Our 50amp transfer unit only switches power from grid to generator after
30 seconds from when it sees power from the gen.

http://www.green-trust.org/wiki/inde...ransfer_Switch

Steve Spence
Dir., Green Trust, http://www.green-trust.org
Contributing Editor, http://www.off-grid.net
http://www.rebelwolf.com/essn.html

Ignoramus25850 wrote:
I have been playing with using relays of various kinds, as well as
contactors. I already built 2 phase converters, and a remote switch,
for instance. I have a few 90A and 75A contactors and solid state
relays and mag starter buttons and whatnot.

Here's what I have been thinking about. I have a 7 kW Onan DJE
generator that I have for emergencies. I want it to power my entire
house in emergencies (I know that I cannot run AC and some other
devices while under generator power).

It is expensive and painful to install a transfer switch. I want to
make something easier and cheaper to power the house in case of
emergencies, while at the same time preventing backfeeding.

I can, instead of a transfer switch, build a system that includes a
contactor, a mag starter, and a relay that only closes the main
generator contactor when the main circuit breaker is in the OFF
position.

It would work something like this. There will be a mechanical device
and a switch such that the switch could be closed only when the main
breaker is off. When the main breaker is on, the switch could not be
closed.

There will be a DC circuit, powered by a 9V battery, that would be a
signal input to a solid state crydom relay. The power contacts of the
relay would be in series with the power from generator. When the relay
is closed (only when the mains breaker is open), and a START button is
pressed on the start/stop switch (like ones used for mag starters),
the main contactor would close. The STOP button interrupts input to
the contactor, causing it to open. Turning the little switch near the
main breaker off would also interrupt the circuit, opening the
contactor.

This seems to be a very fool proof system. I can build it in 30
minutes, except that I would need more time to fabricate a mechanical
switch opener/closer.

I would like to ask that those who can visualize what I am describing,
to comment on this plan. Thanks

i

  #2   Report Post  
Toller
 
Posts: n/a
Default

I don't claim to have really followed it, but do know that the contacts on
my TS relay fused closed. Unless your device accomodates that (on the line
contacts) safely, it is no good.



  #3   Report Post  
SQLit
 
Posts: n/a
Default


"Ignoramus25850" wrote in message
...
I have been playing with using relays of various kinds, as well as
contactors. I already built 2 phase converters, and a remote switch,
for instance. I have a few 90A and 75A contactors and solid state
relays and mag starter buttons and whatnot.

Here's what I have been thinking about. I have a 7 kW Onan DJE
generator that I have for emergencies. I want it to power my entire
house in emergencies (I know that I cannot run AC and some other
devices while under generator power).

It is expensive and painful to install a transfer switch. I want to
make something easier and cheaper to power the house in case of
emergencies, while at the same time preventing backfeeding.

I can, instead of a transfer switch, build a system that includes a
contactor, a mag starter, and a relay that only closes the main
generator contactor when the main circuit breaker is in the OFF
position.

It would work something like this. There will be a mechanical device
and a switch such that the switch could be closed only when the main
breaker is off. When the main breaker is on, the switch could not be
closed.


Where I live the utilities require physcial and electrical interlocks.
Most residential panels do not lend themselves to a physcial interlock.
Square D is the only one that I know of that has a physical interlock
between the main and another breaker.
Then comes to the issue of the equipment being service rated. Then comes UL
listings.
A contactor/motor starter off the shelf I do not believe is service rated.


There will be a DC circuit, powered by a 9V battery, that would be a
signal input to a solid state crydom relay. The power contacts of the
relay would be in series with the power from generator. When the relay
is closed (only when the mains breaker is open), and a START button is
pressed on the start/stop switch (like ones used for mag starters),
the main contactor would close. The STOP button interrupts input to
the contactor, causing it to open. Turning the little switch near the
main breaker off would also interrupt the circuit, opening the
contactor.

This seems to be a very fool proof system. I can build it in 30
minutes, except that I would need more time to fabricate a mechanical
switch opener/closer.

