![]() |
VFD idle power use
I have an apple packing line that runs on three phase. It has four 3/4 hp.
motors and a hoist (1/2 hp) I leave the three phase ilder on 12 hours a day seven days a week. I'm trying to trim my $600 monthly fall electric bill. (mostly 5hp cooler) I get 7 amps usage while none of the packing line is running. It would be nice to get rid of the motor hum also. My question, would a VFD work well to provide three phase for this packing line. Is standby power usage on a VFD near 0? I'd have to bring motors in with the existing control logic and wire VFD so it always powers the output legs. Karl |
VFD as 3P power source or controls for your motors?
Here's a stupid question...why not just turn it off when not in use? "Karl Townsend" remove .NOT to reply wrote in message k.net... I have an apple packing line that runs on three phase. It has four 3/4 hp. motors and a hoist (1/2 hp) I leave the three phase ilder on 12 hours a day seven days a week. I'm trying to trim my $600 monthly fall electric bill. (mostly 5hp cooler) I get 7 amps usage while none of the packing line is running. It would be nice to get rid of the motor hum also. My question, would a VFD work well to provide three phase for this packing line. Is standby power usage on a VFD near 0? I'd have to bring motors in with the existing control logic and wire VFD so it always powers the output legs. Karl |
On Sat, 27 Aug 2005 17:20:47 GMT, "Karl Townsend"
remove .NOT to reply wrote: I have an apple packing line that runs on three phase. It has four 3/4 hp. motors and a hoist (1/2 hp) I leave the three phase ilder on 12 hours a day seven days a week. I'm trying to trim my $600 monthly fall electric bill. (mostly 5hp cooler) I get 7 amps usage while none of the packing line is running. It would be nice to get rid of the motor hum also. My question, would a VFD work well to provide three phase for this packing line. Is standby power usage on a VFD near 0? I'd have to bring motors in with the existing control logic and wire VFD so it always powers the output legs. I'd first check the no-load power consumption of the idler. If it's 7 amps at near 0 power factor, it doesn't cost much to run. Just watch the electric meter for a little while with the idler being the only load running. That (and a bit of calculation) will tell you cost per hour of the idler's overhead. My problem with VFD's is that they're so danged complicated. There are a buncha settings to get right. Maybe some of them have "default" values you can invoke if all you want is 3 phase 60 Hz. |
I'd first check the no-load power consumption of the idler. If it's 7 amps at near 0 power factor, it doesn't cost much to run. Just watch the electric meter for a little while with the idler being the only load running. That (and a bit of calculation) will tell you cost per hour of the idler's overhead. I get 15 cents per hour(7amp*220Volt*$0.10/KwHr), or about $54 per month, or $270 per season as my estimate. I've got no way to check power factor. Just watching the meter, you can see it turns way more than the load from all the lights being on in the barn.(1200 watts total). If the VFD has virtually 0 power use at no load, there is enough savings to install it here. My problem with VFD's is that they're so danged complicated. There are a buncha settings to get right. Maybe some of them have "default" values you can invoke if all you want is 3 phase 60 Hz. I've got VFDs on the mill and lathe. They both ran right outa the box. I agree there's a ton of parameters. Most all of them will run just fine at defaults. To answer another fellow's question, we pack apples between each customer visit all day long. We'd be turning it on/off fifty times a day to shut it off when not running. Not practical. We turn on the lights and phase converter when we open the door in the morning, and off when we lock up. Karl |
"Karl Townsend" remove .NOT to reply wrote in message nk.net... I'd first check the no-load power consumption of the idler. If it's 7 amps at near 0 power factor, it doesn't cost much to run. Just watch the electric meter for a little while with the idler being the only load running. That (and a bit of calculation) will tell you cost per hour of the idler's overhead. I get 15 cents per hour(7amp*220Volt*$0.10/KwHr), or about $54 per month, or $270 per season as my estimate. I've got no way to check power factor. Just watching the meter, you can see it turns way more than the load from all the lights being on in the barn.(1200 watts total). If the VFD has virtually 0 power use at no load, there is enough savings to install it here. My problem with VFD's is that they're so danged complicated. There are a buncha settings to get right. Maybe some of them have "default" values you can invoke if all you want is 3 phase 60 Hz. I've got VFDs on the mill and lathe. They both ran right outa the box. I agree there's a ton of parameters. Most all of them will run just fine at defaults. To answer another fellow's question, we pack apples between each customer visit all day long. We'd be turning it on/off fifty times a day to shut it off when not running. Not practical. We turn on the lights and phase converter when we open the door in the morning, and off when we lock up. Karl Karl Your estimate of the idler's power draw at no load indicates that the idler might be consuming about 2 HP. How big is the idler? Jerry |
