Garage power supply - Recap [Longish]
I participated in (but didn't initiate) the thread back in June - from which
I learned quite a lot - but have a few more questions. My detached double garage is currently being built, and is about 1.1 metres from the house. I intend to use a garage consumer unit - probably http://tinyurl.com/zmmh4, which I intend to connect to a spare way in my domestic CU. This currently has a 6mm^2 T&E cable connected to it, which was originally intended for an electric shower - but we used stored water and a shower pump instead - so this way and cable (with a suitable MCB) can be re-deployed. The 6mm^2 cable ends (with a couple of feet spare) just above the ceiling of an en-suite bathroom - more or less vertically above the point where the house end of the garage connection needs to be. I intend to join some 6mm^2 SWA cable to this cable, and take it through the wall and down the outside of the house, and across a passage door frame into the garage. Although the garage consumer unit can handle 40 amps, this is more than I need (and the sum of the individual MCBs is a lot less than this anyway) so I intend to use a 32 amp Type-B MCB at the house end of the connection - which seems more appropriate than a higher value if relying on the 2.5mm^2 earth within the existing T&E cable. My questions concern earthing arrangements, and physically joining the cables together. From my description of my incoming mains back in June, Andy Wade thought that I have a TN-S system, and David Hansen thought it was more likely TN-C-S. In case it helps, I've posted a photo of the main fuse and meter connection at http://www.mills37.plus.com/Incoming_mains.JPG Just to remind you, I estimate that I have about 10 metres of T&E, and will need about 6 metres of SWA. The options for earthing appear to be as follows: * Use 3-core SWA cable, and use one core (6 mm^2) as the earth - and join it onto the end of the T&E's 2.5mm^2 protective earth conductor - thus exporting the earth from the domestic CU * Use 2-core SWA, and use the steel armour as an earth, again joined to the T&E's earth conductor - again exporting the earth. [There will be no external connections to be subjected to 'weather', so corrosion shouldn't be a problem] * Use 2-core SWA and an earth spike at the garage end - thus providing the garage with its own earth - independent of the house supply * Some combination of the above. [Is there a down side to exporting the earth *and* having an earth spike?] I would welcome constructive comments on the relative merits of each of the above options - plus identification of any viable options I may have missed. Now to joining the cables . . The most convenient solution would be to have the joint inside a deep (metal) socket box high on the wall of the en-suite bathroom - sunk into the blockwork, and covered by a flush blanking plate. The T&E would come down from above, and be chased into the plaster and the SWA would go straight out through the wall from the back of the box - with its gland fitted to a knock-out in the box. Does anyone see any problems with this? How should I physically join the cables? Is a large chocolate block connector (inside the box) ok - or is there anything purpose-made which would be better? Do I need to earth the SWA's armour even if it isn't being used as the protective earth? Your expert advice will be much appreciated. Oh, and in case anyone mentions Part P - I think that what I am doing is probably covered by Part P. AIUI, extending an existing radial circuit isn't, but when you start taking it outside, it is. The building itself is exempt from building regs, being a detached garage of less than 30 M^2 floor area, and meeting the other exemption conditions. My inclination therefore is to forget about Part P and hope that it gets lost in the noise when the property is eventually sold (hopefully far into the future). Nevertheless, I want to ensure that I end up with a 'safe' electrical installation - hence the questions. -- Cheers, Roger ______ Email address maintained for newsgroup use only, and not regularly monitored.. Messages sent to it may not be read for several weeks. PLEASE REPLY TO NEWSGROUP! |
#2
Posted to uk.d-i-y
|
|||
|
|||
Garage power supply - Recap [Longish]
Roger Mills wrote:
