Default furnace blower cycles and shuts off permaturely

Hi,
I hope someone has an answer to this.

The blower of the furnace turns off while the burners keep burning.
After about 30 seconds, the burners shut off (I presume because of high
temp limit, since there is no air blowing), then about 10 seconds after
the burners shut off the blower turns ON again, then the burners kick
in again and the blower runs for about 2-3 minutes but then it shuts
off again while the burners burn, and so on repeteadly. All this while
the therm. is calling for heat. It is as if the blower cannot run
constantly while the burners are burning. Fan is set to Auto on the
therm.

Some more info. When the unit is first turned ON the fan appears to be
able to run for a longer time while the burners are burning, but
eventually shuts off before the burners go out. As the system runs
cycling like this, the blower cycles get shorter, that is the blower
cannot stay on for more than 2-3 minutes while the burners are burning.

I realize this is very dangerous as the burners and the core will get
very hot since there is no air flowing. The exhaust fan is running all
the time while all this cycling is happening. I have called a heating
specialist to come see the system but I want to make sure I am well
educated so that he does not give me the run around.... Also, what
should I expect to be charged in the north east for furnace maintanance
service if no new parts are needed ?

The system is a York 80 Diamond, natural gas, FHA.
The york 80 comes with an electronic furnace controller White-Rodgers
model 50A50-210 (I believe the 50A55 replaces the 50A50), so there is
no hi/lo limit controls that I can adjust... I don't know the age of
the furnace but the house is 20yrs old.
Any help and advice is greatly appreciated.

Thanks!!!!
Tony

  #2   Report Post  
TURTLE
 
Posts: n/a
Default


wrote in message
oups.com...
Hi,
I hope someone has an answer to this.

The blower of the furnace turns off while the burners keep burning.
After about 30 seconds, the burners shut off (I presume because of high
temp limit, since there is no air blowing), then about 10 seconds after
the burners shut off the blower turns ON again, then the burners kick
in again and the blower runs for about 2-3 minutes but then it shuts
off again while the burners burn, and so on repeteadly. All this while
the therm. is calling for heat. It is as if the blower cannot run
constantly while the burners are burning. Fan is set to Auto on the
therm.

Some more info. When the unit is first turned ON the fan appears to be
able to run for a longer time while the burners are burning, but
eventually shuts off before the burners go out. As the system runs
cycling like this, the blower cycles get shorter, that is the blower
cannot stay on for more than 2-3 minutes while the burners are burning.

I realize this is very dangerous as the burners and the core will get
very hot since there is no air flowing. The exhaust fan is running all
the time while all this cycling is happening. I have called a heating
specialist to come see the system but I want to make sure I am well
educated so that he does not give me the run around.... Also, what
should I expect to be charged in the north east for furnace maintanance
service if no new parts are needed ?

The system is a York 80 Diamond, natural gas, FHA.
The york 80 comes with an electronic furnace controller White-Rodgers
model 50A50-210 (I believe the 50A55 replaces the 50A50), so there is
no hi/lo limit controls that I can adjust... I don't know the age of
the furnace but the house is 20yrs old.
Any help and advice is greatly appreciated.

Thanks!!!!
Tony


This is Turtle.

I think you have a blower motor problem and there is 3 things your looking at.
New Motor, Oil the motor, or bad capasitor. After 20 years and you have not been
oiling the motor regularly, the bearings can be down on the motor and cause this
problem.

Now to price in the North east for just a adjustment of a part service call. You
can find out this by just calling back and ask what does a service call cost to
come service my furnace. He will tell you up front what the cost is for every
hvac service contractors have this cost very easily given out.

TURTLE


  #3   Report Post  
 
Posts: n/a
Default

Thanks Turtle.
The bearings are on the motor are sealed/lifetime lubed. The
motor/blower is direct drive. I hand spun the blower and it felt
really smooth and did not have signs of worn bearings (no noises nor
play either). The motor also appears to run well as the force of the
air coming out of the vents has not changed and appears to be
sufficient - not hurricane, but definitely good blowing...

