Default Does Federal Pacific stab and lock make tandem breakers?

I have a Federal Noark panel. I would like to add 2 circuits, but only
have one slot. I need to add a dedicated circuit for a dishwasher and
would like to put in a GFI circuit breaker for the kitchen and
bathroom.

I have been unable to find a Federal Pacific stab and lock tandem
breakers.

I have also read Federal Pacific panels are a fire risk. Is this true
and should I switch panels?

  #2   Report Post  
SQLit
 
Posts: n/a
Default


"Aaron" wrote in message
ups.com...
I have a Federal Noark panel. I would like to add 2 circuits, but only
have one slot. I need to add a dedicated circuit for a dishwasher and
would like to put in a GFI circuit breaker for the kitchen and
bathroom.

I have been unable to find a Federal Pacific stab and lock tandem
breakers.

I have also read Federal Pacific panels are a fire risk. Is this true
and should I switch panels?


Federal lost its UL listing years ago. Yes it was for fires. I remember
doing trouble calls in West Phoenix, when the full summer sun hit the
panels, the breakers would trip.

I can not tell you if you should change the service. That is going to cost
some big bucks.

This link will has 20-20 and 15-15 breakers listed.
http://www.electricsupplyonline.com/...e-breakers.php
Bring your banker for creative financing.

Forget the GFCI breaker idea, MUCH more expensive. Go to your electric
supply/box store and get GFCI outlets and install them. The kitchen and
bathrooms should not be on the same circuit. Kitchens need 2 free circuits
per code (at least) not counting installed equipment. Bathrooms as far as I
am concerned should be on their own circuit. My SO has enough electrical
stuff to make a small load bank. Thank god she can old plug in two items at
a time. I did find a outlet expander in the bathroom once, after destroying
it. I pleaded with her that I was not interested in dealing with a fire nor
her death. I do not think that she really bought it but I have not found any
more outlet expanders in the bathroom.


  #3   Report Post  
Speedy Jim
 
Posts: n/a
Default

Aaron wrote:
I have a Federal Noark panel. I would like to add 2 circuits, but only
have one slot. I need to add a dedicated circuit for a dishwasher and
would like to put in a GFI circuit breaker for the kitchen and
bathroom.

I have been unable to find a Federal Pacific stab and lock tandem
breakers.

I have also read Federal Pacific panels are a fire risk. Is this true
and should I switch panels?


As SQLit said, put GFCI recepts in and forget about a GFCI breaker.

Are FPE Panels risky? You betchum! And this story goes way back to
the 60's.

For a really detailed history:
http://www.inspect-ny.com/fpe/fpepanel.htm

Then you be the judge...

Jim
  #4   Report Post  
RBM
 
Posts: n/a
Default

You can get new circuit breakers made by the American Circuit Breaker Co.
which fit the FPE panel and are U.L. approved. To my knowledge they don't
make any half sized GFCI breakers, which like the others said, I wouldn't
use anyway. You are better off with receptacles. Over all, if it were my
house, I'd scrap the whole panel
"Aaron" wrote in message
ups.com...
I have a Federal Noark panel. I would like to add 2 circuits, but only
have one slot. I need to add a dedicated circuit for a dishwasher and
would like to put in a GFI circuit breaker for the kitchen and
bathroom.

I have been unable to find a Federal Pacific stab and lock tandem
breakers.

I have also read Federal Pacific panels are a fire risk. Is this true
and should I switch panels?



  #5   Report Post  
Aaron
 
Posts: n/a
Default

Thanks for the advice. I think I will look into switching out the
panel. I worked as an electrical apprectice before graduating college.
It has been about 10 years and I don't feel comfortable disconnecting
a live panel. How do you get a panel turned off that does not have a
main switch? Will the city kill your power for a day?

Also when I was working I remember Square D panels being easier to work
on then other brands, so I am thinking getting Square D. Any opinions?



