Wiring up switch w/pilot light.
Wiring up switch w/pilot light...
When wiring up a switch that requires another wire back from the load to attach to the switch to power the pilot-light (illuminated when ON). Do I have to use #14 wire ? Or can I use something smaller like #20 bell wire as long as the jacket is rated at 600v ? Any help is appreciated. |
#2
Posted to alt.home.repair
|
|||
|
|||
Wiring up switch w/pilot light.
On Monday, July 6, 2020 at 2:30:06 PM UTC-4, wrote:
Wiring up switch w/pilot light... When wiring up a switch that requires another wire back from the load to attach to the switch to power the pilot-light (illuminated when ON). Do I have to use #14 wire ? Or can I use something smaller like #20 bell wire as long as the jacket is rated at 600v ? Any help is appreciated. 14, assuming it's a 15A circuit and that wire has to be part of the cable or inside the same conduit, etc. You can't just run another separate wire, even if it's 14 gauge. |
#3
Posted to alt.home.repair
|
|||
|
|||
Wiring up switch w/pilot light.
|
#4
Posted to alt.home.repair
|
|||
|
|||
Wiring up switch w/pilot light.
On Monday, July 6, 2020 at 1:30:06 PM UTC-5, wrote:
Wiring up switch w/pilot light... When wiring up a switch that requires another wire back from the load to attach to the switch to power the pilot-light (illuminated when ON). Do I have to use #14 wire ? Or can I use something smaller like #20 bell wire as long as the jacket is rated at 600v ? Any help is appreciated. The house is in the country and all wiring is Romex. I was shopping and found some 14-3 that was not that expensive. Didn't see anything that was 14-4. (conduit would have been nice) Can I run a 14-3 romex and 14-2 from the light ? |
#6
Posted to alt.home.repair
|
|||
|
|||
Wiring up switch w/pilot light.
On Monday, July 6, 2020 at 3:43:38 PM UTC-4, wrote:
On Monday, July 6, 2020 at 1:30:06 PM UTC-5, wrote: Wiring up switch w/pilot light... When wiring up a switch that requires another wire back from the load to attach to the switch to power the pilot-light (illuminated when ON). Do I have to use #14 wire ? Or can I use something smaller like #20 bell wire as long as the jacket is rated at 600v ? Any help is appreciated. The house is in the country and all wiring is Romex. I was shopping and found some 14-3 that was not that expensive. Didn't see anything that was 14-4. (conduit would have been nice) Can I run a 14-3 romex and 14-2 from the light ? Maybe we should back up and start from the beginning. If the switch powers the load and the load is on when the switch is on, then you would just need a neutral at the switch to power the pilot light. Is that the wire you need to run, because there is no neutral in the box with the switch? If that's the case, then you don't necessarily need the neutral to come from where the load is, it just needs to be the neutral for that circuit, which you might be able to re-wire from somewhere more convenient. How is it wired now, what runs from the switch to the load, etc? |
#7
Posted to alt.home.repair
|
|||
|
|||
Wiring up switch w/pilot light.
On Monday, July 6, 2020 at 7:14:10 PM UTC-4, Scott Lurndal wrote:
writes: Wiring up switch w/pilot light... When wiring up a switch that requires another wire back from the load to attach to the switch to power the pilot-light (illuminated when ON). Do I have to use #14 wire ? Use the appropriate AWG for the breaker and length of run. On a 15A circuit, AWG14 is the minimum AWG, it could be AWG12 for a long run. For a switch pilot light? That would be one hell of a long run to need 12 gauge. If the circuit is protected by a 20A breaker, AGW12 is the smallest size you can use. |
#8
Posted to alt.home.repair
|
|||
|
|||
Wiring up switch w/pilot light.
On Monday, July 6, 2020 at 1:30:06 PM UTC-5, wrote:
Wiring up switch w/pilot light... When wiring up a switch that requires another wire back from the load to attach to the switch to power the pilot-light (illuminated when ON). Do I have to use #14 wire ? Or can I use something smaller like #20 bell wire as long as the jacket is rated at 600v ? Any help is appreciated. The switches are 3-way pilot. I need a neutral as well as a leg from the load. The real problem is that the current switch is in proximity to the light (and I don't want that one to go away), and the people living there can't easily walk the extra 50' to the switch. So they ask for a 2nd switch very close to the door, but from that door you would not be able to see if the light was illuminated or not. I suggested an switch w/pilot. Could use X10 or some other tech stuff, but that just confuses elderly, and in my experience they just don't use it or turn it off. So I am looking at using 3-way switches w/5 screws: 1 line, 2 travelers, 1 neutral, 1 parallel to load (for illumination). Thanks |
#9
Posted to alt.home.repair
|
|||
|
|||
Wiring up switch w/pilot light.
|
#11
Posted to alt.home.repair
|
|||
|
|||
Wiring up switch w/pilot light.