Maybe the CAP has gone, but isn't the CAP only used for starting the
motor? give it some juice so that it does not trip the breaker, and
then once the motor is going th e cap does not serve a function
anymore?


Thanks again for your input
Tony

  #4   Report Post  
TURTLE
 
Posts: n/a
Default


wrote in message
oups.com...
Thanks Turtle.
The bearings are on the motor are sealed/lifetime lubed. The
motor/blower is direct drive. I hand spun the blower and it felt
really smooth and did not have signs of worn bearings (no noises nor
play either). The motor also appears to run well as the force of the
air coming out of the vents has not changed and appears to be
sufficient - not hurricane, but definitely good blowing...

Maybe the CAP has gone, but isn't the CAP only used for starting the
motor? give it some juice so that it does not trip the breaker, and
then once the motor is going th e cap does not serve a function
anymore?


Thanks again for your input
Tony


This is Turtle.

the Capasitor is to help start it but if the capasitor is weak or not working it
will let the motor run hot and start cutting in and out as it get hot and them
cools off to start again.

Motor after starting will run hot and cut out with out the ade of the capasitor.
It need the capasitor to run and start also. Most motor will start with out the
capasitor but will not run for long and start cutting in and out. In this
application it will not run very long with out the ade of the capasitor and
start cutting in and out.

TURTLE


  #5   Report Post  
TURTLE
 
Posts: n/a
Default


"TURTLE" wrote in message
...

wrote in message
oups.com...
Thanks Turtle.
The bearings are on the motor are sealed/lifetime lubed. The
motor/blower is direct drive. I hand spun the blower and it felt
really smooth and did not have signs of worn bearings (no noises nor
play either). The motor also appears to run well as the force of the
air coming out of the vents has not changed and appears to be
sufficient - not hurricane, but definitely good blowing...

Maybe the CAP has gone, but isn't the CAP only used for starting the
motor? give it some juice so that it does not trip the breaker, and
then once the motor is going th e cap does not serve a function
anymore?


Thanks again for your input
Tony


This is Turtle.

the Capasitor is to help start it but if the capasitor is weak or not working
it will let the motor run hot and start cutting in and out as it get hot and
them cools off to start again.

Motor after starting will run hot and cut out with out the ade of the
capasitor. It need the capasitor to run and start also. Most motor will start
with out the capasitor but will not run for long and start cutting in and out.
In this application it will not run very long with out the ade of the
capasitor and start cutting in and out.

TURTLE


This is Turtle Again.

I have seen blower motor turn free and still have bad bearing. It could have
been worn a good bit and then you oil them up and it turns free but the bearings
is letting a armoture come too close to the fields in the motor and cause it to
heat up because of not dragging but the motor verses the field possion in the
motor. Motor on direct drive have to be perfectly in the center of the windins
or it will run hot and start cutting in and out. 5 or 6 thousanths of a inch out
of center will or can start make it run hot and still turn free as can be.

If the capsitor is weak or out the motor will act up running or starting in
either case.

TURTLE




  #6   Report Post  
Andy
 
Posts: n/a
Default

Andy suggests:

If the problem is in the motor/capacitor/bearings, perhaps the
following test could
verify it.:

Run the motor on "fan only" and see if the same problem occurs,
i.e. the motor
starting and stopping. Make sure the thermostat is in a position where
the gas or
air condx function is disabled...



Here is another possible , often overlooked possibility.

Dirty air filter...... This would prevent enough air from moving
thru the
plenum where the high temperature switches are located. They heat up
and shut off the gas.
I have seen this before. Replacing the dirty filters fixed
it....However, the usual sympton is
that the gas shuts off and the motor continues to run, which is NOT
what you are seeing...
Just thought I'd mention it...

If the unit has an integral air conditioning condenser, if it is
clogged with dust and
dirt, the airflow could be restricted just as with the dirty filter.
This is harder to
clean, but possible, and fairly easy to check --- tho you have to undo
a few screws and
use a flashlight...

Just a couple other things to check before selling your car to pay
for a house call......

