Metalworking (rec.crafts.metalworking) Discuss various aspects of working with metal, such as machining, welding, metal joining, screwing, casting, hardening/tempering, blacksmithing/forging, spinning and hammer work, sheet metal work.

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 138
Default Open neutral

I recently lost the neutral between the pole pig and my meter. I had 67VAC on one side and over 160VAC on the other. I heard loud frying sounds as multiple surge supressors died, along with circuit breakers tripping. The break has. Been repaired, but I only have a couple working circuits. I lost my A/C and I only have a few working lights. I need to replace the service. I plan to move it underground. No Internet, phone or TV for almost a month now. The open neutral damage the CATV line when the neutral current was shunted through it. I have very poor cell service here. I hope that this gets posted. It was 98 degrees in my bedroom the other night. No sleeping in that. I had to take a nap in my truck with the engine running so that I could use its A/C.
  #2   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 5,888
Default Open neutral

"Michael Terrell" wrote in message
...

I recently lost the neutral between the pole pig and my meter. I had 67VAC
on one side and over 160VAC on the other. I heard loud frying sounds as
multiple surge supressors died, along with circuit breakers tripping. The
break has. Been repaired, but I only have a couple working circuits. I lost
my A/C and I only have a few working lights. I need to replace the service.
I plan to move it underground. No Internet, phone or TV for almost a month
now. The open neutral damage the CATV line when the neutral current was
shunted through it. I have very poor cell service here. I hope that this
gets posted. It was 98 degrees in my bedroom the other night. No sleeping in
that. I had to take a nap in my truck with the engine running so that I
could use its A/C.

=========================

You have my sympathy. That's both damaging and difficult to recognize in
time.

In my case the resistance to the meter grounding stake and buried water pipe
was low enough to keep the 'phases' balanced most of the time. I first
noticed a fluorescent light buzzing when the refrigerator started. Voltage
measurements showed a solid 240V across the phases and only small
fluctuations in the 120V.

I don't have two outlets on opposite phases close enough together to compare
their voltages with multimeters so I built a box with two analog AC
voltmeters (from Variacs) and power cords long enough to reach between rooms
whose outlets were on opposite phases (which I had mapped). It plainly
showed the simultaneous dip in one phase and rise in the other, to as much
as 180V momentarily when the fridge compressor drew starting current from
the other phase. Digital voltmeters may not respond fast enough to catch
starting surges.
https://theengineeringmindset.com/12...-phase-us-can/

The evidence that convinced the power company to replace the outside drop
and meter box was a clamp-on ammeter reading of 30A flowing through a water
pipe. They cleaned the neutral lug coming into the meter box, and when that
didn't cure it they replaced the weatherhead and meter box.

My long term monitoring solution is this meter that I boxed and wired to a
GFI-equipped outlet strip to display the load on my solar system inverter.
When not on solar power it shows the voltage and current of the appliances I
operate on the stove, like the coffee pot or slow cooker. It can check for
degraded wiring connections by plugging it into one side of a duplex outlet
and the 1000 Watt coffee pot into the other.
https://www.amazon.com/bayite-BAYITE.../dp/B00YY1KOHA

jsw

  #3   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 138
Default Open neutral

Poor soil and no metal pipes around here. Looks like at least a few thousand dollars to make repairs.
  #4   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 172
Default Open neutral

On Fri, 10 Jul 2020 12:03:43 -0700 (PDT)
Michael Terrell wrote:

Poor soil and no metal pipes around here. Looks like at least a few thousand dollars to make repairs.


Probably way ahead of me... but if that was the Power Companys side
of the equipment they should be responsible for any damage caused by
a failure...

--
Leon Fisk
Grand Rapids MI

  #5   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 138
Default Open neutral

Not according to them. Some vines had grown up to them. They don't trim anything past the pole pig. The homeowner bas to do or have it done.


  #6   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 172
Default Open neutral

On Fri, 10 Jul 2020 15:11:13 -0700 (PDT)
Michael Terrell wrote:

Not according to them. Some vines had grown up to them. They don't trim anything past the pole pig. The homeowner bas to do or have it done.


IMO you're in lawsuit territory now. Having the consumer maintain
anything around high-voltage wires is not what they promote in all
their public messages...

--
Leon Fisk
Grand Rapids MI

  #7   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 138
Default Open neutral

I was told that they will disco.ect your service for a day and drop the line on the ground so that you can remove trees and vines.
  #8   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 220
Default Open neutral

On Fri, 10 Jul 2020 07:53:14 -0400, "Jim Wilkins"
wrote:

"Michael Terrell" wrote in message
...

