I was recently told when a plumber cut off a dead leg in our gas pipework
that we had a small (but allowable) leak in our system.

Clearly he wasn't wild about chasing the leak but I'd rather there wasn't
one. Before I start hunting, what's the acceptable leak level in mbar/min?

Tim


  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,488
Default Gas leak limit

In an earlier contribution to this discussion,
Tim Downie wrote:

I was recently told when a plumber cut off a dead leg in our gas
pipework that we had a small (but allowable) leak in our system.

Clearly he wasn't wild about chasing the leak but I'd rather there
wasn't one. Before I start hunting, what's the acceptable leak level
in mbar/min?
Tim


I don't know the answer, but is that the only way to measure leaks - in
mbar/min?

If so, surely that makes the max permissible *absolute* leak rate (gms/min,
or whatever) a function of the volume of your pipework. Is that's what's
intended?
--
Cheers,
Roger
______
Email address maintained for newsgroup use only, and not regularly
monitored.. Messages sent to it may not be read for several weeks.
PLEASE REPLY TO NEWSGROUP!


  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,982
Default Gas leak limit

On Tue, 05 Feb 2008 12:33:24 +0000, Tim Downie wrote:

I was recently told when a plumber cut off a dead leg in our gas pipework
that we had a small (but allowable) leak in our system.

Clearly he wasn't wild about chasing the leak but I'd rather there wasn't
one. Before I start hunting, what's the acceptable leak level in mbar/min?


For pipework it's no observable drop, which IIRC is stated somewhere to be
less than 0.25mbar (over 2 minutes test).

If any appliance is connected then it depends on the type (and volume) of
the gas meter, but if your CORGI registered installer is testing that his
pipework is sound he should shut off appliances so that he's testing only
the pipework. If he's canny he'll have tested the installation before he
made any changes in which case if there was a slight but acceptable drop
beforehand *and no smell of gas* and the drop is no greater afterwards he
can probably put it down to appliance drop and leave it like that.

--
John Stumbles

What is a simile like?
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 146
Default Gas leak limit

John Stumbles wrote:
On Tue, 05 Feb 2008 12:33:24 +0000, Tim Downie wrote:

I was recently told when a plumber cut off a dead leg in our gas
pipework that we had a small (but allowable) leak in our system.

Clearly he wasn't wild about chasing the leak but I'd rather there
wasn't one. Before I start hunting, what's the acceptable leak
level in mbar/min?


For pipework it's no observable drop, which IIRC is stated somewhere
to be less than 0.25mbar (over 2 minutes test).

If any appliance is connected then it depends on the type (and
volume) of the gas meter, but if your CORGI registered installer is
testing that his pipework is sound he should shut off appliances so
that he's testing only the pipework.


It wasn't so long ago that a gas fitter came and did the old "sucking of
teeth" bit when he saw our gas cooker didn't have an isolating valve (which
he then fitted).

It took us some time to realise that the odd smell in the kitchen was coming
from the back of the unit where he had fitted the valve, which was leaking.
;-)

Fortunately, it just took a bit of working the valve open & closed a few
times to get it to seal properly but it's made me a wee bit sceptical about
the benefits of all these valves.

If he's canny he'll have tested
the installation before he made any changes in which case if there
was a slight but acceptable drop beforehand *and no smell of gas* and
the drop is no greater afterwards he can probably put it down to
appliance drop and leave it like that.


We don't have a smell of gas (unlike the time another BG engineer who
supposedly had tested our system cocked up) but I've decided to invest in a
manometer to see if I can isolate the leak.

On several occasions, I have heard mention (from plumbers) of a figure
(something like 4mm or 4mbar over some period or other mentioned), hence my
question.

Tim


  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 146
Default Gas leak limit

John Stumbles wrote:
On Tue, 05 Feb 2008 12:33:24 +0000, Tim Downie wrote:

I was recently told when a plumber cut off a dead leg in our gas
pipework that we had a small (but allowable) leak in our system.

Clearly he wasn't wild about chasing the leak but I'd rather there
wasn't one. Before I start hunting, what's the acceptable leak
level in mbar/min?


