I'm been slowly checking all the sockets in my new house (1930s). In
one socket I found the neutral wires were in the earth terminal and
the earth in the neutral!!! How could this work? I thought any current
feeding back through earth would trip the circuit beaker. Apart from
further dodgy wiring in the house, could this be an indication of a
bigger problem, ie circuit breaker not working?

I'm going to keep checking and fixing the rest of the sockets in the
house, not being an electrician I can only really check the wires and
the correct way round and secure. Is it worth getting a qualified
electrician in to run some continuity checks etc? What else could they
check for?

Cheers

Chris
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,369
Default Neutral and Earth wrong way round



wrote in message
...
I'm been slowly checking all the sockets in my new house (1930s). In
one socket I found the neutral wires were in the earth terminal and
the earth in the neutral!!! How could this work? I thought any current
feeding back through earth would trip the circuit beaker. Apart from
further dodgy wiring in the house, could this be an indication of a
bigger problem, ie circuit breaker not working?


A circuit breaker in a household fuse box only trips if the current is
exceeded. You have to have a RCD type device to trip on earth current which
you probably don't have.



I'm going to keep checking and fixing the rest of the sockets in the
house, not being an electrician I can only really check the wires and
the correct way round and secure. Is it worth getting a qualified
electrician in to run some continuity checks etc? What else could they
check for?

Cheers

Chris


  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 143
Default Neutral and Earth wrong way round


wrote in message
...
I'm been slowly checking all the sockets in my new house (1930s). In
one socket I found the neutral wires were in the earth terminal and
the earth in the neutral!!! How could this work? I thought any current
feeding back through earth would trip the circuit beaker. Apart from
further dodgy wiring in the house, could this be an indication of a
bigger problem, ie circuit breaker not working?

I'm going to keep checking and fixing the rest of the sockets in the
house, not being an electrician I can only really check the wires and
the correct way round and secure. Is it worth getting a qualified
electrician in




If its an old house new to you and you are only able to check sockets - yes.
Ask for a Periodic Inspection Report. Was nothing said about the state
of the electrics during the house purchase? If so definately get the PIR
and revisit your legal advice. If not put that down to experience and get
the report anyway.

Jim A


  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,560
Default Neutral and Earth wrong way round

wrote:

I'm been slowly checking all the sockets in my new house (1930s). In
one socket I found the neutral wires were in the earth terminal and
the earth in the neutral!!! How could this work? I thought any current
feeding back through earth would trip the circuit beaker. Apart from
further dodgy wiring in the house, could this be an indication of a
bigger problem, ie circuit breaker not working?

I'm going to keep checking and fixing the rest of the sockets in the
house, not being an electrician I can only really check the wires and
the correct way round and secure. Is it worth getting a qualified
electrician in to run some continuity checks etc? What else could they
check for?

Cheers

Chris


MCBs are like fuses, they only trip when excess current flows, so
no they don't care about live or earth. It does mean you've got no
working RCD, which probably isnt a problem, but can be in a
minority of cases. Are you in country or town? Do you have
something marked as an RCD or ELCB?

E/N swap is only a tiny risk. It means that like most oldish installs,
things haven't been checked in a while.


NT


  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3
Default Neutral and Earth wrong way round



What sort of things are written on it?

--


They are BS3871, 32A for the socket ring mains.
  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3
Default Neutral and Earth wrong way round


If its an old house new to you and you are only able to check sockets - yes.
Ask for a Periodic Inspection Report. * * Was nothing said about the state
of the electrics during the house purchase? *If so definately get the PIR
and revisit your legal advice. *If not put that down to experience and get
the report anyway.



Thanks Jim, nothing was mentioned on the survey when I purchased the
house (I used the banks full survey option, cost me £1500 and they
were rubbish!). Think it will have to go down to experience!

Any idea what I can expect to pay for a PIR in Greater London?
  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,560
Default Neutral and Earth wrong way round

wrote:

I'm been slowly checking all the sockets in my new house (1930s). In
one socket I found the neutral wires were in the earth terminal and
the earth in the neutral!!! How could this work? I thought any current
feeding back through earth would trip the circuit beaker. Apart from
further dodgy wiring in the house, could this be an indication of a
bigger problem, ie circuit breaker not working?

I'm going to keep checking and fixing the rest of the sockets in the
house, not being an electrician I can only really check the wires and
the correct way round and secure. Is it worth getting a qualified
electrician in to run some continuity checks etc? What else could they
check for?