  #6   Report Post  
SQLit
 
Posts: n/a
Default


"Aaron" wrote in message
oups.com...
Thanks for the advice. I think I will look into switching out the
panel. I worked as an electrical apprectice before graduating college.
It has been about 10 years and I don't feel comfortable disconnecting
a live panel. How do you get a panel turned off that does not have a
main switch? Will the city kill your power for a day?

Also when I was working I remember Square D panels being easier to work
on then other brands, so I am thinking getting Square D. Any opinions?


When I was doing residential change outs that were fed from over head I
would just cut the wires, hot, hot and then the messenger. I taped off the
hots and made sure that they were different lengths. I would tie off the
drop with an rope until I could get the new mast in place. Then using split
bolts I would re connect the drop to the new riser. Not exactly for the fait
of heart or to be done in a rain storm. Shingled roofs are not conductive.
You need to get a permit from the local folks. I was doing so many that I
was pulling 10 permits a week.

Do not know about your neck of the woods. But here if you ask for the power
to be shut off, there is no doubt that it will be off for at least 24 hours.
The utility will not restore power until the AHJ has signed off. Some times
48 hours for the clearance to get thought both parties. My customer were
not interested in that kind of service.

If your not comfortable with working live wires then get someone to do the
job. Panel up grades can have lots of "gotcha's" if your not aware of the
regs.
Biggest one I see around here is the 2 ground rods that are needed, unless
you have an ufer.

Your home your choice of panels. I would look about and see what I could
get the best deal on. Here in Phoenix the best place to buy residential
change outs used to be Evergreen hardware. They actually had a kit all set
up for a common installations.



  #7   Report Post  
RBM
 
Posts: n/a
Default

Killing power is different in all locations. Some places you can simply pull
the meter, others you have to cut the overhead wires. Sounds like it might
be a good idea to get some help. Square D is a nice choice for panels. They
have QO type which is very good and homeline which is OK
"Aaron" wrote in message
ups.com...
I have a Federal Noark panel. I would like to add 2 circuits, but only
have one slot. I need to add a dedicated circuit for a dishwasher and
would like to put in a GFI circuit breaker for the kitchen and
bathroom.

I have been unable to find a Federal Pacific stab and lock tandem
breakers.

I have also read Federal Pacific panels are a fire risk. Is this true
and should I switch panels?



  #10   Report Post  
 
Posts: n/a
Default

The only problem with Federal Pacific breakers is with the two ploe
breakers. I have a FPE panel installed in 1962 and all the original
single pole breakers work just fine (I load tested all of them). I
bought a ground fault breaker off eBay that was fairly new and from
Canada but I don't recommend them because they take up too much space
in your breaker panel. I had no trouble buying used FPE breakers off
eBay, but I got newer used ones with the white numbering, not the old
ones with the red numbers on them).

Now if your Federal Pacific panel has two pole breakers on it then loan
test them by overloading one phase of it and see if it trips both legs
properly. If it does than it's OK. The problem is that on a single
phase overload on a 2 pole breaker it wasn't tripping the other pole.



  #11   Report Post  
SQLit
 
Posts: n/a
Default


wrote in message
oups.com...
The only problem with Federal Pacific breakers is with the two ploe
breakers. I have a FPE panel installed in 1962 and all the original
single pole breakers work just fine (I load tested all of them).


I would be interested in how you really do load test your breakers. I have
tested circuit breakers for a lot of years. We call it primary and secondary
injection. Secondary injection is through the ct's. Your using the original
breaker curve published by FPE?
Our current supplies start out at about $15k for an MS-2 and crank well over
$40k for a Doble unit.

How do you test for LD and Instantous?

snipped


  #12   Report Post  
Speedy Jim
 
Posts: n/a
Default

wrote:
The only problem with Federal Pacific breakers is with the two ploe
breakers.


SNIP

WRONG!
Read all of the report:
http://www.inspect-ny.com/fpe/fpepanel.htm

One of the bigger problems with this design is the type of stab
into the bus. It often results in high-resistance contact and
resulting overheating.

