To all youse high speed spindle guys,
I have now a new 2.2KW VFD and matching 24000 RPM spindle motor. I am
wondering how important line and load reactors are for this setup.
Especially the line reactor because the motor/VFD combo is supposed to
be matched and because the motor wires will be short, 6 feet or so.
From looking online I have determined that a reactor rated at 12 amps,
2.5 mh, and 5% impedence is optimal. Can a reactor with a larger
current rating be used? Also, since the VFD can be connected to single
phase power and I want to use that option, I think I need to use a
reactor with a higher current rating. 18 amps instead of 12, right? I
haven't seen any single phase reactors yet on ebay which is why I am
asking. On the output side I am concerned with noise making problems
for the CNC mill (a Fadal 15XT) that the spindle will be installed in.
Will a reactor help with this sitaution? Do I really need one with
such a small (2.2 KW) motor?
Thanks,
Eric

Jon Elson May 11th 16 06:20 PM

VFDs and line reactors questions
 
wrote:

To all youse high speed spindle guys,
I have now a new 2.2KW VFD and matching 24000 RPM spindle motor. I am
wondering how important line and load reactors are for this setup.
Especially the line reactor because the motor/VFD combo is supposed to
be matched and because the motor wires will be short, 6 feet or so.
From looking online I have determined that a reactor rated at 12 amps,
2.5 mh, and 5% impedence is optimal. Can a reactor with a larger
current rating be used? Also, since the VFD can be connected to single
phase power and I want to use that option, I think I need to use a
reactor with a higher current rating. 18 amps instead of 12, right? I
haven't seen any single phase reactors yet on ebay which is why I am
asking. On the output side I am concerned with noise making problems
for the CNC mill (a Fadal 15XT) that the spindle will be installed in.
Will a reactor help with this sitaution? Do I really need one with
such a small (2.2 KW) motor?

I'm not sure a line reactor, per se is what you need. it does help in large
installations, where dozens of large VFDs cause harmonic problems on the
mains. Do you actually HAVE a problem with line interference?

I had some problems here, mostly hash on my computer screen when the VFD was
running. The fix was to put a line filter unit on the power input to the
VFD. This contains a combination of inductors and capacitors, and is
specifically designed to eliminate interference from equipment getting out
on the mains - and vice versa. These are often installed at the power entry
of various electronic gear, large computers and things like that. I have a
few in my junk box.

Here's one :
http://www.ebay.com/itm/380905940894
You might be able to find one closer.


Jon

Bob La Londe[_7_] May 11th 16 06:51 PM

VFDs and line reactors questions
 
wrote in message
...
To all youse high speed spindle guys,
I have now a new 2.2KW VFD and matching 24000 RPM spindle motor. I am
wondering how important line and load reactors are for this setup.
Especially the line reactor because the motor/VFD combo is supposed to
be matched and because the motor wires will be short, 6 feet or so.
From looking online I have determined that a reactor rated at 12 amps,
2.5 mh, and 5% impedence is optimal. Can a reactor with a larger
current rating be used? Also, since the VFD can be connected to single
phase power and I want to use that option, I think I need to use a
reactor with a higher current rating. 18 amps instead of 12, right? I
haven't seen any single phase reactors yet on ebay which is why I am
asking. On the output side I am concerned with noise making problems
for the CNC mill (a Fadal 15XT) that the spindle will be installed in.
Will a reactor help with this sitaution? Do I really need one with
such a small (2.2 KW) motor?
Thanks,
Eric


From what I have read you DO NOT need a line reactor for short runs. Some
writers disagree about what is considered short, but most say ten feet or
less. Some users have reported no problems with slightly longer runs. I do
use a shielded high flex cable between the VFD and the motor with the shield
going to the same common ground as the VFD. I just connect to the ground
screw on the VFD. I have not noticed any significant noise problems in my
shop with multiple computers running and two CNC machines with VFDs running
at the same time. I haven't even noticed any problems when welding when I
forgot, but I typically do not weld while a CNC machine is running.

