Home Repair (alt.home.repair) For all homeowners and DIYers with many experienced tradesmen. Solve your toughest home fix-it problems.

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
KissHanksAss
 
Posts: n/a
Default

"JonS" wrote in message
oups.com...
Hello All,

I'm hoping I can get some advice from someone out there who may have run
into the scenario I'll describe. Thanks ahead of time for taking the
time to read this.

The most useful piece of advice I can give you, is to ignore anything said
in reply to this post by DNandB, aka Daveinillinois, Advicegiver4U, Hello
Friend, or any of the countless other names he uses, as he is a complete
HVAC Hack, who has been virtually thrown out of the professional HVAC group.

There are Professional HVAC people who reply here, who will give you help.

Hank


  #2   Report Post  
JonS
 
Posts: n/a
Default Need help with HVAC problem ClimateMaster Geo/Trane Air Handler

Hello All,


I'm hoping I can get some advice from someone out there who may have
run into the scenario I'll describe. Thanks ahead of time for taking
the time to read this.


I moved into a new house last spring into which we installed a
geothermal heating system. The house is 3300 sq ft, lots of windows,
open family room, etc. The loop is closed, in three vertical wells and
the unit is a ClimateMaster Genesis Split. There is a 3 ton unit
servicing the 1st floor (sized to accomodate future basement finishing)
and a 2 ton unit for the 2nd floor. The refrigerant line runs to the
attic where it connects to a 2 ton Trane Variable Speed Air Handler.
The original contractor went out of business before the house was
complete without having finished the 2nd floor system (it needed
charged and checked out). I got it charged by another company and they
retured to adjust it once when it tripped off in the summer.


Now, to the winter and the problems. The loop seems to be working fine
- loop temperatures and pressures are reasonable. The 1st floor unit
works like a dream. We have a set temp of 72 deg and even on the
recent days when it's been near zero, the unit does not run full-time
and maintains temperature. The inlet air temp at a return on the floor
is about 70-71 and the exit air temp at the supplies are about 95
degrees. All of this is great, except for the fact that it must be
working harder to help the second floor.


My second floor air handler is running 24 hours a day and is still
failing to meet the set temperature. I've checked and sealed any
ductwork leaks and added additional insulation to the attic. I've got


R30 in the attic and R19 in all the walls. I don't think I'm losing



heat to the attic because on a recent 18 degree morning it was about 19
degrees up there. If I do a heat transfer balance based on the
R-values I should have and the 2nd floor temp, that was the correct
equilibrium temperature.

I'm also not losing it in the ductwork. The new contractor I have
looking at it put his gages on the lineset and said everything looks
fine.


If I take the temperature at the inlet and exit of the air handler, I
get a delta T of only 10 degrees. I'm pretty sure this is where the
problem is, but my HVAC guy has not been able to get out the last
couple days to diagnose it further.
Any thoughts? (and yes, I've changed the filter.)


Thanks.


Jon

  #3   Report Post  
m Ransley
 
Posts: n/a
Default

R 30 for an area that reaches zero is below code in my area of the
midwest. R 35 is usualy a minimum code in zone 5. R35 are minimum code
requirements, key word is minimum, to keep you from going broke to pay
your utility co.. You should be looking at R 60- 70-R 80+. I upped my
attic to R 100- 110 and second floor temps went up 5f. Old standards
need to be upgraded in this area. Also insulation settles and
fiberglass looses efficiency as it get cold. Perhaps as much as 25% at
Zero. Measure what you have in inches and calculate your true R and
put in alot more. How cold does it go in your area.

  #4   Report Post  
m Ransley
 
Posts: n/a
Default

Is the attic open unfinished

  #5   Report Post  
Geoman
 
Posts: n/a
Default


"m Ransley" wrote in message
...
R 30 for an area that reaches zero is below code in my area of the
midwest. R 35 is usualy a minimum code in zone 5. R35 are minimum code
requirements, key word is minimum, to keep you from going broke to pay
your utility co.. You should be looking at R 60- 70-R 80+. I upped my
attic to R 100- 110 and second floor temps went up 5f. Old standards
need to be upgraded in this area. Also insulation settles and
fiberglass looses efficiency as it get cold. Perhaps as much as 25% at
Zero. Measure what you have in inches and calculate your true R and
put in alot more. How cold does it go in your area.


R- 100? That's absurd.

For a 1750 Ft2 home here is what your R-100 does for you

R-38 = 3407 BTU total
R-48= 2590 BTU
r-100= 1290 BTU

So, your very seriously wasted a great deal of money on your R-100.





  #6   Report Post  
Geoman
 
Posts: n/a
Default


"JonS" wrote in message
oups.com...
Hello All,


I'm hoping I can get some advice from someone out there who may have
run into the scenario I'll describe. Thanks ahead of time for taking
the time to read this.


