Kalico August 9th 05 12:55 PM

Cable size question
 
I do not have my OSG to hand, but can anyone tell me what the minimum
cable size is to run an oven rated at 3100W (I have the manual and it
only says use 2.5mm and a 20A fuse) plus a hob for which I do not have
the manual but it has a 30A rating.

Also, is there a type of cooker switch that can be used to supply both
devices?

At present, it has the standard cooker switch with 13A socket
alongside, supplied by a 6mm cable, with the oven being supplied
through a 13A plug. I suspect the 6mm will not be sufficient but it
could be close, depending on diversity etc.

TIA


Replace 'spam' with 'org' to reply

Matt Beard August 9th 05 06:30 PM

Diversity for a domestic cooker is 10A + 30% of the difference so
assuming a worst case of 50A (it should only be ~44A, but the oven says
20A so let's use that) we get 10A + 0.3 * 40A = 22A

Feed this into the calculator at
http://www.tlc-direct.co.uk/Technica...ltageDrop.html (after
converting to 5060W) allows 6mm to be used no problem for lengths up to
about 50m.

If you still include a 13A socket you should add an extra 5A, but
that's still fine for about 45m.

* Normal disclaimers apply: Check the figures yourself, dig out the OSG
before attempting to cook cables etc. etc.


Kalico August 12th 05 01:57 AM

On 9 Aug 2005 10:30:12 -0700, "Matt Beard" wrote:

Diversity for a domestic cooker is 10A + 30% of the difference so
assuming a worst case of 50A (it should only be ~44A, but the oven says
20A so let's use that) we get 10A + 0.3 * 40A = 22A

Feed this into the calculator at
http://www.tlc-direct.co.uk/Technica...ltageDrop.html (after
converting to 5060W) allows 6mm to be used no problem for lengths up to
about 50m.

If you still include a 13A socket you should add an extra 5A, but
that's still fine for about 45m.

* Normal disclaimers apply: Check the figures yourself, dig out the OSG
before attempting to cook cables etc. etc.



Thanks for that Matt. Now all I need to do is find some outlet that
can supply the hob, unfused (since the 6mm cable is protected by a 32A
MCB at the CU) plus something in the way of a 20A fuse/MCB to supply
the oven.

There must be something out there, but I cannot find it. Any ideas?

Rob


Replace 'spam' with 'org' to reply

Matt Beard August 13th 05 10:22 AM

As the oven is supplied with a 13A plug (not uncommon) you could
either:

a) Run 6mm from the cooker switch to a 13A socket behind the oven and
plug it in, or

b) Run 6mm to a switched spur with 13A fuse (above work surface) then
2.5mm down to either a socket or an outlet plate

But don't run 2.5mm before a 13A fuse - otherwise it is not correctly
protected.


Dave Plowman (News) August 13th 05 11:08 AM

In article .com,
Matt Beard wrote:
But don't run 2.5mm before a 13A fuse - otherwise it is not correctly
protected.


Hmm. It's rated at 24 amps. You could use 1mm TW&E if protected by a 13
amp fuse.

--
*Atheism is a non-prophet organization.

Dave Plowman London SW
To e-mail, change noise into sound.

Matt Beard August 16th 05 09:06 AM

But don't run 2.5mm before a 13A fuse - otherwise it is not correctly
protected.


Hmm. It's rated at 24 amps. You could use 1mm TW&E if protected by a 13
amp fuse.


Ok, I get your point... but I meant don't connect 2.5mm twin & earth to
a 32A rated circuit without a fuse. In this case he is planning to add
a fuse for the oven and I suggested 13A as this gives more options. In
this case it should be =4mm until the fuse (I'd prefer 6mm as this is
what the rest of the circuit uses) then 2.5mm after. Theoretically you
could use 2.5mm for the hob, but 2.5mm is what the manual says, so
best to stick to that.