DIYbanter

DIYbanter (https://www.diybanter.com/)
-   Metalworking (https://www.diybanter.com/metalworking/)
-   -   Isolating neutral bus from ground bus (https://www.diybanter.com/metalworking/293166-isolating-neutral-bus-ground-bus.html)

stryped[_3_] December 3rd 09 01:44 AM

Isolating neutral bus from ground bus
 
I was looking at my sub panel beside my main panel. (It is about 2
feet away and was added a few years ago because of lack of space in
main panel).

I believe I read that the netral and ground busses must be isolated on
a sub panel. When I checked with a continity tester, it beeped meaning
they are connected. This is a Square D Homeline series model number
HOMC2OU100C with a main breaker.

It looks like the bonding screw was removed though? There are two blue
screws one at the neutral lug area and one at the ground lug area. I
removed one and still contnuity. I removed both and no continuity.
These look like the screws you remove to remove the interrior of the
cabinet.

SHould I leave the screws out? Can anyone help me with this model?

Bob AZ December 3rd 09 05:48 AM

Isolating neutral bus from ground bus
 
SHould I leave the screws out? Can anyone help me with this model?

Your panels are too close to trust the ohmeter or whatever you are
using to chec for discontinuity. And with many wires in the subpanel
already in use I would not trust your testing. So disconnect
everything and verify there is no connection between the neutral and
ground buss.

Bob AZ


stryped[_3_] December 3rd 09 02:33 PM

Isolating neutral bus from ground bus
 
On Dec 2, 11:48*pm, Bob AZ wrote:
SHould I leave the screws out? Can anyone help me with this model?


Your panels are too close to trust the ohmeter or whatever you are
using to chec for discontinuity. And with many wires in the subpanel
already in use I would not trust your testing. So disconnect
everything and verify there is no connection between the neutral and
ground buss.

Bob *AZ


The power feed from the main panel to the sub panel has been removed.

Doug Miller December 3rd 09 02:56 PM

Isolating neutral bus from ground bus
 
In article , stryped wrote:
On Dec 2, 11:48=A0pm, Bob AZ wrote:
SHould I leave the screws out? Can anyone help me with this model?


Your panels are too close to trust the ohmeter or whatever you are
using to chec for discontinuity. And with many wires in the subpanel
already in use I would not trust your testing. So disconnect
everything and verify there is no connection between the neutral and
ground buss.



The power feed from the main panel to the sub panel has been removed.


And that has what, exactly, to do with the neutrals?

stryped[_3_] December 3rd 09 03:55 PM

Isolating neutral bus from ground bus
 
On Dec 3, 8:56*am, (Doug Miller) wrote:
In article , stryped wrote:

On Dec 2, 11:48=A0pm, Bob *AZ wrote:
SHould I leave the screws out? Can anyone help me with this model?


Your panels are too close to trust the ohmeter or whatever you are
using to chec for discontinuity. And with many wires in the subpanel
already in use I would not trust your testing. So disconnect
everything and verify there is no connection between the neutral and
ground buss.


The power feed from the main panel to the sub panel has been removed.


And that has what, exactly, to do with the neutrals?


I am saying I have 4-3 Romaex, the whole thing was removed. (Including
the neutrals).

Doug Miller December 3rd 09 04:40 PM

Isolating neutral bus from ground bus
 
In article , stryped wrote:
On Dec 3, 8:56=A0am, (Doug Miller) wrote:
In article =

..com, stryped wrote:

On Dec 2, 11:48=3DA0pm, Bob =A0AZ wrote:
SHould I leave the screws out? Can anyone help me with this model?


Your panels are too close to trust the ohmeter or whatever you are
using to chec for discontinuity. And with many wires in the subpanel
already in use I would not trust your testing. So disconnect
everything and verify there is no connection between the neutral and
ground buss.


The power feed from the main panel to the sub panel has been removed.


And that has what, exactly, to do with the neutrals?


I am saying I have 4-3 Romaex, the whole thing was removed. (Including
the neutrals).


Then what's your question?

stryped[_3_] December 3rd 09 04:57 PM

Isolating neutral bus from ground bus
 
On Dec 3, 10:40*am, (Doug Miller) wrote:
In article , stryped wrote:





On Dec 3, 8:56=A0am, (Doug Miller) wrote:
In article =

..com, stryped wrote:


On Dec 2, 11:48=3DA0pm, Bob =A0AZ wrote:
SHould I leave the screws out? Can anyone help me with this model?