For pipework it's no observable drop, which IIRC is stated somewhere
to be less than 0.25mbar (over 2 minutes test).


Just tested the system "appliances isolated" and the good news is that
there's no drop. Still no drop with CH boiler connected. A small drop
(0.5mbar over 2 minutes) with the cooker & tumble dryer connected.

I rather suspect that these bayonet connections account for most of the
leak.

With that pressure drop (& no smell of gas) should I stop worrying?

Tim




  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 22
Default Gas leak limit

On Tue, 5 Feb 2008 13:41:30 -0000, "Tim Downie"
wrote:

John Stumbles wrote:
On Tue, 05 Feb 2008 12:33:24 +0000, Tim Downie wrote:

I was recently told when a plumber cut off a dead leg in our gas
pipework that we had a small (but allowable) leak in our system.

Clearly he wasn't wild about chasing the leak but I'd rather there
wasn't one. Before I start hunting, what's the acceptable leak
level in mbar/min?


For pipework it's no observable drop, which IIRC is stated somewhere
to be less than 0.25mbar (over 2 minutes test).


Just tested the system "appliances isolated" and the good news is that
there's no drop. Still no drop with CH boiler connected. A small drop
(0.5mbar over 2 minutes) with the cooker & tumble dryer connected.



A gas tumble dryer ??
  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,231
Default Gas leak limit

On Tue, 05 Feb 2008 12:49:28 +0000, Roger Mills wrote:

In an earlier contribution to this discussion, Tim Downie
wrote:

I was recently told when a plumber cut off a dead leg in our gas
pipework that we had a small (but allowable) leak in our system.

Clearly he wasn't wild about chasing the leak but I'd rather there
wasn't one. Before I start hunting, what's the acceptable leak level
in mbar/min?
Tim


I don't know the answer, but is that the only way to measure leaks - in
mbar/min?

If so, surely that makes the max permissible *absolute* leak rate
(gms/min, or whatever) a function of the volume of your pipework. Is
that's what's intended?


Since the volume of the pipework+meter is to a first approximation is
similar for all ordinary domestic installations, then the pressure drop
and time equates to roughly similar amount of gas leakage.

If you reckoned that the volume of the pipe+meter is about 10 litres then
4 mbar/2min is about 20cm^3 per min. That's about about 1/2 an egg cup
per min, MAXIMUM when the old appliances are connected and there is NO
SMELL of gas.

If you have a smaller electronic meter (E6 type) or heavy domestic/light
commercial (R5) type then the times and pressures are different.

On large domestic installations and above then calculations are required
to work out the permitted leakage limits.

THE PERMITTED LEAKAGE FOR PIPEWORK (new or old) IS ZERO. I.e. less than
0.25mbar/2min on a normal installation. That's less than 1cm^3 per min.


--
Ed Sirett - Property maintainer and registered gas fitter.
The FAQ for uk.diy is at http://www.diyfaq.org.uk
Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html
Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html
Choosing a Boiler FAQ http://www.makewrite.demon.co.uk/BoilerChoice.html

  #11   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,194
Default Gas leak limit

The message
from "Tim Downie" contains these words:

We don't have a smell of gas (unlike the time another BG engineer who
supposedly had tested our system cocked up) but I've decided to invest in a
manometer to see if I can isolate the leak.


What sort and where from?

I am currently on the lookout for a cheap manometer but so far all I
have found are expensive digital types.

Having written the above I thought I had better do another more specific
search and while I found a number of U tube manometers some were
expensive and it was by no means clear that the cheaper ones could be
used to check for gas soundness.

Any pointers would be appreciated (and no I don't want to make one from
scratch).

--
Roger Chapman
  #12   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,988
Default Gas leak limit

On Tue, 5 Feb 2008 16:27:25 GMT, Roger
wrote:

The message
from "Tim Downie" contains these words:

We don't have a smell of gas (unlike the time another BG engineer who
supposedly had tested our system cocked up) but I've decided to invest in a
manometer to see if I can isolate the leak.


What sort and where from?

I am currently on the lookout for a cheap manometer but so far all I
have found are expensive digital types.

Having written the above I thought I had better do another more specific
search and while I found a number of U tube manometers some were
expensive and it was by no means clear that the cheaper ones could be
used to check for gas soundness.