On Monday, July 6, 2020 at 1:30:06 PM UTC-5, wrote:
Wiring up switch w/pilot light... When wiring up a switch that requires another wire back from the load to attach to the switch to power the pilot-light (illuminated when ON). Do I have to use #14 wire ? Or can I use something smaller like #20 bell wire as long as the jacket is rated at 600v ? Any help is appreciated. I like the idea of a switch-loop, I was thinking about it backwards. So if I run 14-3 from the light and I am adding another gang to the existing gang-box, I could use two wires from the 14-3 romex as the travelers, the 3rd as the load, connect the load to the illumination screw and get the neutral from one of the existing gangs (if its there) ? Again, if the existing switches are just switch loops, I may not find a neutral ? Would it be over the top to just tie the neutral (for illumination) from the switch to the ground and let it get its neutral that way ? Thanks |
#12
Posted to alt.home.repair
|
|||
|
|||
Wiring up switch w/pilot light.
On Mon, 6 Jul 2020 16:38:28 -0700 (PDT), trader_4
wrote: On Monday, July 6, 2020 at 7:14:10 PM UTC-4, Scott Lurndal wrote: writes: Wiring up switch w/pilot light... When wiring up a switch that requires another wire back from the load to attach to the switch to power the pilot-light (illuminated when ON). Do I have to use #14 wire ? Use the appropriate AWG for the breaker and length of run. On a 15A circuit, AWG14 is the minimum AWG, it could be AWG12 for a long run. For a switch pilot light? That would be one hell of a long run to need 12 gauge. If the circuit is protected by a 20A breaker, AGW12 is the smallest size you can use. The smallest "fixture wire" you can put on 15&20a circuits is 18ga. That can only go to loads that are limited by design, like a luminaire or an appliance. If you use smaller wire, you need supplemental O/C protection. "Fixture wire" is also limited to the load end of a branch circuit. If this is run with circuit conductors, it needs to be compliant with 240.4(D), The old 15a =14ga, 20a=12ga rule |
#13
Posted to alt.home.repair
|
|||
|
|||
Wiring up switch w/pilot light.
|
#14
Posted to alt.home.repair
|
|||
|
|||
Wiring up switch w/pilot light.
On Monday, July 6, 2020 at 1:30:06 PM UTC-5, wrote:
Wiring up switch w/pilot light... When wiring up a switch that requires another wire back from the load to attach to the switch to power the pilot-light (illuminated when ON). Do I have to use #14 wire ? Or can I use something smaller like #20 bell wire as long as the jacket is rated at 600v ? Any help is appreciated. No matter how you cut it, I need 4 wires. I did finally find some 14-2-2 at some big-box stores, but min is 250', I probably only need about 70'. One vendor on Ebay has it in several lengths for about $0.80 / foot w/free shipping. Should I go looking for a better price ? |
#16
Posted to alt.home.repair
|
|||
|
|||
Wiring up switch w/pilot light.
|
#17
Posted to alt.home.repair
|
|||
|
|||
Wiring up switch w/pilot light.
