Using generators with class 1 equipment - earth spike?
Should an earth spike be used when a generator is used to power class 1
equipment that normally needs an earth? (thinking of safety and ignoring EMC). I should know the answer to this but can see two sides of the coin and can't choose between the two. On one side it would be good to tie the gen and neutral down to Earth, but on the other side it would seem sensible to let the whole lot float. ... and how would an RCD cope? The particular case is using a gen to provide power for an outdoor PA system (and maybe a band). Dave |
"Dave" wrote in message ... Should an earth spike be used when a generator is used to power class 1 equipment that normally needs an earth? (thinking of safety and ignoring EMC). I should know the answer to this but can see two sides of the coin and can't choose between the two. On one side it would be good to tie the gen and neutral down to Earth, but on the other side it would seem sensible to let the whole lot float. .. and how would an RCD cope? The particular case is using a gen to provide power for an outdoor PA system (and maybe a band). Whatever you do, make sure all the mics and guitars have got their own personal in-line safety isolators. Too many dead musicians in the past due to poor electrics - of course an area part pee doesn't cover at all. |
"Mike" wrote in message ... snip[ Too many dead musicians in the past due to poor electrics - of course an area part pee doesn't cover at all. But there was not need for Part P to cover this, other H&S regs cover it. |
Mike wrote:
"Dave" wrote in message ... Should an earth spike be used when a generator is used to power class 1 equipment that normally needs an earth? (thinking of safety and ignoring EMC). I should know the answer to this but can see two sides of the coin and can't choose between the two. On one side it would be good to tie the gen and neutral down to Earth, but on the other side it would seem sensible to let the whole lot float. .. and how would an RCD cope? The particular case is using a gen to provide power for an outdoor PA system (and maybe a band). Whatever you do, make sure all the mics and guitars have got their own personal in-line safety isolators. Too many dead musicians in the past due to poor electrics - of course an area part pee doesn't cover at all. That's interesting, can you explain a little more. Do you mean isolating transformers? (or opto-isolators?) I google'd and came up with isolators to avoid earth loops but nothing about safety. Dave |
"Dave" wrote in message ... Should an earth spike be used when a generator is used to power class 1 equipment that normally needs an earth? (thinking of safety and ignoring EMC). I should know the answer to this but can see two sides of the coin and can't choose between the two. On one side it would be good to tie the gen and neutral down to Earth, but on the other side it would seem sensible to let the whole lot float. .. and how would an RCD cope? The particular case is using a gen to provide power for an outdoor PA system (and maybe a band). Dave If it is a small 240 volts AC genset, then what do want an earth point on it for. If you're plugging directly in to the generator, then it already has, or better have, its own safety devices protecting it and the supply outlets. A generator doesn't really need an earth point, and some generators don't really like being pinned to the earth, so you'd need to make sure that the metal work, if any, around the performance area was insulated from earth, but not the generator. Blocks of wood under the legs of any metal staging is usually enough to isolate the stage from earth. If you're talking industrial generator here, then you'll need to follow the instructions for the generator you've bought / hired. These sometimes need to be spiked to earth for their own internal safety features to function properly. Others need to be bonded to surrounding conductive materials for the protective devices to work correctly. It all depends on what and how the generator is going to used. |
BigWallop wrote:
"Dave" wrote in message ... Should an earth spike be used when a generator is used to power class 1 equipment that normally needs an earth? (thinking of safety and ignoring EMC). I should know the answer to this but can see two sides of the coin and can't choose between the two. On one side it would be good to tie the gen and neutral down to Earth, but on the other side it would seem sensible to let the whole lot float. .. and how would an RCD cope? The particular case is using a gen to provide power for an outdoor PA system (and maybe a band). Dave If it is a small 240 volts AC genset, then what do want an earth point on it for. If you're plugging directly in to the generator, then it already has, or better have, its own safety devices protecting it and the supply outlets. A generator doesn't really need an earth point, and some generators don't really like being pinned to the earth, so you'd need to make sure that the metal work, if any, around the performance area was insulated from earth, but not the generator. Blocks of wood under the legs of any metal staging is usually enough to isolate the stage from earth. .... snipped It all depends on what and how the generator is going to used. It's a small 240 generator, there's an integral overload breaker but not an RCD. That's spurred a few more questions: - Why would a generator object to being grounded? - What is the metalwork on a generator connected to internally? - If the generator is floating why does any adjacent metalwork need to be isolated from earth? If it's truly floating there wouldn't be a path for current to flow. Dave |
