James October 7th 06 12:29 AM

weatherproof junction box wiring
 
Hi,

I need some advice on this product. The instructions that came with it
don't give any wiring examples.

http://www.tlc-direct.co.uk/Images/P..._3/MK56506.JPG

I got this because I want to join two pieces of 2.5mm T&E outside to
form a single run (the cable is encased in 20mm plastic pipe). There
are reasons I cannot run a single length of cable point to point. Can
anyone help with these questions?

1. Firstly there are 4 terminals on each set of terminal block, I
presume I just don't use the 4th one, as the cable only has 3 wires?

2. Does it matter as to which of the 4 terminals on a block the live,
neutral and earth connect to?

3. I presume the incoming T&E cable goes to any one of the 4 blocks,
the outgoing cables go from another. Is it simply a case of using small
lengths of cable inside the junction box to join the corresponding
terminals as well? If not, what is the proper way to achieve what I
want, preferably using the junction box and knowing I can't have one
single length of cable and the join is outside.

Thanks,

James




John Rumm October 7th 06 02:44 AM

weatherproof junction box wiring
 
James wrote:

I need some advice on this product. The instructions that came with it
don't give any wiring examples.

http://www.tlc-direct.co.uk/Images/P..._3/MK56506.JPG

I got this because I want to join two pieces of 2.5mm T&E outside to
form a single run (the cable is encased in 20mm plastic pipe). There
are reasons I cannot run a single length of cable point to point. Can
anyone help with these questions?

1. Firstly there are 4 terminals on each set of terminal block, I
presume I just don't use the 4th one, as the cable only has 3 wires?


First thing to realise here is there are four terminal blocks, each with
four connections - each of the connections on one terminal block are
elctriacally joined together. So to join three cores you would need to
use two terminals on each of three terminal blocks.

2. Does it matter as to which of the 4 terminals on a block the live,
neutral and earth connect to?


No.

3. I presume the incoming T&E cable goes to any one of the 4 blocks,


If I am understanding correctly what you are saying, then that is a
definite NO!

If you connect all three wires in your cable to three terminals on a
single block, then all you will do is short the lot of them together!

the outgoing cables go from another. Is it simply a case of using small
lengths of cable inside the junction box to join the corresponding
terminals as well? If not, what is the proper way to achieve what I
want, preferably using the junction box and knowing I can't have one
single length of cable and the join is outside.



Each group of four terminals are joined together. So lets say we call them:


# #
# #
# A B #
# #

# #
# C D #
# #
# #


Take the live from your incoming cable to the first terminal of A
take its neutral to terminal 1 on B
and the earth (after sleaving it in green/yellow PVC) to terminal 1 of C
D remains unused.

Now take the live from your ougoing cable and connect to terminal 2 on
A, the neutral to terminal 2 on B, and the earth to terminal 2 on C.

Note that exterior wiring will fall under part P of the building regs.

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/

James October 7th 06 09:19 AM

weatherproof junction box wiring
 
John,

Thanks, that has cleared it up. I realised what I said in point 3 was wrong
after I typed it..

James



"John Rumm" wrote in message
...
James wrote:

I need some advice on this product. The instructions that came with it
don't give any wiring examples.

http://www.tlc-direct.co.uk/Images/P..._3/MK56506.JPG

I got this because I want to join two pieces of 2.5mm T&E outside to
form a single run (the cable is encased in 20mm plastic pipe). There
are reasons I cannot run a single length of cable point to point. Can
anyone help with these questions?

1. Firstly there are 4 terminals on each set of terminal block, I
presume I just don't use the 4th one, as the cable only has 3 wires?


First thing to realise here is there are four terminal blocks, each with
four connections - each of the connections on one terminal block are
elctriacally joined together. So to join three cores you would need to use
two terminals on each of three terminal blocks.

2. Does it matter as to which of the 4 terminals on a block the live,
neutral and earth connect to?


No.

3. I presume the incoming T&E cable goes to any one of the 4 blocks,


If I am understanding correctly what you are saying, then that is a
definite NO!

If you connect all three wires in your cable to three terminals on a
single block, then all you will do is short the lot of them together!

the outgoing cables go from another. Is it simply a case of using small
lengths of cable inside the junction box to join the corresponding
terminals as well? If not, what is the proper way to achieve what I
want, preferably using the junction box and knowing I can't have one
single length of cable and the join is outside.



Each group of four terminals are joined together. So lets say we call
them:


# #
# #
# A B #
# #

# #
# C D #
# #
# #


Take the live from your incoming cable to the first terminal of A
take its neutral to terminal 1 on B
and the earth (after sleaving it in green/yellow PVC) to terminal 1 of C
D remains unused.

Now take the live from your ougoing cable and connect to terminal 2 on A,
the neutral to terminal 2 on B, and the earth to terminal 2 on C.

Note that exterior wiring will fall under part P of the building regs.

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/




Dave Plowman (News) October 7th 06 11:17 AM

weatherproof junction box wiring
 
In article ,
James wrote:
Hi,


I need some advice on this product. The instructions that came with it
don't give any wiring examples.


It's not sold as a DIY product, so you'd be expected to know how to wire
it.

http://www.tlc-direct.co.uk/Images/P..._3/MK56506.JPG


I got this because I want to join two pieces of 2.5mm T&E outside to
form a single run (the cable is encased in 20mm plastic pipe). There
are reasons I cannot run a single length of cable point to point. Can
anyone help with these questions?


1. Firstly there are 4 terminals on each set of terminal block, I
presume I just don't use the 4th one, as the cable only has 3 wires?


Correct. The fourth terminal is for where it's being used for the junction
point of a lighting switch, etc.

2. Does it matter as to which of the 4 terminals on a block the live,
neutral and earth connect to?


No. It would be marked if it did.

3. I presume the incoming T&E cable goes to any one of the 4 blocks,
the outgoing cables go from another. Is it simply a case of using small
lengths of cable inside the junction box to join the corresponding
terminals as well? If not, what is the proper way to achieve what I
want, preferably using the junction box and knowing I can't have one
single length of cable and the join is outside.


Each of the four terminal blocks consists of a strip of brass with 4 holes
in it for the cables and 4 screws which go into the top of those holes,
then moulded into the plastic. So each of the four blocks is internally
connected to itself, but not the others.

Thanks,


James


--
*I used up all my sick days so I called in dead

Dave Plowman London SW
To e-mail, change noise into sound.