On Tue, 7 Jul 2020 06:41:36 -0700 (PDT), trader_4
wrote: On Tuesday, July 7, 2020 at 1:50:14 AM UTC-4, wrote: On Mon, 6 Jul 2020 19:12:22 -0700 (PDT), wrote: On Monday, July 6, 2020 at 1:30:06 PM UTC-5, wrote: Wiring up switch w/pilot light... When wiring up a switch that requires another wire back from the load to attach to the switch to power the pilot-light (illuminated when ON). Do I have to use #14 wire ? Or can I use something smaller like #20 bell wire as long as the jacket is rated at 600v ? Any help is appreciated. I like the idea of a switch-loop, I was thinking about it backwards. So if I run 14-3 from the light and I am adding another gang to the existing gang-box, I could use two wires from the 14-3 romex as the travelers, the 3rd as the load, connect the load to the illumination screw and get the neutral from one of the existing gangs (if its there) ? Again, if the existing switches are just switch loops, I may not find a neutral ? Would it be over the top to just tie the neutral (for illumination) from the switch to the ground and let it get its neutral that way ? Thanks That is technically illegal too. The neutral needs to be from the same circuit and run with the circuit conductors. If it was grabbed from another circuit, that is an AFCI trip for sure when someone tries to install them. If all the circuits in that gang box are on the same circuit, you probably could do it and I doubt the inductive heating (from a metal box) would burn the house down for a pilot light. BTW they do make 4 wire Romex but you need to go to a real electrical supply to get it. It will be called 14-2-2. Same no-go with using the ground as the neutral connection for the pilot light. I don't think there is an exception for a small LED light, just a couple of MA, is there? 14-2-2 is 4 insulated conductors and a bare ground, what he needs. There used to be an exception in the U/L listings that allowed 0.5 MA to go down the ground but it disappeared sometime in the 90s. It might have been around NEC 96 when the NFPA reevaluated all of those ground/neutral exceptions like 3 wire dryer cords and 3 wire feeders to remote buildings. (The 96 ROP process was actually opened in 93) |
#18
Posted to alt.home.repair
|
|||
|
|||
Wiring up switch w/pilot light.
On Monday, July 6, 2020 at 11:14PM, "Scott Lurndal" wrote:
writes: Wiring up switch w/pilot light... When wiring up a switch that requires another wire back from the load to attach to the switch to power the pilot-light (illuminated when ON). Do I have to use #14 wire ? Use the appropriate AWG for the breaker and length of run. On a 15A circuit, AWG14 is the minimum AWG, it could be AWG12 for a long run. If the circuit is protected by a 20A breaker, AGW12 is the smallest size you can use. Pretty much all new construction is going to use 12 gauge hot with maybe even 10 wire for a neutral. |
#19
Posted to alt.home.repair
|
|||
|
|||
Wiring up switch w/pilot light.
|
#20
Posted to alt.home.repair
|
|||
|
|||
Wiring up switch w/pilot light.
On Tue, 07 Jul 2020 14:45:04 GMT, (Scott Lurndal)
wrote: writes: On Mon, 6 Jul 2020 19:12:22 -0700 (PDT), wrote: On Monday, July 6, 2020 at 1:30:06 PM UTC-5, wrote: Wiring up switch w/pilot light... When wiring up a switch that requires another wire back from the load to attach to the switch to power the pilot-light (illuminated when ON). Do I have to use #14 wire ? Or can I use something smaller like #20 bell wire as long as the jacket is rated at 600v ? Any help is appreciated. I like the idea of a switch-loop, I was thinking about it backwards. So if I run 14-3 from the light and I am adding another gang to the existing gang-box, I could use two wires from the 14-3 romex as the travelers, the 3rd as the load, connect the load to the illumination screw and get the neutral from one of the existing gangs (if its there) ? Again, if the existing switches are just switch loops, I may not find a neutral ? Would it be over the top to just tie the neutral (for illumination) from the switch to the ground and let it get its neutral that way ? Thanks That is technically illegal too. The neutral needs to be from the same circuit and run with the circuit conductors. If it was grabbed from another circuit, that is an AFCI trip for sure when someone tries to install them. If all the circuits in that gang box are on the same circuit, you probably could do it and I doubt the inductive heating (from a metal box) would burn the house down for a pilot light. BTW they do make 4 wire Romex but you need to go to a real electrical supply to get it. It will be called 14-2-2. My home depot has 12-2-14-2 in a single romex jacket (w/gnd). Some fancy switches require that, apparently. This was driven by the AFCIs |
#21
Posted to alt.home.repair
|
|||
|
|||
Wiring up switch w/pilot light.
|
#22
Posted to alt.home.repair
|
|||
|
|||
Wiring up switch w/pilot light.