"Dave" wrote in message ... BigWallop wrote: "Dave" wrote in message ... snipped It's a small 240 generator, there's an integral overload breaker but not an RCD. That's spurred a few more questions: - Why would a generator object to being grounded? - What is the metalwork on a generator connected to internally? - If the generator is floating why does any adjacent metalwork need to be isolated from earth? If it's truly floating there wouldn't be a path for current to flow. Dave Try a little test for me. With a voltage meter, place one test probe on the metal casing of the generator. Fix it tightly to the metal. With the other test probe, touch the Live terminal of the socket outlet. Make a note of the voltage reading it shows. Now touch the Neutral terminal and make a note of the voltage it has. Now do a little bit of maths, simple addition, and add both the reading together. What do you get? A generator doesn't have to have an earth point to ground, and some generators are more dangerous if they are fixed electrically to earth ground. It does depend on the generator though, and the in-built safety features it already has. |
Dave wrote:
That's interesting, can you explain a little more. Do you mean isolating transformers? (or opto-isolators?) I google'd and came up with isolators to avoid earth loops but nothing about safety. I think he means RCDs..... Usual practice for small gigs is a 30mA rcd either at the generator (which gives no discrimination), or several at thee distribution board. I often add a 10mA unit just for the backline because backline tends to be the root of all evil in this matter. Do earth the generator frame with a spike, and DO bond the stage metalwork to generator earth (it probably will be via some path anyway and you would rather this didn't involve the screen of the audio snake....). The spike is to protect you the generator operator in the event of an internal fault imposing voltage between the generator frame and the earth connection on the socket which is probably earthed elsewhere (like say the stage). The RCD(s) protect the musicians from faults in the distro and their guitar amps (what never!). Bonding the stage metalwork reduces possible earth loop impedance issues and encourages faster disconnect times. Really once you get past the genny it is all fairly standard event power engineering. HTH. Regards, Dan. |
On Fri, 13 May 2005 18:12:20 +0000 (UTC), Dave wrote:
Should an earth spike be used when a generator is used to power class 1 equipment that normally needs an earth? Yes, and bond the generator chassis to that spike and to which ever phase from the alternator you decide to call "neutral". ie replicate the sort of supply that the equipment is designed to be plugged into. A protective earth wire connected to real ground via a spike, neutral bonded to that earth at the supply source (generator). On one side it would be good to tie the gen and neutral down to Earth, but on the other side it would seem sensible to let the whole lot float. Letting the neutral float is not good. One fault and that phase becomes as near as damn it earth potential but the other is now 240v away from earth. If that fault is in the live side the neutral is now sitting at 240v WRT earth. Single pole switches and/or single pole fuses, some thing looks off but is still very much live. ... and how would an RCD cope? An RCD doesn't care about earths or lack of. All it cares about is that the same amount of current going to the load comes back (within a few tens of mA). If there is a current inbalance the difference must be going somewhere else which is probably A Bad Thing. So put in a spike at the generator bond that to the generator chassis, bond a phase from the alternator to the chassis and earth spike and use an RCD. -- Cheers Dave. pam is missing e-mail |
You need to read the relevant section of BS7671 which I don't