In minor cases, that can mean inconvenience when lights on one
circuit flicker. In severe cases, it can end up with a melt-down
of the panel.

You have not truly lived until you've attempted to pry out an FPE
breaker and had it crumble into dust in your hand....

I used to think that testing of the breakers to ensure that they
tripped was adequate assurance of an FPE panel suitability.
No more.

Jim
  #13   Report Post  
Tekkie
 
Posts: n/a
Default

SQLit posted for all of us....


wrote in message
oups.com...
The only problem with Federal Pacific breakers is with the two ploe
breakers. I have a FPE panel installed in 1962 and all the original
single pole breakers work just fine (I load tested all of them).


I would be interested in how you really do load test your breakers. I have
tested circuit breakers for a lot of years. We call it primary and secondary
injection. Secondary injection is through the ct's. Your using the original
breaker curve published by FPE?
Our current supplies start out at about $15k for an MS-2 and crank well over
$40k for a Doble unit.

How do you test for LD and Instantous?

snipped



We know he "load tests" them. Shorts hot to ground.

Post info on the other stuff you posted, just curious...
--
Tekkie
  #14   Report Post  
Capt Retardo and the Skidmarks
 
Posts: n/a
Default

Previously in alt.home.repair, Speedy Jim proclaimed
:

wrote:
The only problem with Federal Pacific breakers is with the two ploe
breakers.


SNIP

WRONG!
Read all of the report:
http://www.inspect-ny.com/fpe/fpepanel.htm

One of the bigger problems with this design is the type of stab
into the bus. It often results in high-resistance contact and
resulting overheating.

In minor cases, that can mean inconvenience when lights on one
circuit flicker. In severe cases, it can end up with a melt-down
of the panel.

You have not truly lived until you've attempted to pry out an FPE
breaker and had it crumble into dust in your hand....

I used to think that testing of the breakers to ensure that they
tripped was adequate assurance of an FPE panel suitability.
No more.

Jim



...all I know is that our FPE breaker panel is *expensive* to replace
breakers and the lighting store strongly recommended that we replace
the entire panel as soon as possible. It's the original panel that
came with the house when it was built in the early 70's.

We haven't experienced any problems with the panel but it's on our
"to do" list for this spring.


  #15   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1
Default Does Federal Pacific stab and lock make tandem breakers?

replying to SQLit, Randy Hosea III wrote:
Pull the meter its much easier

--
for full context, visit http://www.homeownershub.com/mainten...rs-576823-.htm




  #16   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 7,157
Default Does Federal Pacific stab and lock make tandem breakers?

On Saturday, July 30, 2016 at 9:58:15 PM UTC-5, Randy Hosea III wrote:
replying to SQLit, Randy Hosea III wrote:
Pull the meter its much easier
--

Unfortunately, 11 years ago, Mr. SQLit was killed during a service call when he disturbed a hive of Aficanized Honey Bees. He died of blood loss due to all the bullet wounds from the tiny Glocks the bees shot him with. He is survived by a remarried wife, 3 Gay children and 56 gerbils. The gerbils really miss him. 8-(

[8~{} Uncle Pistol Monster
  #17   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 3,515
Default Does Federal Pacific stab and lock make tandem breakers?

Uncle Monster posted for all of us...



On Saturday, July 30, 2016 at 9:58:15 PM UTC-5, Randy Hosea III wrote:
replying to SQLit, Randy Hosea III wrote:
Pull the meter its much easier
--

Unfortunately, 11 years ago, Mr. SQLit was killed during a service call when he disturbed a hive of Aficanized Honey Bees. He died of blood loss due to all the bullet wounds from the tiny Glocks the bees shot him with. He is survived by a remarried wife, 3 Gay children and 56 gerbils. The gerbils really miss him. 8-(

[8~{} Uncle Pistol Monster


This site has a lot of gerbil activity. Has this ever been discussed? I
think fire ants would have taken over.