On Tuesday, July 7, 2020 at 3:56:35 PM UTC-4, wrote:
On Monday, July 6, 2020 at 11:14PM, "Scott Lurndal" wrote: writes: Wiring up switch w/pilot light... When wiring up a switch that requires another wire back from the load to attach to the switch to power the pilot-light (illuminated when ON). Do I have to use #14 wire ? Use the appropriate AWG for the breaker and length of run. On a 15A circuit, AWG14 is the minimum AWG, it could be AWG12 for a long run. If the circuit is protected by a 20A breaker, AGW12 is the smallest size you can use. Pretty much all new construction is going to use 12 gauge hot with maybe even 10 wire for a neutral. IDK where you are, but here in US plenty of 14 gauge all over in new residential construction. Far more 14g than 12g. Why would you run 12g, which costs more and is harder to work with, to support some small lighting circuits, for example? And why would you make the neutral larger? WTF? |
#23
Posted to alt.home.repair
|
|||
|
|||
Wiring up switch w/pilot light.
On Tue, 07 Jul 2020 19:58:37 -0400, wrote:
On Tue, 7 Jul 2020 12:56:29 -0700 (PDT), wrote: On Monday, July 6, 2020 at 11:14PM, "Scott Lurndal" wrote: writes: Wiring up switch w/pilot light... When wiring up a switch that requires another wire back from the load to attach to the switch to power the pilot-light (illuminated when ON). Do I have to use #14 wire ? Use the appropriate AWG for the breaker and length of run. On a 15A circuit, AWG14 is the minimum AWG, it could be AWG12 for a long run. If the circuit is protected by a 20A breaker, AGW12 is the smallest size you can use. Pretty much all new construction is going to use 12 gauge hot with maybe even 10 wire for a neutral. Huh? You must not see much actual construction. In 1 & 2 family, 14-2 is alive and well for general lighting circuits. #12 is only used for kitchens, laundries and bathrooms. In my housing development, there isn't an inch of 14ga anywhere. All of the 120v circuit breakers are 20a and all of the Romex is yellow, no exceptions for lighting circuits. The only place you see "super neutrals" is on 208 3p wye and then only where you have a lot of reactive load. It would actually be 2 sizes bigger too. (#8 on a 20a circuit) |
#24
Posted to alt.home.repair
|
|||
|
|||
Wiring up switch w/pilot light.
On Wed, 08 Jul 2020 13:45:10 -0500, Jim Joyce
wrote: On Tue, 07 Jul 2020 19:58:37 -0400, wrote: On Tue, 7 Jul 2020 12:56:29 -0700 (PDT), wrote: On Monday, July 6, 2020 at 11:14PM, "Scott Lurndal" wrote: writes: Wiring up switch w/pilot light... When wiring up a switch that requires another wire back from the load to attach to the switch to power the pilot-light (illuminated when ON). Do I have to use #14 wire ? Use the appropriate AWG for the breaker and length of run. On a 15A circuit, AWG14 is the minimum AWG, it could be AWG12 for a long run. If the circuit is protected by a 20A breaker, AGW12 is the smallest size you can use. Pretty much all new construction is going to use 12 gauge hot with maybe even 10 wire for a neutral. Huh? You must not see much actual construction. In 1 & 2 family, 14-2 is alive and well for general lighting circuits. #12 is only used for kitchens, laundries and bathrooms. In my housing development, there isn't an inch of 14ga anywhere. All of the 120v circuit breakers are 20a and all of the Romex is yellow, no exceptions for lighting circuits. On the surface that might sound good but you usually end up with fewer circuits. The breakers are sized by square footage, not the number of outlets. |
#25
Posted to alt.home.repair
|
|||
|
|||
Wiring up switch w/pilot light.
On Wed, 08 Jul 2020 21:01:22 -0400, wrote:
On Wed, 08 Jul 2020 13:45:10 -0500, Jim Joyce wrote: On Tue, 07 Jul 2020 19:58:37 -0400, wrote: On Tue, 7 Jul 2020 12:56:29 -0700 (PDT), wrote: On Monday, July 6, 2020 at 11:14PM, "Scott Lurndal" wrote: writes: Wiring up switch w/pilot light... When wiring up a switch that requires another wire back from the load to attach to the switch to power the pilot-light (illuminated when ON). Do I have to use #14 wire ? Use the appropriate AWG for the breaker and length of run. On a 15A circuit, AWG14 is the minimum AWG, it could be AWG12 for a long run. If the circuit is protected by a 20A breaker, AGW12 is the smallest size you can use. Pretty much all new construction is going to use 12 gauge hot with maybe even 10 wire for a neutral. Huh? You must not see much actual construction. In 1 & 2 family, 14-2 is alive and well for general lighting circuits. #12 is only used for kitchens, laundries and bathrooms. In my housing development, there isn't an inch of 14ga anywhere. All of the 120v circuit breakers are 20a and all of the Romex is yellow, no exceptions for lighting circuits. On the surface that might sound good but you usually end up with fewer circuits. The breakers are sized by square footage, not the number of outlets. Yeah, I don't think it's a good thing. For example, the entire M-I-L suite is served by a single 20a breaker. That part of the house includes a living room, a bedroom, a walk-in closet, and a bathroom, all with lights and receptacles throughout. It's basically an apartment inside the house, and the whole thing is served by a single breaker. |
#26
Posted to alt.home.repair
|
|||
|
|||
Wiring up switch w/pilot light.