Andy

  #7   Report Post  
Bubba
 
Posts: n/a
Default

On 22 Dec 2004 10:08:41 -0800, "Andy" wrote:

Andy suggests:

If the problem is in the motor/capacitor/bearings, perhaps the
following test could
verify it.:

Run the motor on "fan only" and see if the same problem occurs,
i.e. the motor
starting and stopping. Make sure the thermostat is in a position where
the gas or
air condx function is disabled...



Here is another possible , often overlooked possibility.

Dirty air filter...... This would prevent enough air from moving
thru the
plenum where the high temperature switches are located. They heat up
and shut off the gas.
I have seen this before. Replacing the dirty filters fixed
it....However, the usual sympton is
that the gas shuts off and the motor continues to run, which is NOT
what you are seeing...
Just thought I'd mention it...

If the unit has an integral air conditioning condenser, if it is
clogged with dust and
dirt, the airflow could be restricted just as with the dirty filter.
This is harder to
clean, but possible, and fairly easy to check --- tho you have to undo
a few screws and
use a flashlight...

Just a couple other things to check before selling your car to pay
for a house call......

Andy


Andy,
I see you've been charged $80+ for changing a dirty air filter that
you were too stupid to remember to do.
Not all techs are that way.
As I see it, before you get all testy, this nasty comment makes up for
your last "one liner". Now, Fire Away.
Have a nice day.
Bubba
  #8   Report Post  
 
Posts: n/a
Default

Thanks for the help again Turtle.
I can run the fan in ON position and it keeps running continuously
without stopping. As a matter of fact, that is how I have it now until
the service tech arrives. I also changed the filter last month.

The diagnostic light on the ECU remains OFF, so the ECU is not noting
any problems with its sensors.


Tony

  #9   Report Post  
 
Posts: n/a
Default

Bubba,
I am sorry if I offended you by saying that I don't want to get the
"run around".
You may be or not a honest tech, that I don't know, but I've been
screwed too many times by dishonest people. So I am just trying to get
sufficient knowledge to be able to determine if I am being B.S.'ed or
if the technician is honest. Can you blame me?

Tony

  #10   Report Post  
Mark
 
Posts: n/a
Default

Is there a thermal overload switch in the motor? If so, it could be
sensing too much heat, real or 'imagined', & shutting it down.

--
Mark
Pepperell, MA

wrote in message
oups.com...
Thanks for the help again Turtle.
I can run the fan in ON position and it keeps running continuously
without stopping. As a matter of fact, that is how I have it now until
the service tech arrives. I also changed the filter last month.

The diagnostic light on the ECU remains OFF, so the ECU is not noting
any problems with its sensors.


Tony





  #13   Report Post  
TURTLE
 
Posts: n/a
Default


wrote in message
oups.com...
Thanks for the help again Turtle.
I can run the fan in ON position and it keeps running continuously
without stopping. As a matter of fact, that is how I have it now until
the service tech arrives. I also changed the filter last month.

The diagnostic light on the ECU remains OFF, so the ECU is not noting
any problems with its sensors.


Tony


This is Turtle.

This still does not prove anything.

#1 first when you turn the thermostat to cont. fan mode it shifts the motor to a
higher speed winding and a motor can be burnt up on heating / low or med. speed
and still run fine on high speed for cooling.

#2 The heating mode of the furnace relay board or relay system will run low or
medium speed to run the heat and high speed for cooling mode. You can have bad
bearing on a motor and start cutting out on low or medium speed but run fine on
high speed for you have more horse power on high and can over come the drag of
the bearings. Direct drive blower motor have different house power on each speed
as here : [ High Speed 1/2 H.P. 1075 R.P.M.'s ] [ Medium 1/3 H.P. 975 R.P.M.'s ]
[ Low Speed 1/4 H.P. 875 R.P.M. ] .

#3 Most all older blower motors have 3 or 4 speed types have completely
different motor built into them. A 4 speed motor has 4 different motors built
into it. You can burn up 1 or 2 or three of the speeds and still have 1 or more
that will still work fine. So your testing just showed that high speed of your
furnace is ok but never looked at heat speed or medium speed as it being good or
not.