Any pointers would be appreciated (and no I don't want to make one from
scratch).


B&Q - about 15 quid.

--
Frank Erskine
  #13   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 146
Default Gas leak limit

Roger wrote:
The message
from "Tim Downie" contains these
words:

We don't have a smell of gas (unlike the time another BG engineer
who supposedly had tested our system cocked up) but I've decided to
invest in a manometer to see if I can isolate the leak.


What sort and where from?


A Monument one like this one.

http://www.amazon.co.uk/gp/product/B...F8&me=&seller=

I got mine in B&Q (same price) but if you get one there, make very sure that
the rubber connecting tube in in the pack with it. Two out of the three in
stock in my local store were missing their tubes. (Light fingered plumbers I
guess).

Tim


  #14   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 146
Default Gas leak limit

Ed Sirett wrote:

THE PERMITTED LEAKAGE FOR PIPEWORK (new or old) IS ZERO. I.e. less
than
0.25mbar/2min on a normal installation.


So 0.24mbar/2min is okay? ;-)

As it happens, my pipework seems fine and since redoing my dryer connection,
my "appliance leak" seems to have gone too.

Thanks for the info.

Tim


  #15   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,488
Default Gas leak limit

In an earlier contribution to this discussion,
Roger wrote:


I am currently on the lookout for a cheap manometer but so far all I
have found are expensive digital types.

Any pointers would be appreciated (and no I don't want to make one
from scratch).


Why ever not? This *is* uk-d-i-y!

I made one years ago by bending some clear plastic tube into e U shape, and
fixing it onto a piece of floorboard, with a sheet of graph paper behind it.
I think I've still got it somehere!
--
Cheers,
Roger
______
Email address maintained for newsgroup use only, and not regularly
monitored.. Messages sent to it may not be read for several weeks.
PLEASE REPLY TO NEWSGROUP!




  #16   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 6,766
Default Gas leak limit

It happens that Roger formulated :
The message
from "Tim Downie" contains these words:

We don't have a smell of gas (unlike the time another BG engineer who
supposedly had tested our system cocked up) but I've decided to invest in a
manometer to see if I can isolate the leak.


What sort and where from?

I am currently on the lookout for a cheap manometer but so far all I
have found are expensive digital types.

Having written the above I thought I had better do another more specific
search and while I found a number of U tube manometers some were
expensive and it was by no means clear that the cheaper ones could be
used to check for gas soundness.

Any pointers would be appreciated (and no I don't want to make one from
scratch).


You only need a bit of clear plastic tube formed into a U shape,
clipped to a bit of wood and filled with water.

--
Regards,
Harry (M1BYT) (L)
http://www.ukradioamateur.co.uk


  #17   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,194
Default Gas leak limit

The message
from "Tim Downie" contains these words:

What sort and where from?


A Monument one like this one.


http://www.amazon.co.uk/gp/product/B...F8&me=&seller=


30 mbar.

I got mine in B&Q (same price) but if you get one there, make very
sure that
the rubber connecting tube in in the pack with it. Two out of the three in
stock in my local store were missing their tubes. (Light fingered
plumbers I
guess).


Thanks Tim and Frank.

I think I must be going senile. I had managed to get it into my head
that the domestic gas pressure was 80 mbar, not 20 mbar.

--
Roger Chapman
  #18   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,194
Default Gas leak limit

The message
from "Roger Mills" contains these words:

Any pointers would be appreciated (and no I don't want to make one
from scratch).


Why ever not? This *is* uk-d-i-y!


Because I have too many other tuits of the round sort and if I have to
go shopping for the tubing I might just as well get the finished
article.

--
Roger Chapman
  #19   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,982
Default Gas leak limit

On Tue, 05 Feb 2008 16:27:25 +0000, Roger wrote:

I am currently on the lookout for a cheap manometer but so far all I
have found are expensive digital types.

Having written the above I thought I had better do another more specific
search and while I found a number of U tube manometers some were
expensive and it was by no means clear that the cheaper ones could be
used to check for gas soundness.


