if my generator can output 30 amps 240, i can take the 240 and split it to
120 and output a total of 60 amps, 30 each leg, now how much current is
flowing on the neutral? i have a 10/3 stranded cable about 90 feet long, i
dont know if it will be 60 or 30. my service entrance cable all three look
the same size wire so i guessing it will be 30. thanks tony


  #2   Report Post  
Jerry Martes
 
Posts: n/a
Default


"Tony" wrote in message
...
if my generator can output 30 amps 240, i can take the 240 and split it to
120 and output a total of 60 amps, 30 each leg, now how much current is
flowing on the neutral? i have a 10/3 stranded cable about 90 feet long,
i dont know if it will be 60 or 30. my service entrance cable all three
look the same size wire so i guessing it will be 30. thanks tony

Tony

I know this isnt a TRICK question. But, with both 110 lines loaded the
same, and resistive, there will be no current in the neutral, even though
power is being delivered to the two loads.

Jerry


  #3   Report Post  
carl mciver
 
Posts: n/a
Default

"Jerry Martes" wrote in message
news:eMjae.637$Nc.339@trnddc09...
|
| "Tony" wrote in message
| ...
| if my generator can output 30 amps 240, i can take the 240 and split it
to
| 120 and output a total of 60 amps, 30 each leg, now how much current is
| flowing on the neutral? i have a 10/3 stranded cable about 90 feet
long,
| i dont know if it will be 60 or 30. my service entrance cable all three
| look the same size wire so i guessing it will be 30. thanks tony
|
| Tony
|
| I know this isnt a TRICK question. But, with both 110 lines loaded the
| same, and resistive, there will be no current in the neutral, even though
| power is being delivered to the two loads.
|
| Jerry

Alright, I had to think about this one, and for the sake of the
unknowing, it should be explained. If a 220V load is being used, then
current flows from leg to leg, not leg to neutral, so the neutral carries no
current, as noted by older 220V circuits not using the neutral or ground,
just the two legs. If both legs are running 110V loads, however, then when
one leg is at maximum positive voltage, current will also be at a maximum
through that leg. However, the other leg will also be at maximum negative
voltage, so current will also be at a maximum on that leg too. If the loads
are equally balanced, then the neutral line that is shared between the two
(not the neutral for each leg) will have no current, as the current will be
going from leg to leg and not through the common neutral. However, since
current is rarely balanced between legs, only the difference between the
currents will pass through the neutral, and no more than the maximum current
of one leg (say, if one leg is maxxed out and the other one with no load)
then the common neutral will carry no more than the load from the loaded
leg.
It can get fancy with inductive loads, where currents and voltage do not
always line up evenly, but I'm too rusty on this one to make any more
statements.

  #4   Report Post  
Bruce L. Bergman
 
Posts: n/a
Default

On Fri, 22 Apr 2005 22:40:13 -0400, "Tony" wrote:

if my generator can output 30 amps 240, i can take the 240 and split it to
120 and output a total of 60 amps, 30 each leg, now how much current is
flowing on the neutral? i have a 10/3 stranded cable about 90 feet long, i
dont know if it will be 60 or 30. my service entrance cable all three look
the same size wire so i guessing it will be 30. thanks tony


If it's setup as a center-tapped neutral like normal, and you are
drawing an even 30 amps on each 120V leg at the end of the cable run,
the current on the neutral is zero. They balance each other out.
Worst case is 30 amps on the neutral if one hot leg is unloaded.

But you do not want that neutral to go open under any circumstances,
because very bad things happen when the loads get unbalanced - the
voltages start swinging.

Some old generators can be jumpered to provide true 60A 120V with
the windings in parallel. But then you can't use that 10/3 cable,
more like 4-3 - and voltage drop is a more serious problem...

-- Bruce --
--
Bruce L. Bergman, Woodland Hills (Los Angeles) CA - Desktop
Electrician for Westend Electric - CA726700
5737 Kanan Rd. #359, Agoura CA 91301 (818) 889-9545
Spamtrapped address: Remove the python and the invalid, and use a net.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electrical question Backlash Metalworking 13 February 12th 05 05:31 AM
Updates/Clarified Electrical Question Michael Roback Home Repair 3 January 23rd 05 11:58 PM
Slightly OT Electrical Question Anthony Bowles UK diy 21 October 20th 04 12:45 AM
Question about certification of electrical works Dave UK diy 1 September 29th 04 09:35 PM


All times are GMT +1. The time now is 03:29 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"