"Karl Townsend" remove .NOT to reply wrote in message k.net... I have an apple packing line that runs on three phase. It has four 3/4 hp. motors and a hoist (1/2 hp) I leave the three phase ilder on 12 hours a day seven days a week. I'm trying to trim my $600 monthly fall electric bill. (mostly 5hp cooler) I get 7 amps usage while none of the packing line is running. It would be nice to get rid of the motor hum also. My question, would a VFD work well to provide three phase for this packing line. Is standby power usage on a VFD near 0? I'd have to bring motors in with the existing control logic and wire VFD so it always powers the output legs. Karl VFDs don't seem to create much heat when idling, so I can't imagine they're using much power. I've never checked one with a wattmeter, though. |
In article et,
Karl Townsend remove .NOT to reply wrote: I'd first check the no-load power consumption of the idler. If it's 7 amps at near 0 power factor, it doesn't cost much to run. Just watch the electric meter for a little while with the idler being the only load running. That (and a bit of calculation) will tell you cost per hour of the idler's overhead. I get 15 cents per hour(7amp*220Volt*$0.10/KwHr), or about $54 per month, or $270 per season as my estimate. Do you have a power-factor correction capacitor on the rotary converter? What you do is connect AC run capacitors between the two sides of the 220V line as it enters the rotary converter, measuring the current in one of those legs (between the circuit breaker and where you add the capacitors), until you get a minimum current. Past a certain amount of added capacitance, you will start to increase the current again. Anyway -- the current at the minimum will be pretty much the "real" current, and any above that will be "imaginary" current. (They add at 90 degrees, so you can't really just add them, but for most power services, the "real" current is all that you are charged for, and the benefits of tuning the power factor are mostly less heating of the wires and less chance of nuisance trips at the circuit breaker (if your "real" + "imaginary" current takes it close to the trip point.) I've got no way to check power factor. Just watching the meter, you can see it turns way more than the load from all the lights being on in the barn.(1200 watts total). If the VFD has virtually 0 power use at no load, there is enough savings to install it here. It does, indeed. The problem with using a single VFD for driving several machines is that you are then tempted to switch the power to the individual machines between the VFD and the machine, instead of setting things up so the machine commands the VFD to apply power or not to the machine. Switching between the VFD and the machine increases the risk of damaging the output circuits of the VFD with the switching spikes. I've gotten away with it when using a 1 hp milling machine on a 7-1/2 hp VFD, but I'm not sure how long I will get away with it even with that big a difference between capacity and load. Enjoy, DoN. -- Email: | Voice (all times): (703) 938-4564 (too) near Washington D.C. | http://www.d-and-d.com/dnichols/DoN.html --- Black Holes are where God is dividing by zero --- |
On Sun, 28 Aug 2005 03:07:37 GMT, "Karl Townsend"
remove .NOT to reply wrote: I'd first check the no-load power consumption of the idler. If it's 7 amps at near 0 power factor, it doesn't cost much to run. Just watch the electric meter for a little while with the idler being the only load running. That (and a bit of calculation) will tell you cost per hour of the idler's overhead. I get 15 cents per hour(7amp*220Volt*$0.10/KwHr), or about $54 per month, or $270 per season as my estimate. I've got no way to check power factor. Just watching the meter, you can see it turns way more than the load from all the lights being on in the barn.(1200 watts total). If the VFD has virtually 0 power use at no load, there is enough savings to install it here. My problem with VFD's is that they're so danged complicated. There are a buncha settings to get right. Maybe some of them have "default" values you can invoke if all you want is 3 phase 60 Hz. I've got VFDs on the mill and lathe. They both ran right outa the box. I agree there's a ton of parameters. Most all of them will run just fine at defaults. To answer another fellow's question, we pack apples between each customer visit all day long. We'd be turning it on/off fifty times a day to shut it off when not running. Not practical. We turn on the lights and phase converter when we open the door in the morning, and off when we lock up. Karl OK. So when should I visit to get some Honeycrisp apples? |