Your panels are too close to trust the ohmeter or whatever you are
using to chec for discontinuity. And with many wires in the subpanel
already in use I would not trust your testing. So disconnect
everything and verify there is no connection between the neutral and
ground buss.


The power feed from the main panel to the sub panel has been removed.


And that has what, exactly, to do with the neutrals?


I am saying I have 4-3 Romaex, the whole thing was removed. (Including
the neutrals).


Then what's your question?- Hide quoted text -

- Show quoted text -


If all main wires are removed (2 hots neutral, ground) and the green
bonding screw is removed, why am I getting continuity between the
neutral bus and ground bus?

Doug Miller December 3rd 09 05:16 PM

Isolating neutral bus from ground bus
 
In article , stryped wrote:

If all main wires are removed (2 hots neutral, ground) and the green
bonding screw is removed, why am I getting continuity between the
neutral bus and ground bus?


Because you messed up somewhere. Without seeing it first-hand, it's hard to
say just where you messed up, but here are a few things to check:

- Have you confused the neutral and ground busses?

- Is there a jumper connecting the two busses?

- Is there a second bonding screw? I seem to recall from earlier discussions
that your panel has two neutral busses. If they're bonded together, and to the
box, and you removed only one bonding screw, well...

- Have you connected neutral and ground somewhere in your branch circuit
wiring? Remove *all* wires (the branch circuit neutrals) from the neutral bus,
and check again to see if there's continuity to the ground bus. If not, put
them back one at a time until there is continuity -- then you've found a
circuit with a problem. Don't assume that's the only such circuit.

- One way in which you can make an inadvertent connection between ground and
neutral is to overtighten the cable clamp on a Romex cable enough that it cuts
through the conductor insulation.

- Another way is through careless placement of ground wires in a receptacle
box (touching the neutral screws on the receptacle).

- Yet another way is by failing to understand that ground and neutral are
different things, and thus failing to understand that they need to be kept
separate when making fixture connections.

stryped[_3_] December 3rd 09 06:46 PM

Isolating neutral bus from ground bus
 
On Dec 3, 11:16*am, (Doug Miller) wrote:
In article , stryped wrote:

If all main wires are removed (2 hots neutral, ground) and the green
bonding screw is removed, why am I getting continuity between the
neutral bus and ground bus?


Because you messed up somewhere. Without seeing it first-hand, it's hard to
say just where you messed up, but here are a few things to check:

- Have you confused the neutral and ground busses?

- Is there a jumper connecting the two busses?

- Is there a second bonding screw? I seem to recall from earlier discussions
that your panel has two neutral busses. If they're bonded together, and to the
box, and you removed only one bonding screw, well...

- Have you connected neutral and ground somewhere in your branch circuit
wiring? Remove *all* wires (the branch circuit neutrals) from the neutral bus,
and check again to see if there's continuity to the ground bus. If not, put
them back one at a time until there is continuity -- then you've found a
circuit with a problem. Don't assume that's the only such circuit.

- One way in which you can make an inadvertent connection between ground and
neutral is to overtighten the cable clamp on a Romex cable enough that it cuts
through the conductor insulation.

- Another way is through careless placement of ground wires in a receptacle
box (touching the neutral screws on the receptacle).

- Yet another way is by failing to understand that ground and neutral are
different things, and thus failing to understand that they need to be kept
separate when making fixture connections.


My detached garage has the two grounding busses. (The one this sub
panel will feed.).

There are only two items hooked to this sub panel and they dont have a
neutral. One to a 50 amp breaker for my upstairs 1 ton unit and one 20
amp breaker to my outside unit. (This is my small heat pump for a
bonus room), Black wire to breaker, white wire to breaker, and ground.
That is it.

Doug Miller December 3rd 09 07:09 PM

Isolating neutral bus from ground bus
 
In article , stryped wrote:
My detached garage has the two grounding busses. (The one this sub
panel will feed.).


Post another photo. My recollection from the previous discussion a couple
months back is that the photo you posted then showed two _neutral_ busses and
one grounding bus, and you were confused about which was which -- you thought
one of the neutral busses was the grounding bus, and you had no idea what the
actual grounding bus was for.

I think you're still confused.

There are only two items hooked to this sub panel and they dont have a
neutral. One to a 50 amp breaker for my upstairs 1 ton unit and one 20
amp breaker to my outside unit. (This is my small heat pump for a
bonus room), Black wire to breaker, white wire to breaker, and ground.
That is it.


OK, so it's not a problem in your branch circuit wiring. What about all the
*other* things I told you to check? (reproduced below)

- Have you confused the neutral and ground busses?

- Is there a jumper connecting the two busses?