have to hand, and I don't remember that section off the top of my head, but I've guessed some answers below. "Dave" wrote in message ... Should an earth spike be used when a generator is used to power class 1 equipment that normally needs an earth? (thinking of safety and ignoring Yes. EMC). I should know the answer to this but can see two sides of the coin and can't choose between the two. On one side it would be good to tie the gen and neutral down to Earth, but on the other side it would seem sensible to let the whole lot float. .. and how would an RCD cope? The particular case is using a gen to provide power for an outdoor PA system (and maybe a band). If the generator was supplying only one appliance, you could regard it as an isolated floating supply or an IT earthing system. However, as soon as you are driving multiple appliances (particularly something like an outdoor PA/band), it's not isolated anymore, and you probably need to make it a TT earthing system. In either case, the wiring regs still apply to the whole installation. -- Andrew Gabriel |
BigWallop wrote:
A generator doesn't have to have an earth point to ground, and some generators are more dangerous if they are fixed electrically to earth ground. It does depend on the generator though, and the in-built safety features it already has. Cite please? I don't think I have EVER seen a general purpose generator which did NOT have either the star point OR the neutral end of the winding (if single phase) tied to both the ground terminal and the case! Sure you can argue that an IT system is safer (but only if it has a earth fault detector) then a conventionally earthed system, but I don't think I have ever seen it done on an event site. For any normal event power generator, drive a local earth stake and bond all the exposed metalwork to it (including the stage structure if appropriate) and make sure you use RCDs in the distro. Regards, Dan. |
"Dave" wrote in message ... Whatever you do, make sure all the mics and guitars have got their own personal in-line safety isolators. Too many dead musicians in the past due to poor electrics - of course an area part pee doesn't cover at all. That's interesting, can you explain a little more. Do you mean isolating transformers? (or opto-isolators?) I google'd and came up with isolators to avoid earth loops but nothing about safety. Most guitarists will have one of these or similar already. Get something similar for any non radio handheld mics you provide. http://www.bss.co.uk/includes/produc...#attachmen ts But of course you should also have RCDs in the supplies as other have mentioned. |
BigWallop wrote:
If it is a small 240 volts AC genset, then what do want an earth point on it for. If you're plugging directly in to the generator, then it already has, or better have, its own safety devices protecting it and the supply outlets. A generator doesn't really need an earth point, and some generators don't really like being pinned to the earth, so you'd need to make sure that the metal work, if any, around the performance area was insulated from earth, but not the generator. Blocks of wood under the legs of any metal staging is usually enough to isolate the stage from earth. truly, no, this is not a Good Idea (tm). NT |
In article ,
Mike wrote: Whatever you do, make sure all the mics and guitars have got their own personal in-line safety isolators. Too many dead musicians in the past due to poor electrics - of course an area part pee doesn't cover at all. Often down to faulty instruments or PA systems. The common way these days is to PAT them all before use. Older method was to use a mains isolation transformer on each and every instrument. But this was in the days of valve amps where some didn't include their own internal isolating transformers. Most solid state gear will, as it runs off a lower voltage 'HT' rail. We often have a 100 KVA genny out for filming where mains isn't available. And I don't *think* they sink an earth spike. They run a 45 amp (or two) circuit to a sort of rugged CU, and 15 amp circuits from that. I'm not actually sure what sort of breakers are in that CU, though. I'll ask on Monday. -- *I have plenty of talent and vision. I just don't care. Dave Plowman London SW To e-mail, change noise into sound. |
In article om,
Dave Liquorice wrote: Should an earth spike be used when a generator is used to power class 1 equipment that normally needs an earth? Yes, and bond the generator chassis to that spike and to which ever phase from the alternator you decide to call "neutral". ie replicate the sort of supply that the equipment is designed to be plugged into. A protective earth wire connected to real ground via a spike, neutral bonded to that earth at the supply source (generator). Is this the practice when you have a genny on location, Dave? I'm pretty certain Lee Electrics don't do this with us, but not absolutely certain. But we have a genny out on Monday so I'll try and get chapter and verse from the operator. -- *Of course I'm against sin; I'm against anything that I'm too old to enjoy. Dave Plowman London SW To e-mail, change noise into sound. |
In article ,