I moved into a new house last spring into which we installed a
geothermal heating system. The house is 3300 sq ft, lots of windows,
open family room, etc. The loop is closed, in three vertical wells and
the unit is a ClimateMaster Genesis Split.


Did they install the geo pipe into water wells? What antifreeze solution did
they use?


There is a 3 ton unit
servicing the 1st floor (sized to accomodate future basement finishing)
and a 2 ton unit for the 2nd floor. The refrigerant line runs to the
attic where it connects to a 2 ton Trane Variable Speed Air Handler.


Do you mean the loop water line or an actual refrigerant line? If its a
refrigerant line then you have a split unit? thats were the compressor is
separate from the air handler? Is the air handler in the attic or
conditioned space?


The original contractor went out of business before the house was
complete without having finished the 2nd floor system (it needed
charged and checked out). I got it charged by another company and they
retured to adjust it once when it tripped off in the summer.




Now, to the winter and the problems. The loop seems to be working fine
- loop temperatures and pressures are reasonable. The 1st floor unit
works like a dream. We have a set temp of 72 deg and even on the
recent days when it's been near zero, the unit does not run full-time
and maintains temperature. The inlet air temp at a return on the floor
is about 70-71 and the exit air temp at the supplies are about 95
degrees. All of this is great, except for the fact that it must be
working harder to help the second floor.


This is NOT an indication that everything is fine!!! All this tells me is
the back up heat is working and your paying about four times the amount of
electric than if your unit was running by itself.





My second floor air handler is running 24 hours a day and is still
failing to meet the set temperature.


Geo's will run all the time when its cold outside.


I've checked and sealed any
ductwork leaks and added additional insulation to the attic. I've got


R30 in the attic and R19 in all the walls. I don't think I'm losing


R-44 to 48 is the standard.



heat to the attic because on a recent 18 degree morning it was about 19
degrees up there. If I do a heat transfer balance based on the
R-values I should have and the 2nd floor temp, that was the correct
equilibrium temperature.

I'm also not losing it in the ductwork. The new contractor I have
looking at it put his gages on the lineset and said everything looks
fine.


What else did he do? I need exact information here.




If I take the temperature at the inlet and exit of the air handler, I
get a delta T of only 10 degrees.


All this tells me is the back up heat isn't working and the geothermal unit
is. But it doesn't tell me what the geothermal system is actually moving in
BTU's.



I'm pretty sure this is where the
problem is, but my HVAC guy has not been able to get out the last
couple days to diagnose it further.
Any thoughts? (and yes, I've changed the filter.)


Yep, I think your HVAC guy needs to be fired, there are tests that will
prove what is wrong with your system. One thing I notice is the upstairs
units back up reistance heat or what ever type you have isn't installed,
hooked up or isn't working or being called to work.

The downstairs unit temperatures tell me that the resistance heat is working
but maybe not the Geo. The HVAC guy could have done all the necessary tests
without puting his gauges on the refrigerant lines. As a matter of fact, if
this is the only thing he did you got ripped off big time.


Thanks.


Jon



  #7   Report Post  
JonS
 
Posts: n/a
Default

Geoman (and others),

Consider this a blanket reply to some of the posts already.

1. Yes, standard for this zone (central pennsylvania) call R-25 a
minimum in the attic and R-49 the recommended value. While increasing
the amount of insulation does help, it also reaches a point of
diminishing returns. I've installed an additional R-25 over the
bedrooms where the thermostat is present and it has show no difference.

2. Actually, the contractor working on it is taking it at the pace I
originally requested. He first checked the charge and settings on the
system, fixed some horrendous duct work issues, did a basic system
check and moved the thermostat from the open hallway over the living
room (where it kicked off when the fireplace was on). I asked him to
check back after I had a week or so of cold weather to analyze whether
those fixes helped. He just hasn't had the chance to get back and
check out the air handler. When I called him last, he is the one that
asked me to check the inlet and exit air temperatures and indicated it
should be something closer to 20-25 degrees.

Geoman, comments below to yours. Thanks.

Geoman wrote:
Did they install the geo pipe into water wells? What antifreeze

solution did
they use?

The vertical wells are closed loop. They drilled through limestone,
but did hit water in some regions. I believe the solution in the pipes
is a methanol solution, don't know what concentration.

Do you mean the loop water line or an actual refrigerant line? If its

a
refrigerant line then you have a split unit? thats were the

compressor is
separate from the air handler? Is the air handler in the attic or
conditioned space?


Yes, it is a split unit. The refrigerant line runs crom the compressor
to the air handler. The air handler is in the attic - unconditioned
space. I also noticed they only used R-4 supply pipes in the attic,
but the temperature drop from the unit exit to the room supplies is
minimal.


