On Tuesday, June 11, 2019 at 11:19:22 PM UTC-4, wrote:
On Tue, 11 Jun 2019 16:55:43 -0700 (PDT), trader_4
wrote:

On Tuesday, June 11, 2019 at 7:46:48 PM UTC-4, wrote:
On Tue, 11 Jun 2019 14:20:47 -0700 (PDT), trader_4
wrote:

On Tuesday, June 11, 2019 at 5:05:03 PM UTC-4, wrote:
On Tue, 11 Jun 2019 10:21:46 -0700 (PDT), trader_4
wrote:

On Tuesday, June 11, 2019 at 12:47:52 PM UTC-4, Terry Coombs wrote:
On 6/11/2019 8:32 AM, wrote:


Why is the ground rod at the service any better than the one at the
shop? I agree 4 is better than 2 but they are already bonded together
via the neutral in a 3 wire feeder. I doubt he wants to dig up the
yard. This was done this way for 90 years and we didn't pile up a lot
of bodies. The code change was mostly just to make the language
consistent with the rest of the code. Same with ranges and dryers. The
grandfather clause is still there for things done pre 96 adoption.
It does mean you have to be more careful with your bonding and
grounding tho.
the ground connection serves 2 purposes

1) a path for lightning
the ground rod is to provide a path for lightning etc.
this NEEDS to be a path to actual Earth ground because that is where lightning will go.

2) protection from shock due to equipment faults
this is to protect you from a shock if the hot wire shorts to the metal case inside an appliance. Think of a motor with all those windings of enameled wire. If the insulation should fail and connect the power to the metal case of the appliance, you can be shocked by touching the appliance. If the case is grounded

however,
when the short happens, a large fault current will flow and blow the breaker. For a LARGE fault current to flow, the ground must be low resistance. So you want a BOND WIRE between the neutral and ground in the system. This provides a path for the fault current to flow sufficient to blow the breaker if there is a ground
fault.
Often a ground rod alone is too high resistance.

#2 is an important safety feature, I would not skimp on this.


So if have only 3 wires between the buildings and you can't add the 4th wire, I think bonding the outbuilding neutral and ground together at the entrance to the outbuilding is the safer option compared to relying on a ground rod alone.

You can also add a ground rod there to help for lightning.

If you don't need 240V and need only 120V in the outbuilding, you can use the 3 wires as hot neutral and ground. That is 100% safe and legal but you give up having 240V.



mark


Â* Done is done , I have bonded the ground/neutral in the sub panel and
added a ground rod out in the shop . Doing without 240V is unacceptable
, I have 2 welders and an air compressor that all need 240V . And plans
are to install a 240V 3 phase motor with a VFD on the mill in the future
. Lightning is unlikely down in The Holler , but still possible .. This
is a "hobby" shop , but is very well equipped - pretty much a full
machine and welding shop .

--
Snag
Yes , I'm old
and crochety - and armed .
Get outta my woods !

That's what I would have done too, except probably adding a second ground
rod. IDK how you're going to install 3 phase eqpt though, without redoing
what you just did and a whole new service, for that matter?

You can get a VFD that is single phase in and 3 phase out

I see, well that solves that.

So here's another puzzling question. In that thread about solar panels
that has now run amok, Danny brought up the issue of preventing backfeeding
into the grid. AFAIK, that's built into the inverters, but how do they
do it? It would seem like the chicken and the egg problem. You need to
detect the grid power going off, but you are connected directly to it and
also powering it. So, how do they detect it? Obviously before connecting
they must first monitor the voltage, freq and phase and sync to it, but
once you connect, how do you then tell the other grid sources are gone?
I guess you could look for voltage drop, since with the grid down
you'd expect 99.9% there will be big voltage decrease. But is that
sufficient? And what do they really do inside those inverters?

Hypothetically, suppose there are 6 houses on a utility line that
have solar and that segment is connected to the whole distribution
system. The sun is shining, those houses are using significantly
less than the panels put out. I cut the line to the rest of the grid,
leaving just those 6 connected. What happens? Is the "grid" down?
How do those inverters detect it? Do they? What happens?