--
Tekkie
  #18   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 7,157
Default Does Federal Pacific stab and lock make tandem breakers?

On Monday, August 1, 2016 at 3:04:46 PM UTC-5, Tekkie® wrote:
Uncle Monster posted for all of us...



On Saturday, July 30, 2016 at 9:58:15 PM UTC-5, Randy Hosea III wrote:
replying to SQLit, Randy Hosea III wrote:
Pull the meter its much easier
--

Unfortunately, 11 years ago, Mr. SQLit was killed during a service call when he disturbed a hive of Aficanized Honey Bees. He died of blood loss due to all the bullet wounds from the tiny Glocks the bees shot him with. He is survived by a remarried wife, 3 Gay children and 56 gerbils. The gerbils really miss him. 8-(

[8~{} Uncle Pistol Monster


This site has a lot of gerbil activity. Has this ever been discussed? I
think fire ants would have taken over.
--
Tekkie


I can't keep any pets here at the nursing and rehab center so gerbils are out of the question but I did have a cockroach hang out with me for a little while. The poor little guy met a tragic death when he tried to befriend one of the nurses. ^_^

[8~{} Uncle Roach Monster
  #19   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 3,515
Default Does Federal Pacific stab and lock make tandem breakers?

Uncle Monster posted for all of us...



On Monday, August 1, 2016 at 3:04:46 PM UTC-5, Tekkie® wrote:
Uncle Monster posted for all of us...



On Saturday, July 30, 2016 at 9:58:15 PM UTC-5, Randy Hosea III wrote:
replying to SQLit, Randy Hosea III wrote:
Pull the meter its much easier
--

Unfortunately, 11 years ago, Mr. SQLit was killed during a service call when he disturbed a hive of Aficanized Honey Bees. He died of blood loss due to all the bullet wounds from the tiny Glocks the bees shot him with. He is survived by a remarried wife, 3 Gay children and 56 gerbils. The gerbils really miss him. 8-(

[8~{} Uncle Pistol Monster


This site has a lot of gerbil activity. Has this ever been discussed? I
think fire ants would have taken over.
--
Tekkie


I can't keep any pets here at the nursing and rehab center so gerbils are out of the question but I did have a cockroach hang out with me for a little while. The poor little guy met a tragic death when he tried to befriend one of the nurses. ^_^

[8~{} Uncle Roach Monster


The kind you inhale? g

--
Tekkie
  #20   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 7,157
Default Does Federal Pacific stab and lock make tandem breakers?

On Wednesday, August 3, 2016 at 1:35:55 PM UTC-5, Tekkie® wrote:
Uncle Monster posted for all of us...

On Monday, August 1, 2016 at 3:04:46 PM UTC-5, Tekkie® wrote:
Uncle Monster posted for all of us...

On Saturday, July 30, 2016 at 9:58:15 PM UTC-5, Randy Hosea III wrote:
replying to SQLit, Randy Hosea III wrote:
Pull the meter its much easier
--
Unfortunately, 11 years ago, Mr. SQLit was killed during a service call when he disturbed a hive of Aficanized Honey Bees. He died of blood loss due to all the bullet wounds from the tiny Glocks the bees shot him with.. He is survived by a remarried wife, 3 Gay children and 56 gerbils. The gerbils really miss him. 8-(

[8~{} Uncle Pistol Monster

This site has a lot of gerbil activity. Has this ever been discussed? I
think fire ants would have taken over.
--
Tekkie


I can't keep any pets here at the nursing and rehab center so gerbils are out of the question but I did have a cockroach hang out with me for a little while. The poor little guy met a tragic death when he tried to befriend one of the nurses. ^_^

[8~{} Uncle Roach Monster


The kind you inhale? g
--
Tekkie


Why on earth would I inhale an insect? They really bug me. o_O

[8~{} Uncle Bug-eyed Monster
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT +1. The time now is 02:15 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"