Where you need to derate is at the VFD itself. 1/3in 3out VFDs typically
must be derated by about 30% when running on single phase. This isn't even
an issue unless you will have peaks in that top 30% of rating. I am running
a couple 800kw spindles on 1/3 750Kw VFDs without issue. I plan all cuts at
..25hp or less anyway. I go for light fast cuts for most jobs. Usually in
the .11hp or less range.

On my Hurco KMB1 I am running a 5HP Leland spindle motor with a 3.7Kw
Mitsubishi VFD with no issues. I overloaded it once or twice and it just
shut down. I have my SF calculator set at 3hp for that machine now, and
have had no issues since. I would note that Hurco did not originally rate
the machine at 5HP either. You do need to be aware of load in corners of
pockets etc. Typically that peak it doesn't last long enough to be a
problem. Only sustained cutting at max load, which I don't do anymore.

Spedestar makes a line of VFDs that are rated for full label load (peaks)
with single phase input. I have debated on buying one for the Hurco, but I
really don't need to push it that hard anyway. By going with lighter cuts
and faster feeds I get better parts (in my opinion) anyway. Except for
large bit drilliing in steel I rarely get calculated loads anywhere my self
determined limit of 3HP anyway.






Bob La Londe[_7_] May 11th 16 07:00 PM

VFDs and line reactors questions
 
"Bob La Londe" wrote in message
...
wrote in message
...
To all youse high speed spindle guys,
I have now a new 2.2KW VFD and matching 24000 RPM spindle motor. I am
wondering how important line and load reactors are for this setup.
Especially the line reactor because the motor/VFD combo is supposed to
be matched and because the motor wires will be short, 6 feet or so.
From looking online I have determined that a reactor rated at 12 amps,
2.5 mh, and 5% impedence is optimal. Can a reactor with a larger
current rating be used? Also, since the VFD can be connected to single
phase power and I want to use that option, I think I need to use a
reactor with a higher current rating. 18 amps instead of 12, right? I
haven't seen any single phase reactors yet on ebay which is why I am
asking. On the output side I am concerned with noise making problems
for the CNC mill (a Fadal 15XT) that the spindle will be installed in.
Will a reactor help with this sitaution? Do I really need one with
such a small (2.2 KW) motor?
Thanks,
Eric


From what I have read you DO NOT need a line reactor for short runs. Some
writers disagree about what is considered short, but most say ten feet or
less. Some users have reported no problems with slightly longer runs. I
do use a shielded high flex cable between the VFD and the motor with the
shield going to the same common ground as the VFD.


I only do that on my high speed spindles. The Hurco is wired with stranded
THHN in flex conduit, and then open inside the head.

I rarely get calculated loads anywhere NEAR my self determined limit of
3HP anyway.




[email protected] May 11th 16 07:11 PM

VFDs and line reactors questions
 
On Wed, 11 May 2016 12:20:35 -0500, Jon Elson
wrote:

wrote:

To all youse high speed spindle guys,
I have now a new 2.2KW VFD and matching 24000 RPM spindle motor. I am
wondering how important line and load reactors are for this setup.
Especially the line reactor because the motor/VFD combo is supposed to
be matched and because the motor wires will be short, 6 feet or so.
From looking online I have determined that a reactor rated at 12 amps,
2.5 mh, and 5% impedence is optimal. Can a reactor with a larger
current rating be used? Also, since the VFD can be connected to single
phase power and I want to use that option, I think I need to use a
reactor with a higher current rating. 18 amps instead of 12, right? I
haven't seen any single phase reactors yet on ebay which is why I am
asking. On the output side I am concerned with noise making problems
for the CNC mill (a Fadal 15XT) that the spindle will be installed in.
Will a reactor help with this sitaution? Do I really need one with
such a small (2.2 KW) motor?

I'm not sure a line reactor, per se is what you need. it does help in large
installations, where dozens of large VFDs cause harmonic problems on the
mains. Do you actually HAVE a problem with line interference?

