curiousdog February 8th 07 04:23 PM

Heating pump challenges
 
I have what I think is a conventional heating system (perhaps, maybe)
and have had several challenges over the years, must to do with the
motorised flow-control valve breaking.

More recently I have a concern with the pump. It's installed
vertically pushing against gravrity up to the valve where it splits to
the heating and the storage tank. On setting 1 it runs very quietly
but the pressure seems to be very low and the radiators don't really
heat up as they should. The water in the storage tank also takes
forever to re-heat. I am pretty sure there are no airlocks anywhere.

So, logically, I tried to set the pump speed to 2. The pump speed
picks up and makes a lot more noise and then stops and restarts
itself. There also seems to be a lot more noise in the pipes, water
sounds. But the end result of all this is a lot of air that I have to
keep\bleeding out every 15 minutes.

So, is the pump faulty?

Should it be installed vertically pushing against gravity?

There is only a 4" run of pipiong between the pump and the valve.
Could this be a problem?

thanks for any assistance/advice anyone can offer


Roger Mills February 8th 07 05:04 PM

Heating pump challenges
 
In an earlier contribution to this discussion,
curiousdog wrote:

I have what I think is a conventional heating system (perhaps, maybe)
and have had several challenges over the years, must to do with the
motorised flow-control valve breaking.

More recently I have a concern with the pump. It's installed
vertically pushing against gravrity up to the valve where it splits to
the heating and the storage tank. On setting 1 it runs very quietly
but the pressure seems to be very low and the radiators don't really
heat up as they should. The water in the storage tank also takes
forever to re-heat. I am pretty sure there are no airlocks anywhere.

So, logically, I tried to set the pump speed to 2. The pump speed
picks up and makes a lot more noise and then stops and restarts
itself. There also seems to be a lot more noise in the pipes, water
sounds. But the end result of all this is a lot of air that I have to
keep\bleeding out every 15 minutes.

So, is the pump faulty?


I doubt it.


Should it be installed vertically pushing against gravity?


Yes, that's fine!


There is only a 4" run of pipiong between the pump and the valve.
Could this be a problem?


No, that's fine!


thanks for any assistance/advice anyone can offer


Is it an open vented system (with a small fill & expansion tank in the
attic)? If so, it's very likely that the higher pump speed is causing it to
'pump over'. This means that, when the pump is running, there is a constant
flow of water out of the up and over vent pipe back into the tank. This is
very bad, and will result in a lot of air being introduced into the system.
It usually results from the vent and fill pipes not being connected into the
system in the right way, and is likely to need some pipework changes to
fix - or conversion to a non-vented (pressurised) system if your boiler is
suitable.
--
Cheers,
Roger
______
Email address maintained for newsgroup use only, and not regularly
monitored.. Messages sent to it may not be read for several weeks.
PLEASE REPLY TO NEWSGROUP!



Ed Sirett February 8th 07 08:14 PM

Heating pump challenges
 
On Thu, 08 Feb 2007 17:04:26 +0000, Roger Mills wrote:

In an earlier contribution to this discussion,
curiousdog wrote:

I have what I think is a conventional heating system (perhaps, maybe)
and have had several challenges over the years, must to do with the
motorised flow-control valve breaking.

More recently I have a concern with the pump. It's installed
vertically pushing against gravrity up to the valve where it splits to
the heating and the storage tank. On setting 1 it runs very quietly
but the pressure seems to be very low and the radiators don't really
heat up as they should. The water in the storage tank also takes
forever to re-heat. I am pretty sure there are no airlocks anywhere.

So, logically, I tried to set the pump speed to 2. The pump speed
picks up and makes a lot more noise and then stops and restarts
itself. There also seems to be a lot more noise in the pipes, water
sounds. But the end result of all this is a lot of air that I have to
keep\bleeding out every 15 minutes.

So, is the pump faulty?


I doubt it.


Should it be installed vertically pushing against gravity?


Yes, that's fine!


There is only a 4" run of pipiong between the pump and the valve.
Could this be a problem?