My detached double garage is currently being built, and is about 1.1 metres from the house. I intend to use a garage consumer unit - probably http://tinyurl.com/zmmh4, which I intend to connect to a spare way in my domestic CU. This It looks rather like the RCD covers both ways on that. Depending on how you plan to use the garage you may wish to opt for some arrangement that will not lose the lights at the same time you lop through a power cord with a still spinning circular saw! (i.e. switched two way CU with a RCBO for the sockets, or perhaps the one pictured with a non maintained emergency light) Although the garage consumer unit can handle 40 amps, this is more than I need (and the sum of the individual MCBs is a lot less than this anyway) so I intend to use a 32 amp Type-B MCB at the house end of the connection - which seems more appropriate than a higher value if relying on the 2.5mm^2 earth within the existing T&E cable. On the same theme as above you may need to bear in mind is descrimination of the protective devices. You want to try and ensure that a trip on the power circuit in the garrage only takes out the local MCB and not the upstream one in the main CU as well hence losing your lights. My questions concern earthing arrangements, and physically joining the cables together. From my description of my incoming mains back in June, Andy Wade thought that I have a TN-S system, and David Hansen thought it was more likely TN-C-S. In case it helps, I've posted a photo of the main fuse and meter connection at http://www.mills37.plus.com/Incoming_mains.JPG Just to remind you, I estimate that I have about 10 metres of T&E, and will need about 6 metres of SWA. That is a different cable head end from any I have seen in use in this area, so can't give you a definitive answer. However the connection of the (undersized!) earth connector to the side of the main cutout like that would suggest TN-C-S. Where does that other earth wire go that drops down from the CU? What is that little box at the bottom of the frame? The options for earthing appear to be as follows: * Use 3-core SWA cable, and use one core (6 mm^2) as the earth - and join it onto the end of the T&E's 2.5mm^2 protective earth conductor - thus exporting the earth from the domestic CU This is slightly more reliable that the next option in that there is less chance of the earth becoming poor due to corrosian etc at the gland - but as you later say these are internal connections and a new garage is unlikly to be damp so there is not much in it. If doing this I would tend to use one core *and* the screen. * Use 2-core SWA, and use the steel armour as an earth, again joined to the T&E's earth conductor - again exporting the earth. [There will be no external connections to be subjected to 'weather', so corrosion shouldn't be a problem] One slight advantage with this one is the cable will be a little thinner and easier to handle. * Use 2-core SWA and an earth spike at the garage end - thus providing the garage with its own earth - independent of the house supply If the house end is not already TT then the arguments for a separate TT supply in an outbuilding usually come down two one of two reasons - either it is a long distance (obviuosly not the case here), or, when there will be potential difficulty extending the house's equipotetial zone into the outbuilding (of most concern with a PME house). * Some combination of the above. [Is there a down side to exporting the earth *and* having an earth spike?] I would welcome constructive comments on the relative merits of each of the above options - plus identification of any viable options I may have missed. Now to joining the cables . . The most convenient solution would be to have the joint inside a deep (metal) socket box high on the wall of the en-suite bathroom - sunk into the blockwork, and covered by a flush blanking plate. The T&E would come down from above, and be chased into the plaster and the If coming from above, could you not have an adaptable metal box in the loft space instead? SWA would go straight out through the wall from the back of the box - with its gland fitted to a knock-out in the box. Does anyone see any problems with this? How should I physically join the cables? Is a large chocolate block connector (inside the box) ok - or is there anything purpose-made which would be better? You could use crimps, but since it will remain accessable screw connectors are ok. If you opt for using the screen as a CPC I would be reluctant to have the gland connection burried in a wall behind a metal box. Do I need to earth the SWA's armour even if it isn't being used as the protective earth? It is good practice since it offers better protection to the cable (especially since you don't currently appear to have a RCD at the head end). If you were using TT in the garage then you can earth it at the head end, but leave the other end disconnected (would require a insualted CU in the garage) Your expert advice will be much appreciated. As usual it is worth what you paid! ;-) -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#3
Posted to uk.d-i-y
|
|||
|
|||
Garage power supply - Recap [Longish]
On Thu, 24 Aug 2006 00:44:13 +0100 someone who may be John Rumm