Cheers

Chris


MCBs trip on overcurrent, so they won't care. It means you have
no working RCD or ELCB supplying the sockets, which is usually
not a problem, but if you're out in the country on a TT install that
would be a big problem.

The risk caused by a N/E swap is tiny. It means your electrics havent
been checked in a while, which is usual for non-new installs.


NT
  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 143
Default Neutral and Earth wrong way round


"ChrisP" wrote in message
...

If its an old house new to you and you are only able to check sockets -
yes.
Ask for a Periodic Inspection Report. Was nothing said about the state
of the electrics during the house purchase? If so definately get the PIR
and revisit your legal advice. If not put that down to experience and get
the report anyway.



Thanks Jim, nothing was mentioned on the survey when I purchased the
house (I used the banks full survey option, cost me £1500 and they
were rubbish!). Think it will have to go down to experience!

Any idea what I can expect to pay for a PIR in Greater London?

Can't help with the actual costs because it's impossible to quantify except
to say the remediation costs are likely to exceed the cost of the Report
which is a report and not a fix. I've sat in on NICEIC PIR seminars at trade
shows and the open endedness of the process is a little worrying. The
tester is supposed to discuss with you what you want (how much?).
Unfortunately the background, 70 years or so of inadequate electrics, years
of possible botching, recent change of ownership and already identified
faults are actually what the process is designed to address.

Not endorsing NICEIC, there are other bodies too, but research their website
and Google generally about PIRs first.

Jim A




  #11   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,560
Default Neutral and Earth wrong way round

ChrisP wrote:

What sort of things are written on it?


They are BS3871, 32A for the socket ring mains.


MCBs then


NT
  #12   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,356
Default Neutral and Earth wrong way round

On Sun, 16 Mar 2008 05:16:12 -0700 (PDT) someone who may be ChrisP
wrote this:-

What sort of things are written on it?


They are BS3871, 32A for the socket ring mains.


Then it is an MCB and it would not operate for this sort of fault.


--
David Hansen, Edinburgh
I will *always* explain revoked encryption keys, unless RIP prevents me
http://www.opsi.gov.uk/acts/acts2000/00023--e.htm#54
  #13   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,024
Default Neutral and Earth wrong way round

On Sun, 16 Mar 2008 05:18:43 -0700 (PDT), ChrisP
wrote:


Any idea what I can expect to pay for a PIR in Greater London?


Probably about £150-300. For this you will get about 2-4 hours of
work (so don't expect any amount of detailed inspection) and a tick
the box report such as the examples at

http://www.checkedelectrics.co.uk/Pe...portSample.pdf
http://www.asec.ltd.uk/assets/docume...415_Sample.pdf

This will tell you your overall assessment is "unsatisfactory" and
that your installation doesn't meet current standards (it doesn't,
nor does it need to), that it needs a new consumer unit (it probably
doesn't) and a rewire (it almost certainly doesn't). It will also
include a few items requiring "urgent attention" (they probably
don't).

In fact many of the items on those example documents will appear on
yours, they may as well be pre-printed. A Periodic Inspection Report
is an important sales opportunity for any ambitious electrician.

For checking the wiring in your sockets you can either visually
inspect them after removing them or use a socket tester such as :-

http://www.tlc-direct.co.uk/Main_Ind...ter/index.html

Simple socket tester will alert you to wiring faults but not to earth
fault loop impedance faults. More complex ones such as

http://www.tlc-direct.co.uk/Products/TMEZ150.html

will also test earth impedance.


  #14   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Neutral and Earth wrong way round

Peter Parry wrote:

I would agree with most points, but:

nor does it need to), that it needs a new consumer unit (it probably
doesn't) and a rewire (it almost certainly doesn't). It will also


Much depends on the state of the cables. A '30s place could well still
have rubber insulated wiring and urgently need rewiring.


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #15   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,024
Default Neutral and Earth wrong way round

On Sun, 16 Mar 2008 16:26:59 +0000, John Rumm
wrote:

Much depends on the state of the cables. A '30s place could well still
have rubber insulated wiring and urgently need rewiring.


It could, but as it already has MCB's that is very unlikely. Even if
it was rubber it might well not even be picked up in a Periodic
Inspection Report unless its somewhere it can be seen without lifting
boards etc. PIRs are far more of a customer paid for sales
opportunity for electricians than anything useful.



  #16   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,560
Default Neutral and Earth wrong way round

Peter Parry wrote:
On Sun, 16 Mar 2008 16:26:59 +0000, John Rumm
wrote:


Much depends on the state of the cables. A '30s place could well still
have rubber insulated wiring and urgently need rewiring.