I had some problems here, mostly hash on my computer screen when the VFD was
running. The fix was to put a line filter unit on the power input to the
VFD. This contains a combination of inductors and capacitors, and is
specifically designed to eliminate interference from equipment getting out
on the mains - and vice versa. These are often installed at the power entry
of various electronic gear, large computers and things like that. I have a
few in my junk box.

Here's one : http://www.ebay.com/itm/380905940894
You might be able to find one closer.


Jon

I have as yet not powered anything up but have read about problems,
one of them being drives failing from power surges upon powering up.
Apparently a line reactor helps to prevent damage from current surges
upon powering up.
Eric

[email protected] May 11th 16 07:30 PM

VFDs and line reactors questions
 
On Wed, 11 May 2016 10:51:19 -0700, "Bob La Londe"
wrote:

wrote in message
.. .
To all youse high speed spindle guys,
I have now a new 2.2KW VFD and matching 24000 RPM spindle motor. I am
wondering how important line and load reactors are for this setup.
Especially the line reactor because the motor/VFD combo is supposed to
be matched and because the motor wires will be short, 6 feet or so.
From looking online I have determined that a reactor rated at 12 amps,
2.5 mh, and 5% impedence is optimal. Can a reactor with a larger
current rating be used? Also, since the VFD can be connected to single
phase power and I want to use that option, I think I need to use a
reactor with a higher current rating. 18 amps instead of 12, right? I
haven't seen any single phase reactors yet on ebay which is why I am
asking. On the output side I am concerned with noise making problems
for the CNC mill (a Fadal 15XT) that the spindle will be installed in.
Will a reactor help with this sitaution? Do I really need one with
such a small (2.2 KW) motor?
Thanks,
Eric


From what I have read you DO NOT need a line reactor for short runs. Some
writers disagree about what is considered short, but most say ten feet or
less. Some users have reported no problems with slightly longer runs. I do
use a shielded high flex cable between the VFD and the motor with the shield
going to the same common ground as the VFD. I just connect to the ground
screw on the VFD. I have not noticed any significant noise problems in my
shop with multiple computers running and two CNC machines with VFDs running
at the same time. I haven't even noticed any problems when welding when I
forgot, but I typically do not weld while a CNC machine is running.

Where you need to derate is at the VFD itself. 1/3in 3out VFDs typically
must be derated by about 30% when running on single phase. This isn't even
an issue unless you will have peaks in that top 30% of rating. I am running
a couple 800kw spindles on 1/3 750Kw VFDs without issue. I plan all cuts at
.25hp or less anyway. I go for light fast cuts for most jobs. Usually in
the .11hp or less range.

On my Hurco KMB1 I am running a 5HP Leland spindle motor with a 3.7Kw
Mitsubishi VFD with no issues. I overloaded it once or twice and it just
shut down. I have my SF calculator set at 3hp for that machine now, and
have had no issues since. I would note that Hurco did not originally rate
the machine at 5HP either. You do need to be aware of load in corners of
pockets etc. Typically that peak it doesn't last long enough to be a
problem. Only sustained cutting at max load, which I don't do anymore.

Spedestar makes a line of VFDs that are rated for full label load (peaks)
with single phase input. I have debated on buying one for the Hurco, but I
really don't need to push it that hard anyway. By going with lighter cuts
and faster feeds I get better parts (in my opinion) anyway. Except for
large bit drilliing in steel I rarely get calculated loads anywhere my self
determined limit of 3HP anyway.




The run from VFD to motor is short, the run from the VFD to the
breaker panel is long, about 45 feet. All the wires in my shop run in
either metal wire ways or metal flex conduit. I don't know if this
makes any difference. The wires for powering the VFD are in the same
conduit and wire way as the wires powering the Fadal and I don't know
if this might be a problem either. I also am a little concerned about
grounding. The VFD manual says it should have its own ground, to not
share ground with anything else. For the larger machines in the shop
each has a ground wire running from the machine to the load center
ground bus bar. For some smaller machines, less than 3 HP, grounds are
shared. So there is a ground wire running through the wire way with
pigtails going to several machines. The circuit I want to run this VFD
from has this shared ground. I could pull another ground wire but it's
a real hassle to pull wire through the overhead flex conduit that the
supplies power to the side of the shop the VFD will be on. Any
thoughts on that? On your advice I bought a spindle/VFD package that
is rated about twice as powerful as the heaviest cut I plan to make.
So it looks like the derating business is taken care of. I program
virtually all inside corner milling as arcs and use cutters with a
smaller radius than the inside corner in order to reduce cutter load
and chatter.
Thanks,
Eric