Mike wrote: That's interesting, can you explain a little more. Do you mean isolating transformers? (or opto-isolators?) I google'd and came up with isolators to avoid earth loops but nothing about safety. Most guitarists will have one of these or similar already. Get something similar for any non radio handheld mics you provide. You're joking? Never ever seen this done. For a start, most decent mics are phantom powered, so need a DC path on screen and both signal lines. Of course vocal mics are often non powered types, but I'd not be keen on introducing an extra transformer there. I'd say all mixers if CE approved etc will be perfectly safe if fed from a safe power supply, so I'd make that the route to follow. -- *Never underestimate the power of very stupid people in large groups * Dave Plowman London SW To e-mail, change noise into sound. |
Dave Plowman (News) wrote:
In article , Mike wrote: Whatever you do, make sure all the mics and guitars have got their own personal in-line safety isolators. Too many dead musicians in the past due to poor electrics - of course an area part pee doesn't cover at all. Often down to faulty instruments or PA systems. The common way these days is to PAT them all before use. Older method was to use a mains isolation transformer on each and every instrument. But this was in the days of valve amps where some didn't include their own internal isolating transformers. Most solid state gear will, as it runs off a lower voltage 'HT' rail. We often have a 100 KVA genny out for filming where mains isn't available. And I don't *think* they sink an earth spike. They run a 45 amp (or two) circuit to a sort of rugged CU, and 15 amp circuits from that. I'm not actually sure what sort of breakers are in that CU, though. I'll ask on Monday. I'm guessing that the metal frame of a 100kVA gen would make good connection with earth without any spike. NT |
In article .com,
wrote: We often have a 100 KVA genny out for filming where mains isn't available. And I don't *think* they sink an earth spike. They run a 45 amp (or two) circuit to a sort of rugged CU, and 15 amp circuits from that. I'm not actually sure what sort of breakers are in that CU, though. I'll ask on Monday. I'm guessing that the metal frame of a 100kVA gen would make good connection with earth without any spike. Years ago when I worked on large OBs with gennys large enough to run several scanners with air-con, they *did* sink an earth rod. But export mains to remotes perhaps a mile away using a multicores - and joints - which had mains and several video and audio circuits all in one. Makes I laugh at the how do I get power to my shed type questions. ;-) -- *Change is inevitable, except from a vending machine. Dave Plowman London SW To e-mail, change noise into sound. |
On Sat, 14 May 2005 11:37:54 +0100, Dave Plowman (News) wrote:
Yes, and bond the generator chassis to that spike and to which ever phase from the alternator you decide to call "neutral". ie replicate the sort of supply that the equipment is designed to be plugged into. A protective earth wire connected to real ground via a spike, neutral bonded to that earth at the supply source (generator). Is this the practice when you have a genny on location, Dave? Firstly this is for a single phase supply from a alternator with a single winding. Don't know about 3 phase, with star connected the central point is "neutral" and I think would be earth bonded at the source. Delta connected, I think there is still a "neutral" wire so like wise. On a single winding alternator (ie two phases 180 deg apart) I'm 99.99% sure. Though the "earth spike" may just be laid on the tarmac and one of the wheels driven onto it... If there is a handy bit of open ground I have seen them hammered in but more often than not it's simply parked on. I'm pretty certain Lee Electrics don't do this with us, but not absolutely certain. But we have a genny out on Monday so I'll try and get chapter and verse from the operator. Be interesting to know, I really don't like the idea of a floating neutral for the reasons I stated earlier. Ordinary equipment is not designed to be "safe" with the neutral floating, single pole switches and fuses in the live only etc. I expect we'll be off a generator at St James's Park tommorow. If I can track down the operator I'll ask as well. -- Cheers Dave. pam is missing e-mail |
On Sat, 14 May 2005 14:51:00 +0100, Dave Plowman (News) wrote:
I'm guessing that the metal frame of a 100kVA gen would make good connection with earth without any spike. Not when the genny is built into the sound proof back of a truck with nice big rubber tyres between the chassis and the ground... Years ago when I worked on large OBs with gennys large enough to run several scanners with air-con, they *did* sink an earth rod. Conversely I have never seen a generator in use without an earth spike out at the generator, it might just be parked on but it's always there. But export mains to remotes perhaps a mile away using a multicores - and joints - which had mains and several video and audio circuits all in one. Makes I laugh at the how do I get power to my shed type questions. ;-) All those exported feeds are RCD protected and I think in the case of MkVII interlocked, no mains on the cable unless there is a box on the end. -- Cheers Dave. pam is missing e-mail |