wrote this:- I've posted a photo of the main fuse and meter connection at http://www.mills37.plus.com/Incoming_mains.JPG That is a different cable head end from any I have seen in use in this area, so can't give you a definitive answer. However the connection of the (undersized!) earth connector to the side of the main cutout like that would suggest TN-C-S. Agreed. If you opt for using the screen as a CPC I would be reluctant to have the gland connection burried in a wall behind a metal box. Agreed. An excellent way to introduce corrosion into the CPC. In addition, although I don't share the panic about using steel as the CPC I think it must be easily accessible for inspection. Provided the extra lengths are acceptable I too would look at the loft as the place to make the joint. -- David Hansen, Edinburgh I will *always* explain revoked encryption keys, unless RIP prevents me http://www.opsi.gov.uk/acts/acts2000/00023--e.htm#54 |
#4
Posted to uk.d-i-y
|
|||
|
|||
Garage power supply - Recap [Longish]
John Rumm wrote:
It looks rather like the RCD covers both ways on that. Depending on how you plan to use the garage you may wish to opt for some arrangement that will not lose the lights at the same time you lop through a power cord with a still spinning circular saw! (i.e. switched two way CU with a RCBO for the sockets, or perhaps the one pictured with a non maintained emergency light) Yes, for TT a main switch and two RCBOs would be a good option, or main switch with one MCB (lights) and one RCBO (power) for TN. I'd be inclined to make the 'power' RCBO a 20 A one - RCBOs only come as Type B and 16 A Type B might tend to trip on motor starting currents, or the inrush current of a 230 - 115 V tool transformer. (Alternatively keep the 16 A circuit for sockets only and provide separate motor circuits for any machines.) You can buy all the MK consumer unit parts separately from a wholesaler, including TLC if you want to buy on-line. On the same theme as above you may need to bear in mind is descrimination of the protective devices. You want to try and ensure that a trip on the power circuit in the garrage only takes out the local MCB and not the upstream one in the main CU as well hence losing your lights. That would probably require the feed to be via a separate switch-fuse rather than an MCB in the CU - certainly a better arrangement, but does involve teeing in to the meter tails with a service connector block. That is a different cable head end from any I have seen in use in this area, so can't give you a definitive answer. However the connection of the (undersized!) earth connector to the side of the main cutout like that would suggest TN-C-S. Looks like TN-C-S to me, with old earthing and bonding conductors which are undersized by current standards. These ought to be upgraded if you intend to use the exported PME earth. Where does that other earth wire go that drops down from the CU? One of the main bonds? What is that little box at the bottom of the frame? Looks a bit like an old GPO telephone wiring junction box (a 'block terminal' something-or-other)? * Use 3-core SWA cable, and use one core (6 mm^2) as the earth - and join it onto the end of the T&E's 2.5mm^2 protective earth conductor - thus exporting the earth from the domestic CU This is slightly more reliable that the next option in that there is less chance of the earth becoming poor due to corrosian etc at the gland - but as you later say these are internal connections and a new garage is unlikly to be damp so there is not much in it. If doing this I would tend to use one core *and* the screen. * Use 2-core SWA, and use the steel armour as an earth, again joined to the T&E's earth conductor - again exporting the earth. [There will be no external connections to be subjected to 'weather', so corrosion shouldn't be a problem] One slight advantage with this one is the cable will be a little thinner and easier to handle. Using a core as CPC gives you a 6 mm^2 conductor with a resistance of about 3.7 milliohm/m. Using the armour gives you a CPC equivalent to 9.8 mm^2 copper, but with a resistance of around 7 milliohm/m. I'd use the 2-core unless the CPC resistance (R2) is a problem in the design. The weakest link in this design though is the 2.5 mm^2 CPC in the T&E cable. Note that it would not be acceptable to use this if there are any metal services rising in the garage that would need main bonding - this because the CPC of the submain also acts as the main bonding conductor, so would need to be a minimum of 10 mm^2 Cu equivalent. * Use 2-core SWA and an earth spike at the garage end - thus providing the garage with its own earth - independent of the house supply If the house end is not already TT then the arguments for a separate TT supply in an outbuilding usually come down two one of two reasons - either it is a long distance (obviuosly not the case here), or, when there will be potential difficulty extending the house's equipotetial zone into the outbuilding (of most concern with a PME house). As I usually say here, the TT/TN decision depends on the use of the outbuilding and the practicality of creating an equipotential zone there. At one extreme is a dry workshop building where