MCB Current Rating for Ring Main
Is there anything that says an MCB rating for a ring main has to be 32
amps, could it be 16 amps? I want to put my kitchen on its own circuit but the MCB's are no longer made by Crabtree but I have two unused 16 amp MCB's. If I use the 32 amp that is currently the downstairs ring main for the kitchen then put the front room/hall on one 16 amp ring and the living room on another 16 amp ring would I run into problems? Kevin |
#2
Posted to uk.d-i-y
|
|||
|
|||
MCB Current Rating for Ring Main
You might get some nuisance tripping if you try doing the hoovering and
ironing whilst watching a DVD with surround sound by the light of a collection of floor lamps :-) |
#3
Posted to uk.d-i-y
|
|||
|
|||
MCB Current Rating for Ring Main
"Kev" wrote in message oups.com... Is there anything that says an MCB rating for a ring main has to be 32 amps, could it be 16 amps? I want to put my kitchen on its own circuit but the MCB's are no longer made by Crabtree but I have two unused 16 amp MCB's. If I use the 32 amp that is currently the downstairs ring main for the kitchen then put the front room/hall on one 16 amp ring and the living room on another 16 amp ring would I run into problems? Kevin Are you are refering to the Crabtree MCBs that came before the plug in type? ie is it a screw the fastens the MCB to the bus bar? If so then I was able to buy a 40 amp one from Newey and Eyres last week. I did have to order it in but it did arrive the next day. I am also sure I will have an old type 32 amp MCB knocking about in the garage, it will be guaranteed second hand but I will post it to you if you want. Adam |
#4
Posted to uk.d-i-y
|
|||
|
|||
MCB Current Rating for Ring Main
Kev wrote:
Is there anything that says an MCB rating for a ring main has to be 32 amps, could it be 16 amps? I want to put my kitchen on its own circuit but the MCB's are no longer made by Crabtree but I have two unused 16 amp MCB's. If I use the 32 amp that is currently the downstairs ring main for the kitchen then put the front room/hall on one 16 amp ring and the living room on another 16 amp ring would I run into problems? Kevin it can be 16 if you want. 16A mcbs dont trip at 16.1A, and as long as you dont have kitchen, immersion or electric heating on them, all should be fine. NT |
#5
Posted to uk.d-i-y
|
|||
|
|||
MCB Current Rating for Ring Main
Hi;
Good idea to have a seperate final ring circuit in the kitchen. Most sparks I know who do this would use 4m T&E as well. If you have the kettle on, switch the toaster on while the kettle boils then warn the beans up in a Micro wave, what happens ? Didn't trip, Umm, now the fridge kicks in and it does trip!! Is it worth the cost of a 32 Amp MCB ? Who is going to Insect and Test this for your Part P certificate? I would probably fail it on the grounds of the MCB being too small to take a kitchen load by exposing the MCB to too much in overcurrent operations. What if the MCB failed in the ON position, Presto - No protection and you would not know - hence the need for Part P. Then, perhaps the Kettle is on the cooker switch and all is fine. Regards Ian |
#6
Posted to uk.d-i-y
|
|||
|
|||
MCB Current Rating for Ring Main
Kev wrote: Is there anything that says an MCB rating for a ring main has to be 32 amps, could it be 16 amps? 16th ed IEE wiring regs is very lean on requirements for ring circuits. Most of the stuff in earlier editions has been taken out and appears (if it does) in the IEE On-Site Guide - mostly in Appendix 8. There's some relevant additional info in Appendix 1 (diversity). Appendix 8 implies that ring final circuits should be protected at 30A or 32A & be run using cable rated = 20A - ie =2.5mmsq if in FTE. Possibly there is a further implication in Appendix 8, that if you use BS1363 socket outlets (the std uk flat pin type) then any ring they are inserted in must comply table 8A - ie for a ring circuit you need 30/32A MCB. I want to put my kitchen on its own circuit but the MCB's are no longer made by Crabtree but I have two unused 16 amp MCB's. If I use the 32 amp that is currently the downstairs ring main for the kitchen then put the front room/hall on one 16 amp ring and the living room on another 16 amp ring would I run into problems? Frankly a false economy. Use some of the money you are saving by DIY to do a proper job with fittings that will last. Invest in a new CU if you possibly can. HTH |
#7
Posted to uk.d-i-y
|
|||
|
|||
MCB Current Rating for Ring Main
jim_in_sussex wrote:
Frankly a false economy. Use some of the money you are saving by DIY to do a proper job with fittings that will last. Invest in a new CU if you possibly can. Although there's nothing wrong with the OP's idea of using the one available 32 A MCB for the kitchen ring and splitting the other ring into two radial circuits, assuming each circuit covers 50 m^2 floor area. However, these should be 20 A circuits, not 16 A. With 16 A MCBs they would be non-standard circuits and could be seen as under-rated for general household loading - likely to be overloaded if the CH breaks down and all those old electric heaters come out, for example. -- Andy |
#8
Posted to uk.d-i-y
|
|||
|
|||
MCB Current Rating for Ring Main
ARWadsworth wrote: "Kev" wrote in message oups.com... Is there anything that says an MCB rating for a ring main has to be 32 amps, could it be 16 amps? I want to put my kitchen on its own circuit but the MCB's are no longer made by Crabtree but I have two unused 16 amp MCB's. If I use the 32 amp that is currently the downstairs ring main for the kitchen then put the front room/hall on one 16 amp ring and the living room on another 16 amp ring would I run into problems? Kevin Are you are refering to the Crabtree MCBs that came before the plug in type? ie is it a screw the fastens the MCB to the bus bar? If so then I was able to buy a 40 amp one from Newey and Eyres last week. I did have to order it in but it did arrive the next day. I am also sure I will have an old type 32 amp MCB knocking about in the garage, it will be guaranteed second hand but I will post it to you if you want. Adam It is a plugin type. The current starbreakers have exactly the same type if fitting and are interchangeable but the newer ones stick out more and are supposed to foul the front cover slightly. I may just try one and see. The cover has a lip that I could file down a bit if the fit interfears. Kevin |
#9
Posted to uk.d-i-y
|
|||
|
|||
MCB Current Rating for Ring Main
|
#11
Posted to uk.d-i-y
|
|||
|
|||
MCB Current Rating for Ring Main
jim_in_sussex wrote: If I use the 32 amp that is currently the downstairs ring main for the kitchen then put the front room/hall on one 16 amp ring and the living room on another 16 amp ring would I run into problems? Frankly a false economy. Use some of the money you are saving by DIY to do a proper job with fittings that will last. Invest in a new CU if you possibly can. HTH I have thought of a new CU but am I then not into the realms of having the whole installation in the house tested. Somebody at work went that route then got his house electrics condemned because of something that was donkeys years old wasn't up to spec. The work involved would be minimal if only I could trace a suitable MCB. Kevin |
#12
Posted to uk.d-i-y
|
|||
|
|||
MCB Current Rating for Ring Main
"Kev" wrote in message ups.com... ARWadsworth wrote: "Kev" wrote in message oups.com... Is there anything that says an MCB rating for a ring main has to be 32 amps, could it be 16 amps? I want to put my kitchen on its own circuit but the MCB's are no longer made by Crabtree but I have two unused 16 amp MCB's. If I use the 32 amp that is currently the downstairs ring main for the kitchen then put the front room/hall on one 16 amp ring and the living room on another 16 amp ring would I run into problems? Kevin Are you are refering to the Crabtree MCBs that came before the plug in type? ie is it a screw the fastens the MCB to the bus bar? If so then I was able to buy a 40 amp one from Newey and Eyres last week. I did have to order it in but it did arrive the next day. I am also sure I will have an old type 32 amp MCB knocking about in the garage, it will be guaranteed second hand but I will post it to you if you want. Adam It is a plugin type. The current starbreakers have exactly the same type if fitting and are interchangeable but the newer ones stick out more and are supposed to foul the front cover slightly. I may just try one and see. The cover has a lip that I could file down a bit if the fit interfears. Kevin I also have those types of MCBs knocking about if you want one. Adam |
#13
Posted to uk.d-i-y
|
|||
|
|||
MCB Current Rating for Ring Main
Andy Wade wrote: jim_in_sussex wrote: Frankly a false economy. Use some of the money you are saving by DIY to do a proper job with fittings that will last. Invest in a new CU if you possibly can. Although there's nothing wrong with the OP's idea of using the one available 32 A MCB for the kitchen ring and splitting the other ring into two radial circuits, ....but unless I have very much misunderstood the original post, the suggestion was to break the circuit into 2 separate 16A rings. As you suggest breaking it into 2 radials is perfectly OK (or even just making it into 1 20A radial) & might make the OP's MCB hunt easier as finding a 20A MCB would also put him back in business. How does the risk of reusing old MCBs untested rate versus installing a brand new reputable make CU with only basic continuity testing ? My money would go on a the new CU as the safer bet. If the OP is reusing old second hand MCBs then perhaps he should consider testing them properly. |