.... OK. So when should I visit to get some Honeycrisp apples? I've got a monster crop this year. They'll start Sept 24 and go to Dec 18 (last day open) I've got discounts for Semi truck loads. Karl |
Your estimate of the idler's power draw at no load indicates that the idler might be consuming about 2 HP. How big is the idler? 5 hp. idler. I've got a 5 hp VFD waiting for my Hardinge upgrade. I think I'll stick it in and try it for the fall. Karl |
"DoN. Nichols" wrote in message ... In article et, Karl Townsend remove .NOT to reply wrote: I'd first check the no-load power consumption of the idler. If it's 7 amps at near 0 power factor, it doesn't cost much to run. Just watch the electric meter for a little while with the idler being the only load running. That (and a bit of calculation) will tell you cost per hour of the idler's overhead. I get 15 cents per hour(7amp*220Volt*$0.10/KwHr), or about $54 per month, or $270 per season as my estimate. Do you have a power-factor correction capacitor on the rotary converter? What you do is connect AC run capacitors between the two sides of the 220V line as it enters the rotary converter, measuring the current in one of those legs (between the circuit breaker and where you add the capacitors), until you get a minimum current. Past a certain amount of added capacitance, you will start to increase the current again. Anyway -- the current at the minimum will be pretty much the "real" current, and any above that will be "imaginary" current. (They add at 90 degrees, so you can't really just add them, but for most power services, the "real" current is all that you are charged for, and the benefits of tuning the power factor are mostly less heating of the wires and less chance of nuisance trips at the circuit breaker (if your "real" + "imaginary" current takes it close to the trip point.) I've got no way to check power factor. Just watching the meter, you can see it turns way more than the load from all the lights being on in the barn.(1200 watts total). If the VFD has virtually 0 power use at no load, there is enough savings to install it here. It does, indeed. The problem with using a single VFD for driving several machines is that you are then tempted to switch the power to the individual machines between the VFD and the machine, instead of setting things up so the machine commands the VFD to apply power or not to the machine. Switching between the VFD and the machine increases the risk of damaging the output circuits of the VFD with the switching spikes. I've gotten away with it when using a 1 hp milling machine on a 7-1/2 hp VFD, but I'm not sure how long I will get away with it even with that big a difference between capacity and load. Enjoy, DoN. One VFD for each machine is really the right way to do it. Not really that expensive for the small motors involved. I wouldn't be surprised if the occasional nuisance fault shuts the line down. We found that out with heating circulators- all of a sudden you put a VFD on and you're dealing with another point of possible failure. |
In article . net, Karl Townsend
says... Your estimate of the idler's power draw at no load indicates that the idler might be consuming about 2 HP. How big is the idler? 5 hp. idler. How were you measuring that 7 amp current draw? With an amp-clamp meter, right? Well it was giving you the number that you didn't need to know - it was giving you the total of both in-phase *and* out-of-phase current. The phase angle for the current flowing an unloaded idler motor like that is about 90 degrees. It's not real current and won't spin your meter. Get a proper test setup to measure the phase angle and compute the *real* power while it's unloaded, and you will see your idler runs between 200 and 250 watts, most likely. That's the result I found with my 5hp converter. My estimation is that your converter is not what's costing you the money. Jim -- ================================================== please reply to: JRR(zero) at pkmfgvm4 (dot) vnet (dot) ibm (dot) com ================================================== |
OK, Karl. Don't forget the sack you owe me from a couple years back.
Bob Swinney "Karl Townsend" remove .NOT to reply wrote in message nk.net... ... OK. So when should I visit to get some Honeycrisp apples? I've got a monster crop this year. They'll start Sept 24 and go to Dec 18 (last day open) I've got discounts for Semi truck loads. Karl |
All times are GMT +1. The time now is 05:35 AM. |
Powered by vBulletin® Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
Copyright ©2004 - 2014 DIYbanter