I recently lost the neutral between the pole pig and my meter. I had 67VAC
on one side and over 160VAC on the other. I heard loud frying sounds as
multiple surge supressors died, along with circuit breakers tripping. The
break has. Been repaired, but I only have a couple working circuits. I lost
my A/C and I only have a few working lights. I need to replace the service.
I plan to move it underground. No Internet, phone or TV for almost a month
now. The open neutral damage the CATV line when the neutral current was
shunted through it. I have very poor cell service here. I hope that this
gets posted. It was 98 degrees in my bedroom the other night. No sleeping in
that. I had to take a nap in my truck with the engine running so that I
could use its A/C.

=========================

You have my sympathy. That's both damaging and difficult to recognize in
time.

In my case the resistance to the meter grounding stake and buried water pipe
was low enough to keep the 'phases' balanced most of the time. I first
noticed a fluorescent light buzzing when the refrigerator started. Voltage
measurements showed a solid 240V across the phases and only small
fluctuations in the 120V.

I don't have two outlets on opposite phases close enough together to compare
their voltages with multimeters so I built a box with two analog AC
voltmeters (from Variacs) and power cords long enough to reach between rooms
whose outlets were on opposite phases (which I had mapped). It plainly
showed the simultaneous dip in one phase and rise in the other, to as much
as 180V momentarily when the fridge compressor drew starting current from
the other phase. Digital voltmeters may not respond fast enough to catch
starting surges.
https://theengineeringmindset.com/12...-phase-us-can/

The evidence that convinced the power company to replace the outside drop
and meter box was a clamp-on ammeter reading of 30A flowing through a water
pipe. They cleaned the neutral lug coming into the meter box, and when that
didn't cure it they replaced the weatherhead and meter box.

My long term monitoring solution is this meter that I boxed and wired to a
GFI-equipped outlet strip to display the load on my solar system inverter.
When not on solar power it shows the voltage and current of the appliances I
operate on the stove, like the coffee pot or slow cooker. It can check for
degraded wiring connections by plugging it into one side of a duplex outlet
and the 1000 Watt coffee pot into the other.
https://www.amazon.com/bayite-BAYITE.../dp/B00YY1KOHA

jsw


PPL electric around here, from the weatherhead on down is the
homeowners, service drop to pole is theirs.

I had an Anchor brand meter base fail, fixed it on my dime. BTW
Anchor meter bases have a 100% failure rate.

If one ground rod is not suffcient use two. Then they recommend
copper sulfate soultion to soak the ground or a large copper plate at
least 3 feet deep underground.

Remove 333 to reply.
Randy
  #9   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 138
Default Open neutral

Grounding is difficult in many areas of Florida. Sand over limestone and dry. They repaired the drop, the real damage was indoors.
  #10   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 1,384
Default Open neutral

Michael Terrell wrote:

I recently lost the neutral between the pole pig and my meter. I had 67VAC
on one side and over 160VAC on the other. I heard loud frying sounds as
multiple surge supressors died, along with circuit breakers tripping. The
break has. Been repaired, but I only have a couple working circuits. I
lost my A/C and I only have a few working lights. I need to replace the
service. I plan to move it underground. No Internet, phone or TV for
almost a month now. The open neutral damage the CATV line when the neutral
current was shunted through it. I have very poor cell service here. I hope
that this gets posted. It was 98 degrees in my bedroom the other night. No
sleeping in that. I had to take a nap in my truck with the engine running
so that I could use its A/C.

The good news is that your AC runs mostly off of 240 V, and all those
components (compressor, fan motors) should be fine. Probably the control
transformers are fried, that should be a relatively inexpensive fix.

Many computers and LCD monitors should accept anything between 86 and 265
V, if they don't have voltage selector switches. Anything with a wall-wart
will at least need a new wall wart power supply (if on the high phase).

Jon


  #11   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 4,564
Default Open neutral

On Tue, 14 Jul 2020 19:35:10 -0500, Jon Elson
wrote:

Michael Terrell wrote:

I recently lost the neutral between the pole pig and my meter. I had 67VAC
on one side and over 160VAC on the other. I heard loud frying sounds as
multiple surge supressors died, along with circuit breakers tripping. The
break has. Been repaired, but I only have a couple working circuits. I
lost my A/C and I only have a few working lights. I need to replace the
service. I plan to move it underground. No Internet, phone or TV for
almost a month now. The open neutral damage the CATV line when the neutral
current was shunted through it. I have very poor cell service here. I hope
that this gets posted. It was 98 degrees in my bedroom the other night. No
sleeping in that. I had to take a nap in my truck with the engine running
so that I could use its A/C.