On 7/8/2020 10:26 PM, Jim Joyce wrote:
On Wed, 08 Jul 2020 21:01:22 -0400, wrote: On Wed, 08 Jul 2020 13:45:10 -0500, Jim Joyce wrote: On Tue, 07 Jul 2020 19:58:37 -0400, wrote: On Tue, 7 Jul 2020 12:56:29 -0700 (PDT), wrote: On Monday, July 6, 2020 at 11:14PM, "Scott Lurndal" wrote: writes: Wiring up switch w/pilot light... When wiring up a switch that requires another wire back from the load to attach to the switch to power the pilot-light (illuminated when ON). Do I have to use #14 wire ? Use the appropriate AWG for the breaker and length of run. On a 15A circuit, AWG14 is the minimum AWG, it could be AWG12 for a long run. If the circuit is protected by a 20A breaker, AGW12 is the smallest size you can use. Pretty much all new construction is going to use 12 gauge hot with maybe even 10 wire for a neutral. Huh? You must not see much actual construction. In 1 & 2 family, 14-2 is alive and well for general lighting circuits. #12 is only used for kitchens, laundries and bathrooms. In my housing development, there isn't an inch of 14ga anywhere. All of the 120v circuit breakers are 20a and all of the Romex is yellow, no exceptions for lighting circuits. On the surface that might sound good but you usually end up with fewer circuits. The breakers are sized by square footage, not the number of outlets. Yeah, I don't think it's a good thing. For example, the entire M-I-L suite is served by a single 20a breaker. That part of the house includes a living room, a bedroom, a walk-in closet, and a bathroom, all with lights and receptacles throughout. It's basically an apartment inside the house, and the whole thing is served by a single breaker. Ouch! Was that wired by a pro? Lights and receptacles on the same breaker? My house is 1583 sq ft and has 16 breakers. Also have a **** load of receptacles and switches. |
#27
Posted to alt.home.repair
|
|||
|
|||
Wiring up switch w/pilot light.
On Wed, 8 Jul 2020 23:27:21 -0400, Ed Pawlowski wrote:
On 7/8/2020 10:26 PM, Jim Joyce wrote: On Wed, 08 Jul 2020 21:01:22 -0400, wrote: On Wed, 08 Jul 2020 13:45:10 -0500, Jim Joyce wrote: On Tue, 07 Jul 2020 19:58:37 -0400, wrote: On Tue, 7 Jul 2020 12:56:29 -0700 (PDT), wrote: On Monday, July 6, 2020 at 11:14PM, "Scott Lurndal" wrote: writes: Wiring up switch w/pilot light... When wiring up a switch that requires another wire back from the load to attach to the switch to power the pilot-light (illuminated when ON). Do I have to use #14 wire ? Use the appropriate AWG for the breaker and length of run. On a 15A circuit, AWG14 is the minimum AWG, it could be AWG12 for a long run. If the circuit is protected by a 20A breaker, AGW12 is the smallest size you can use. Pretty much all new construction is going to use 12 gauge hot with maybe even 10 wire for a neutral. Huh? You must not see much actual construction. In 1 & 2 family, 14-2 is alive and well for general lighting circuits. #12 is only used for kitchens, laundries and bathrooms. In my housing development, there isn't an inch of 14ga anywhere. All of the 120v circuit breakers are 20a and all of the Romex is yellow, no exceptions for lighting circuits. On the surface that might sound good but you usually end up with fewer circuits. The breakers are sized by square footage, not the number of outlets. Yeah, I don't think it's a good thing. For example, the entire M-I-L suite is served by a single 20a breaker. That part of the house includes a living room, a bedroom, a walk-in closet, and a bathroom, all with lights and receptacles throughout. It's basically an apartment inside the house, and the whole thing is served by a single breaker. Ouch! Was that wired by a pro? Lights and receptacles on the same breaker? Yes, the electricians are pros, but Fretwell is fond of saying any monkey can get a license. I asked them about the wiring because I've had a lot of electrical issues in the first year and they said that the builder, DR Horton, wants them to do it that way. Take the 3-car garage, as another example. A single 20a breaker covers 3 receptacles on the walls, 2 receptacles on the ceiling for the GDOs, a pair of light fixtures on the driveway and 4 weatherproof receptacles on the exterior of the house. The GFCI on that circuit was way too twitchy, tripping every week or two for no reason, so they changed the breaker and it's been better so far. At my last house, all of that was on 3 breakers rather than one. All of the houses out here are the same way. I know because I've walked through all of them while they were under construction. We talked about that a while back. My house is 1583 sq ft and has 16 breakers. Also have a **** load of receptacles and switches. My house is about twice that size with 19 breakers. |
#28
Posted to alt.home.repair
|
|||
|
|||
Wiring up switch w/pilot light.