#14
Posted to uk.d-i-y
|
|||
|
|||
MCB Current Rating for Ring Main
"jim_in_sussex" wrote in message oups.com... Andy Wade wrote: jim_in_sussex wrote: Frankly a false economy. Use some of the money you are saving by DIY to do a proper job with fittings that will last. Invest in a new CU if you possibly can. Although there's nothing wrong with the OP's idea of using the one available 32 A MCB for the kitchen ring and splitting the other ring into two radial circuits, ...but unless I have very much misunderstood the original post, the suggestion was to break the circuit into 2 separate 16A rings. As you suggest breaking it into 2 radials is perfectly OK (or even just making it into 1 20A radial) & might make the OP's MCB hunt easier as finding a 20A MCB would also put him back in business. How does the risk of reusing old MCBs untested rate versus installing a brand new reputable make CU with only basic continuity testing ? How do you test an MCB? Adam |
#15
Posted to uk.d-i-y
|
|||
|
|||
MCB Current Rating for Ring Main
ARWadsworth wrote:
How do you test an MCB? Pass current through it and see if it trips. Use a variac and a low-voltage high current transformer, and wind the current up slowly. Not really necessary though, since (IME) they never fail, unlike RCDs. -- Andy |
#16
Posted to uk.d-i-y
|
|||
|
|||
MCB Current Rating for Ring Main
"Andy Wade" wrote in message ... jim_in_sussex wrote: Frankly a false economy. Use some of the money you are saving by DIY to do a proper job with fittings that will last. Invest in a new CU if you possibly can. Although there's nothing wrong with the OP's idea of using the one available 32 A MCB for the kitchen ring and splitting the other ring into two radial circuits, assuming each circuit covers 50 m^2 floor area. However, these should be 20 A circuits, not 16 A. With 16 A MCBs they would be non-standard circuits and could be seen as under-rated for general household loading - likely to be overloaded if the CH breaks down and all those old electric heaters come out, for example. -- Andy Why do garage/shed CUs usually arrive pre loaded with one 16 amp and one 6 amp breaker? Adam |
#17
Posted to uk.d-i-y
|
|||
|
|||
MCB Current Rating for Ring Main
"Andy Wade" wrote in message ... ARWadsworth wrote: How do you test an MCB? Pass current through it and see if it trips. Use a variac and a low-voltage high current transformer, and wind the current up slowly. Not really necessary though, since (IME) they never fail, unlike RCDs. -- Andy That is not a test used on any NICEIC inspection. Maybe it should be. Adam |
#18
Posted to uk.d-i-y
|
|||
|
|||
MCB Current Rating for Ring Main
On Wed, 07 Jun 2006 23:45:50 GMT, "ARWadsworth"
wrote: "Andy Wade" wrote in message ... jim_in_sussex wrote: Frankly a false economy. Use some of the money you are saving by DIY to do a proper job with fittings that will last. Invest in a new CU if you possibly can. Although there's nothing wrong with the OP's idea of using the one available 32 A MCB for the kitchen ring and splitting the other ring into two radial circuits, assuming each circuit covers 50 m^2 floor area. However, these should be 20 A circuits, not 16 A. With 16 A MCBs they would be non-standard circuits and could be seen as under-rated for general household loading - likely to be overloaded if the CH breaks down and all those old electric heaters come out, for example. -- Andy Why do garage/shed CUs usually arrive pre loaded with one 16 amp and one 6 amp breaker? Adam Power and light. |
#19
Posted to uk.d-i-y
|
|||
|
|||
MCB Current Rating for Ring Main
jim 16th ed IEE wiring regs is very lean on requirements for ring circuits. Most of the stuff in earlier editions has been taken out and appears (if it does) in the IEE On-Site Guide - mostly in Appendix 8. There's some relevant additional info in Appendix 1 (diversity). I think this is why quality sparks use radials in the kitchen. Ring final circuits are rather a UK under specified specification that maybe are OK in todays low power cumsumable appliances found in all but the kitchen. I suspect that the worst case a rfc would cope with is the Vac starting up or the lawnmower getting clogged on a wet lawn. Go into EU sparking areas and its all redials. As 17th addition is round the corner we await with abated breath. Yes I hope to have my 2391 soon (Exam mid July) so I can legally apply my hate of the amount poor sparking near and around me. My dad has a huge column drill on a 13amp extension lead with 1.5T&E, of course the earth wire has fractured and he complains of a tingle when drilling !! Perhaps Mum is waiting for his eyes for glow !! Regards Ian |
#20
Posted to uk.d-i-y
|
|||
|
|||
MCB Current Rating for Ring Main
Go into EU sparking areas and its all redials.