We got a pitch on these things a while ago. Basically a grid tie
inverter is clocked from the grid. No grid, no output.


But the question remains, the inverter is part of the grid, the inverters
along the block are part of the grid, in addition to some generators
somewhere. So, how does it know that the "grid" is down?

Hypothetically, suppose there are 6 houses on a utility line that
have solar and that segment is connected to the whole distribution
system. The sun is shining, those houses are using significantly
less than the panels put out. I cut the line to the rest of the grid,
leaving just those 6 connected. What happens? Is the "grid" down?
How do those inverters detect it? Do they? What happens?


That is an interesting question but theoretically each grid tied
inverter would lose clocking and shut down.


But they don't really lose clocking, because if you have six houses,
each was following the "grid" which is whatever sources, including
the other solar. So, they would then follow collectively what is
there which at the moment the segement is cut off, it 60 hz and A-OK.
So they would be following each other. But I think what happens is
that since they are each following the other and constantly trying
to match, it does lead to the freq starting to vary slightly.



I have posed this question to everyone I have talked to without an
answer. What happens if you disconnect from the grid, drop all of
your loads and connect a battery powered inverter. Will that clock
your grid tie and allow you to add loads until you overwhelm it?


Right, same idea. Would the grid tie inverter recognize that the
battery powered inverter isn't the "grid". Whatever the "grid"
even means. I guess the grid they are looking for would be
defined as having at least one power company generator source. But wait,
not sure even that's right. Power companies have solar and wind
today too. If a disconnected segment had power solar, it's like
the solar from home we're talking about. Wind, IDK, but that would
seem to have the same issues, I assume they are using inverters too
and not a generator where the rotation speed governs the freq.





They run at a
voltage that can be potentially slightly higher than the grid so if
there is any power left over, it flows backward into the grid. A smart
meter will see that and meter based on your local tariff agreement.
The old style would just run backward if net flow was out instead of
in. If you netted more use than you fed back in, no harm, just a
lower bill. If you showed a negative bill I guess you would be talking
to the PoCo.
That is how people used to steal power, plug the meter in upside down
it runs backward so there is a chance you would be starting in the
fraud department if they did not know about your solar.
The "plug in" collectors plug in just like your toaster and will boost
the power on that side of your service. These things are usually too
small to ever feed back into the grid if you have anything running at
all.


But from everything I see, a 10KW home solar system behaves exactly
like the plug in ones and needs to detect when to disconnect.


That is the way I understand it. Each inverter should detect loss of
grid and shut down. It would be interesting if you had something else
feeding the grid like your generator idea that the plan might fail. I
also doubt there is enough power going into the grid to sustain it if
you are not getting utility power, even if you have a lot of people
with a black roof.


I agree. In 99.9% of the cases of a segment coming disconnected from
the rest of the utility, you'd think there would be big, obvious
problems, starting with a big voltage drop. I also ran across a
study of whether this is such a big deal or not. In terms of being
a possible danger to linemen, the study concluded it really isn't,
that they take precautions and it's extremely unlikely they would
be injured. Higher chance of first responders, but even there very
low incidence. Even damage to eqpt that was connected was rated
very low. The biggest issue was that automatic reclosers on the
grid that try to close to restore power could be affected and not
close like they should.