Now, to the winter and the problems. The loop seems to be working

fine
- loop temperatures and pressures are reasonable. The 1st floor

unit
works like a dream. We have a set temp of 72 deg and even on the
recent days when it's been near zero, the unit does not run

full-time
and maintains temperature. The inlet air temp at a return on the

floor
is about 70-71 and the exit air temp at the supplies are about 95
degrees. All of this is great, except for the fact that it must be
working harder to help the second floor.


This is NOT an indication that everything is fine!!! All this tells

me is
the back up heat is working and your paying about four times the

amount of
electric than if your unit was running by itself.


My fault for not providing all the information. Up until last week
when it dipped below zero, I have had the breaker for the electric
backup on the first floor unit turned off. I haven't needed it. On a
standard 10 degree day the unit runs about 1/2 time to sustain the set
temp without the use of the backup. Only during the cold nights when
the 2nd floor temp has been dropping to 65 has the first floor unit
kicked the back-up on. I've been monitoring it and it has not been on
much.

My second floor air handler is running 24 hours a day and is still
failing to meet the set temperature.


Geo's will run all the time when its cold outside.

Again, just not what I'm seeing with the first floor unit. That's the
primary thing that confuses my new contractor. He said he would have
expected to see the first floor unit running full-time to try to
supplement the 2nd floor, but it's not working that way. It still
cycles on and off without calling the electric. The entire first floor
is comfortable.


I've checked and sealed any
ductwork leaks and added additional insulation to the attic. I've

got


R30 in the attic and R19 in all the walls. I don't think I'm

losing

R-44 to 48 is the standard.



heat to the attic because on a recent 18 degree morning it was

about 19
degrees up there. If I do a heat transfer balance based on the
R-values I should have and the 2nd floor temp, that was the correct
equilibrium temperature.

I'm also not losing it in the ductwork. The new contractor I have
looking at it put his gages on the lineset and said everything

looks
fine.


What else did he do? I need exact information here.


I'm not sure, I was not home at the time.




If I take the temperature at the inlet and exit of the air handler,

I
get a delta T of only 10 degrees.


All this tells me is the back up heat isn't working and the

geothermal unit
is. But it doesn't tell me what the geothermal system is actually

moving in
BTU's.


That is the one thing I am trying to rectify. The second floor air
handler was installed without the heater because the original
contractor (now out of business) indicated it wouldn't be needed. I
need to add the breaker and run the additional line up to the attic in
order to add the heater. That said, while some of this might be offset
by the heater, I still think there is an issue. Even on a moderate day
in the 30's, the unit runs non-stop and the exit air temperature is
low.



I'm pretty sure this is where the
problem is, but my HVAC guy has not been able to get out the last
couple days to diagnose it further.
Any thoughts? (and yes, I've changed the filter.)


Yep, I think your HVAC guy needs to be fired, there are tests that

will
prove what is wrong with your system. One thing I notice is the

upstairs
units back up reistance heat or what ever type you have isn't

installed,
hooked up or isn't working or being called to work.

The downstairs unit temperatures tell me that the resistance heat is

working
but maybe not the Geo. The HVAC guy could have done all the necessary

tests
without puting his gauges on the refrigerant lines. As a matter of

fact, if
this is the only thing he did you got ripped off big time.


Again, this is the third contractor - original one out of business,
second one just to charge the lineset for 2nd floor unit, and this one
recommended by other builders and the ClimateMaster distributor. He is
aware the 2nd floor unit does not have the electric backup and is
ordering one for me. However, his other houses in the area with Geo
are not having problems. My neighbor has the same ClimateMaster Split
system and has not even turned on the breaker for the electric backup.
They keep a slightly lower set temp, about 69.

I have a stick thermometer at home and will get the inlet and exit geo
loop temps tonight. If you have any other thought on simple things I
can check, I would appreciate it. What would help? Pressure reading
from the gage on the primary unit? Loop temps? Is there a way I can
get flow rate based on jumpers/dip switches and line diameters. I've
found the ClimateMaster manual to be mostly useless for troubleshooting
unless I get a fault code (which I'm not). The Trane air handler
manual has no technical specs whatsoever, so I'm not sure what kind of
delta T I should get across the air handler.
Thanks.

Jon

Thanks.


Jon


  #8   Report Post  
JonS
 
Posts: n/a
Default

Some follow up info:

Attic Air Handler is Trane Model TWE031E13FB1, marked as using
Refrigerant 22.

The ground loop is split between the two ClimateMaster Units. Loop
temp in is 30.8 deg, loop temp out is 26.7 deg. Current outside temp
about 10 degrees.

