CHeating Problem: Danfoss 3port contractor pack HELP!
 
Hello

Installed DanfossRandall Y plan contractor pack.

The HW circuit works fine in all respects, but CH circuit doesn't.
Someone gave me this table:

ORANGE BROWN/WHITE GREY
OFF 0v 0v 240v

DHWonly 240 0 0

DHW + CH 240 240 reduced voltage

CHonly 240 240 240


I checked these off and they all came up fine, BUT
when I pulled off the actuator head to watch it cycling through the
positions it failed to return to the HW only position when I turned off
everything at the controller. Cutting power to the controller DID make
it return. Is this most likely to be an Actuator or Controller fault?

Also, when I manipulated the spindle of the 3 port valve manually it
made the pump sound as though it was having problems when set to the CH
only position, and it still failed to get the pipes warm...

Also (!) the Boiler fails to stay alight for longer than a few minutes
at a time, especially when set to CH only... under what conditions does
the boiler shut down other than over heat? It is a Glow Worm Space
saver 52. Would it shut down if it was pushing against flow restriction
in the rad circuit ?

Taking all this into account, I reckon I have 3 possible (maybe 4?)
problems.

1 flow restriction in the CH circuit
2 Faulty controller
3 Faulty Actuator
(4 sticky valve in 3 port body causing 1?)

Bearing in mind all voltages across actuator seem fine and it cycles
through all positions smoothly my opinion is that it is an actuator
problem causing it to fail to return to its default HW only position.
But it also seems I have a flow restriction causing the pump some
problems...

Please release me from this plumbing hell, its getting cold and I live
with 3 slightly concerned tenants! At least they can have a hot shower.




Cheers


Andrew Gabriel November 12th 05 04:18 PM

CHeating Problem: Danfoss 3port contractor pack HELP!
 
I couldn't follow everything you wrote.
However, I'll just point out that a mid position valve may well
stay in the mid position if you just remove all power from it.
To keep the valve in mid-position, the motor is fed with DC
to lock the rotor. This magnetises the yoke which can continue
to hold the actuator against the spring if you just remove the
power (although the holding force is very weak and it will
probably release if you touch it). In normal operation, a tiny
AC current is leaked through the motor when it isn't operating
to degauss the yoke, and ensure the spring returns the actuator
to its resting position.

--
Andrew Gabriel

Set Square November 12th 05 05:53 PM

CHeating Problem: Danfoss 3port contractor pack HELP!
 
In an earlier contribution to this discussion,
wrote:

Hello

Installed DanfossRandall Y plan contractor pack.

The HW circuit works fine in all respects, but CH circuit doesn't.
Someone gave me this table:

ORANGE BROWN/WHITE GREY
OFF 0v 0v 240v

DHWonly 240 0 0

DHW + CH 240 240 reduced voltage

CHonly 240 240 240


I checked these off and they all came up fine, BUT
when I pulled off the actuator head to watch it cycling through the
positions it failed to return to the HW only position when I turned
off everything at the controller. Cutting power to the controller DID
make it return. Is this most likely to be an Actuator or Controller
fault?

Also, when I manipulated the spindle of the 3 port valve manually it
made the pump sound as though it was having problems when set to the
CH only position, and it still failed to get the pipes warm...

Also (!) the Boiler fails to stay alight for longer than a few minutes
at a time, especially when set to CH only... under what conditions
does the boiler shut down other than over heat? It is a Glow Worm
Space saver 52. Would it shut down if it was pushing against flow
restriction in the rad circuit ?

Taking all this into account, I reckon I have 3 possible (maybe 4?)
problems.

1 flow restriction in the CH circuit
2 Faulty controller
3 Faulty Actuator
(4 sticky valve in 3 port body causing 1?)

Bearing in mind all voltages across actuator seem fine and it cycles
through all positions smoothly my opinion is that it is an actuator
problem causing it to fail to return to its default HW only position.
But it also seems I have a flow restriction causing the pump some
problems...

Please release me from this plumbing hell, its getting cold and I live
with 3 slightly concerned tenants! At least they can have a hot
shower.




Cheers


The valve doesn't always need to return to the HW position when there's no
demand - it sometimes stays put. Clearly, it needs to return when there is
an unsatisfied HW demand but no CH demand, and it must return when you
remove *all* power by switching off at the FCU rather than at the
programmer. As long as it does these things, it's ok. [Note that the valve
actuator is still powered when HW is off at the programmer - hence the need
to switch off at the FCU].