wrote in message ... On 13 May, SNIP We hired a generator from a reputable firm to plug into a fixed socket to supply fixed equipment via a changeover switch during a mains outage. The generator was 230 volts and had it's centre tap earthed, giving 115-0-115 output relative to earth. On the fixed wiring was a fault, not showing normally of an earthed neutral. This resulted in a lot of fried wiring. Without the earth spike/bonding it could have been fried operator. It is essential that for a temporary arrangement all safety checks are carried out *and* earthing arrangements verified. The fact that the portable geny had an earthed centre tap would make it extremely UNsuitable for use with an external earthed output leg. As you say it is essential that whoever installs the system fully verifies it. You could of course argue that having a maximum of 115 volts to earth shock potential from the source would make it safer to use and a double pole 30mA RCD on the geny output should detect (and isolate) any imbalance or leakage to earth current. |
|
In message , "Dave Plowman (News)"
writes I'm pretty certain Lee Electrics don't do this with us, but not absolutely certain. But we have a genny out on Monday so I'll try and get chapter and verse from the operator. Did you know Joe from Lee? He did a lot of the Beeb golf OB's an interesting character!!!!!!!!!!! -- Bill |
In article ,
Bill wrote: I'm pretty certain Lee Electrics don't do this with us, but not absolutely certain. But we have a genny out on Monday so I'll try and get chapter and verse from the operator. Did you know Joe from Lee? He did a lot of the Beeb golf OB's an interesting character!!!!!!!!!!! Not offhand, but I'd guess they employ hundreds. And we don't normally use the large gennys you'd get on golf, etc. And most sparks are characters. ;-) -- *Do infants enjoy infancy as much as adults enjoy adultery? Dave Plowman London SW To e-mail, change noise into sound. |
On Fri, 13 May 2005 22:55:03 +0100, Dan Mills
wrote: I don't think I have EVER seen a general purpose generator which did NOT have either the star point OR the neutral end of the winding (if single phase) tied to both the ground terminal and the case! I have two single phase general purpose generators both of which earth at the midpoint between neutral and line - 110v. -- Peter Parry. http://www.wpp.ltd.uk/ |
Peter Parry wrote:
On Fri, 13 May 2005 22:55:03 +0100, Dan Mills wrote: I don't think I have EVER seen a general purpose generator which did NOT have either the star point OR the neutral end of the winding (if single phase) tied to both the ground terminal and the case! I have two single phase general purpose generators both of which earth at the midpoint between neutral and line - 110v. Ahh, sorry I should have added 240V as a rider on that, given we were talking event power it seemed reasonable to assume.... 55-0-55 is of course standard for building site power tools. Regards, Dan. |
On Mon, 16 May 2005 19:14:55 +0100, Dan Mills
wrote: Peter Parry wrote: Ahh, sorry I should have added 240V as a rider on that, given we were talking event power it seemed reasonable to assume.... 55-0-55 is of course standard for building site power tools. My apologies, I meant 240VAC with the earth at 110V so 110-0-110. -- Peter Parry. http://www.wpp.ltd.uk/ |
Dan Mills wrote:
Dave wrote: That's interesting, can you explain a little more. Do you mean isolating transformers? (or opto-isolators?) I google'd and came up with isolators to avoid earth loops but nothing about safety. I think he means RCDs..... Usual practice for small gigs is a 30mA rcd either at the generator (which gives no discrimination), or several at thee distribution board. I often add a 10mA unit just for the backline because backline tends to be the root of all evil in this matter. Do earth the generator frame with a spike, and DO bond the stage metalwork to generator earth (it probably will be via some path anyway and you would rather this didn't involve the screen of the audio snake....). The spike is to protect you the generator operator in the event of an internal fault imposing voltage between the generator frame and the earth connection on the socket which is probably earthed elsewhere (like say the stage). The RCD(s) protect the musicians from faults in the distro and their guitar amps (what never!). Bonding the stage metalwork reduces possible earth loop impedance issues and encourages faster disconnect times. Really once you get past the genny it is all fairly standard event power engineering. HTH. Regards, Dan. Thanks Dan, very useful. The gig went ahead successfully, the only problem was that we couldn't get the earth spike out so had to hammer it further into the ground. Dave |
Dave Plowman (News) wrote:
.... snipped We often have a 100 KVA genny out for filming where mains isn't available. And I don't *think* they sink an earth spike. They run a 45 amp (or two) circuit to a sort of rugged CU, and 15 amp circuits from that. I'm not actually sure what sort of breakers are in that CU, though. I'll ask on Monday. Did you ask? Dave |