This might work if you had one guy on a street full of solar power
systems with a generator back feeding the street to tickle everyone's
inverter, all residents being frugal and a line cut isolating that
street from the rest of the grid.
It would work until sundown anyway ;-)


I found this that explains a lot. We're on the right track of thinking
about what happens and that it's kind of a paradox as to how to detect
the loss of the "grid". They call this problem "islanding". This
talks about the ways they detect it, it's complicated and even includes
active action by inverters to deliberately try to destabilize the
grid so that it goes off kilter and all the other inverters can more
quickly detect it. It looks like they use voltage changes, freq changes
and power factor changes as possible parts of the algorithms and
that it's not a trivial problem. I think this gear is more for a larger
commercial array, but the same principles should apply to all inverters.


https://www.solectria.com/blog/anti-...-pv-inverters/
  #44   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 810
Default Sub Panel neutral bonding



I found this that explains a lot. We're on the right track of thinking
about what happens and that it's kind of a paradox as to how to detect
the loss of the "grid". They call this problem "islanding". This
talks about the ways they detect it, it's complicated and even includes
active action by inverters to deliberately try to destabilize the
grid so that it goes off kilter and all the other inverters can more
quickly detect it. It looks like they use voltage changes, freq changes
and power factor changes as possible parts of the algorithms and
that it's not a trivial problem. I think this gear is more for a larger
commercial array, but the same principles should apply to all inverters.


https://www.solectria.com/blog/anti-...-pv-inverters/


that is interesting

it is also what makes the frustrating situation for people that spent a lot of money for a solar system, and they still have no electricity when the grid is down, even when the sun is out.

m
  #45   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 15,279
Default Sub Panel neutral bonding

On Wednesday, June 12, 2019 at 1:31:12 PM UTC-4, wrote:

I found this that explains a lot. We're on the right track of thinking
about what happens and that it's kind of a paradox as to how to detect
the loss of the "grid". They call this problem "islanding". This
talks about the ways they detect it, it's complicated and even includes
active action by inverters to deliberately try to destabilize the
grid so that it goes off kilter and all the other inverters can more
quickly detect it. It looks like they use voltage changes, freq changes
and power factor changes as possible parts of the algorithms and
that it's not a trivial problem. I think this gear is more for a larger
commercial array, but the same principles should apply to all inverters.


https://www.solectria.com/blog/anti-...-pv-inverters/


that is interesting

it is also what makes the frustrating situation for people that spent a lot of money for a solar system, and they still have no electricity when the grid is down, even when the sun is out.

m


Agree. When solar electric was first rolling out, I assumed that would be
a big advantage, that you could have power during the day with the grid
down. If someone could figure out a way to do that without batteries,
it would be a big selling advantage. The essence of the problem I guess
is that the sun varies and it would be difficult to maintain constant
power. Still, you'd think if it's say a 8KW system, couldn't they provide
2KW to whatever loads you wanted to have emergency power? If the sun
isn't sufficient, then it shuts down. If it gets sun sufficient for
3KW, then it turns back on. Software could impose off time delays
and lengthen the off times if starts cycling too much, etc. But I
guess a lot of people wouldn't pay much for that, having unpredictable
power that comes and goes and only during the day.


  #46   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 14,141
Default Sub Panel neutral bonding

On Wed, 12 Jun 2019 11:14:35 -0500, Terry Coombs
wrote:

On 6/12/2019 8:48 AM, wrote:

Â* Done is done , I have bonded the ground/neutral in the sub panel and
added a ground rod out in the shop .

snip...

I agree using the 3 wire system and bonding the neutral and ground is the most practical solution. But be aware, if that third ground/neutral wire should fail open, there will be a dangerous condition in the outbuilding. Everything that was ground, can become energized.



mark



Â* The likelihood of that 3/0 cable failing is very very slim ... I'll
also be bonding the metal frame of the shop to the panel , it has some
serious ground contact , including either 6 or 8 5/8" rods a couple of
feet long driven thru the bottom member into the ground before I poured
the concrete . I've been running stuff out there with a 3 wire
ungrounded neutral bonded supply for 5 years or so , never had a problem
. That was with lighter wire , part of the install of the new panel
included running the 3/0 aluminum cable all the way to the shop to
replace that section of smaller wire .


