Default Vokera Excell 80 SP - No Hot Water

Hi,

My Vokera Excell 80 SP boiler will heat the radiators, but it doesn't
seem to know when the taps are switched on, as such the hot water
doesn't work.

I have checked the pressure, and it's about 1.5bar.

Can anyone suggest how I might troubleshoot the problem further?

Thanks,

Kenny

  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,703
Default Vokera Excell 80 SP - No Hot Water

In article .com,
writes
Hi,

My Vokera Excell 80 SP boiler will heat the radiators, but it doesn't
seem to know when the taps are switched on, as such the hot water
doesn't work.

I have checked the pressure, and it's about 1.5bar.

Can anyone suggest how I might troubleshoot the problem further?

This boiler gets mentions here quite a lot so you could do worse than
doing a google groups search for it.

The installer manual for it has good fault finding flows and is available from
http://www.vokera.co.uk/ (needs flash), head for Installer Product Info
Discontinued Products. Reading this will let you know what bits are where
and guide you through a fault finding session.

The flow switch would be a prime candidate and easy to check, disconnect
power, turn on tap and check for operation of the switch using a multimeter
on ohms/continuity. Next best is probably the diverter valve, check back at
previous posts as this is mentioned there. Finally, the soldered joints on
the pcb for the H/W (and C/H) temp control are prone to failure, an easy
job to re-make them if you can solder but leave that option til last (if
wiggling the spindle causes a momentary spring back into life then this is
a good bet).

This is a pretty simple boiler so is a good candidate diy but watch out for
live parts and don't touch gas carrying parts unless you are competent.

Oh, also see the Gas-News forums:
http://www.gas-news.co.uk/discus/mes...tml?1124134482
They are pretty trade oriented so may be less likely to help an amateur but
there is a lot of useful existing content.

Good luck.
--
fred
Plusnet - I hope you like vanilla
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,285
Default Vokera Excell 80 SP - No Hot Water

fred wrote:

This boiler gets mentions here quite a lot


I've come to know the 80SP quite well over the last few months...

The flow switch would be a prime candidate and easy to check, disconnect
power, turn on tap and check for operation of the switch using a multimeter
on ohms/continuity. Next best is probably the diverter valve,


In this design secondary water flow is sensed hydraulically by pressure
difference across a diaphragm (the "domestic diaphragm") which moves a
push-pin which operates a pivoted arm (the fulcrum arm) which in turn
operates the diverter valve mechanically. When the arm has reached full
travel a microswitch ("domestic microswitch") which initiates the firing
sequence.

Firstly check that the arm is moving full-travel when secondary water is
flowing - full-travel being far enough to operate the microswitch. If
not, I'll lay a penny to a pound that the problem is a knackered
domestic diaphragm (Vokera part no. 6882, GC no. 301-180). Replacement
is an easy job.

If the arm moves OK and the boiler isn't firing I'd look at the domestic
microswitch next - this is easily isolated and can be safely tested with
a multimeter with the boiler powered down, since operation of the arm
does not depend on a supply of electricity.

--
Andy
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,285
Default Vokera Excell 80 SP - No Hot Water

I wrote:

When the arm has reached full travel a microswitch ("domestic
microswitch") which initiates the firing sequence.


I'm sorry, I'll write that again:

When the arm has reached full travel it also operates a microswitch (the
"domestic microswitch") which initiates [etc.]

--
Andy
  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,703
Default Vokera Excell 80 SP - No Hot Water

In article , Andy Wade
writes
fred wrote:

This boiler gets mentions here quite a lot


I've come to know the 80SP quite well over the last few months...

The flow switch would be a prime candidate and easy to check, disconnect
power, turn on tap and check for operation of the switch using a multimeter
on ohms/continuity. Next best is probably the diverter valve,


In this design secondary water flow is sensed hydraulically by pressure
difference across a diaphragm (the "domestic diaphragm") which moves a
push-pin which operates a pivoted arm (the fulcrum arm) which in turn
operates the diverter valve mechanically. When the arm has reached full
travel a microswitch ("domestic microswitch") which initiates the firing
sequence.