Peter Parry wrote:
On Mon, 16 May 2005 19:14:55 +0100, Dan Mills wrote: Peter Parry wrote: Ahh, sorry I should have added 240V as a rider on that, given we were talking event power it seemed reasonable to assume.... 55-0-55 is of course standard for building site power tools. My apologies, I meant 240VAC with the earth at 110V so 110-0-110. OUCH! Given that UK practice only fuses (and switches) one leg (and in fact that I have seen RCDs that only switch one leg), how could this ever be viewed as safe in the UK? It is standard in America where most domestic power is done this way, but I cannot see such a thing as being safe in the UK. Regards, Dan (Very surprised to hear about this). |
In article ,
Dave wrote: We often have a 100 KVA genny out for filming where mains isn't available. And I don't *think* they sink an earth spike. They run a 45 amp (or two) circuit to a sort of rugged CU, and 15 amp circuits from that. I'm not actually sure what sort of breakers are in that CU, though. I'll ask on Monday. Did you ask? Fooking ran on batteries all day because of no genny. So no heating in the van - and there was a cold wind. Tomorrow, definitely a genny. A wasteland in Greenwich. ;-) And and 0.700 start so I'm off to bed... -- *You're just jealous because the voices only talk to me * Dave Plowman London SW To e-mail, change noise into sound. |
On Tue, 17 May 2005 22:42:56 +0100, Dave Plowman (News) wrote:
Fooking ran on batteries all day because of no genny. So no heating in the van - and there was a cold wind. A van? A VAN! Get out there man with yer trolly and brolly. Namby pamby sutherners. B-) I forgot to ask at St James's Park. One of the nice twin sets as well rather than a single. -- Cheers Dave. pam is missing e-mail |
In article om,
Dave Liquorice wrote: Fooking ran on batteries all day because of no genny. So no heating in the van - and there was a cold wind. A van? A VAN! Get out there man with yer trolly and brolly. Namby pamby sutherners. B-) But we don't grade the pictures afterwards. So the LD needs a controlled lighting environment to adjust the camera correctly. Ie a blacked out rear crew area of a van. And I like my own space too. ;-) Easier to concentrate - and I can use a speaker for rehearsals. Ok. Soft southerners. ;-) I forgot to ask at St James's Park. One of the nice twin sets as well rather than a single. The 100KVA genny simply parked on concrete with its earth rod under one front wheel. Each 'CU' has a main RCD, and RCDs feeding each circuit from it. Neutral not tied to earth - although I'm told some do. Warning lights on the 'CU' for polarity reversal. We were running single phase. -- *Toilet stolen from police station. Cops have nothing to go on. Dave Plowman London SW To e-mail, change noise into sound. |
"Dave Plowman (News)" wrote in message ... snip -- *Toilet stolen from police station. Cops have nothing to go on. Been peaking at the next script Dave ?!.... :~) |
In article ws.net,
:::Jerry:::: wrote: *Toilet stolen from police station. Cops have nothing to go on. Been peaking at the next script Dave ?!.... :~) No. That would be that after an alien attack from the planet Zog the same sex uniforms rape one another in the writing room. It's part of the set that needs using. Then, after their families get wiped out by a massive sunspot, they convert to Buddhism. Absolutely PC. And Terry and Rimini have a whispered conversation that only they can hear - almost. Below the noise of the genny which can't be situated where I wanted it because they haven't got long enough cables. Oh yes. Tomorrow, under the arches a few metres from Clapham Junction. Trains every 30 seconds. Which at least will drown out the helicopters. But I don't care. I'll start writing crappy poetry. -- *A bicycle can't stand alone because it's two tyred.* Dave Plowman London SW To e-mail, change noise into sound. |
On Wed, 18 May 2005 19:12:13 +0100, Dave Plowman (News) wrote:
The 100KVA genny simply parked on concrete with its earth rod under one front wheel. That is "normal". Each 'CU' has a main RCD, and RCDs feeding each circuit from it. Neutral not tied to earth - although I'm told some do. With *everything* through RCDs the N - E bond is not quite so important. A L - E fault will probably cause a big enough inbalance to trip one of the RCDs. Even if it doesn't anyone coming into contact the now "live" E will trip the RCD. -- Cheers Dave. pam is missing e-mail |
Dave Plowman (News) wrote:
*Toilet stolen from police station. Cops have nothing to go on. Been peaking at the next script Dave ?!.... :~) No. That would be that after an alien attack from the planet Zog the same sex uniforms rape one another in the writing room. Oh no, not *another* Gay Sex That Shocks The Tabloid Headline Writers episode. I can't imagine anything more frightening than Gina Gold and June Ackland in Hot Lesbian Truncheon Action :-) Owain |
All times are GMT +1. The time now is 04:42 AM. |