If there is a total of 10' or more of steel in contact with that
concrete footer you have a Ufer (concrete encased electrode) and that
is far better than the rods you drove. In fact with a Ufer, you don't
even need the rods. You should be using a #4 or larger to connect the
Ufer, Rods only require a #6. That should tell you something right
there. If I was doing it I would have run another #5 rebar around the
footer, tying all of the down rods together and then you have serious
contact with the concrete and a stronger footer.
  #47   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 14,141
Default Sub Panel neutral bonding

On Wed, 12 Jun 2019 09:17:16 -0700 (PDT), trader_4
wrote:

On Tuesday, June 11, 2019 at 11:19:22 PM UTC-4, wrote:
On Tue, 11 Jun 2019 16:55:43 -0700 (PDT), trader_4
wrote:

On Tuesday, June 11, 2019 at 7:46:48 PM UTC-4, wrote:
On Tue, 11 Jun 2019 14:20:47 -0700 (PDT), trader_4
wrote:

On Tuesday, June 11, 2019 at 5:05:03 PM UTC-4, wrote:
On Tue, 11 Jun 2019 10:21:46 -0700 (PDT), trader_4
wrote:

On Tuesday, June 11, 2019 at 12:47:52 PM UTC-4, Terry Coombs wrote:
On 6/11/2019 8:32 AM, wrote:


Why is the ground rod at the service any better than the one at the
shop? I agree 4 is better than 2 but they are already bonded together
via the neutral in a 3 wire feeder. I doubt he wants to dig up the
yard. This was done this way for 90 years and we didn't pile up a lot
of bodies. The code change was mostly just to make the language
consistent with the rest of the code. Same with ranges and dryers. The
grandfather clause is still there for things done pre 96 adoption.
It does mean you have to be more careful with your bonding and
grounding tho.
the ground connection serves 2 purposes

1) a path for lightning
the ground rod is to provide a path for lightning etc.
this NEEDS to be a path to actual Earth ground because that is where lightning will go.

2) protection from shock due to equipment faults
this is to protect you from a shock if the hot wire shorts to the metal case inside an appliance. Think of a motor with all those windings of enameled wire. If the insulation should fail and connect the power to the metal case of the appliance, you can be shocked by touching the appliance. If the case is grounded

however,
when the short happens, a large fault current will flow and blow the breaker. For a LARGE fault current to flow, the ground must be low resistance. So you want a BOND WIRE between the neutral and ground in the system. This provides a path for the fault current to flow sufficient to blow the breaker if there is a

ground
fault.
Often a ground rod alone is too high resistance.

#2 is an important safety feature, I would not skimp on this.


So if have only 3 wires between the buildings and you can't add the 4th wire, I think bonding the outbuilding neutral and ground together at the entrance to the outbuilding is the safer option compared to relying on a ground rod alone.

You can also add a ground rod there to help for lightning.

If you don't need 240V and need only 120V in the outbuilding, you can use the 3 wires as hot neutral and ground. That is 100% safe and legal but you give up having 240V.



mark


Â* Done is done , I have bonded the ground/neutral in the sub panel and
added a ground rod out in the shop . Doing without 240V is unacceptable
, I have 2 welders and an air compressor that all need 240V . And plans
are to install a 240V 3 phase motor with a VFD on the mill in the future
. Lightning is unlikely down in The Holler , but still possible . This
is a "hobby" shop , but is very well equipped - pretty much a full
machine and welding shop .

--
Snag
Yes , I'm old
and crochety - and armed .
Get outta my woods !

That's what I would have done too, except probably adding a second ground
rod. IDK how you're going to install 3 phase eqpt though, without redoing
what you just did and a whole new service, for that matter?

You can get a VFD that is single phase in and 3 phase out

I see, well that solves that.

So here's another puzzling question. In that thread about solar panels
that has now run amok, Danny brought up the issue of preventing backfeeding
into the grid. AFAIK, that's built into the inverters, but how do they
do it? It would seem like the chicken and the egg problem. You need to
detect the grid power going off, but you are connected directly to it and
also powering it. So, how do they detect it? Obviously before connecting
they must first monitor the voltage, freq and phase and sync to it, but
once you connect, how do you then tell the other grid sources are gone?
I guess you could look for voltage drop, since with the grid down
you'd expect 99.9% there will be big voltage decrease. But is that
sufficient? And what do they really do inside those inverters?