You really only need a length of winemaking tube folded into a U shape
taped alongside a ruler. 1" is one inch water gauge: 30' of water is 1
bar: the rest is arithmetic.

Any pointers would be appreciated (and no I don't want to make one from
scratch).


OK then, BES do a U-tube type for about a tenner (pipe not included: they
do black rubber pipe for NG separately). It's useful to find a bit of
larger diameter pipe whick fits snugly over the non-manometer end of the
tube to fit onto meter test nipples which are too big to get the regular
diameter tube over. I've got a very nice bit which was once the boot that
went over the spark plug from an ignition lead.

While you're ordering from BES get some of their flourescent dye to put in
the water in the u-tube. Or you can use a minute dab of food colour,
though prolonged use is likely to leave a precipitate on the inside of the
tube making it harder to read.


I gather there's a website somewhere all about u-tubes. :^|

--
John Stumbles

A: Because it messes up the order in which people read text.
Q: Why is top-posting a bad thing?
  #21   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,369
Default Gas leak limit



"Tim Downie" wrote in message
...
I was recently told when a plumber cut off a dead leg in our gas pipework
that we had a small (but allowable) leak in our system.

Clearly he wasn't wild about chasing the leak but I'd rather there wasn't
one. Before I start hunting, what's the acceptable leak level in
mbar/min?


Zero!
Unless you know the gas is being vented to the outside air how do you know
it will not go *BANG*?
It may take weeks or months to build to an explosive mixture but how do you
know it hasn't?

  #22   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,369
Default Gas leak limit



"Roger" wrote in message
k...
The message
from "Tim Downie" contains these words:

We don't have a smell of gas (unlike the time another BG engineer who
supposedly had tested our system cocked up) but I've decided to invest in
a
manometer to see if I can isolate the leak.


What sort and where from?

I am currently on the lookout for a cheap manometer but so far all I
have found are expensive digital types.

Having written the above I thought I had better do another more specific
search and while I found a number of U tube manometers some were
expensive and it was by no means clear that the cheaper ones could be
used to check for gas soundness.

Any pointers would be appreciated (and no I don't want to make one from
scratch).


A piece of wood, some staples and a plastic tube too DIY? ;-)

  #23   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 418
Default Gas leak limit


"dennis@home" wrote in message
...


"Tim Downie" wrote in message
...
I was recently told when a plumber cut off a dead leg in our gas pipework
that we had a small (but allowable) leak in our system.

Clearly he wasn't wild about chasing the leak but I'd rather there wasn't
one. Before I start hunting, what's the acceptable leak level in
mbar/min?


Zero!


No such thing as zero. That would mean waiting infinitely long to prove
that there was no leak.

Unless you know the gas is being vented to the outside air how do you know
it will not go *BANG*?


Funnily enough, I have a nose. It's proved a lot more reliable than BG gas
fitter's testing proceedures.

It may take weeks or months to build to an explosive mixture but how do
you know it hasn't?


If we were talking about LPG, I would worry more but natural gas has a lower
density than air, so it's less inclined to lurk.

Tim


  #24   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,231
Default Gas leak limit

On Tue, 05 Feb 2008 17:23:27 +0000, Tim Downie wrote:

Ed Sirett wrote:

THE PERMITTED LEAKAGE FOR PIPEWORK (new or old) IS ZERO. I.e. less than
0.25mbar/2min on a normal installation.


So 0.24mbar/2min is okay? ;-)

As it happens, my pipework seems fine and since redoing my dryer
connection, my "appliance leak" seems to have gone too.

Thanks for the info.

Tim


The 0.25 mbar is a way of saying no detectable drop.
You could probably observe a smaller drop than that, but even holding the
gas pipe with a warm hand can put 0.5 mbar or more onto the gauge.

When using an electronic manometer they are very very sensitive and the
last digit is 0.01 mbar i.e. Pascals i.e next to nothing. The digits will
move around all the while when testing.

--
Ed Sirett - Property maintainer and registered gas fitter.
The FAQ for uk.diy is at http://www.diyfaq.org.uk
Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html
Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html
Choosing a Boiler FAQ http://www.makewrite.demon.co.uk/BoilerChoice.html

  #25   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,369
Default Gas leak limit



"Tim Downie" wrote in message
...