I would like to ask that those who can visualize what I am describing,
to comment on this plan. Thanks

i


Check with your local authorities and utility before embarking on the
project.
If you can build this in 30 minutes, your a lot better than I am.


  #4   Report Post  
Chris
 
Posts: n/a
Default


"SQLit" wrote in message
...

"Ignoramus25850" wrote in message
...
I have been playing with using relays of various kinds, as well as
contactors. I already built 2 phase converters, and a remote switch,
for instance. I have a few 90A and 75A contactors and solid state
relays and mag starter buttons and whatnot.

Here's what I have been thinking about. I have a 7 kW Onan DJE
generator that I have for emergencies. I want it to power my entire
house in emergencies (I know that I cannot run AC and some other
devices while under generator power).

It is expensive and painful to install a transfer switch. I want to
make something easier and cheaper to power the house in case of
emergencies, while at the same time preventing backfeeding.

I can, instead of a transfer switch, build a system that includes a
contactor, a mag starter, and a relay that only closes the main
generator contactor when the main circuit breaker is in the OFF
position.

It would work something like this. There will be a mechanical device
and a switch such that the switch could be closed only when the main
breaker is off. When the main breaker is on, the switch could not be
closed.


Where I live the utilities require physcial and electrical interlocks.
Most residential panels do not lend themselves to a physcial interlock.
Square D is the only one that I know of that has a physical interlock
between the main and another breaker.
Then comes to the issue of the equipment being service rated. Then comes
UL
listings.
A contactor/motor starter off the shelf I do not believe is service rated.


There will be a DC circuit, powered by a 9V battery, that would be a
signal input to a solid state crydom relay. The power contacts of the
relay would be in series with the power from generator. When the relay
is closed (only when the mains breaker is open), and a START button is
pressed on the start/stop switch (like ones used for mag starters),
the main contactor would close. The STOP button interrupts input to
the contactor, causing it to open. Turning the little switch near the
main breaker off would also interrupt the circuit, opening the
contactor.

This seems to be a very fool proof system. I can build it in 30
minutes, except that I would need more time to fabricate a mechanical
switch opener/closer.


One piece of advice. I am not seeing it in your description, but I might be
missing it. Do you have a plan for seeing that the incoming power from the
street is back on?

I only mention this as I once had a friend do something similar, and failed
that part. Worse yet, he had to get into his car to drive by a few
neighbors to see if power had been restored. Even worse yet he had to drive
by two of them as they had generators. Remote area it was.

--
Chris

If you can read this, thank a teacher. If it is in English, thank a
soldier. If it is in ebonics, thank your Congressman.


  #5   Report Post  
 
Posts: n/a
Default

On Tue, 6 Sep 2005 11:47:41 -0400, "Chris" wrote:


"SQLit" wrote in message
...

"Ignoramus25850" wrote in message
...
I have been playing with using relays of various kinds, as well as
contactors. I already built 2 phase converters, and a remote switch,
for instance. I have a few 90A and 75A contactors and solid state
relays and mag starter buttons and whatnot.

Here's what I have been thinking about. I have a 7 kW Onan DJE
generator that I have for emergencies. I want it to power my entire
house in emergencies (I know that I cannot run AC and some other
devices while under generator power).

It is expensive and painful to install a transfer switch. I want to
make something easier and cheaper to power the house in case of
emergencies, while at the same time preventing backfeeding.

I can, instead of a transfer switch, build a system that includes a
contactor, a mag starter, and a relay that only closes the main
generator contactor when the main circuit breaker is in the OFF
position.

It would work something like this. There will be a mechanical device
and a switch such that the switch could be closed only when the main
breaker is off. When the main breaker is on, the switch could not be
closed.


Where I live the utilities require physcial and electrical interlocks.
Most residential panels do not lend themselves to a physcial interlock.
Square D is the only one that I know of that has a physical interlock
between the main and another breaker.
Then comes to the issue of the equipment being service rated. Then comes
UL
listings.
A contactor/motor starter off the shelf I do not believe is service rated.