there will be little use of electrical equipment outdoors (TN OK here) and at the other extreme is the metal greenhouse (TT essential). Any use extensive of portable Class 1 (earthed) equipment outdoors again signals the need for TT earthing. * Some combination of the above. [Is there a down side to exporting the earth *and* having an earth spike?] No, and there is an advantage to doing that - but understand that it's still TN-C-S with its attendant risks. You are adding another earth to the M (multiple) in PME, so you'll help reduce the touch voltage in the event of a broken supply neutral. You do need a damn good earth electrode to do much good though, and it should be connected to the main earth terminal in the house, not at the garage end via a weedy 2.5 mm^2 CPC. [...] SWA would go straight out through the wall from the back of the box - with its gland fitted to a knock-out in the box. Does anyone see any problems with this? That's completely impractical because you've go no access to the back of the box to tighten the gland nut. It would also be extremely fiddly to do this with a single-gang accessory box. Better as John said to connect the SWA in the loft, alternatively take the T&E through the wall to a box on the outside, and run the SWA straight down from there. [...] Do I need to earth the SWA's armour even if it isn't being used as the protective earth? Yes, definitely, to provide protection in case the cable is damaged. -- Andy |
#5
Posted to uk.d-i-y
|
|||
|
|||
Garage power supply - Recap [Longish]
Andy Wade wrote:
John Rumm wrote: On the same theme as above you may need to bear in mind is descrimination of the protective devices. You want to try and ensure that a trip on the power circuit in the garrage only takes out the local MCB and not the upstream one in the main CU as well hence losing your lights. That would probably require the feed to be via a separate switch-fuse rather than an MCB in the CU - certainly a better arrangement, but does involve teeing in to the meter tails with a service connector block. Hager do a MCB sized HRC fuse carrier, which can solve that problem in many cases.... although having just typed that, I remembered that Roger's CU ain't a DIN rail jobbie anyway, so this is of little practical use to him! ;-) -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#6
Posted to uk.d-i-y
|
|||
|
|||
Garage power supply - Recap [Longish]
John Rumm wrote:
Hager do a MCB sized HRC fuse carrier, which can solve that problem in many cases.... Oops, quite right, I forgot that option. although having just typed that, I remembered that Roger's CU ain't a DIN rail jobbie anyway, so this is of little practical use to him! ;-) Doh! - his picture tells all, and I guess the new circuit is going in the empty fuseway on the right (currently 15 A). In this case the obvious thing to do is to use a 30 A BS 1361 fuse and not another plug-in MCB. -- Andy |
#7
Posted to uk.d-i-y
|
|||
|
|||
Garage power supply - Recap [Longish]
In an earlier contribution to this discussion,
Andy Wade wrote: John Rumm wrote: Hager do a MCB sized HRC fuse carrier, which can solve that problem in many cases.... Oops, quite right, I forgot that option. although having just typed that, I remembered that Roger's CU ain't a DIN rail jobbie anyway, so this is of little practical use to him! ;-) Doh! - his picture tells all, and I guess the new circuit is going in the empty fuseway on the right (currently 15 A). In this case the obvious thing to do is to use a 30 A BS 1361 fuse and not another plug-in MCB. Yes, the circuit is going at the extreme right - which currently has a blue base for a 16A MCB. I may well still have a 30A fuse - not sure about the BS1361 bit though - is that something special? [The CU started off with fuses, and was converted to MCBs!] What is the rationale for using a fuse rather than an MCB? Is it that it takes longer to blow, making it more likely that the one at the garage end will trip instead? If so, it makes sense, but it flies in the face of the advice given in the earlier thread which said that I needed a Type B (and *not* Type C) MCB on account of only having a 2.5mm^2 earth wire for most of the length. -- Cheers, Roger ______ Email address maintained for newsgroup use only, and not regularly monitored.. Messages sent to it may not be read for several weeks. PLEASE REPLY TO NEWSGROUP! |
#8
Posted to uk.d-i-y
|
|||
|
|||
Garage power supply - Recap [Longish]
In an earlier contribution to this discussion,