#4 Now you have high speed running for the tech to see but when he gets there ,
tell him to check the problem speed of medium or the low speed set for heating.

#5 Now you still don't know what it is but you can use the high speed to heat
with till he gets there.

TURTLE


  #14   Report Post  
Rob
 
Posts: n/a
Default


"TURTLE" wrote in message
...

wrote in message
oups.com...
Thanks for the help again Turtle.
I can run the fan in ON position and it keeps running continuously
without stopping. As a matter of fact, that is how I have it now until
the service tech arrives. I also changed the filter last month.

The diagnostic light on the ECU remains OFF, so the ECU is not noting
any problems with its sensors.


Tony


This is Turtle.

This still does not prove anything.

#1 first when you turn the thermostat to cont. fan mode it shifts the
motor to a higher speed winding and a motor can be burnt up on heating /
low or med. speed and still run fine on high speed for cooling.

#2 The heating mode of the furnace relay board or relay system will run
low or medium speed to run the heat and high speed for cooling mode. You
can have bad bearing on a motor and start cutting out on low or medium
speed but run fine on high speed for you have more horse power on high and
can over come the drag of the bearings. Direct drive blower motor have
different house power on each speed as here : [ High Speed 1/2 H.P. 1075
R.P.M.'s ] [ Medium 1/3 H.P. 975 R.P.M.'s ] [ Low Speed 1/4 H.P. 875
R.P.M. ] .

#3 Most all older blower motors have 3 or 4 speed types have completely
different motor built into them. A 4 speed motor has 4 different motors
built into it. You can burn up 1 or 2 or three of the speeds and still
have 1 or more that will still work fine. So your testing just showed that
high speed of your furnace is ok but never looked at heat speed or medium
speed as it being good or not.

#4 Now you have high speed running for the tech to see but when he gets
there , tell him to check the problem speed of medium or the low speed set
for heating.

#5 Now you still don't know what it is but you can use the high speed to
heat with till he gets there.

Can't the 'Fan-on' speeds be changed to match the speed during the heat
cycle?


  #15   Report Post  
Andy
 
Posts: n/a
Default

Naw, Bubba. Did it myself......

I don't go runnin' to a unionized repair shop every time I
have a little problem...

Testy,.... hell, no.... But thanks for telling me what a new
filter can cost..... I only pay 50 cents....
Andy



  #16   Report Post  
Andy
 
Posts: n/a
Default

Andy writes:

I'm retired, too. I hardly find anything offensive....

Chill out...... Smell the roses.....

Andy

  #17   Report Post  
TURTLE
 
Posts: n/a
Default


"Rob" wrote in message news:5Rtyd.16567$dv1.5410@edtnps89...

"TURTLE" wrote in message
...

wrote in message
oups.com...
Thanks for the help again Turtle.
I can run the fan in ON position and it keeps running continuously
without stopping. As a matter of fact, that is how I have it now until
the service tech arrives. I also changed the filter last month.

The diagnostic light on the ECU remains OFF, so the ECU is not noting
any problems with its sensors.


Tony


This is Turtle.

This still does not prove anything.

#1 first when you turn the thermostat to cont. fan mode it shifts the motor
to a higher speed winding and a motor can be burnt up on heating / low or
med. speed and still run fine on high speed for cooling.

#2 The heating mode of the furnace relay board or relay system will run low
or medium speed to run the heat and high speed for cooling mode. You can have
bad bearing on a motor and start cutting out on low or medium speed but run
fine on high speed for you have more horse power on high and can over come
the drag of the bearings. Direct drive blower motor have different house
power on each speed as here : [ High Speed 1/2 H.P. 1075 R.P.M.'s ] [ Medium
1/3 H.P. 975 R.P.M.'s ] [ Low Speed 1/4 H.P. 875 R.P.M. ] .

#3 Most all older blower motors have 3 or 4 speed types have completely
different motor built into them. A 4 speed motor has 4 different motors built
into it. You can burn up 1 or 2 or three of the speeds and still have 1 or
more that will still work fine. So your testing just showed that high speed
of your furnace is ok but never looked at heat speed or medium speed as it
being good or not.