It could, but as it already has MCB's that is very unlikely. Even if
it was rubber it might well not even be picked up in a Periodic
Inspection Report unless its somewhere it can be seen without lifting
boards etc. PIRs are far more of a customer paid for sales
opportunity for electricians than anything useful.


I'm wondering how practical it is to suggest the OP could do the
main points with a bit of reading or explaining. Its not particularly
hard.


NT
  #17   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3
Default Neutral and Earth wrong way round

The house has been rewired, I'm just not sure when.

The offending socket has been used fine, including a vaccum cleaner
which i think consume a fair number of watts.

I've checked a few more sockets and found loose wires where spurs
(sometimes more than one!) have been added. Just looks like a bad DIY
by the previous owners I can rectify myself.

Thanks everyone, your comments are very helpful.
  #19   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,231
Default Neutral and Earth wrong way round

On Sun, 16 Mar 2008 03:31:38 -0700, chrisproud wrote:

I'm been slowly checking all the sockets in my new house (1930s). In one
socket I found the neutral wires were in the earth terminal and the
earth in the neutral!!! How could this work? I thought any current
feeding back through earth would trip the circuit beaker. Apart from
further dodgy wiring in the house, could this be an indication of a
bigger problem, ie circuit breaker not working?

I'm going to keep checking and fixing the rest of the sockets in the
house, not being an electrician I can only really check the wires and
the correct way round and secure. Is it worth getting a qualified
electrician in to run some continuity checks etc? What else could they
check for?

Cheers

Chris


As others have said this will not cause a circuit breaker to trip.
Given that this particula fault is rather rare (it is plausible to
misplace Line and Neutral bit much less the Earth with a Conductor).
It brings a serious question mark over the whole installation.



--
Ed Sirett - Property maintainer and registered gas fitter.
The FAQ for uk.diy is at http://www.diyfaq.org.uk
Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html
Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html
Choosing a Boiler FAQ http://www.makewrite.demon.co.uk/BoilerChoice.html

  #20   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,285
Default Neutral and Earth wrong way round

Andy Champ wrote:

I don't see the relevance of the age.


If the cabling is pre-1984 2.5 mm^2 T&E - quite possible in view of the
older BS 3871 type MCB mentioned - then the earth conductors acting as
neutral will only be 1 mm^2 and could be liable to serious overheating
under overload, not protected by the MCB. With later 2.5 T&E the
problem won't be quite so bad.

--
Andy


  #21   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Neutral and Earth wrong way round

ChrisP wrote:

The house has been rewired, I'm just not sure when.


Thinks like a whole house RCD would date it to somewhere early 80's
(like the place we just moved into)

The offending socket has been used fine, including a vaccum cleaner
which i think consume a fair number of watts.


With a TN-S or TN-C-S earth, then it probably would work ok... not good
though!

I've checked a few more sockets and found loose wires where spurs
(sometimes more than one!) have been added. Just looks like a bad DIY
by the previous owners I can rectify myself.


Loose wires are not uncommon on older installs. It would probably be
worth the tedium of taking off every faceplate and tightening as
required and carrying out a visual inspection as you go.



--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #23   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4
Default Neutral and Earth wrong way round


nothing was mentioned on the survey when I purchased the
house (I used the banks full survey option, cost me £1500 and they
were rubbish!). Think it will have to go down to experience!


If you just had a survey - even a full one - a surveyor will carry it
out. They are looking at the structure of the building and the result
usually explicitly says that it is not an electrical survey.

I gave up having electrical surveys after just one as it seemed to be
more concerned with the fact that the house did not fully meet the
_current_ wiring regulations and had some 45 degree cable runs and did
not spot the spur from spur from spur set up in one room. I was more
worried that there might be something dangerous in place.

dan

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
9v shown between live and neutral/earth on mulit-meter David WE Roberts UK diy 11 November 6th 07 12:09 AM
4 gauge neutral wire doesn't fit in my neutral bus panel? sparty Home Repair 8 July 22nd 06 01:50 AM
Musing about wood going round and round. Where it stops nobodyknows! Arch Woodturning 3 April 4th 06 06:50 PM
Earth Connected to Neutral keenbutconfused UK diy 12 June 24th 05 02:11 AM
Earth to Neutral differences Alan UK diy 12 February 3rd 05 06:18 PM


All times are GMT +1. The time now is 08:13 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"