James P. Javery November 23rd 04 05:56 AM

240 volt service
 
I'm considering setting up a 240 volt appliance in my garage and I need to
determine whether it is being supplied with 220-240 volt service. The
breaker box in the garage has three wires coming in from elsewhere in the
building, one white wired to the neutral bus bar and two black wired to a 70
amp double pole breaker.

1. multimeter shows ~116 volts from hot to neutral for each of the two poles
on the main breaker
2. multimeter shows 0 volts from hot to hot between the two poles on the
main breaker
3. multimeter shows 0 ohms resistance between from hot to hot between the
two poles on the main breaker

Am I not testing this properly, or is it possible that my garage is not
wired for "three wire single phase" as I suppose electricians prefer to call
it? My understanding would lead me to believe that the two hot wires are
connected upstream to the same half of my building's electrical supply, so
I'm only getting 120 in my garage despite the two hot wires.

Any ideas? Are there any other tests I can perform to verify or invalidate
my conclusions? Thanks for any help you may provide...

-James



Greg November 23rd 04 06:36 AM

You have both "hots" on the same phase. Go back to the main panel and figure
out why.


Mad Mac November 23rd 04 06:36 AM

I agree with your diagnosis. I used to run into this when I was
repairing dryers, people had the supply installed by a "handyman" or did
it themselves and wondered why the dryer didn't dry.

James P. Javery wrote:
I'm considering setting up a 240 volt appliance in my garage and I need to
determine whether it is being supplied with 220-240 volt service. The
breaker box in the garage has three wires coming in from elsewhere in the
building, one white wired to the neutral bus bar and two black wired to a 70
amp double pole breaker.

1. multimeter shows ~116 volts from hot to neutral for each of the two poles
on the main breaker
2. multimeter shows 0 volts from hot to hot between the two poles on the
main breaker
3. multimeter shows 0 ohms resistance between from hot to hot between the
two poles on the main breaker

Am I not testing this properly, or is it possible that my garage is not
wired for "three wire single phase" as I suppose electricians prefer to call
it? My understanding would lead me to believe that the two hot wires are
connected upstream to the same half of my building's electrical supply, so
I'm only getting 120 in my garage despite the two hot wires.

Any ideas? Are there any other tests I can perform to verify or invalidate
my conclusions? Thanks for any help you may provide...

-James



zxcvbob November 23rd 04 06:47 AM

James P. Javery wrote:
I'm considering setting up a 240 volt appliance in my garage and I need to
determine whether it is being supplied with 220-240 volt service. The
breaker box in the garage has three wires coming in from elsewhere in the
building, one white wired to the neutral bus bar and two black wired to a 70
amp double pole breaker.

1. multimeter shows ~116 volts from hot to neutral for each of the two poles
on the main breaker
2. multimeter shows 0 volts from hot to hot between the two poles on the
main breaker
3. multimeter shows 0 ohms resistance between from hot to hot between the
two poles on the main breaker

Am I not testing this properly, or is it possible that my garage is not
wired for "three wire single phase" as I suppose electricians prefer to call
it? My understanding would lead me to believe that the two hot wires are
connected upstream to the same half of my building's electrical supply, so
I'm only getting 120 in my garage despite the two hot wires.

Any ideas? Are there any other tests I can perform to verify or invalidate
my conclusions? Thanks for any help you may provide...

-James




Also, the breaker box in the garage should have 4 wires coming into it,
since it's being fed as a subpanel from another panel elsewhere in the
building. If it were a detached garage, you could use the grounded wire
as a neutral and make a new ground.

In your case, with only 3 wires, you need to tape the ends of the wire
green and you don't have a neutral. It would be best not to have a
breaker box in the garage (and just hardwire the appliance) if you do
this, because someday someone will want to hook up a 120V circuit and
try to use thata ground for a neutral connection.

Bob

Dan November 23rd 04 11:32 AM

On Tue, 23 Nov 2004 05:56:59 GMT, "James P. Javery"
wrote:

I'm considering setting up a 240 volt appliance in my garage and I need to
determine whether it is being supplied with 220-240 volt service. The
breaker box in the garage has three wires coming in from elsewhere in the
building, one white wired to the neutral bus bar and two black wired to a 70
amp double pole breaker.