Hypothetically, suppose there are 6 houses on a utility line that
have solar and that segment is connected to the whole distribution
system. The sun is shining, those houses are using significantly
less than the panels put out. I cut the line to the rest of the grid,
leaving just those 6 connected. What happens? Is the "grid" down?
How do those inverters detect it? Do they? What happens?

We got a pitch on these things a while ago. Basically a grid tie
inverter is clocked from the grid. No grid, no output.

But the question remains, the inverter is part of the grid, the inverters
along the block are part of the grid, in addition to some generators
somewhere. So, how does it know that the "grid" is down?

Hypothetically, suppose there are 6 houses on a utility line that
have solar and that segment is connected to the whole distribution
system. The sun is shining, those houses are using significantly
less than the panels put out. I cut the line to the rest of the grid,
leaving just those 6 connected. What happens? Is the "grid" down?
How do those inverters detect it? Do they? What happens?


That is an interesting question but theoretically each grid tied
inverter would lose clocking and shut down.


But they don't really lose clocking, because if you have six houses,
each was following the "grid" which is whatever sources, including
the other solar. So, they would then follow collectively what is
there which at the moment the segement is cut off, it 60 hz and A-OK.
So they would be following each other. But I think what happens is
that since they are each following the other and constantly trying
to match, it does lead to the freq starting to vary slightly.


I think they are smart enough to each know the grid dropped and they
all shut down.

I have posed this question to everyone I have talked to without an
answer. What happens if you disconnect from the grid, drop all of
your loads and connect a battery powered inverter. Will that clock
your grid tie and allow you to add loads until you overwhelm it?


Right, same idea. Would the grid tie inverter recognize that the
battery powered inverter isn't the "grid". Whatever the "grid"
even means. I guess the grid they are looking for would be
defined as having at least one power company generator source. But wait,
not sure even that's right. Power companies have solar and wind
today too. If a disconnected segment had power solar, it's like
the solar from home we're talking about. Wind, IDK, but that would
seem to have the same issues, I assume they are using inverters too
and not a generator where the rotation speed governs the freq.

Since the net flow of that clock would be "in" I think it would keep
going but I can't get a real answer.
The battery inverter would need to be strong enough to handle the
connected load at the time tho.
PoCo connected sources are probably monitored in a different way.



They run at a
voltage that can be potentially slightly higher than the grid so if
there is any power left over, it flows backward into the grid. A smart
meter will see that and meter based on your local tariff agreement.
The old style would just run backward if net flow was out instead of
in. If you netted more use than you fed back in, no harm, just a
lower bill. If you showed a negative bill I guess you would be talking
to the PoCo.
That is how people used to steal power, plug the meter in upside down
it runs backward so there is a chance you would be starting in the
fraud department if they did not know about your solar.
The "plug in" collectors plug in just like your toaster and will boost
the power on that side of your service. These things are usually too
small to ever feed back into the grid if you have anything running at
all.

But from everything I see, a 10KW home solar system behaves exactly
like the plug in ones and needs to detect when to disconnect.


That is the way I understand it. Each inverter should detect loss of
grid and shut down. It would be interesting if you had something else
feeding the grid like your generator idea that the plan might fail. I
also doubt there is enough power going into the grid to sustain it if
you are not getting utility power, even if you have a lot of people
with a black roof.


I agree. In 99.9% of the cases of a segment coming disconnected from
the rest of the utility, you'd think there would be big, obvious
problems, starting with a big voltage drop. I also ran across a
study of whether this is such a big deal or not. In terms of being
a possible danger to linemen, the study concluded it really isn't,
that they take precautions and it's extremely unlikely they would
be injured. Higher chance of first responders, but even there very
low incidence. Even damage to eqpt that was connected was rated
very low. The biggest issue was that automatic reclosers on the
grid that try to close to restore power could be affected and not
close like they should.