John Rumm wrote: On the same theme as above you may need to bear in mind is descrimination of the protective devices. You want to try and ensure that a trip on the power circuit in the garrage only takes out the local MCB and not the upstream one in the main CU as well hence losing your lights. Many thanks for your response. The local MCBs are 16A for power and 6A for lighting - so, under overload conditions, should trip prior to the 32A one at the house end. Of course, if I cut through a wire and connect live to earth before live to neutral, the RCD will trip and I'll lose the lights as well. I guess I have to live with that. That is a different cable head end from any I have seen in use in this area, so can't give you a definitive answer. However the connection of the (undersized!) earth connector to the side of the main cutout like that would suggest TN-C-S. Where does that other earth wire go that drops down from the CU? What is that little box at the bottom of the frame? The other earth wire goes into an adjoining cupboard which houses the gas meter, and is clamped onto a gas pipe. The little box at the bottom is a junction box for telephone wiring. If coming from above, could you not have an adaptable metal box in the loft space instead? I *could* join it in the loft space - but that bit of loft is pretty inaccessible, so I was trying to avoid it. What does an adaptable metal box look like? You could use crimps, but since it will remain accessable screw connectors are ok. If you opt for using the screen as a CPC I would be reluctant to have the gland connection burried in a wall behind a metal box. I guess I'd need a half-way decent ratchet crimping tool to use crimps - which I don't have. I take your point about burying the gland in the wall. Your expert advice will be much appreciated. As usual it is worth what you paid! ;-) If you're selective about what advice you accept, much of the advice given here is actually worth a lot more than we pay for it! -- Cheers, Roger ______ Email address maintained for newsgroup use only, and not regularly monitored.. Messages sent to it may not be read for several weeks. PLEASE REPLY TO NEWSGROUP! |
#9
Posted to uk.d-i-y
|
|||
|
|||
Garage power supply - Recap [Longish]
Roger Mills wrote:
Many thanks for your response. The local MCBs are 16A for power and 6A for lighting - so, under overload conditions, should trip prior to the 32A one at the house end. Of course, if I cut through a wire and connect live to earth before live to neutral, the RCD will trip and I'll lose the lights as well. I guess I have to live with that. By a slight change to the choice of CU though that is easy enough to avoid. Where does that other earth wire go that drops down from the CU? What is that little box at the bottom of the frame? The other earth wire goes into an adjoining cupboard which houses the gas meter, and is clamped onto a gas pipe. So no main bond to the water service then? The little box at the bottom is a junction box for telephone wiring. Thought as much, but thought I had better check! If coming from above, could you not have an adaptable metal box in the loft space instead? I *could* join it in the loft space - but that bit of loft is pretty inaccessible, so I was trying to avoid it. What does an adaptable metal box look like? Box looks like: http://www.tlc-direct.co.uk/Main_Ind...ble/index.html or http://www.tlc-direct.co.uk/Main_Ind...ded/index.html You could use crimps, but since it will remain accessable screw connectors are ok. If you opt for using the screen as a CPC I would be reluctant to have the gland connection burried in a wall behind a metal box. I guess I'd need a half-way decent ratchet crimping tool to use crimps - which I don't have. I take your point about burying the gland in the wall. In which case why not chase down the bathroom wall as described, but rather than installing a metal box in the bathroom, simply drill throught the wall at that point (keeping within 6" of the bathroom ceiling). You can stick some capping over the T&E to facilitate future replacement if you wish. Now install your cable and plaster over the chase leaving no visible accessory in the bathroom. Now visit the other side of the wall where hopefully you have a bit of T&E dangling, and poke it into the back of one of the aformentiond boxes (a IP65 one would probably be a good choice here). Screw it to the wall, and you can then stick a nice neat SWA gland into the knockout at the base of the box. Choose the right box ad you may even get one complete with junction terminals. That means your joint is accessable and serviceable, no extra clutter to tile round the bathroom, and no groveling in the loft! Your expert advice will be much appreciated. As usual it is worth what you paid! ;-) If you're selective about what advice you accept, much of the advice given here is actually worth a lot more than we pay for it! Yup, second that many times over, thanks guys! -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#10
Posted to uk.d-i-y
|
|||
|
|||
Garage power supply - Recap [Longish]
In an earlier contribution to this discussion,
