Plumbing question: No hot water
 
Hi,

I know very little about plumbing, and am looking for some advice on
diagnosing a problem.

We have what I suspect is a fairly average heating system. A Potterton
Neataheat boiler and controller box downstairs in the kitchen and a hot
water storage tank upstairs in the bathroom. The pump is next to the
tank and feeds into the tank and radiator system via a couple of
motorised three-way valves.

A few of days ago we stopped getting hot water through the taps.
Here's what I've obsrved:

- If we turn on only the heating then the boiler fires up, the pump
starts, and the radiators heat-up.
- If we turn on the heating and hot water then the boiler and pump star
and the storage tank fills with hot water. The 'lever' on the back of
the motor controlling the heating valve moves, so I think we get hot
water in this case because the heating-circuit valve is opening on
command and the pump is moving hot water through both valves.
- If we turn on only the hot water then the valve motor appears to open
the heating circuit valve, but the pump does not activate. Neither does
the boiler.

I'm hoping for some advice on what could be causing this. The valves,
pump, and boiler appear to be okay. I suspect that the thermostat on
the hot water tank is faulty, and the pump and boiler aren't starting
because the system thinks that the tank is full of hot. Thats just a
guess, though, because I don't know much...

I'd be grateful if anyone can suggest things I should check to solve
this. In particular, how to test the tank thermostat. I'm fairly
proficient with electrics, and can get access to a test meter if
necessary.

Thanks, Andy


John August 16th 05 10:08 PM


"Andy Johnson" wrote in message
ups.com...
Hi,

I know very little about plumbing, and am looking for some advice on
diagnosing a problem.

We have what I suspect is a fairly average heating system. A Potterton
Neataheat boiler and controller box downstairs in the kitchen and a hot
water storage tank upstairs in the bathroom. The pump is next to the
tank and feeds into the tank and radiator system via a couple of
motorised three-way valves.

A few of days ago we stopped getting hot water through the taps.
Here's what I've obsrved:

- If we turn on only the heating then the boiler fires up, the pump
starts, and the radiators heat-up.
- If we turn on the heating and hot water then the boiler and pump star
and the storage tank fills with hot water. The 'lever' on the back of
the motor controlling the heating valve moves, so I think we get hot
water in this case because the heating-circuit valve is opening on
command and the pump is moving hot water through both valves.
- If we turn on only the hot water then the valve motor appears to open
the heating circuit valve, but the pump does not activate. Neither does
the boiler.

I'm hoping for some advice on what could be causing this. The valves,
pump, and boiler appear to be okay. I suspect that the thermostat on
the hot water tank is faulty, and the pump and boiler aren't starting
because the system thinks that the tank is full of hot. Thats just a
guess, though, because I don't know much...

I'd be grateful if anyone can suggest things I should check to solve
this. In particular, how to test the tank thermostat. I'm fairly
proficient with electrics, and can get access to a test meter if
necessary.

Thanks, Andy


Forget the tank thermostat - if the motor in the valve is energised then it
must have a supply to it. the most likely fault is the microswitch in the
valve head has failed or the conductor (usually orange and grey wires) from
it to the terminals in the junction box are open circuit. (what make of
motorised valve do you have?)



Andy Johnson August 16th 05 10:37 PM

I'm not sure what make the valve is - I can't see any identifying marks
on the body of the value, but access is rather cramped. Also, someone
(not me) has painted it. The metal seems like plain brass (no zinc
finish).

The motor is a synchron motor. About 1 1/2" high. Round on the top and
tear-drop shaped on the base with a small toothed wheel emerging
slightly off-centre.
It looks like this:
http://www.screwfix.com/sfd/i/cat/84/p1055284_l.jpg. It sits under a
metal cover above the valve.

Are you saying that when the valve opens fully it trips the microswitch
which turns on the pump and boiler? If so, would it make sense to
disconnect the microswitch from the junction box and use a continuity
tester to see if trips when I turn on the hot water? Or am I still not
understanding? :)

Andy


Set Square August 16th 05 10:40 PM

In an earlier contribution to this discussion,
Andy Johnson wrote:

Hi,

I know very little about plumbing, and am looking for some advice on
diagnosing a problem.

We have what I suspect is a fairly average heating system. A
Potterton Neataheat boiler and controller box downstairs in the
kitchen and a hot water storage tank upstairs in the bathroom. The
pump is next to the tank and feeds into the tank and radiator system
via a couple of motorised three-way valves.