The line out of the smaller compressor that runs to the attic measures
about 151 deg when I place the stick thermometer inside the insulation
and next to the copper (3/4 inch). In the attic I again placed the
thermometer along side the line before it runs into the air handler.
There I measured just under 140 deg. Not sure if it lost that much
heat over the trip or if it's just because the measurement is in
unconditioned attic.

Pressure gage on the 1st floor geo loop connection reads 49 psi.

Anything else I can measure or check myself, just let me know.
Thanks again.

Jon

  #9   Report Post  
Geoman
 
Posts: n/a
Default


"JonS" wrote in message
oups.com...
Some follow up info:

Attic Air Handler is Trane Model TWE031E13FB1, marked as using
Refrigerant 22.

The ground loop is split between the two ClimateMaster Units. Loop
temp in is 30.8 deg, loop temp out is 26.7 deg. Current outside temp
about 10 degrees.

The line out of the smaller compressor that runs to the attic measures
about 151 deg when I place the stick thermometer inside the insulation
and next to the copper (3/4 inch). In the attic I again placed the
thermometer along side the line before it runs into the air handler.
There I measured just under 140 deg. Not sure if it lost that much
heat over the trip or if it's just because the measurement is in
unconditioned attic.

Pressure gage on the 1st floor geo loop connection reads 49 psi.

Anything else I can measure or check myself, just let me know.
Thanks again.

Jon


Jon, the HVAC guy must start from the beginning and have no short cuts.

Ask him if he knows how to mathematically calculate and determine CFM's
Ask if he KNOWS how to determine the actual BTU's that the Geothermal is
delivering into the home.

If he can't answer with a solid answer then call another dealer, he isn't
familiar with the proper way to test and perform checks on Geothermal,
especially Climate Master.

If he doesn't know what ARI ratings of the geothermal is and doesn't have
them, tell him to leave, he doesn't know what he's doing.

Now, the unit not having a back up heater is bull. What if the unit fails?
No wonder the original company went out of business.

I'm still don't think the HVAC guy still isn't the right one for the job or
he would have done this when he first came on the lower unit. He should be
able to tell you exactly what BTU's are being delivered into your lower
unit. After you install the heaters he should be able to tell you the same
thing about upstairs. Even without heaters he could perform tests and
determine this value, especially if it was in AC mode.

Now, if he can do all this and knows what he's doing and everything tests
out ok including the loop, then the next step is to do a heat loss/gain and
see if its too small. Then if the heat loss is ok, the unit is sized right,
the loop performance is good then get someone in with a blower door and see
what those numbers are.

To be honest, there is no one in the world that can put a set of gauges on a
system and say, 'everything looks good'. All the gauges do is give you
pressures and tells you nothing about capacity, COP, EER, Seer and other
information. Those who put a set of gauges on and determine that
everything's ok is defined as a 'hack'.

In 15 years I have only two times put my gauges on a geothermal unit, it
usually is never necessary. Everytime you put gauges on a system you
introduce contaminants, and why put them on when they aren't going to tell
you very much...

Keep us informed.

Rich


  #10   Report Post  
JonS
 
Posts: n/a
Default

Rich,

Thank you for the comments. I will certainly ask him those questions
when he returns my call. Unfortunately, the subcontractors in this
area jump when the builders say jump and there is just too much new
construction going on right now. I General Contracted the house on my
own and did about half of the work. It actually came out better than
some of the spec homes in the area, it's just the headaches of dealing
with subs that don't make you a priority.

I've been trying to gather some of that information to do the calcs
myself. I've got BS and MS degrees in engineering, so the heat
transfer equation is no big deal. I don't have access (as far as I
know) to Manual J, etc, but I did compute total wall area, knock off
for windows, doors, figured for R-values, etc. - the basics. If I
could find the info in the manual as to how to determine the flow
rates, blower speeds, etc, I could do it. If you can point me in the
right direction or are willing to walk me through it, I would
appreciate it.

The interesting thing looking back is that I originally had 4 companies
bid this house. I still have the original quotes and the range in unit
sizes is : 4 Ton unit whole house, 2 1/2 ton first floor + 1 1/2 ton
2nd floor, 3 ton 1st + 2 ton 2nd (my system) and a 6 ton whole house
unit at the high end. Yet all of them were in the range of 600 to 750
feet of ground loop, with 750 being what i have.

Thanks again.

Jon

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Goldstar CNR-2994P Tuner problem Jerry G. Electronics Repair 4 June 21st 04 07:39 PM
Viewsonic Vertical Problem Scott Nielson Electronics Repair 6 May 15th 04 05:02 PM
Problem with retrace lines on EIZO F55S... [email protected] Electronics Repair 2 October 20th 03 01:29 AM
RCA tv 36" color problem TURTLE Electronics Repair 10 September 7th 03 07:16 PM
problem seamus Electronics Repair 1 July 25th 03 02:50 AM


All times are GMT +1. The time now is 03:14 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us