There will be a DC circuit, powered by a 9V battery, that would be a
signal input to a solid state crydom relay. The power contacts of the
relay would be in series with the power from generator. When the relay
is closed (only when the mains breaker is open), and a START button is
pressed on the start/stop switch (like ones used for mag starters),
the main contactor would close. The STOP button interrupts input to
the contactor, causing it to open. Turning the little switch near the
main breaker off would also interrupt the circuit, opening the
contactor.

This seems to be a very fool proof system. I can build it in 30
minutes, except that I would need more time to fabricate a mechanical
switch opener/closer.


One piece of advice. I am not seeing it in your description, but I might be
missing it. Do you have a plan for seeing that the incoming power from the
street is back on?

I only mention this as I once had a friend do something similar, and failed
that part. Worse yet, he had to get into his car to drive by a few
neighbors to see if power had been restored. Even worse yet he had to drive
by two of them as they had generators. Remote area it was.

On my brothers recreational property the meter is at the road (with a
disconnect and main breaker) and there is a red pilot lite on the back
of the service box that tells him power is on. His transfer switch is
back at the buildings. When the light is on, he knows the grid is up.


  #6   Report Post  
 
Posts: n/a
Default

On Tue, 06 Sep 2005 15:21:20 GMT, Ignoramus25850
wrote:

I have been playing with using relays of various kinds, as well as
contactors. I already built 2 phase converters, and a remote switch,
for instance. I have a few 90A and 75A contactors and solid state
relays and mag starter buttons and whatnot.

Here's what I have been thinking about. I have a 7 kW Onan DJE
generator that I have for emergencies. I want it to power my entire
house in emergencies (I know that I cannot run AC and some other
devices while under generator power).

It is expensive and painful to install a transfer switch. I want to
make something easier and cheaper to power the house in case of
emergencies, while at the same time preventing backfeeding.

I can, instead of a transfer switch, build a system that includes a
contactor, a mag starter, and a relay that only closes the main
generator contactor when the main circuit breaker is in the OFF
position.

It would work something like this. There will be a mechanical device
and a switch such that the switch could be closed only when the main
breaker is off. When the main breaker is on, the switch could not be
closed.

There will be a DC circuit, powered by a 9V battery, that would be a
signal input to a solid state crydom relay. The power contacts of the
relay would be in series with the power from generator. When the relay
is closed (only when the mains breaker is open), and a START button is
pressed on the start/stop switch (like ones used for mag starters),
the main contactor would close. The STOP button interrupts input to
the contactor, causing it to open. Turning the little switch near the
main breaker off would also interrupt the circuit, opening the
contactor.

This seems to be a very fool proof system. I can build it in 30
minutes, except that I would need more time to fabricate a mechanical
switch opener/closer.

I would like to ask that those who can visualize what I am describing,
to comment on this plan. Thanks

i

Sounds like a good idea - BUT. Can you ensure the generator contactor
can NOT stay closed when the switch is shut off to turn the main
disconnect on? You need a failsafe system that makes it IMPOSSIBLE for
the generator to "lock on" - whether by killing the generator before
being able to reconnect to mains or whatever. That is why virtually
all transfer switches employ what boils down to a mechanical DPDT
knife switch.
  #7   Report Post  
John Grabowski
 
Posts: n/a
Default

Since you are going for a manual changeover, you might want to consider one
of these simple kits: http://www.interlockkit.com/intro.html



"Ignoramus25850" wrote in message
...
I have been playing with using relays of various kinds, as well as
contactors. I already built 2 phase converters, and a remote switch,
for instance. I have a few 90A and 75A contactors and solid state
relays and mag starter buttons and whatnot.

Here's what I have been thinking about. I have a 7 kW Onan DJE
generator that I have for emergencies. I want it to power my entire
house in emergencies (I know that I cannot run AC and some other
devices while under generator power).

It is expensive and painful to install a transfer switch. I want to
make something easier and cheaper to power the house in case of
emergencies, while at the same time preventing backfeeding.

I can, instead of a transfer switch, build a system that includes a
contactor, a mag starter, and a relay that only closes the main
generator contactor when the main circuit breaker is in the OFF
position.

It would work something like this. There will be a mechanical device
and a switch such that the switch could be closed only when the main
breaker is off. When the main breaker is on, the switch could not be
closed.