"dennis@home" wrote in message
...


"Tim Downie" wrote in message
...
I was recently told when a plumber cut off a dead leg in our gas
pipework that we had a small (but allowable) leak in our system.

Clearly he wasn't wild about chasing the leak but I'd rather there
wasn't one. Before I start hunting, what's the acceptable leak level in
mbar/min?


Zero!


No such thing as zero. That would mean waiting infinitely long to prove
that there was no leak.

Unless you know the gas is being vented to the outside air how do you
know it will not go *BANG*?


Funnily enough, I have a nose. It's proved a lot more reliable than BG
gas fitter's testing proceedures.


Well there is your first error.. to smell it means it has to be escaping
into the room, what about the roof/floor/wall spaces where you don't stick
your nose.


It may take weeks or months to build to an explosive mixture but how do
you know it hasn't?


If we were talking about LPG, I would worry more but natural gas has a
lower density than air, so it's less inclined to lurk.


Checked your roof space recently? ;-)

LPG is very dangerous on boats as they tend to be gas tight and there have
been some very big bangs.
Like I said any leak is dangerous unless you know where it is going.





  #26   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 369
Default Gas leak limit

In message , "dennis@home"
writes
If we were talking about LPG, I would worry more but natural gas has
a lower density than air, so it's less inclined to lurk.


Checked your roof space recently? ;-)

LPG is very dangerous on boats as they tend to be gas tight and there
have been some very big bangs.


We were holidaying on a boat on the Norfolk Broads a few years back when
the cooker stopped working. Boatyard sent someone out to fix it and we
carried on... until I realised the inside was increasingly smelling of
rotten cabbage. Very fast mooring and evacuation followed. The boatyard
offered us compensation without us asking.

--
Si
  #27   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 146
Default Gas leak limit

dennis@home wrote:
"Tim Downie" wrote in message
...

"dennis@home" wrote in message
...


"Tim Downie" wrote in message
...
I was recently told when a plumber cut off a dead leg in our gas
pipework that we had a small (but allowable) leak in our system.

Clearly he wasn't wild about chasing the leak but I'd rather
there wasn't one. Before I start hunting, what's the
acceptable leak level in mbar/min?

Zero!


No such thing as zero. That would mean waiting infinitely long to
prove that there was no leak.

Unless you know the gas is being vented to the outside air how do
you know it will not go *BANG*?


Funnily enough, I have a nose. It's proved a lot more reliable
than BG gas fitter's testing proceedures.


Well there is your first error.. to smell it means it has to be
escaping into the room, what about the roof/floor/wall spaces where
you don't stick your nose.


Actually, I *do* stick my nose under the floor and into the loft. Haven't
got any joints in my wall cavities.

It may take weeks or months to build to an explosive mixture but
how do you know it hasn't?


If we were talking about LPG, I would worry more but natural gas
has a lower density than air, so it's less inclined to lurk.


Checked your roof space recently? ;-)


See above.


LPG is very dangerous on boats as they tend to be gas tight and there
have been some very big bangs.


Why are you telling me something I already know? I'm trying to make the
point that a lighter than air gas is most unlikely to "take weeks or months"
to build to an explosive mixture in a typically ventilated house. I'll
wager that every gas induced house explosion with natural gas has been due
to an accummulation *much* faster than "weeks or months".

Like I said any leak is dangerous unless you know where it is going.


Leak tested your own pipework and appliances lately? Or do you trust
someone who's in a hurry and *doesn't* live in the same property as he/she
is testing?

Tim


  #28   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,194
Default Gas leak limit

The message
from "dennis@home" contains these words:

Any pointers would be appreciated (and no I don't want to make one from
scratch).


A piece of wood, some staples and a plastic tube too DIY? ;-)


Life is too short to do everything.

--
Roger Chapman
  #29   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 369
Default Gas leak limit

In message , Huge
writes
On 2008-02-06, Si $3o&m wrote:

We were holidaying on a boat on the Norfolk Broads a few years back when
the cooker stopped working. Boatyard sent someone out to fix it and we
carried on... until I realised the inside was increasingly smelling of
rotten cabbage.