|
#29
Posted to alt.home.repair
|
|||
|
|||
Wiring up switch w/pilot light.
|
#31
Posted to alt.home.repair
|
|||
|
|||
Wiring up switch w/pilot light.
|
#32
Posted to alt.home.repair
|
|||
|
|||
Wiring up switch w/pilot light.
On Thu, 9 Jul 2020 10:32:18 -0400, Ralph Mowery
wrote: In article , says... Ouch! Was that wired by a pro? Lights and receptacles on the same breaker? Yes, the electricians are pros, but Fretwell is fond of saying any monkey can get a license. I asked them about the wiring because I've had a lot of electrical issues in the first year and they said that the builder, DR Horton, wants them to do it that way. Take the 3-car garage, as another example. A single 20a breaker covers 3 receptacles on the walls, 2 receptacles on the ceiling for the GDOs, a pair of light fixtures on the driveway and 4 weatherproof receptacles on the exterior of the house. The GFCI on that circuit was way too twitchy, tripping every week or two for no reason, so they changed the breaker and it's been better so far. At my last house, all of that was on 3 breakers rather than one. I worked with a monkey that had his electrical license. Around 1972 I moved into a duplex that had 2 bedrooms, kitchen, living room and bathroom. It had a disconect switch in the kitchen and it had 2 20 amp fuses in it. I don't know how they were wired,but thought that sure was a small ammount. The apartment was built either just before or just after WW2. I do not recall which. I an not sure I ever said a monkey could get an EC license (I only remember talking about "home inspectors") but if that monkey can pass 2 or 3, 100 question, multiple guess, open book tests and come up with the bond and insurance money, they can be an EC here. In some mobbed up union states up north, the IBEW certifies electricians and it depends on who you know down at the local hall. As for how many breakers, the code calls for 3va per square foot of living space so you can see how 20a circuits can quickly cover that area with a minimum of breakers. (one 20 can cover 800 sq/ft), NFPA has added to the breaker count with rules starting in the 70s that now require dedicated 20s for the kitchen (2), the laundry and the bathrooms. Some AHJs also want dedicated circuits for certain fixed in place appliances like dish washers, microwaves and disposals. Obviously some contractors squeeze that nickel as hard as they can, installing a small disposal so it can legally share with the dish washer, stuff like that. I suggest if they cut corners on things like that which are easy to see, imagine what is going on inside the walls. |
#33
Posted to alt.home.repair
|
|||
|
|||
Wiring up switch w/pilot light.