My neighbor is a lineman for FPL doing local distribution and he says
that would not be an issue for him safety wise since they assume every
wire is hot before they ground it to work on it. He did say if they
track power back to your generator, your drop will be laying in your
yard until every street light and rusty transformer is replaced.
Then they will go to lunch and think about handling your call ...
maybe next week.

This might work if you had one guy on a street full of solar power
systems with a generator back feeding the street to tickle everyone's
inverter, all residents being frugal and a line cut isolating that
street from the rest of the grid.
It would work until sundown anyway ;-)


I found this that explains a lot. We're on the right track of thinking
about what happens and that it's kind of a paradox as to how to detect
the loss of the "grid". They call this problem "islanding". This
talks about the ways they detect it, it's complicated and even includes
active action by inverters to deliberately try to destabilize the
grid so that it goes off kilter and all the other inverters can more
quickly detect it. It looks like they use voltage changes, freq changes
and power factor changes as possible parts of the algorithms and
that it's not a trivial problem. I think this gear is more for a larger
commercial array, but the same principles should apply to all inverters.


https://www.solectria.com/blog/anti-...-pv-inverters/

I think that is just a complicated way of saying that without a stable
clock, these things will just go nuts and shut down
  #48   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 14,141
Default Sub Panel neutral bonding

On Wed, 12 Jun 2019 10:31:06 -0700 (PDT), wrote:



I found this that explains a lot. We're on the right track of thinking
about what happens and that it's kind of a paradox as to how to detect
the loss of the "grid". They call this problem "islanding". This
talks about the ways they detect it, it's complicated and even includes
active action by inverters to deliberately try to destabilize the
grid so that it goes off kilter and all the other inverters can more
quickly detect it. It looks like they use voltage changes, freq changes
and power factor changes as possible parts of the algorithms and
that it's not a trivial problem. I think this gear is more for a larger
commercial array, but the same principles should apply to all inverters.


https://www.solectria.com/blog/anti-...-pv-inverters/

that is interesting

it is also what makes the frustrating situation for people that spent a lot of money for a solar system, and they still have no electricity when the grid is down, even when the sun is out.

m


Hence my question, could you disconnect from the grid and use a small
inverter or a little Honda to clock your solar inverter and rock on.
There is not much of an advantage with a construction generator but a
little inverter generator might be able to run at idle speed for days
on a tank of gas while the solar array does all of the heavy lifting,
Same with a 12v inverter, except you could use your solar power to
keep your 12v battery up.
I just have not found a guy with a grid tie system who was brave
enough to try it.
To really be effective you would need a 240v centertapped supply. That
might be as simple as a transformer tho.
  #49   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 15,279
Default Sub Panel neutral bonding

On Wednesday, June 12, 2019 at 2:51:36 PM UTC-4, wrote:
On Wed, 12 Jun 2019 10:31:06 -0700 (PDT), wrote:



I found this that explains a lot. We're on the right track of thinking
about what happens and that it's kind of a paradox as to how to detect
the loss of the "grid". They call this problem "islanding". This
talks about the ways they detect it, it's complicated and even includes
active action by inverters to deliberately try to destabilize the
grid so that it goes off kilter and all the other inverters can more
quickly detect it. It looks like they use voltage changes, freq changes
and power factor changes as possible parts of the algorithms and
that it's not a trivial problem. I think this gear is more for a larger
commercial array, but the same principles should apply to all inverters.


https://www.solectria.com/blog/anti-...-pv-inverters/

that is interesting

it is also what makes the frustrating situation for people that spent a lot of money for a solar system, and they still have no electricity when the grid is down, even when the sun is out.

m


Hence my question, could you disconnect from the grid and use a small
inverter or a little Honda to clock your solar inverter and rock on.