A few of days ago we stopped getting hot water through the taps.
Here's what I've obsrved:

- If we turn on only the heating then the boiler fires up, the pump
starts, and the radiators heat-up.
- If we turn on the heating and hot water then the boiler and pump
star and the storage tank fills with hot water. The 'lever' on the
back of the motor controlling the heating valve moves, so I think we
get hot water in this case because the heating-circuit valve is
opening on command and the pump is moving hot water through both
valves. - If we turn on only the hot water then the valve motor
appears to open the heating circuit valve, but the pump does not
activate. Neither does the boiler.

I'm hoping for some advice on what could be causing this. The valves,
pump, and boiler appear to be okay. I suspect that the thermostat on
the hot water tank is faulty, and the pump and boiler aren't starting
because the system thinks that the tank is full of hot. Thats just a
guess, though, because I don't know much...

I'd be grateful if anyone can suggest things I should check to solve
this. In particular, how to test the tank thermostat. I'm fairly
proficient with electrics, and can get access to a test meter if
necessary.

Thanks, Andy


I'm slightly confused by your description - because you would normally have
ONE three-way valve or TWO two-way valves, but not TWO three-way valves. So
I will assume they are two-way valves - each having just an inlet and an
outlet for the water.

If I am right, you have an S-Plan system. You can see both a schematic
diagram and a wiring diagram by looking at S-Plan in
http://content.honeywell.com/uk/homes/systems.htm

The principle of operation is that the motorised valves are controlled by
the programmer and thermostats (room stat for the CH valve and cylinder stat
for the HW valve). Each valve has an additional set of contacts which close
when the valve is fully open. These contacts are totally separate from the
motor wires, and are used to turn on the boiler in pump. So as soon as
either (or both) valves open, the boiler and pump start up.

From your description, it sounds as if your HW valve is opening (so the cyl
stat is ok) but it isn't turning the boiler and pump on. However, if the
boiler and pump are turned by the CH valve, the hot water gets hot because
the HW valve is open.

So there appears to be a problem with these so-called volt-free contacts in
the HW valve. Either they're not closing, or something has become
disconnected.

Armed with the wiring diagram from the above reference, you should hopefully
be able to isolate the problem.
--
Cheers,
Set Square
______
Please reply to newsgroup. Reply address is invalid.



Set Square August 16th 05 10:51 PM

In an earlier contribution to this discussion,
Andy Johnson wrote:

I'm not sure what make the valve is - I can't see any identifying
marks on the body of the value, but access is rather cramped. Also,
someone (not me) has painted it. The metal seems like plain brass (no
zinc finish).

The motor is a synchron motor. About 1 1/2" high. Round on the top
and tear-drop shaped on the base with a small toothed wheel emerging
slightly off-centre.
It looks like this:
http://www.screwfix.com/sfd/i/cat/84/p1055284_l.jpg. It sits under a
metal cover above the valve.

Are you saying that when the valve opens fully it trips the
microswitch which turns on the pump and boiler? If so, would it make
sense to disconnect the microswitch from the junction box and use a
continuity tester to see if trips when I turn on the hot water? Or am
I still not understanding? :)

Andy


You're on the right lines. See my other post. If it's a Honeywell valve (and
probably if it isn't!) it's the grey and orange wires you need to be looking
at. The internal contacts (micro-switch) should connect these togther when
the valve is open. So you could disconnect the remote end of these wires and
then use a continuity tester between them. There's probably a junction box
in the airing cupboard with all the connections in. [But be careful working
on mains electrics - and get help unless you're sure what you're doing!]
--
Cheers,
Set Square
______
Please reply to newsgroup. Reply address is invalid.



Andy Johnson August 16th 05 11:04 PM

Set Square,

Thanks for replying - you've made a lot of things clearer. And you're
right. I have two two-way valves.

I'm not clear what the 'volt-free' contacts are. Is this the
microswitch in the motor housing that John mentioned, or is it part of
the valve itself? I removed the motor cover, and unscrewed and
lifted-out the motor, and I could see a green plastic microswitch
underneath with a kind of cam that nudges it as the valve turns. Is
this what you mean?

Andy


Sparks August 17th 05 12:05 AM


"Andy Johnson" wrote in message
oups.com...
Set Square,

Thanks for replying - you've made a lot of things clearer. And you're
right. I have two two-way valves.

