The way my installation has been done (not all by me!) is....



Live and Neutral enter my CU from my meter directly into a 80A RCD (MK model
No LN 5780)



There is an earth wire coming out of the bottom of the electricity companies
fuse box that runs to the CU (via a sealed (metal loops of wire with a lead
like lump on) little box



I am in the process of trying to get the electricity board to come out and
disconnect my main fuse so I can install a 100A isolator in between the
meter and the CU, as I am intending wiring in a generator transfer switch
(it's on the wall already!))



Off the 80A RCD are the following MCB's (nearest to furthest)

30A 30A 30A 20A 15A 10A



There is then some wire connected to the same terminals as the incoming
supply (looks like 2.5mm) that then goes to the input of the lighting RCD
(MK number 6730), this then has three 5A MCB's connected to it that supply
all the lighting in the house.



(This is all in a single consumer unit)



My first question is, is this correct - I am concerned that the wires that
run from the top (inlet) of the first RCD to the inlet of the second
(lighting) RCD are not sufficiently protected (the only thing protecting
them is the 80A electricity board fuse)



My next set of question start with....

There is a 15A MCB for the outside power - There is a 2.5mm T&E cable that
runs from the CU to the workshop

It used to run to an old shed, but we have got a new one due to the fact it
practically fell down! This old shed was supplied form the house via an
overhead 2.5mm cable attached to a galvanised wire (this bit was about 5
meters)



The new workshop is slightly closer, so I have just moved the cable over to
the new location - This overhead run is now about 4 Meters from the house to
the workshop



In the old shed there was a crappy old fuse box - This has gone in the skip
as it was rusty, and sometimes tripped the main RCD when it was switched
off!



I have installed a new consumer unit in the new workshop



This has a 30mA RCD



The sockets in the workshop are connected to a 15A MCB

The lights in the workshop are connected to a 5A MCB



There is another shed right next to the workshop, this too has it's own 15A
MCB for the sockets, and a 5A for the lights



The cables to the other shed are run through a length of green corrugated
plastic pipe, remarkably similar to what NTL use from the tee in the road to
the drop box - As I said before, the shed is right next to the workshop,
so the pipe is only about 15cms long!



There is then a 2.5mm T&E cable that runs from a 15A MCB in the workshop,
through the other shed, then underground (in what looks like water pipe) to
the garage at the top of the garden (about 25M away)



This currently has yet another CU with two fuses, one 15A for the sockets,
and a 5A for the lights.



Then from this garage, wired into the 15A fuse (along with a socket in the
garage), there is a 1.5mm T&E cable that runs to the greenhouse (to one
water proof switched un-fused socket)





It may seem a lot running off the one 15A MCB in the house, but it has never
tripped as there is not a lot of power used outside (Two pond pumps, a few
lights, and the occasional use of hedge trimmers, strimmers, power tools and
Christmas lights!)



Does this all look OK or not?

Everything is electrically protected as far as I can see (There are no
cables rated under the rating of its supplying RCD or MCB)



The things I am concerned about are...



It is all earthed from the house - should I install an earth rod at the
workshop, garage or both? (I have installed an earth rod for the generator
witch is located next to the workshop - could I use this one rod for two
earthing points?



The overhead cable is just bog standard T&E - I expect this should be either
in a pipe of some sort, or armoured?



The cable that runs up to the garage is also bog standard T&E - it is
protected by the water pipe it is in, but should it be armoured really?



Should I replace the old fuse box in the garage with yet another RCD/MCB
box?



People say you should not have RCD's connected to RCD's - why? - Surely is
it just more protection?



Thanks for you comments!



Sparks


  #2   Report Post  
Wheelbarrowbob
 
Posts: n/a
Default My Consumer unit, and outside power system

Live and Neutral enter my CU from my meter directly into a 80A RCD (MK model
No LN 5780)


Sounds right(via a sealed (metal loops of wire with a lead
like lump on) little box


This is the suppliers seal and should not be brokenthe electricity board to
come out and
disconnect my main fuse so I can install a 100A isolator in between the
meter and the CU,

When they disconnect your supply and you put your isolater in install a henley
block ( connection device for 25 mm tails ) for your outbuilding supply rcd.

There is then some wire connected to the same terminals as the incoming
supply (looks like 2.5mm) that then goes to the input of the lighting RCD
(MK number 6730), this then has three 5A MCB's connected to it that supply


There is then some wire connected to the same terminals as the incoming
supply (looks like 2.5mm) that then goes to the input of the lighting RCD
(MK number 6730), this then has three 5A MCB's connected to it that supply


You have a MK split consumer unit with your ring circuits being RCD protected

Off the 80A RCD are the following MCB's (nearest to furthest)

30A 30A 30A 20A 15A 10A

Have you an electric cooker or electric shower ?
They should be on there own circuits, 45A mcbs

his then has three 5A MCB's connected to it that supply
all the lighting in the house.


Sounds right.My first question is, is this correct - I am concerned that the
wires that
run from the top (inlet) of the first RCD to the inlet of the second
(lighting) RCD are not sufficiently protected (the only thing protecting
them is the 80A electricity board fuse)


If it is an MK split board it should be pre wired and the protection should be
ok


For your outbuildings, I would do it this way, from Henley block 25mm tails to
30ma RCD and 2.5mm to your first building to a consumer unit. If you use a
catenary wire, ( overhead ) it must be earthed at the house end from your main
earthing point. and your 2.5 mm supported every 250mm ( cable ties ) . At the
consumer unit provide an earth using an earth electrode, get this tested, the
earth electrode resistance must be below 200 ohms.
Then design your power circuits, ring circuits protected by 32A mcbs, radials
by 20A mcbs and lighting by 5A mcbs
The 25m garage run if underground should be in SWA using glands to metal boxes
then for extra safety connect it to a FCU.
Hope this has been of help, if you can not understand this e mail me as i have
a great diagram which is very clear and i will send it to you
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT +1. The time now is 03:43 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"