On Thu, 9 Jul 2020 10:32:18 -0400, Ralph Mowery
wrote: In article , says... Ouch! Was that wired by a pro? Lights and receptacles on the same breaker? Yes, the electricians are pros, but Fretwell is fond of saying any monkey can get a license. I asked them about the wiring because I've had a lot of electrical issues in the first year and they said that the builder, DR Horton, wants them to do it that way. Take the 3-car garage, as another example. A single 20a breaker covers 3 receptacles on the walls, 2 receptacles on the ceiling for the GDOs, a pair of light fixtures on the driveway and 4 weatherproof receptacles on the exterior of the house. The GFCI on that circuit was way too twitchy, tripping every week or two for no reason, so they changed the breaker and it's been better so far. At my last house, all of that was on 3 breakers rather than one. I worked with a monkey that had his electrical license. Around 1972 I moved into a duplex that had 2 bedrooms, kitchen, living room and bathroom. It had a disconect switch in the kitchen and it had 2 20 amp fuses in it. I don't know how they were wired,but thought that sure was a small ammount. The apartment was built either just before or just after WW2. I do not recall which. I an not sure I ever said a monkey could get an EC license (I only remember talking about "home inspectors") but if that monkey can pass 2 or 3, 100 question, multiple guess, open book tests and come up with the bond and insurance money, they can be an EC here. In some mobbed up union states up north, the IBEW certifies electricians and it depends on who you know down at the local hall. As for how many breakers, the code calls for 3va per square foot of living space so you can see how 20a circuits can quickly cover that area with a minimum of breakers. (one 20 can cover 800 sq/ft), NFPA has added to the breaker count with rules starting in the 70s that now require dedicated 20s for the kitchen (2), the laundry and the bathrooms. Some AHJs also want dedicated circuits for certain fixed in place appliances like dish washers, microwaves and disposals. Obviously some contractors squeeze that nickel as hard as they can, installing a small disposal so it can legally share with the dish washer, stuff like that. I suggest if they cut corners on things like that which are easy to see, imagine what is going on inside the walls. |
#34
Posted to alt.home.repair
|
|||
|
|||
Wiring up switch w/pilot light.
On Thu, 9 Jul 2020 10:32:18 -0400, Ralph Mowery
wrote: In article , says... Ouch! Was that wired by a pro? Lights and receptacles on the same breaker? Yes, the electricians are pros, but Fretwell is fond of saying any monkey can get a license. I asked them about the wiring because I've had a lot of electrical issues in the first year and they said that the builder, DR Horton, wants them to do it that way. Take the 3-car garage, as another example. A single 20a breaker covers 3 receptacles on the walls, 2 receptacles on the ceiling for the GDOs, a pair of light fixtures on the driveway and 4 weatherproof receptacles on the exterior of the house. The GFCI on that circuit was way too twitchy, tripping every week or two for no reason, so they changed the breaker and it's been better so far. At my last house, all of that was on 3 breakers rather than one. I worked with a monkey that had his electrical license. Around 1972 I moved into a duplex that had 2 bedrooms, kitchen, living room and bathroom. It had a disconect switch in the kitchen and it had 2 20 amp fuses in it. I don't know how they were wired,but thought that sure was a small ammount. The apartment was built either just before or just after WW2. I do not recall which. I an not sure I ever said a monkey could get an EC license (I only remember talking about "home inspectors") but if that monkey can pass 2 or 3, 100 question, multiple guess, open book tests and come up with the bond and insurance money, they can be an EC here. In some mobbed up union states up north, the IBEW certifies electricians and it depends on who you know down at the local hall. As for how many breakers, the code calls for 3va per square foot of living space so you can see how 20a circuits can quickly cover that area with a minimum of breakers. (one 20 can cover 800 sq/ft), NFPA has added to the breaker count with rules starting in the 70s that now require dedicated 20s for the kitchen (2), the laundry and the bathrooms. Some AHJs also want dedicated circuits for certain fixed in place appliances like dish washers, microwaves and disposals. Obviously some contractors squeeze that nickel as hard as they can, installing a small disposal so it can legally share with the dish washer, stuff like that. I suggest if they cut corners on things like that which are easy to see, imagine what is going on inside the walls. |
#35
Posted to alt.home.repair
|
|||
|
|||
Wiring up switch w/pilot light.