There will be a DC circuit, powered by a 9V battery, that would be a
signal input to a solid state crydom relay. The power contacts of the
relay would be in series with the power from generator. When the relay
is closed (only when the mains breaker is open), and a START button is
pressed on the start/stop switch (like ones used for mag starters),
the main contactor would close. The STOP button interrupts input to
the contactor, causing it to open. Turning the little switch near the
main breaker off would also interrupt the circuit, opening the
contactor.

This seems to be a very fool proof system. I can build it in 30
minutes, except that I would need more time to fabricate a mechanical
switch opener/closer.

I would like to ask that those who can visualize what I am describing,
to comment on this plan. Thanks

i


  #8   Report Post  
RoyJ
 
Posts: n/a
Default

Crossposts deleted

I'm all for building stuff that does what you want it to. But when you
start talking 7 kw of power plus the potential to have life endangering
consequences I start to drag out my "safety first" speech.

Officious speech mode on
There must be a POSITIVE interlock to avoid backfeeding to the grid.
This interlock should satisfy BOTH the power company and the electrical
inspector. Period. No discussion. Positive in this case means you, your
neighbor, an electican, or your power company guy can all work it
correctly without fear of screwing up. It should also be physically
positive in the sense that it won't bend short of using a vice grip or
prybar. Your description says something about some vague "mechanical
device" to accomplish this. I don't buy it.
Officious speech mode off

Other than that, why are you going though all the hassle of relays, 9
volt batteries, etc when all you need to do is switch a couple of circuits?

I also think you will have some issues with trying to power the whole
house with the 7 kw generator. I see a few neighbors trying to run their
houses with 5 kw (granted these are a bit smaller), modern houses take a
LOT of power, if several things come on at once, you kill the generator.
But with proper power management, you should have enough power to run
a small window AC unit as well as the rest of the required items like
refrigerator, freezer, well, and a few lights.

Most folks just use the 60 amp (??) Square D transfer switch to have 4
circuits that can be cut over to the generator. $100 or so, UL listed,
NEC compliant, looks like a sub panel, takes an afternoon to install.
The even simpler route is to have the critical items (eg furnace)on
plugs, just move the plug from grid to generator as required.

Cheers.

Ignoramus25850 wrote:
I have been playing with using relays of various kinds, as well as
contactors. I already built 2 phase converters, and a remote switch,
for instance. I have a few 90A and 75A contactors and solid state
relays and mag starter buttons and whatnot.

Here's what I have been thinking about. I have a 7 kW Onan DJE
generator that I have for emergencies. I want it to power my entire
house in emergencies (I know that I cannot run AC and some other
devices while under generator power).

It is expensive and painful to install a transfer switch. I want to
make something easier and cheaper to power the house in case of
emergencies, while at the same time preventing backfeeding.

I can, instead of a transfer switch, build a system that includes a
contactor, a mag starter, and a relay that only closes the main
generator contactor when the main circuit breaker is in the OFF
position.

It would work something like this. There will be a mechanical device
and a switch such that the switch could be closed only when the main
breaker is off. When the main breaker is on, the switch could not be
closed.

There will be a DC circuit, powered by a 9V battery, that would be a
signal input to a solid state crydom relay. The power contacts of the
relay would be in series with the power from generator. When the relay
is closed (only when the mains breaker is open), and a START button is
pressed on the start/stop switch (like ones used for mag starters),
the main contactor would close. The STOP button interrupts input to
the contactor, causing it to open. Turning the little switch near the
main breaker off would also interrupt the circuit, opening the
contactor.

This seems to be a very fool proof system. I can build it in 30
minutes, except that I would need more time to fabricate a mechanical
switch opener/closer.

I would like to ask that those who can visualize what I am describing,
to comment on this plan. Thanks

i

  #9   Report Post  
ATP*
 
Posts: n/a
Default


"Ignoramus25850" wrote in message
...
I have been playing with using relays of various kinds, as well as
contactors. I already built 2 phase converters, and a remote switch,
for instance. I have a few 90A and 75A contactors and solid state
relays and mag starter buttons and whatnot.