John Rumm wrote: The local MCBs are 16A for power and 6A for lighting - so, under overload conditions, should trip prior to the 32A one at the house end. Of course, if I cut through a wire and connect live to earth before live to neutral, the RCD will trip and I'll lose the lights as well. I guess I have to live with that. By a slight change to the choice of CU though that is easy enough to avoid. Could you elaborate on that please? The other earth wire goes into an adjoining cupboard which houses the gas meter, and is clamped onto a gas pipe. So no main bond to the water service then? Yes there *is* - but the water comes in elsewhere. The earth wire goes up through the ceiling from the CU, and drops down into the kitchen where the mains stop-tap is located. Box looks like: http://www.tlc-direct.co.uk/Main_Ind...ble/index.html or http://www.tlc-direct.co.uk/Main_Ind...ded/index.html Thanks for the links. I now see what you mean. I take your point about burying the gland in the wall. In which case why not chase down the bathroom wall as described, but rather than installing a metal box in the bathroom, simply drill throught the wall at that point (keeping within 6" of the bathroom ceiling). You can stick some capping over the T&E to facilitate future replacement if you wish. Now install your cable and plaster over the chase leaving no visible accessory in the bathroom. Now visit the other side of the wall where hopefully you have a bit of T&E dangling, and poke it into the back of one of the aformentiond boxes (a IP65 one would probably be a good choice here). Screw it to the wall, and you can then stick a nice neat SWA gland into the knockout at the base of the box. Choose the right box ad you may even get one complete with junction terminals. That means your joint is accessable and serviceable, no extra clutter to tile round the bathroom, and no groveling in the loft! That's certainly a possibility. It means that I would be making the connection while perched 16' up a ladder, but I could probably terminate the SWA in the box before fixing the box to the wall. How would I seal round where the T&E would come in? -- Cheers, Roger ______ Email address maintained for newsgroup use only, and not regularly monitored.. Messages sent to it may not be read for several weeks. PLEASE REPLY TO NEWSGROUP! |
#11
Posted to uk.d-i-y
|
|||
|
|||
Garage power supply - Recap [Longish]
Although the garage consumer unit can handle 40 amps, this is more than I
need (and the sum of the individual MCBs is a lot less than this anyway) so I intend to use a 32 amp Type-B MCB at the house end of the connection - which seems more appropriate than a higher value if relying on the 2.5mm^2 earth within the existing T&E cable. Don't be so sure. You want the house end to blow as slowly as possible to get maximum possible discrimination with the garage CU. I would consider a Type C MCB, or even an HRC fuse. If 40A is allowed as well, then use that, too. I haven't done the calculations so can't tell you what you will get away with. This way, any fault is more likely to be picked up at the local MCB in the garage. * Use 3-core SWA cable, and use one core (6 mm^2) as the earth - and join it onto the end of the T&E's 2.5mm^2 protective earth conductor - thus exporting the earth from the domestic CU I'd just do this given you are only 1.1m from the house. This is only possible if the garage has no main equipotential bonding requirements, or the main equipotential bonding can actually be achieved. Remember to use the armour as earth as well, both to get the ELI even lower and because the armour must be earthed anyway. The reason to have the additional copper conductor is that copper doesn't rust at the termination and is more reliable over the decades. The most convenient solution would be to have the joint inside a deep (metal) socket box high on the wall of the en-suite bathroom - sunk into the blockwork, and covered by a flush blanking plate. The T&E would come down from above, and be chased into the plaster and the SWA would go straight out through the wall from the back of the box - with its gland fitted to a knock-out in the box. Does anyone see any problems with this? No problem. How should I physically join the cables? Is a large chocolate block connector (inside the box) ok - or is there anything purpose-made which would be better? Chocolate block or crimp is fine. Do I need to earth the SWA's armour even if it isn't being used as the protective earth? Yes. Either earthed by using a metal box, or using a decent earth ring, not the ****e one that you get with the gland. Christian. |
#12
Posted to uk.d-i-y
|
|||
|
|||
Garage power supply - Recap [Longish]
In an earlier contribution to this discussion,
