Mogweed December 12th 05 11:42 PM

Equipotential bonding in bathroom
 
What size conductor should be used to bond everything that's metal to
everything else that's metal in the bathroom (but not run back to the CU)?

Cheers,

Mogweed.



[email protected] December 13th 05 05:40 AM

Equipotential bonding in bathroom
 
Mogweed wrote:
What size conductor should be used to bond everything that's metal to
everything else that's metal in the bathroom (but not run back to the CU)?

Cheers,

Mogweed.


4mm2 insulated, or 6mm2 bare.

NT


Mogweed December 13th 05 09:43 AM

Equipotential bonding in bathroom
 

wrote in message
oups.com...
Mogweed wrote:
What size conductor should be used to bond everything that's metal to
everything else that's metal in the bathroom (but not run back to the
CU)?

Cheers,

Mogweed.


4mm2 insulated, or 6mm2 bare.

NT


Thanks very much NT.

Mogweed.



Andy Wade December 13th 05 09:49 AM

Equipotential bonding in bathroom
 
wrote:

4mm2 insulated,


Correct.

or 6mm2 bare.

Wrong. Bare protective conductors, whether circuit protective
conductors or equipotential bonding conductors, are not permitted for
sizes of less than 10 mm^2. [See regulation 543-03-02]

--