Firstly check that the arm is moving full-travel when secondary water is
flowing - full-travel being far enough to operate the microswitch. If
not, I'll lay a penny to a pound that the problem is a knackered
domestic diaphragm (Vokera part no. 6882, GC no. 301-180). Replacement
is an easy job.

If the arm moves OK and the boiler isn't firing I'd look at the domestic
microswitch next - this is easily isolated and can be safely tested with
a multimeter with the boiler powered down, since operation of the arm
does not depend on a supply of electricity.

Thanks for the details Andy, the one I look after has just developed the
same fault, H/W only when C/H is already on, I'll make sure I have the
diaphragm when I get round to looking at it.
--
fred
Plusnet - I hope you like vanilla


  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,285
Default Vokera Excell 80 SP - No Hot Water

fred wrote:

Thanks for the details Andy, the one I look after has just developed the
same fault, H/W only when C/H is already on, I'll make sure I have the
diaphragm when I get round to looking at it.


You get those symptoms when the diaphragm starts to fail; the arm moves
enough to give partial operation of the diverter valve, but not enough
to activate the DHW microswitch. IME it deteriorates rapidly after that
and you'll soon have no HW at all, even if the burner is already firing
for CH.

--
Andy
  #7   Report Post  
Junior Member
 
Posts: 2
Default

Quote:
Originally Posted by Andy Wade View Post
fred wrote:

Thanks for the details Andy, the one I look after has just developed the
same fault, H/W only when C/H is already on, I'll make sure I have the
diaphragm when I get round to looking at it.


You get those symptoms when the diaphragm starts to fail; the arm moves
enough to give partial operation of the diverter valve, but not enough
to activate the DHW microswitch. IME it deteriorates rapidly after that
and you'll soon have no HW at all, even if the burner is already firing
for CH.

--
Andy
Hi - I'm a newbie but this is exactly the problem I've got. when I pull the diverter valve manually with enough force, it reaches the microswitch. But when I just allow the hot water to do it, the pin from the diaphragm doesn't seem strong enough to overcome the natural resistance to push the fulcrum hard enough to reach the microswitch. I don't know if the natural resistance is too high, or the diaphragm is knackered and doesn't push hard enough. I've ordered a new diaphragm from ebay for 4 quid - how do I replace it? THere's no instructions in the service manual. Do I have to drain the water first? I hoped it would only be domestic hot water running through that diaphragm because it's after the diverter valve isn't it? So I'm hoping I can replace it and just not turn on the hot water till I'm done! From the diagram I imagine I have to undo the 6 screws and just replace the rubber disk. Is that right?

THanks!!!!!!!!!!!!!
  #8   Report Post  
Junior Member
 
Posts: 2
Default

Quote:
Originally Posted by Vizzage View Post
Hi - I'm a newbie but this is exactly the problem I've got. when I pull the diverter valve manually with enough force, it reaches the microswitch. But when I just allow the hot water to do it, the pin from the diaphragm doesn't seem strong enough to overcome the natural resistance to push the fulcrum hard enough to reach the microswitch. I don't know if the natural resistance is too high, or the diaphragm is knackered and doesn't push hard enough. I've ordered a new diaphragm from ebay for 4 quid - how do I replace it? THere's no instructions in the service manual. Do I have to drain the water first? I hoped it would only be domestic hot water running through that diaphragm because it's after the diverter valve isn't it? So I'm hoping I can replace it and just not turn on the hot water till I'm done! From the diagram I imagine I have to undo the 6 screws and just replace the rubber disk. Is that right?

THanks!!!!!!!!!!!!!
Anyone? :-)
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Vokera Excell 80SP Andy Wade UK diy 7 February 12th 07 10:01 AM
vokera excell 80 sp smartrad UK diy 0 January 23rd 06 06:57 PM
Vokera Excell 80 SP boiler. Neil UK diy 1 November 25th 05 07:07 PM
Vokera Excell boiler problem Starling UK diy 2 December 31st 04 06:44 PM
Vokera Excell problem Starling UK diy 1 December 31st 04 01:58 PM


All times are GMT +1. The time now is 08:45 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"