1. multimeter shows ~116 volts from hot to neutral for each of the two poles
on the main breaker
2. multimeter shows 0 volts from hot to hot between the two poles on the
main breaker
3. multimeter shows 0 ohms resistance between from hot to hot between the
two poles on the main breaker

Am I not testing this properly, or is it possible that my garage is not
wired for "three wire single phase" as I suppose electricians prefer to call
it? My understanding would lead me to believe that the two hot wires are
connected upstream to the same half of my building's electrical supply, so
I'm only getting 120 in my garage despite the two hot wires.

Any ideas? Are there any other tests I can perform to verify or invalidate
my conclusions? Thanks for any help you may provide...

-James


Sounds like your double pole breaker feeding the garage needs to be
moved one position. It is apparently connected to the same phase on
both sides. Some panels will let that happen, some are keyed so it
won't.

Dan

[email protected] November 23rd 04 04:54 PM

On Tue, 23 Nov 2004 00:47:07 -0600, zxcvbob
wrote:

James P. Javery wrote:
I'm considering setting up a 240 volt appliance in my garage and I need to
determine whether it is being supplied with 220-240 volt service. The
breaker box in the garage has three wires coming in from elsewhere in the
building, one white wired to the neutral bus bar and two black wired to a 70
amp double pole breaker.

1. multimeter shows ~116 volts from hot to neutral for each of the two poles
on the main breaker
2. multimeter shows 0 volts from hot to hot between the two poles on the
main breaker
3. multimeter shows 0 ohms resistance between from hot to hot between the
two poles on the main breaker

Am I not testing this properly, or is it possible that my garage is not
wired for "three wire single phase" as I suppose electricians prefer to call
it? My understanding would lead me to believe that the two hot wires are
connected upstream to the same half of my building's electrical supply, so
I'm only getting 120 in my garage despite the two hot wires.

Any ideas? Are there any other tests I can perform to verify or invalidate
my conclusions? Thanks for any help you may provide...

-James




Also, the breaker box in the garage should have 4 wires coming into it,
since it's being fed as a subpanel from another panel elsewhere in the
building. If it were a detached garage, you could use the grounded wire
as a neutral and make a new ground.

In your case, with only 3 wires, you need to tape the ends of the wire
green and you don't have a neutral. It would be best not to have a
breaker box in the garage (and just hardwire the appliance) if you do
this, because someday someone will want to hook up a 120V circuit and
try to use thata ground for a neutral connection.

Bob


Are you allowed to re-identify a wire as an equipment grounding
conductor?

The question I would ask, what type of cable is feeding the subpanel,
is it AC or is it all EMT, since he mentions no specific ground.

As for the 0 volts accross both ungrounded bars, I'm sensing this was
a 'home owner' installation, and caution needs to be taken by this
homeowner in trouble shooting and fixing to get 240 volt properly
supplied.

IMHO,

tom @ FreelancingProjects.com



HaHaHa November 24th 04 01:17 AM

From: Dan


On Tue, 23 Nov 2004 05:56:59 GMT, "James P. Javery"
wrote:

I'm considering setting up a 240 volt appliance in my garage and I need to
determine whether it is being supplied with 220-240 volt service. The
breaker box in the garage has three wires coming in from elsewhere in the
building, one white wired to the neutral bus bar and two black wired to a 70


amp double pole breaker.

1. multimeter shows ~116 volts from hot to neutral for each of the two poles


on the main breaker
2. multimeter shows 0 volts from hot to hot between the two poles on the
main breaker
3. multimeter shows 0 ohms resistance between from hot to hot between the
two poles on the main breaker

Am I not testing this properly, or is it possible that my garage is not
wired for "three wire single phase" as I suppose electricians prefer to call


it? My understanding would lead me to believe that the two hot wires are
connected upstream to the same half of my building's electrical supply, so
I'm only getting 120 in my garage despite the two hot wires.

Any ideas? Are there any other tests I can perform to verify or invalidate
my conclusions? Thanks for any help you may provide...

-James


Sounds like your double pole breaker feeding the garage needs to be
moved one position. It is apparently connected to the same phase on
both sides. Some panels will let that happen, some are keyed so it
won't.

Dan


ZINSCO!