In CH-only mode, the boiler and pump will only run when there is a demand
from the room stat. [What is that set at? Check that it's wired up
correctly!]. Even then, the boiler will cycle on its own stat if the rads
are not dissipating heat as fast as the boiler can produce it.

If the rads are not getting hot, it could be for any of a number of reasons
including:
* a blockage in the CH circuit
* TRVs at too low a setting
* manual radiator valves or lockshields turned down too much
* a by-pass circuit wide open - providing a much easier path for the water
than going through the rads
* a massive airlock somewhere, preventing proper circulation

There's a few things to have a go at!
--
Cheers,
Set Square
______
Please reply to newsgroup. Reply address is invalid.



Ed Sirett November 12th 05 06:16 PM

CHeating Problem: Danfoss 3port contractor pack HELP!
 
On Sat, 12 Nov 2005 16:53:53 +0000, Set Square wrote:

In an earlier contribution to this discussion,
wrote:

Hello

Installed DanfossRandall Y plan contractor pack.

The HW circuit works fine in all respects, but CH circuit doesn't.
Someone gave me this table:

ORANGE BROWN/WHITE GREY
OFF 0v 0v 240v

DHWonly 240 0 0

DHW + CH 240 240 reduced voltage

CHonly 240 240 240


I checked these off and they all came up fine, BUT
when I pulled off the actuator head to watch it cycling through the
positions it failed to return to the HW only position when I turned
off everything at the controller. Cutting power to the controller DID
make it return. Is this most likely to be an Actuator or Controller
fault?

Also, when I manipulated the spindle of the 3 port valve manually it
made the pump sound as though it was having problems when set to the
CH only position, and it still failed to get the pipes warm...

Also (!) the Boiler fails to stay alight for longer than a few minutes
at a time, especially when set to CH only... under what conditions
does the boiler shut down other than over heat? It is a Glow Worm
Space saver 52. Would it shut down if it was pushing against flow
restriction in the rad circuit ?

Taking all this into account, I reckon I have 3 possible (maybe 4?)
problems.

1 flow restriction in the CH circuit
2 Faulty controller
3 Faulty Actuator
(4 sticky valve in 3 port body causing 1?)

Bearing in mind all voltages across actuator seem fine and it cycles
through all positions smoothly my opinion is that it is an actuator
problem causing it to fail to return to its default HW only position.
But it also seems I have a flow restriction causing the pump some
problems...

Please release me from this plumbing hell, its getting cold and I live
with 3 slightly concerned tenants! At least they can have a hot
shower.




Cheers


The valve doesn't always need to return to the HW position when there's no
demand - it sometimes stays put. Clearly, it needs to return when there is
an unsatisfied HW demand but no CH demand, and it must return when you
remove *all* power by switching off at the FCU rather than at the
programmer. As long as it does these things, it's ok. [Note that the valve
actuator is still powered when HW is off at the programmer - hence the need
to switch off at the FCU].

In CH-only mode, the boiler and pump will only run when there is a demand
from the room stat. [What is that set at? Check that it's wired up
correctly!]. Even then, the boiler will cycle on its own stat if the rads
are not dissipating heat as fast as the boiler can produce it.

If the rads are not getting hot, it could be for any of a number of reasons
including:
* a blockage in the CH circuit
* TRVs at too low a setting
* manual radiator valves or lockshields turned down too much
* a by-pass circuit wide open - providing a much easier path for the water
than going through the rads
* a massive airlock somewhere, preventing proper circulation

There's a few things to have a go at!


Agreed.
I used to name the problem with heating in autumn "The October problem".
With the weather this year looking suspiciously like a climate change the
problem may have to be renamed the "The November Problem".

The problem is that the weather has got colder not so much in absolute
terms but in relative terms. The indoor comfort levels have dropped and we
are not yet wearing warmer clothing and/or getting used to being cooler
indoors.

However the heating system is not triggered by your comfort level but by
the temperature which is still usually enough to keep the heating off.
TRVs often keep radiators shut until it's cooler inside.

Also TRVs that weren't set to maximum for the summer months (that'll be
99%+ of them) tend to jam closed.

--
Ed Sirett - Property maintainer and registered gas fitter.
The FAQ for uk.diy is at
http://www.diyfaq.org.uk
Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html
Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html



gastec November 12th 05 09:37 PM

Quote:

Originally Posted by
Hello

Installed DanfossRandall Y plan contractor pack.

The HW circuit works fine in all respects, but CH circuit doesn't.
Someone gave me this table:

ORANGE BROWN/WHITE GREY
OFF 0v 0v 240v

DHWonly 240 0 0

DHW + CH 240 240 reduced voltage

CHonly 240 240 240


I checked these off and they all came up fine, BUT
when I pulled off the actuator head to watch it cycling through the
positions it failed to return to the HW only position when I turned off
everything at the controller. Cutting power to the controller DID make
it return. Is this most likely to be an Actuator or Controller fault?