I think if you read that description I provided of how they detect
the loss of the grid, the answer is almost certainly not. They are
looking for stability in voltage, freq, power factor and it's
unlikely a typical home generator is going to fool it. Especially
with variable load, which you'd have when a fridge cycles on, etc.
Of course that description looks like it's for a bigger solar install than
a home one, but the home ones have to comply with regs and must use
similar techniques. Most interesting in that was that the inverters
described there actually deliberately screw with the grid when they
think they may be in an island situation, the idea being that you
can't perturb a true grid, but if the "grid" is an island with just
some other solar sources, you can and then other inverters will see
the deviation and shut down too.




There is not much of an advantage with a construction generator but a
little inverter generator might be able to run at idle speed for days
on a tank of gas while the solar array does all of the heavy lifting,
Same with a 12v inverter, except you could use your solar power to
keep your 12v battery up.
I just have not found a guy with a grid tie system who was brave
enough to try it.
To really be effective you would need a 240v centertapped supply. That
might be as simple as a transformer tho.


  #50   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 14,141
Default Sub Panel neutral bonding

On Wed, 12 Jun 2019 10:59:23 -0700 (PDT), trader_4
wrote:

On Wednesday, June 12, 2019 at 1:31:12 PM UTC-4, wrote:

I found this that explains a lot. We're on the right track of thinking
about what happens and that it's kind of a paradox as to how to detect
the loss of the "grid". They call this problem "islanding". This
talks about the ways they detect it, it's complicated and even includes
active action by inverters to deliberately try to destabilize the
grid so that it goes off kilter and all the other inverters can more
quickly detect it. It looks like they use voltage changes, freq changes
and power factor changes as possible parts of the algorithms and
that it's not a trivial problem. I think this gear is more for a larger
commercial array, but the same principles should apply to all inverters.


https://www.solectria.com/blog/anti-...-pv-inverters/


that is interesting

it is also what makes the frustrating situation for people that spent a lot of money for a solar system, and they still have no electricity when the grid is down, even when the sun is out.

m


Agree. When solar electric was first rolling out, I assumed that would be
a big advantage, that you could have power during the day with the grid
down. If someone could figure out a way to do that without batteries,
it would be a big selling advantage. The essence of the problem I guess
is that the sun varies and it would be difficult to maintain constant
power. Still, you'd think if it's say a 8KW system, couldn't they provide
2KW to whatever loads you wanted to have emergency power? If the sun
isn't sufficient, then it shuts down. If it gets sun sufficient for
3KW, then it turns back on. Software could impose off time delays
and lengthen the off times if starts cycling too much, etc. But I
guess a lot of people wouldn't pay much for that, having unpredictable
power that comes and goes and only during the day.


Probably the easiest way would be an inverter generator capable of
providing 120/240. It could just loaf along at idle when the sun was
shining and kick it up if a cloud came over or the sun went down.
You would still need transfer equipment tho.




  #51   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,367
Default Sub Panel neutral bonding

dpb posted for all of us...


Still have all the old mother-of-pearl
inlaid pushbutton light switches that are classic in looks but not up to
120 VAC, sadly.


Ahh, still remember them from my childhood.

--
Tekkie
  #52   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,367
Default Sub Panel neutral bonding

Terry Coombs posted for all of us...



* Done is done , I have bonded the ground/neutral in the sub panel and
added a ground rod out in the shop . Doing without 240V is unacceptable
, I have 2 welders and an air compressor that all need 240V . And plans
are to install a 240V 3 phase motor with a VFD on the mill in the future
. Lightning is unlikely down in The Holler , but still possible . This
is a "hobby" shop , but is very well equipped - pretty much a full
machine and welding shop .


I have a couple of 'projects' for you

--
Tekkie
  #53   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 3,115
Default Sub Panel neutral bonding

On 6/12/2019 2:44 PM, Tekkie® wrote:
Terry Coombs posted for all of us...


* Done is done , I have bonded the ground/neutral in the sub panel and
added a ground rod out in the shop . Doing without 240V is unacceptable
, I have 2 welders and an air compressor that all need 240V . And plans
are to install a 240V 3 phase motor with a VFD on the mill in the future
. Lightning is unlikely down in The Holler , but still possible . This
is a "hobby" shop , but is very well equipped - pretty much a full
machine and welding shop .