#4 Now you have high speed running for the tech to see but when he gets there
, tell him to check the problem speed of medium or the low speed set for
heating.

#5 Now you still don't know what it is but you can use the high speed to heat
with till he gets there.

Can't the 'Fan-on' speeds be changed to match the speed during the heat cycle?


This is Turtle.

Yes it sure can be done. I do them all the time by putting the heat and cooling
on the high speed but have to watch the heat rise of the heat by having the high
speed blowing on the heat mode. There is speed selectors on most all gas or
electric furnaces and you can select any speed you want for heating or cooling
modes. There is only on gas furnaces over 35 years or older before you just have
one speed for both and have no selection set up.

Now if the low or medium speed is running the motor hot due to bad bearing. You
have about 6 months to 2 years before the high speed will not work either and
catch you when it is freezing weather and want heat to not freeze to death. Fix
it now when you have time to work on it and not wait till your in trouble and
need it NOW type job. Now jobs cost a whole lot more than a job done in routen
work done on the furnace. It's like a water pump leaking water on your car and
then you just put it off till your going on vacation and get in the middle of no
where and need a water pump changed out. Done at a regular tiome it would cost
about $150.00 and on the road with a wrecker charges and Billy & Bob auto
service could cost you about $500.00+ in some cases. The furnace is the same
thing. Fix it now when you have time and service to do it on a timely manner.

TURTLE


  #18   Report Post  
Andy
 
Posts: n/a
Default

Andy writes:

Turtle knows more about this than I do.

If you are marginally technical, you can set the thing for normal
operation, pull one of
the clips off the gas valve (so it can't get gas), and see if the motor
still cuts out.
If it doesn't, it is probably a temp limit problem...

Bearing problems are tricky. I havn't ever run into one. Turtle
probably has....

However, the more you can do yourself to figure out the problem, the
less likely you
are to be at the mercy of incompetent techs who want to replace every
thing in your
furnace in order to cure the problem.

If it turns out to be a temp problem, you can short the temp sensor.
If , shorted with
a jumper, it still
works( and don't do this for very long) you need to replace a $3 temp
sensor,
which you maybe can do yourself...

Many repair men do not have the high morals of those who post here...
Andy

  #19   Report Post  
TURTLE
 
Posts: n/a
Default


"Andy" wrote in message
oups.com...
Andy writes:

Turtle knows more about this than I do.

If you are marginally technical, you can set the thing for normal
operation, pull one of
the clips off the gas valve (so it can't get gas), and see if the motor
still cuts out.
If it doesn't, it is probably a temp limit problem...

Bearing problems are tricky. I havn't ever run into one. Turtle
probably has....

However, the more you can do yourself to figure out the problem, the
less likely you
are to be at the mercy of incompetent techs who want to replace every
thing in your
furnace in order to cure the problem.

If it turns out to be a temp problem, you can short the temp sensor.
If , shorted with
a jumper, it still
works( and don't do this for very long) you need to replace a $3 temp
sensor,
which you maybe can do yourself...

Many repair men do not have the high morals of those who post here...
Andy


This is Turtle.

If you want to see if it is a Temperature switch you can watch these things and
tell in just a little while. Run the furnace up to 90ºF on the thermostat and
watch the flames on the furnace. If the High Temp switch / TSH is tripping it
out. The gas flames will go out when it trips and the fan will keep going. Then
in a little while when it cools back down the flames will come back on. Now the
fan will never stop blowing during all this time. You don't have to jump it but
just watch it .

TURTLE


  #20   Report Post  
 
Posts: n/a
Default

Thanks for the help again Turtle.
I can run the fan in ON position and it keeps running continuously
without stopping. As a matter of fact, that is how I have it now until
the service tech arrives. I also changed the filter last month.

The diagnostic light on the ECU remains OFF, so the ECU is not noting
any problems with its sensors.


Tony

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT +1. The time now is 06:20 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"