Jon Elson[_3_] May 11th 16 07:49 PM

VFDs and line reactors questions
 
wrote:


I have as yet not powered anything up but have read about problems,
one of them being drives failing from power surges upon powering up.
Apparently a line reactor helps to prevent damage from current surges
upon powering up.

VFDs should be desinged to handle the inrush surge. Small VFDs may use NTC
thermistors or resistor/SCR circuits, my big VFD (11 KW) has a contactor
that clunks a half second after power-on, so it uses a resistor and relay to
short the resistor after the cap bank is charged.

2.5 mH is sure not going to help much with the inrush surge.

Jon

Jon Elson[_3_] May 11th 16 07:51 PM

VFDs and line reactors questions
 
Bob La Londe wrote:


From what I have read you DO NOT need a line reactor for short runs. Some
writers disagree about what is considered short, but most say ten feet or
less.

I think you are talkign about a LOAD reactor in this case. It is to protect
the motor windings from high voltage and rapid voltage swings from the VFD
OUTPUT. The OP is asking about reactors on the INPUT to the VFD.

Jon

DoN. Nichols[_2_] May 12th 16 02:32 AM

VFDs and line reactors questions
 
On 2016-05-11, Bob La Londe wrote:
wrote in message
...


To all youse high speed spindle guys,
I have now a new 2.2KW VFD and matching 24000 RPM spindle motor. I am
wondering how important line and load reactors are for this setup.
Especially the line reactor because the motor/VFD combo is supposed to
be matched and because the motor wires will be short, 6 feet or so.


[ ... ]

From what I have read you DO NOT need a line reactor for short runs. Some
writers disagree about what is considered short, but most say ten feet or
less. Some users have reported no problems with slightly longer runs. I do
use a shielded high flex cable between the VFD and the motor with the shield
going to the same common ground as the VFD. I just connect to the ground
screw on the VFD. I have not noticed any significant noise problems in my
shop with multiple computers running and two CNC machines with VFDs running
at the same time. I haven't even noticed any problems when welding when I
forgot, but I typically do not weld while a CNC machine is running.


And if you have the cable (unshielded) already -- you can try
with that for the run from VFD to motor and see whether there is any
interference. If you see what looks like some, get a roll of aluminum
foil, wrap it around the cable full length and ground it at the VFD end.
If what you considered to be interference goes away, then it is time to
spend the extra money for the shielded cable. Or route it through
flexible conduit which does a pretty good job at shielding anyway, and
protects the cable from abrasion.

Good Luck,
DoN.

--
Remove oil spill source from e-mail
Email: | (KV4PH) Voice (all times): (703) 938-4564
(too) near Washington D.C. | http://www.d-and-d.com/dnichols/DoN.html
--- Black Holes are where God is dividing by zero ---

[email protected] May 12th 16 05:44 PM

VFDs and line reactors questions
 
On Wed, 11 May 2016 13:49:44 -0500, Jon Elson
wrote:

wrote:


I have as yet not powered anything up but have read about problems,
one of them being drives failing from power surges upon powering up.
Apparently a line reactor helps to prevent damage from current surges
upon powering up.

VFDs should be desinged to handle the inrush surge. Small VFDs may use NTC
thermistors or resistor/SCR circuits, my big VFD (11 KW) has a contactor
that clunks a half second after power-on, so it uses a resistor and relay to
short the resistor after the cap bank is charged.

2.5 mH is sure not going to help much with the inrush surge.

Jon

Thanks Jon. Even though I'm pretty good at wiring up and fixing my
machines, both the mechanical and electronic parts, I still often need
some hand holding and/or guidance. Help from folks like you is really
appreciated.