Also, when I manipulated the spindle of the 3 port valve manually it
made the pump sound as though it was having problems when set to the CH
only position, and it still failed to get the pipes warm...

Also (!) the Boiler fails to stay alight for longer than a few minutes
at a time, especially when set to CH only... under what conditions does
the boiler shut down other than over heat? It is a Glow Worm Space
saver 52. Would it shut down if it was pushing against flow restriction
in the rad circuit ?

Taking all this into account, I reckon I have 3 possible (maybe 4?)
problems.

1 flow restriction in the CH circuit
2 Faulty controller
3 Faulty Actuator
(4 sticky valve in 3 port body causing 1?)

Bearing in mind all voltages across actuator seem fine and it cycles
through all positions smoothly my opinion is that it is an actuator
problem causing it to fail to return to its default HW only position.
But it also seems I have a flow restriction causing the pump some
problems...

Please release me from this plumbing hell, its getting cold and I live
with 3 slightly concerned tenants! At least they can have a hot shower.




Cheers

you have a diverter 3 port valve not a mid position valve....also you have probably wired it wrong along with a probable air lock

gastec November 12th 05 09:46 PM

Quote:

Originally Posted by
Hello

Installed DanfossRandall Y plan contractor pack.

The HW circuit works fine in all respects, but CH circuit doesn't.
Someone gave me this table:

ORANGE BROWN/WHITE GREY
OFF 0v 0v 240v

DHWonly 240 0 0

DHW + CH 240 240 reduced voltage

CHonly 240 240 240


I checked these off and they all came up fine, BUT
when I pulled off the actuator head to watch it cycling through the
positions it failed to return to the HW only position when I turned off
everything at the controller. Cutting power to the controller DID make
it return. Is this most likely to be an Actuator or Controller fault?

Also, when I manipulated the spindle of the 3 port valve manually it
made the pump sound as though it was having problems when set to the CH
only position, and it still failed to get the pipes warm...

Also (!) the Boiler fails to stay alight for longer than a few minutes
at a time, especially when set to CH only... under what conditions does
the boiler shut down other than over heat? It is a Glow Worm Space
saver 52. Would it shut down if it was pushing against flow restriction
in the rad circuit ?

Taking all this into account, I reckon I have 3 possible (maybe 4?)
problems.

1 flow restriction in the CH circuit
2 Faulty controller
3 Faulty Actuator
(4 sticky valve in 3 port body causing 1?)

Bearing in mind all voltages across actuator seem fine and it cycles
through all positions smoothly my opinion is that it is an actuator
problem causing it to fail to return to its default HW only position.
But it also seems I have a flow restriction causing the pump some
problems...

Please release me from this plumbing hell, its getting cold and I live
with 3 slightly concerned tenants! At least they can have a hot shower.




Cheers

http://www.cambourne.info/BOILER/MPEDOC_3.PDF#search='danfoss%203%20port%20valve%20 wiring'

oooops you do have a mid position valve..make sure the wiring is correct...see link

raden November 13th 05 01:13 AM

CHeating Problem: Danfoss 3port contractor pack HELP!
 
In message , gastec
writes

Please release me from this plumbing hell, its getting cold and I live
with 3 slightly concerned tenants! At least they can have a hot
shower.





Cheers

you have a diverter 3 port valve not a mid position valve....also you
have probably wired it wrong along with a probable air lock



You really are a mine of disinformation, aren't you

The danger is that someone will actually take you seriously.


--
geoff

[email protected] November 14th 05 11:10 PM

CHeating Problem: Danfoss 3port contractor pack HELP!
 
Thanks for all your help. I now know how to sort it out, but at a cost!

Every single TRV on the system was jammed shut and so old that when I
was messing around with one the rubber valve inside disentegrated and
started leaking all over the floor... luckily I had a drain on the
drain cock in case and I had started on the room with no carpets to be
on the safe side!

I believe what had happened was the boiler was just shutting down
because all the water was returning too hot, not having passed through
any radiators.

I'm sorry to have got you writing all this stuff when it was really a
very basic problem. I had allready removed the TRV heads and freed the
first pin, so I thought I'd done the neccessary, but it was really the
plunger that was causing the problem.

Anyway a lesson well learned. Anyone fancy taking the day off to help
me replace all the TRVs on Thursday? Hello? Hello? Anyone there?