No, that's fine!


thanks for any assistance/advice anyone can offer


Is it an open vented system (with a small fill & expansion tank in the
attic)? If so, it's very likely that the higher pump speed is causing it to
'pump over'. This means that, when the pump is running, there is a constant
flow of water out of the up and over vent pipe back into the tank. This is
very bad, and will result in a lot of air being introduced into the system.
It usually results from the vent and fill pipes not being connected into the
system in the right way, and is likely to need some pipework changes to
fix - or conversion to a non-vented (pressurised) system if your boiler is
suitable.



Just as likely is that thew higher speed is causing air to drawn down into
the circuit.

Unless the positioned of the vent and feed pipes are known relative to the
pump we can only speculate.


--
Ed Sirett - Property maintainer and registered gas fitter.
The FAQ for uk.diy is at http://www.diyfaq.org.uk
Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html
Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html
Choosing a Boiler FAQ http://www.makewrite.demon.co.uk/BoilerChoice.html
Gas Fitting Standards Docs he http://www.makewrite.demon.co.uk/GasFittingStandards

John February 9th 07 11:56 AM

Heating pump challenges
 

"Ed Sirett" wrote in message
...
On Thu, 08 Feb 2007 17:04:26 +0000, Roger Mills wrote:

In an earlier contribution to this discussion,
curiousdog wrote:

I have what I think is a conventional heating system (perhaps, maybe)
and have had several challenges over the years, must to do with the
motorised flow-control valve breaking.

More recently I have a concern with the pump. It's installed
vertically pushing against gravrity up to the valve where it splits to
the heating and the storage tank. On setting 1 it runs very quietly
but the pressure seems to be very low and the radiators don't really
heat up as they should. The water in the storage tank also takes
forever to re-heat. I am pretty sure there are no airlocks anywhere.

So, logically, I tried to set the pump speed to 2. The pump speed
picks up and makes a lot more noise and then stops and restarts
itself. There also seems to be a lot more noise in the pipes, water
sounds. But the end result of all this is a lot of air that I have to
keep\bleeding out every 15 minutes.

So, is the pump faulty?


I doubt it.


Should it be installed vertically pushing against gravity?



Mindset change required - consider it to be a "Circulator" rather than a
pump. The heating circuit is a loop - the "circulator is merely making the
water flow around the circuit. The height of the system has no effect.




Bob Mannix February 9th 07 12:03 PM

Heating pump challenges
 

"John" wrote in message
...

"Ed Sirett" wrote in message
...
On Thu, 08 Feb 2007 17:04:26 +0000, Roger Mills wrote:

In an earlier contribution to this discussion,
curiousdog wrote:

I have what I think is a conventional heating system (perhaps, maybe)
and have had several challenges over the years, must to do with the
motorised flow-control valve breaking.

More recently I have a concern with the pump. It's installed
vertically pushing against gravrity up to the valve where it splits to
the heating and the storage tank. On setting 1 it runs very quietly
but the pressure seems to be very low and the radiators don't really
heat up as they should. The water in the storage tank also takes
forever to re-heat. I am pretty sure there are no airlocks anywhere.

So, logically, I tried to set the pump speed to 2. The pump speed
picks up and makes a lot more noise and then stops and restarts
itself. There also seems to be a lot more noise in the pipes, water
sounds. But the end result of all this is a lot of air that I have to
keep\bleeding out every 15 minutes.

So, is the pump faulty?

I doubt it.


Should it be installed vertically pushing against gravity?



Mindset change required - consider it to be a "Circulator" rather than a
pump. The heating circuit is a loop - the "circulator is merely making the
water flow around the circuit. The height of the system has no effect.


Yes to that but [and see other thread on Bubbling Central Heating System] it
could be an incorrectly installed vent pipe. On setting 1 the negative
presssure at an incorrectly installed vent pipe position is not enough to
suck air down. On setting 2 it is. Not saying this IS the problem, but it
might be.


--
Bob Mannix
(anti-spam is as easy as 1-2-3 - not)



Ed Sirett February 9th 07 07:54 PM

Heating pump challenges
 
On Fri, 09 Feb 2007 11:56:10 +0000, John wrote:

"Ed Sirett" wrote in message
...
On Thu, 08 Feb 2007 17:04:26 +0000, Roger Mills wrote:

In an earlier contribution to this discussion,
curiousdog wrote:

I have what I think is a conventional heating system (perhaps, maybe)
and have had several challenges over the years, must to do with the
motorised flow-control valve breaking.