Here's what I have been thinking about. I have a 7 kW Onan DJE
generator that I have for emergencies. I want it to power my entire
house in emergencies (I know that I cannot run AC and some other
devices while under generator power).

Not a DIY job. Get a UL listed transfer switch, have a licensed electrician
install it and get it inspected.


  #10   Report Post  
Steve Spence
 
Posts: n/a
Default

riggghhttt. anyone with a bit of sense can install a transfer switch.

Steve Spence
Dir., Green Trust, http://www.green-trust.org
Contributing Editor, http://www.off-grid.net
http://www.rebelwolf.com/essn.html

ATP* wrote:

Not a DIY job. Get a UL listed transfer switch, have a licensed electrician
install it and get it inspected.




  #11   Report Post  
ATP*
 
Posts: n/a
Default


"Steve Spence" wrote in message
...
riggghhttt. anyone with a bit of sense can install a transfer switch.

Steve Spence
Dir., Green Trust, http://www.green-trust.org
Contributing Editor, http://www.off-grid.net
http://www.rebelwolf.com/essn.html


I've seen plenty of simpler electrical jobs screwed up or just poorly
executed by people with more than a bit of sense. In any case, it has to be
listed and inspected per the local utility regulations.

ATP* wrote:

Not a DIY job. Get a UL listed transfer switch, have a licensed
electrician install it and get it inspected.



  #12   Report Post  
Steve Spence
 
Posts: n/a
Default

maybe in your community, but not in mine. I wired my whole house, panels
and entrance. The power company only dropped to the meter on the pole.
that was the end of it. I did the rest.

Steve Spence
Dir., Green Trust, http://www.green-trust.org
Contributing Editor, http://www.off-grid.net
http://www.rebelwolf.com/essn.html

ATP* wrote:


I've seen plenty of simpler electrical jobs screwed up or just poorly
executed by people with more than a bit of sense. In any case, it has to be
listed and inspected per the local utility regulations.


ATP* wrote:


Not a DIY job. Get a UL listed transfer switch, have a licensed
electrician install it and get it inspected.




  #13   Report Post  
Eric R Snow
 
Posts: n/a
Default

On Wed, 07 Sep 2005 18:51:51 -0400, Steve Spence
wrote:

maybe in your community, but not in mine. I wired my whole house, panels
and entrance. The power company only dropped to the meter on the pole.
that was the end of it. I did the rest.

Steve Spence
Dir., Green Trust, http://www.green-trust.org
Contributing Editor, http://www.off-grid.net
http://www.rebelwolf.com/essn.html

ATP* wrote:


I've seen plenty of simpler electrical jobs screwed up or just poorly
executed by people with more than a bit of sense. In any case, it has to be
listed and inspected per the local utility regulations.


ATP* wrote:


Not a DIY job. Get a UL listed transfer switch, have a licensed
electrician install it and get it inspected.




In Washington state you are allowed to wire your own house. It then
must pass inspection. After that you must live in it for five years
before you can sell it. This is done to prevent bad wiring done by
people who are building spec homes. Not that everybody who builds a
spec home is going to do a bad job. Just that some people will skimp
and not use qualified people to do the wiring.
ERS
  #14   Report Post  
Bruce L. Bergman
 
Posts: n/a
Default

On Wed, 07 Sep 2005 18:51:51 -0400, Steve Spence
wrote:
ATP* wrote:


I've seen plenty of simpler electrical jobs screwed up or just poorly
executed by people with more than a bit of sense. In any case, it has to be
listed and inspected per the local utility regulations.


Some of the most screwed up DIY installations I've ever had to
rework were done by engineers and (literally) 'Rocket Scientists' who
thought they knew better. I think half the parts the former owner
used for the additions at this house (before we bought it) "fell off
the loading dock" at Rocketdyne in the '60's, though I can't prove it.

maybe in your community, but not in mine. I wired my whole house, panels
and entrance. The power company only dropped to the meter on the pole.
that was the end of it. I did the rest.


