives the boiler a long run rather than topping up the
cylinder (OSO unvented) temp.

I see why you ask the question, if the new zone is to be completely
independent of the other zones, then the time-switching should be part
of the zone controls. If we want a whole-house time-switch then the
Stat should be fed from the common time-switch.

In fact I'm going to use a Programmable Stat (Hostmann Centaurstat), so
I don't really need the 699 in the feed.

As you say in the other thread on wring diagrams (good thread BTW)
there are a lot of ways that a fully zoned system can be done. And
this is why I may trash the Sundial Wiring Centre and put in a big
choc-block!

Thanks for the inputs. I feel quite confident about it now I've got
the logic of the thing worked out.

R.


I have sent you some info if your email iscorrect

Is it is not correct and you want the info email me.

Adam

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Revised Honeywell Sundial Plans Dave Osborne[_2_] UK diy 17 November 30th 09 10:37 AM
Honeywell acuator wiring - old to new Neil DG UK diy 1 August 20th 07 01:28 AM
Need Help Wiring Honeywell RTH7500 carpathia Home Repair 3 October 23rd 06 02:26 AM
Wiring a Honeywell RTH7500 Norwalk Paul Home Repair 2 October 23rd 05 08:22 PM
Tower Wiring Centre for domestic central heating Jimmy UK diy 4 December 12th 03 05:07 PM


All times are GMT +1. The time now is 09:06 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"