More recently I have a concern with the pump. It's installed
vertically pushing against gravrity up to the valve where it splits to
the heating and the storage tank. On setting 1 it runs very quietly
but the pressure seems to be very low and the radiators don't really
heat up as they should. The water in the storage tank also takes
forever to re-heat. I am pretty sure there are no airlocks anywhere.

So, logically, I tried to set the pump speed to 2. The pump speed
picks up and makes a lot more noise and then stops and restarts
itself. There also seems to be a lot more noise in the pipes, water
sounds. But the end result of all this is a lot of air that I have to
keep\bleeding out every 15 minutes.

So, is the pump faulty?

I doubt it.


Should it be installed vertically pushing against gravity?



Mindset change required - consider it to be a "Circulator" rather than a
pump. The heating circuit is a loop - the "circulator is merely making the
water flow around the circuit. The height of the system has no effect.


I disagree, at least in the way you have expressed it.
Where the feed pipe joins the circuit, the height of the header tank and
the position of the circulator within the circuit are absolutely crucial
to the correct operation or otherwise of the heating system.

Last week my apprentice and I fixed a system where the feed pipe had been
installed after the pump. We moved it to the right place but also had to
spend half a day powerflushing the system to remove (most of) the effects
of the misplaced pipe.


--
Ed Sirett - Property maintainer and registered gas fitter.
The FAQ for uk.diy is at http://www.diyfaq.org.uk
Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html
Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html
Choosing a Boiler FAQ http://www.makewrite.demon.co.uk/BoilerChoice.html
Gas Fitting Standards Docs he http://www.makewrite.demon.co.uk/GasFittingStandards

John February 10th 07 04:17 PM

Heating pump challenges
 

"Ed Sirett" wrote in message
...
On Fri, 09 Feb 2007 11:56:10 +0000, John wrote:

"Ed Sirett" wrote in message
...
On Thu, 08 Feb 2007 17:04:26 +0000, Roger Mills wrote:

In an earlier contribution to this discussion,
curiousdog wrote:

I have what I think is a conventional heating system (perhaps, maybe)
and have had several challenges over the years, must to do with the
motorised flow-control valve breaking.

More recently I have a concern with the pump. It's installed
vertically pushing against gravrity up to the valve where it splits to
the heating and the storage tank. On setting 1 it runs very quietly
but the pressure seems to be very low and the radiators don't really
heat up as they should. The water in the storage tank also takes
forever to re-heat. I am pretty sure there are no airlocks anywhere.

So, logically, I tried to set the pump speed to 2. The pump speed
picks up and makes a lot more noise and then stops and restarts
itself. There also seems to be a lot more noise in the pipes, water
sounds. But the end result of all this is a lot of air that I have to
keep\bleeding out every 15 minutes.

So, is the pump faulty?

I doubt it.


Should it be installed vertically pushing against gravity?



Mindset change required - consider it to be a "Circulator" rather than a
pump. The heating circuit is a loop - the "circulator is merely making
the
water flow around the circuit. The height of the system has no effect.


I disagree, at least in the way you have expressed it.
Where the feed pipe joins the circuit, the height of the header tank and
the position of the circulator within the circuit are absolutely crucial
to the correct operation or otherwise of the heating system.

Last week my apprentice and I fixed a system where the feed pipe had been
installed after the pump. We moved it to the right place but also had to
spend half a day powerflushing the system to remove (most of) the effects
of the misplaced pipe.


--
Ed Sirett - Property maintainer and registered gas fitter.
The FAQ for uk.diy is at http://www.diyfaq.org.uk
Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html
Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html
Choosing a Boiler FAQ http://www.makewrite.demon.co.uk/BoilerChoice.html
Gas Fitting Standards Docs he
http://www.makewrite.demon.co.uk/GasFittingStandards


I agree that there are many issues about vent pipes and feed pipes.