Yes, but Norfolk smnells like that.

This was definitely not NfN

--
Si
  #30   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 418
Default Gas leak limit


"Si" $3o&m wrote in message
...
In message , "dennis@home"
writes
If we were talking about LPG, I would worry more but natural gas has a
lower density than air, so it's less inclined to lurk.


Checked your roof space recently? ;-)

LPG is very dangerous on boats as they tend to be gas tight and there have
been some very big bangs.


We were holidaying on a boat on the Norfolk Broads a few years back when
the cooker stopped working. Boatyard sent someone out to fix it and we
carried on... until I realised the inside was increasingly smelling of
rotten cabbage. Very fast mooring and evacuation followed. The boatyard
offered us compensation without us asking.


Serious question, why can't you get bottled natural gas specifically for use
on boats? Given that boat makers can't use the ideal solution (i.e. drill
holes in the bottom to let the gas out), it would seem immensely sensible to
use a lighter than air gas on board boats.

Tim

--
Si





  #31   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,982
Default Gas leak limit

On Thu, 07 Feb 2008 17:11:09 +0000, Tim Downie wrote:

Serious question, why can't you get bottled natural gas specifically for
use on boats? Given that boat makers can't use the ideal solution (i.e.
drill holes in the bottom to let the gas out), it would seem immensely
sensible to use a lighter than air gas on board boats.


Because natural gas can't be liquefied (at room temps & acheivable
pressures)

--
John Stumbles

87.5% of statistics are made up
  #32   Report Post  
Posted to uk.d-i-y
Rod Rod is offline
external usenet poster
 
Posts: 2,892
Default Gas leak limit

Tim Downie wrote:
snip
Serious question, why can't you get bottled natural gas specifically for use
on boats? Given that boat makers can't use the ideal solution (i.e. drill
holes in the bottom to let the gas out), it would seem immensely sensible to
use a lighter than air gas on board boats.

Didn't I hear that the Hindenburg started out as a boat... ??

--
Rod
  #33   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 146
Default Gas leak limit

John Stumbles wrote:
On Thu, 07 Feb 2008 17:11:09 +0000, Tim Downie wrote:

Serious question, why can't you get bottled natural gas
specifically for use on boats? Given that boat makers can't use
the ideal solution (i.e. drill holes in the bottom to let the gas
out), it would seem immensely sensible to use a lighter than air
gas on board boats.


Because natural gas can't be liquefied (at room temps & acheivable
pressures)


Darn! Knew there had to be a good reason. ;-)

Tim


  #34   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,369
Default Gas leak limit



"Rod" wrote in message
...
Tim Downie wrote:
snip
Serious question, why can't you get bottled natural gas specifically for
use on boats? Given that boat makers can't use the ideal solution (i.e.
drill holes in the bottom to let the gas out), it would seem immensely
sensible to use a lighter than air gas on board boats.

Didn't I hear that the Hindenburg started out as a boat... ??


It was a ship!

  #35   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,982
Default Gas leak limit

On Thu, 07 Feb 2008 18:05:41 +0000, Tim Downie wrote:

Because natural gas can't be liquefied (at room temps & acheivable
pressures)


Darn! Knew there had to be a good reason. ;-)


Actually it can be stored compressed, but it need sto be in the sort of
bottles used for other compressed gases such as oxygen, nitrogen, CO2 etc.
If you've come across these in a welding shop, science lab or hospital etc
you'll know they are firkling *heavy*. However I recall seeing cars fitted
with compressed methane bottles on roofracks in Ancona, Italy, in 1977. It
was some sort of renewable scheme. Evidently didn't catch on.

--
John Stumbles

Pessimists are never disappointed
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Bag Limit ValveJob Home Repair 19 July 1st 07 07:09 PM
gas hot water heater age limit Trail Blazer Home Repair 8 March 27th 07 11:12 AM
My Current Limit -Getting a Handle on It George Woodturning 9 February 5th 06 12:28 AM
Small limit MCBs. Ian Stirling UK diy 2 August 5th 05 10:06 PM
32gig limit hash Electronics Repair 7 February 8th 05 04:45 AM


All times are GMT +1. The time now is 03:37 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"