Yes, but they get 16A socket circuits with limited sockets on each circuit. It is only UK style systems that give us the flexibility to go around sticking 3kW appliances in where we see fit and have some chance of not blowing a fuse. Christian. |
#21
Posted to uk.d-i-y
|
|||
|
|||
MCB Current Rating for Ring Main
wrote in message ups.com... SNIP Yes I hope to have my 2391 soon (Exam mid July) so I can legally apply my hate of the amount poor sparking near and around me. My dad has a huge column drill on a 13amp extension lead with 1.5T&E, of course the earth wire has fractured and he complains of a tingle when drilling !! Perhaps Mum is waiting for his eyes for glow !! Regards Ian Now as I understand health and safety law in a work environment NOBODY from the bog cleaner up to the CEO can avoid blame if they become aware of a problem and do nothing about it. In a home / family situation surely the moral issue is even stronger if not the law, and particularly if an individual is training / trained in the area of hazzard . . . AWEM |
#22
Posted to uk.d-i-y
|
|||
|
|||
MCB Current Rating for Ring Main
On Thu, 8 Jun 2006 16:57:30 +0100, "Andrew Mawson"
wrote: Now as I understand health and safety law in a work environment NOBODY from the bog cleaner up to the CEO can avoid blame if they become aware of a problem and do nothing about it. That came in at the end of the 70's, and a jolly shock it was to employers. "Safety Officers" were appointed immediately,(Me), regardless of how little they knew. When I enquired, I was told to see if we had "any loose carpet on the stairs". I went around and listed defects and gave them to the manager. He binned it, but I had a copy on file elsewhere and had shown it to other staff. ) |
#23
Posted to uk.d-i-y
|
|||
|
|||
MCB Current Rating for Ring Main
"EricP" wrote in message ... On Wed, 07 Jun 2006 23:45:50 GMT, "ARWadsworth" wrote: "Andy Wade" wrote in message .. . jim_in_sussex wrote: Frankly a false economy. Use some of the money you are saving by DIY to do a proper job with fittings that will last. Invest in a new CU if you possibly can. Although there's nothing wrong with the OP's idea of using the one available 32 A MCB for the kitchen ring and splitting the other ring into two radial circuits, assuming each circuit covers 50 m^2 floor area. However, these should be 20 A circuits, not 16 A. With 16 A MCBs they would be non-standard circuits and could be seen as under-rated for general household loading - likely to be overloaded if the CH breaks down and all those old electric heaters come out, for example. -- Andy Why do garage/shed CUs usually arrive pre loaded with one 16 amp and one 6 amp breaker? Adam Power and light. So they should come with 20A and a 6A then Adam |
#24
Posted to uk.d-i-y
|
|||
|
|||
MCB Current Rating for Ring Main
|
#25
|
|||
|
|||
Quote:
A2 Radial = 32A 4.0mm2 A3 Radial = 20A 2.5mm2 correct me if im wrong Level 3 qualified 2330 |
#26
|
|||
|
|||
Quote:
By the way how many idiots out there still are no good at fault finding Continuity test ring a bell |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Question on adding 220V and 110V circuits to garage | Home Repair | |||
Flywheel on a rotary phase convertor | Metalworking | |||
sequence of tripping CB | UK diy | |||
How to reduce current on a cheapo mig welder? | Metalworking | |||
Phase converter balancing | Metalworking |