- Is there a second bonding screw? I seem to recall from earlier discussions
that your panel has two neutral busses. If they're bonded together, and to
the box, and you removed only one bonding screw, well...


stryped[_3_] December 3rd 09 09:05 PM

Isolating neutral bus from ground bus
 
On Dec 3, 1:09*pm, (Doug Miller) wrote:
In article , stryped wrote:

My detached garage has the two grounding busses. (The one this sub
panel will feed.).


Post another photo. My recollection from the previous discussion a couple
months back is that the photo you posted then showed two _neutral_ busses and
one grounding bus, and you were confused about which was which -- you thought
one of the neutral busses was the grounding bus, and you had no idea what the
actual grounding bus was for.

I think you're still confused.



There are only two items hooked to this sub panel and they dont have a
neutral. One to a 50 amp breaker for my upstairs 1 ton unit and one 20
amp breaker to my outside unit. (This is my small heat pump for a
bonus room), Black wire to breaker, white wire to breaker, and ground.
That is it.


OK, so it's not a problem in your branch circuit wiring. What about all the
*other* things I told you to check? (reproduced below)



- Have you confused the neutral and ground busses?


- Is there a jumper connecting the two busses?


- Is there a second bonding screw? I seem to recall from earlier discussions
that your panel has two neutral busses. If they're bonded together, and to
the box, and you removed only one bonding screw, well...- Hide quoted text -


- Show quoted text -


The photo you are refering to was to a second sub panel in the
detached garage. This one is in my attached garage.

I think I have figured out what is wrong.

I dont think the square d panel I am refering to in the attached
garage came with a grounding bus. (The GE panel int he attached garage
did). What I was thinking was the grounding bus is actually I believe
a second neutral bus.

I will check for continuity between the two busses in the cabinet and
the enclosure and if there is none, will buy one or two grounding
buses. I think that might be the problem all along.

What I dont understand is why the need to separate the neutral bus and
ground as they all end up combined in the main panel anyway.

Also, I always heard it was bad to have multiple ground paths. If I
have a ground rod for the house and one for the detached garage, arent
these all connected? All sub panels will be attached to the house
ground and the sub panel in the detached garage will also be attached
to another ground rod. AM I misisng something?

Robert Nichols December 4th 09 12:33 AM

Isolating neutral bus from ground bus
 
In article ,
stryped wrote:
:
:What I dont understand is why the need to separate the neutral bus and
:ground as they all end up combined in the main panel anyway.

The problem is that if the neutral connection breaks there is nothing to
indicate that there is a fault. The ground wire is carrying the
current. The fault can go undetected indefinitely. Now, if the ground
wire should break too, all of the supposedly grounded equipment
downstream of the break has AC line voltage on its "grounded" frame -- a
lethal hazard.

It is never permitted to have the ground conductor carrying any
non-fault current, and that includes current shared with another,
parallel conductor.

--
Bob Nichols AT comcast.net I am "RNichols42"

Doug Miller December 4th 09 03:03 AM

Isolating neutral bus from ground bus
 
In article , stryped wrote:

What I dont understand is why the need to separate the neutral bus and
ground as they all end up combined in the main panel anyway.


Because the neutral conductor _carries_current_. If you combine neutral and
ground anywhere except in the main panel, then all of your ground conductors
*everywhere* are carrying current also.

Also, I always heard it was bad to have multiple ground paths. If I
have a ground rod for the house and one for the detached garage, arent
these all connected? All sub panels will be attached to the house
ground and the sub panel in the detached garage will also be attached
to another ground rod. AM I misisng something?


Yes, you're missing a basic understanding of residential electrical wiring --
which is why a number of people have told you to hire an electrician.

ATP* December 4th 09 03:34 AM

Isolating neutral bus from ground bus
 

"Doug Miller" wrote in message
...
In article
,
stryped wrote:

What I dont understand is why the need to separate the neutral bus and
ground as they all end up combined in the main panel anyway.


Because the neutral conductor _carries_current_. If you combine neutral
and
ground anywhere except in the main panel, then all of your ground
conductors
*everywhere* are carrying current also.

Not everywhere, because there should be no cause for current to flow on
equipment grounding conductors connected to equipment in good condition.
Specifically on the feeder to the subpanel. The grounding conductor would be
paralleled with the grounded conductor (sharing the neutral load), and could
be an unsafe situation particularly if the grounding conductor is metallic
conduit, and especially if the neutral is impaired by poor connections,
etc..




All times are GMT +1. The time now is 01:24 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004 - 2014 DIYbanter