I'm not clear what the 'volt-free' contacts are. Is this the
microswitch in the motor housing that John mentioned, or is it part of
the valve itself? I removed the motor cover, and unscrewed and
lifted-out the motor, and I could see a green plastic microswitch
underneath with a kind of cam that nudges it as the valve turns. Is
this what you mean?

Andy


Yes,

All the heating controller and thermostats do, is control the opening of
these valves, the valves then trip the little switch inside themselves, and
turn on the boiler/pump.

So..

You tell the heating controller you want to turn on the hot water, so power
is applied to the thermostat strapped to the tank. The stat is not satisfied
with the current water temperature, so sends the power along to the valve to
open it.

The valve, when it opens, presses a small switch inside it's casing, to turn
on the boiler and pump (It is done like this, so if the valve gets stuck in
the off position, the boiler does not fire up, and have nowhere to pump the
water)

Armed with this info, if you open the Hot water valve, and see what wires
are connected to the little switch, then, when the valve is open (and only
then!) you could try shorting these two wires together (THEY ARE CHARRING
MAINS VOLTAGE BE CAREFUL!!)
If this starts the pump and boiler, then you have a faulty switch if not,
you probably have a loose connection somewhere!
This is what I would do, as I am happy dealing with live wires, however if
you are not...

Set the programmer to HW and CH
Set the CH room stat high (So it wants the boiler on)
Set the HW stat high, so it too wants the boiler on
Turn everything off with the main CH fused spur.
Make sure everything is now dead before proceeding!
Connect the wires going to the possibly faulty microswitch together
Turn it all back on (As the programmer is set to CH and HW, and the stat is
not happy about the temperature in the house, it all should fire up)
Make sure the HW valve has opened
set the room stat low or set the programmer to HW only - this should close
the CH valve, but hopefully keep the pump and boiler running.
If so, then your microswitch in the HW valve is shagged
If not, and it goes off, then there is a problem with the wiring somewhere!

Now turn it all off, and put it all back how it was. (Remember the HW Stat!)
Whatever the outcome DO NOT LEAVE the two microswitch wires connected, or
you may damage something!

Sparks...(Who has never wired up central heating (yet), but thinks he knows
how it all works :P)



Set Square August 17th 05 12:10 AM

In an earlier contribution to this discussion,
Andy Johnson wrote:

Set Square,

Thanks for replying - you've made a lot of things clearer. And you're
right. I have two two-way valves.

I'm not clear what the 'volt-free' contacts are. Is this the
microswitch in the motor housing that John mentioned, or is it part of
the valve itself? I removed the motor cover, and unscrewed and
lifted-out the motor, and I could see a green plastic microswitch
underneath with a kind of cam that nudges it as the valve turns. Is
this what you mean?

Andy


Yes - it's electrically separate from the motor supply - and can be used to
switch anything that needs to be switched when the valve is fully open. In
an S-Plan configuration, it is used (in parallel with the contacts on the
other zone valve) to switch the boiler and pump on. When the valve is open,
the cam should operate the switch in a way which closes its contacts.
--
Cheers,
Set Square
______
Please reply to newsgroup. Reply address is invalid.



Andy Johnson August 17th 05 01:52 PM

Thanks to everyone who left comments and help - very much appreciated!

Seems like its probably the microswitch. I'll have a look at it
tonight.

Andy


Christian McArdle August 17th 05 05:28 PM

Seems like its probably the microswitch. I'll have a look at it
tonight.


It is also just as likely to be a loose connection, such as in the terminal
box where the zone valve switch contacts are paralleled together.

Christian.



John August 17th 05 07:21 PM


"Andy Johnson" wrote in message
ups.com...
I'm not sure what make the valve is - I can't see any identifying marks
on the body of the value, but access is rather cramped. Also, someone
(not me) has painted it. The metal seems like plain brass (no zinc
finish).

The motor is a synchron motor. About 1 1/2" high. Round on the top and
tear-drop shaped on the base with a small toothed wheel emerging
slightly off-centre.
It looks like this:
http://www.screwfix.com/sfd/i/cat/84/p1055284_l.jpg. It sits under a
metal cover above the valve.

Are you saying that when the valve opens fully it trips the microswitch
which turns on the pump and boiler? If so, would it make sense to
disconnect the microswitch from the junction box and use a continuity
tester to see if trips when I turn on the hot water? Or am I still not
understanding? :)

Andy


Nice to see someone with a clear appreciation of the operation and a good
idea of how to test it. In other words - exactly so g