In EVERY community I know of, the electrical utility won't tie onto
a power panel and provide a meter unless the panel has been inspected
and approved as safe by /somebody/ referred to as the Authority Having
Jurisdiction or AHJ.

If there isn't a city building inspector, the job falls back to the
county or parish level. If it's on state or federally owned property,
then their inspector has the authority. The power utility doesn't
want the legal liability if someone gets hurt or killed, so they
insist on it.

Now after the AHJ has passed the installation, the utility has
connected the feed, and both parties are long gone, /then/ you can do
additional work without a permit, and cheat as much as you want, with
one gigantic caveat: As long as they never see it.

And if the AHJ comes back to check something else and sees you have
cheated, now you have a problem. They can (and will) force you to fix
it. If you don't, their ultimate recourse is to call the utility and
tell them to cut the feed and pull the meter, the installation is no
longer safe. Darkness and quiet quickly ensues. (*)

(* At least on things run from utility power, noting the crosspost.)

Except for mobile homes / manufactured housing in California, where
inspection of the meter pedestal and outside wiring is a city or
county responsibility like normal, but anything electrical inside or
on the coach itself is inspected by a State bureaucrat. Our local
mobile home inspector drives into Western LA County from Riverside,
where the closest office is.

-- Bruce --
--
Bruce L. Bergman, Woodland Hills (Los Angeles) CA - Desktop
Electrician for Westend Electric - CA726700
5737 Kanan Rd. #359, Agoura CA 91301 (818) 889-9545
Spamtrapped address: Remove the python and the invalid, and use a net.
  #15   Report Post  
Too_Many_Tools
 
Posts: n/a
Default

Excellent suggestion.

Ig, you come across as an enterprising and resourceful individual. I
would suggest focusing your talents on something that is not so
dangerous to...

- your finances
- your power company employees

If this homebrew setup would fail with fatal results for someone, you
will be on the hook litigation wise. There are reasons why sometimes we
spend the money on UL listed products, have a licensed electrician do
the work and have inspections....all to cover us legally.It only takes
one fatal failure to wipe you and your family out financially.

Let know how you end up doing it.

TMT



  #16   Report Post  
Bruce L. Bergman
 
Posts: n/a
Default

On Tue, 06 Sep 2005 15:21:20 GMT, Ignoramus25850
wrote:

I have been playing with using relays of various kinds, as well as
contactors. I already built 2 phase converters, and a remote switch,
for instance. I have a few 90A and 75A contactors and solid state
relays and mag starter buttons and whatnot.

Here's what I have been thinking about. I have a 7 kW Onan DJE
generator that I have for emergencies. I want it to power my entire
house in emergencies (I know that I cannot run AC and some other
devices while under generator power).

It is expensive and painful to install a transfer switch. I want to
make something easier and cheaper to power the house in case of
emergencies, while at the same time preventing backfeeding.

I can, instead of a transfer switch, build a system that includes a
contactor, a mag starter, and a relay that only closes the main
generator contactor when the main circuit breaker is in the OFF
position.


Go get yourself a UL Listed transfer switch of some sort. The
cheapest way is a Double-Throw safety switch. Looks just like the
fused disconnect for a motor, but the lever goes On-Off-On.

Or do some heavy-duty scrounging and buy a new or good used
automatic transfer switch that you can install. DO NOT TRY TO INVENT
THIS YOURSELF. It is life-safety critical, and there is absolutely no
reason for you to reinvent the wheel. Better you should pay a bit for
the right equipment - Use a proven design.

If your homebrewed transfer switch design is flawed, creates a
backfeed and kills a lineman or two working on power restoration (or
even just surprises the hell out of them when they find out the line
is energized) I can guarantee that they will find you, and that the
proceedings will not be pleasant.

If you do anything permanent, get it checked out and passed by the
local building inspector, and by the local utility. This is critical.

-- Bruce --

--
Bruce L. Bergman, Woodland Hills (Los Angeles) CA - Desktop
Electrician for Westend Electric - CA726700
5737 Kanan Rd. #359, Agoura CA 91301 (818) 889-9545
Spamtrapped address: Remove the python and the invalid, and use a net.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT +1. The time now is 05:10 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"