On Thu, 9 Jul 2020 10:32:18 -0400, Ralph Mowery
wrote: In article , says... Ouch! Was that wired by a pro? Lights and receptacles on the same breaker? Yes, the electricians are pros, but Fretwell is fond of saying any monkey can get a license. I asked them about the wiring because I've had a lot of electrical issues in the first year and they said that the builder, DR Horton, wants them to do it that way. Take the 3-car garage, as another example. A single 20a breaker covers 3 receptacles on the walls, 2 receptacles on the ceiling for the GDOs, a pair of light fixtures on the driveway and 4 weatherproof receptacles on the exterior of the house. The GFCI on that circuit was way too twitchy, tripping every week or two for no reason, so they changed the breaker and it's been better so far. At my last house, all of that was on 3 breakers rather than one. I worked with a monkey that had his electrical license. Around 1972 I moved into a duplex that had 2 bedrooms, kitchen, living room and bathroom. It had a disconect switch in the kitchen and it had 2 20 amp fuses in it. I don't know how they were wired,but thought that sure was a small ammount. The apartment was built either just before or just after WW2. I do not recall which. I an not sure I ever said a monkey could get an EC license (I only remember talking about "home inspectors") but if that monkey can pass 2 or 3, 100 question, multiple guess, open book tests and come up with the bond and insurance money, they can be an EC here. In some mobbed up union states up north, the IBEW certifies electricians and it depends on who you know down at the local hall. As for how many breakers, the code calls for 3va per square foot of living space so you can see how 20a circuits can quickly cover that area with a minimum of breakers. (one 20 can cover 800 sq/ft), NFPA has added to the breaker count with rules starting in the 70s that now require dedicated 20s for the kitchen (2), the laundry and the bathrooms. Some AHJs also want dedicated circuits for certain fixed in place appliances like dish washers, microwaves and disposals. Obviously some contractors squeeze that nickel as hard as they can, installing a small disposal so it can legally share with the dish washer, stuff like that. I suggest if they cut corners on things like that which are easy to see, imagine what is going on inside the walls. |
#36
Posted to alt.home.repair
|
|||
|
|||
Wiring up switch w/pilot light.
|
#37
Posted to alt.home.repair
|
|||
|
|||
Wiring up switch w/pilot light.
|
#38
Posted to alt.home.repair
|
|||
|
|||
Wiring up switch w/pilot light.
|
#39
Posted to alt.home.repair
|
|||
|
|||
Wiring up switch w/pilot light.
|
#40
Posted to alt.home.repair
|
|||
|
|||
Wiring up switch w/pilot light.
On Wednesday, July 8, 2020 11:27PM, Ed Pawlowski wrote:
On 7/8/2020 10:26 PM, Jim Joyce wrote: On Wed, 08 Jul 2020 21:01:22 -0400, wrote: On Wed, 08 Jul 2020 13:45:10 -0500, Jim Joyce wrote: On Tue, 07 Jul 2020 19:58:37 -0400, wrote: On Tue, 7 Jul 2020 12:56:29 -0700 (PDT), wrote: On Monday, July 6, 2020 at 11:14PM, "Scott Lurndal" wrote: writes: Wiring up switch w/pilot light... When wiring up a switch that requires another wire back from the load to attach to the switch to power the pilot-light (illuminated when ON). Do I have to use #14 wire ? Use the appropriate AWG for the breaker and length of run. On a 15A circuit, AWG14 is the minimum AWG, it could be AWG12 for a long run. If the circuit is protected by a 20A breaker, AGW12 is the smallest size you can use. Pretty much all new construction is going to use 12 gauge hot with maybe even 10 wire for a neutral. Huh? You must not see much actual construction. In 1 & 2 family, 14-2 is alive and well for general lighting circuits. #12 is only used for kitchens, laundries and bathrooms. In my housing development, there isn't an inch of 14ga anywhere. All of the 120v circuit breakers are 20a and all of the Romex is yellow, no exceptions for lighting circuits. On the surface that might sound good but you usually end up with fewer circuits. The breakers are sized by square footage, not the number of outlets. Yeah, I don't think it's a good thing. For example, the entire M-I-L suite is served by a single 20a breaker. That part of the house includes a living room, a bedroom, a walk-in closet, and a bathroom, all with lights and receptacles throughout. It's basically an apartment inside the house, and the whole thing is served by a single breaker. Ouch! Was that wired by a pro? Lights and receptacles on the same breaker? Believe it or not, some residential slash commercial establishments have a high-leg conductor from a 120/240V 3 phase where an exit sign and an outlet (and flood light?) can be attached to 277v lighting (for emergency reasons). |
Reply |
|
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Converting SINGLE light switch to MULTIPLE light switch usingWIRELESS control? | Home Repair | |||
Medway Automatic Pilot Flame Spreader Wanted...or Pilot Block... | UK diy | |||
Medway Automatic Pilot Flame Spreader Wanted...or Pilot Block... | UK diy | |||
Questions about Pilot Lights (not gas pilot lights) | Electronics Repair | |||
Neon Pilot Won't Light on Wall Switch | Home Repair |