Christian McArdle wrote: Don't be so sure. You want the house end to blow as slowly as possible to get maximum possible discrimination with the garage CU. I would consider a Type C MCB, or even an HRC fuse. If 40A is allowed as well, then use that, too. I haven't done the calculations so can't tell you what you will get away with. This way, any fault is more likely to be picked up at the local MCB in the garage. Is there an idiot's guide somewhere, defining the calculations which I need to do? As mentioned in my post in answer to Andy Wade, I had previously been advised (back in June) to use a Type B MCB, and to go for 32A rather than 40A in the light of my rather weedy 2.5mm^2 earth wire - so I'm getting a bit confused! * Use 3-core SWA cable, and use one core (6 mm^2) as the earth - and join it onto the end of the T&E's 2.5mm^2 protective earth conductor - thus exporting the earth from the domestic CU I'd just do this given you are only 1.1m from the house. This is only possible if the garage has no main equipotential bonding requirements, or the main equipotential bonding can actually be achieved. It's 1.1 metres as the crow flies - but about 6 metres of SWA down the wall, across the gap, and into the garage. Does this make any difference - or are we only looking at the likely difference in earth potential between 2 adjacent buildings? There will be no 'services' (water, gas, etc) in the garage, and no equipotential bonding is required AIUI. -- Cheers, Roger ______ Email address maintained for newsgroup use only, and not regularly monitored.. Messages sent to it may not be read for several weeks. PLEASE REPLY TO NEWSGROUP! |
#13
Posted to uk.d-i-y
|
|||
|
|||
Garage power supply - Recap [Longish]
Roger Mills wrote:
ice will be much appreciated. Oh, and in case anyone mentions Part P - I think that what I am doing is probably covered by Part P. AIUI, extending an existing radial circuit isn't, but when you start taking it outside, it is. The building itself is exempt from building regs, being a detached garage of less than 30 M^2 floor area, and meeting the other exemption conditions. My inclination therefore is to forget about Part P and hope that it gets lost in the noise when the property is eventually sold (hopefully far into the future). Nevertheless, I want to ensure that I end up with a 'safe' electrical installation - hence the questions. a) It's covered by part P b) I'd google anyone I was buying a house from, and find this thread. c) It probably won't get lost in the noise, because it's the noise that is precisely the problem when buying a house. Well, that and solicitors covering their backs. d) But, if I found it by google, I'd then chat to you, and provided I was convinced that you knew what you were doing and did it properly, I'd tell you to forget about disclosing anything about it, and the solicitors would never be the wiser. Much the best way. Anyway, just pointing out that posting plans to ignore buildings control isn't a good idea when done under your real name! Cheers, Ben |
#14
Posted to uk.d-i-y
|
|||
|
|||
Garage power supply - Recap [Longish]
Ben Blaukopf wrote:
Roger Mills wrote: Oh, and in case anyone mentions Part P - I think that what I am doing is probably covered by Part P. AIUI, extending an existing radial circuit isn't, but when you start taking it outside, it is. The building itself is exempt from building regs, being a detached garage of less than 30 M^2 floor area, and meeting the other exemption conditions. My inclination therefore is to forget about Part P and hope that it gets lost in the noise when the property is eventually sold (hopefully far into the future). Nevertheless, I want to ensure that I end up with a 'safe' electrical installation - hence the questions. a) It's covered by part P Yup, agreed. b) I'd google anyone I was buying a house from, and find this thread. I bet few would though.... still its certainly possible. (I hope you like reading - there are getting on for 10,000 posts that mention Rogers's name!) c) It probably won't get lost in the noise, because it's the noise that is precisely the problem when buying a house. Well, that and solicitors covering their backs. I expect a few years into the future they wil be showing as much interest as they do in FENSA certs now (i.e. getting progressively less) d) But, if I found it by google, I'd then chat to you, and provided I was convinced that you knew what you were doing and did it properly, I'd tell you to forget about disclosing anything about it, and the solicitors would never be the wiser. Much the best way. Yup, I would much rather find evidence of someone asking sensible questions before doing a job! Anyway, just pointing out that posting plans to ignore buildings control isn't a good idea when done under your real name! Hmmm, doubt there are many on this group who haven't wrt part P! -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Sony GDM-FW900 power supply MCZ3001D info needed | Electronics Repair | |||
Tektronix 3001GPX Power supply info needed | Electronics Repair | |||
Wanted: Someone to examine switchmode power supply... | Electronics Repair | |||
Metal Working Machinery New and Used in Australia and for Export | Metalworking | |||
Switching Power Supply Failure | Electronics Repair |