The good news is that your AC runs mostly off of 240 V, and all those
components (compressor, fan motors) should be fine. Probably the control
transformers are fried, that should be a relatively inexpensive fix.

Many computers and LCD monitors should accept anything between 86 and 265
V, if they don't have voltage selector switches. Anything with a wall-wart
will at least need a new wall wart power supply (if on the high phase).

Jon

Unless, like virtually ALL of mine, they are SMPS warts which ALSO
work from 84 to 240 volts - - -
  #12   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 138
Default Open neutral

It was a 120VAC window AC. It won't even turn on its fan. The computer and monitor were still working at 67VAC.
  #13   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 669
Default Open neutral

Sorry to hear that. A friend in Denver just had this issue in the apartment
he moved into last week. He bought two
https://www.amazon.com/dp/B015H0A3FO
meters which made it quite clear.

At my advice he used the words "Open Neutral" and "Fire Hazard"
on the ticket. He also unplugged everything not run by UPS &
logged UPS input voltage every which made it quite clear.

The electrician took one look and called the PoCo. They
responded ~4 hours later. They soon found poorly torqued
neutrals in the 14 meter panel/ main disconnect.

The two phases then stayed equal and stable.

On your losses, check your homeowner's insurance coverage.
--
A host is a host from coast to
& no one will talk to a host that's close..........................
Unless the host (that isn't close).........................pob 1433
is busy, hung or dead....................................20915-1433
  #14   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 138
Default Open neutral

On Friday, August 14, 2020 at 10:37:21 PM UTC-4, David Lesher wrote:
Sorry to hear that. A friend in Denver just had this issue in the apartment
he moved into last week. He bought two
https://www.amazon.com/dp/B015H0A3FO
meters which made it quite clear.

At my advice he used the words "Open Neutral" and "Fire Hazard"
on the ticket. He also unplugged everything not run by UPS &
logged UPS input voltage every which made it quite clear.

The electrician took one look and called the PoCo. They
responded ~4 hours later. They soon found poorly torqued
neutrals in the 14 meter panel/ main disconnect.

The two phases then stayed equal and stable.

On your losses, check your homeowner's insurance coverage.


I already had one of those. It isn't very accurate. I drilled a tiny hole in the back of the case to adjust the calibration pot, without having to open it again.

I reported it to Duke Energy as an open Neutral. They canceled the order, because the so called 'smart' meter showed 245 volts. I threatened to turn them over to the Florida PUCO if they did it a second time. The woman told me that it was only logged as an outage. I told her that I didn't care what their computer showed, I had given the same information both times. Tat time they showed up. Te bare neutral was arcing on the Triplex service drop where it had cracked and separated. I saved one end of the broken conductor, for evidence.
  #15   Report Post  
Posted to rec.crafts.metalworking
external usenet poster
 
Posts: 669
Default Open neutral

Michael Terrell writes:

https://www.amazon.com/dp/B015H0A3FO


On your losses, check your homeowner's insurance coverage.


I already had one of those. It isn't very accurate. I drilled a tiny hole i=
n the back of the case to adjust the calibration pot, without having to ope=
n it again.


The electrician the building hired was no dummy. Maxwell told me
the first thing he did was plug both meters into one socket to
check if they agreed. They did.

(I suspect even before that, he knew it was an open neutral, but
it was the right test to run.)

--
A host is a host from coast to
& no one will talk to a host that's close..........................
Unless the host (that isn't close).........................pob 1433
is busy, hung or dead....................................20915-1433
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
4 gauge neutral wire doesn't fit in my neutral bus panel? sparty Home Repair 8 July 22nd 06 02:50 AM
Can you help fix an "open neutral" G'day mates Home Repair 4 December 19th 05 09:38 PM
Open Neutral indication on switched split wired receptacle circuit [email protected] Home Ownership 0 November 10th 05 03:29 PM
Open Neutral Outlet BigMike Home Repair 7 April 29th 05 12:34 AM
Open Neutral?? JohnF Home Repair 7 January 13th 05 03:22 PM


All times are GMT +1. The time now is 07:19 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us