I have a couple of 'projects' for you


* Whatcha got ?

--
Snag
Yes , I'm old
and crochety - and armed .
Get outta my woods !

  #54   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 3,115
Default Sub Panel neutral bonding

On 6/12/2019 1:33 PM, wrote:
On Wed, 12 Jun 2019 11:14:35 -0500, Terry Coombs
wrote:

On 6/12/2019 8:48 AM,
wrote:

Â* Done is done , I have bonded the ground/neutral in the sub panel and
added a ground rod out in the shop .

snip...

I agree using the 3 wire system and bonding the neutral and ground is the most practical solution. But be aware, if that third ground/neutral wire should fail open, there will be a dangerous condition in the outbuilding. Everything that was ground, can become energized.



mark



Â* The likelihood of that 3/0 cable failing is very very slim ... I'll
also be bonding the metal frame of the shop to the panel , it has some
serious ground contact , including either 6 or 8 5/8" rods a couple of
feet long driven thru the bottom member into the ground before I poured
the concrete . I've been running stuff out there with a 3 wire
ungrounded neutral bonded supply for 5 years or so , never had a problem
. That was with lighter wire , part of the install of the new panel
included running the 3/0 aluminum cable all the way to the shop to
replace that section of smaller wire .

If there is a total of 10' or more of steel in contact with that
concrete footer you have a Ufer (concrete encased electrode) and that
is far better than the rods you drove. In fact with a Ufer, you don't
even need the rods. You should be using a #4 or larger to connect the
Ufer, Rods only require a #6. That should tell you something right
there. If I was doing it I would have run another #5 rebar around the
footer, tying all of the down rods together and then you have serious
contact with the concrete and a stronger footer.


Â* There is a total of 40 linear feet of galvanized 2" square tube in
contact with concrete on 2 sides - I spaced the tubes off the ground and
worked the concrete under them . I think a 5/16" lag screw thru the side
of the enclosure and into the square tube oughta do it ... I do have
some #4 stranded and some solder on lugs if that's necessary . The rods
into the ground are to keep the dern thing from blowin' in the wind .

--
Snag
Yes , I'm old
and crochety - and armed .
Get outta my woods !

  #55   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 14,141
Default Sub Panel neutral bonding

On Wed, 12 Jun 2019 12:17:50 -0700 (PDT), trader_4
wrote:

On Wednesday, June 12, 2019 at 2:51:36 PM UTC-4, wrote:
On Wed, 12 Jun 2019 10:31:06 -0700 (PDT), wrote:



I found this that explains a lot. We're on the right track of thinking
about what happens and that it's kind of a paradox as to how to detect
the loss of the "grid". They call this problem "islanding". This
talks about the ways they detect it, it's complicated and even includes
active action by inverters to deliberately try to destabilize the
grid so that it goes off kilter and all the other inverters can more
quickly detect it. It looks like they use voltage changes, freq changes
and power factor changes as possible parts of the algorithms and
that it's not a trivial problem. I think this gear is more for a larger
commercial array, but the same principles should apply to all inverters.


https://www.solectria.com/blog/anti-...-pv-inverters/

that is interesting

it is also what makes the frustrating situation for people that spent a lot of money for a solar system, and they still have no electricity when the grid is down, even when the sun is out.

m


Hence my question, could you disconnect from the grid and use a small
inverter or a little Honda to clock your solar inverter and rock on.


I think if you read that description I provided of how they detect
the loss of the grid, the answer is almost certainly not. They are
looking for stability in voltage, freq, power factor and it's
unlikely a typical home generator is going to fool it. Especially
with variable load, which you'd have when a fridge cycles on, etc.
Of course that description looks like it's for a bigger solar install than
a home one, but the home ones have to comply with regs and must use
similar techniques. Most interesting in that was that the inverters
described there actually deliberately screw with the grid when they
think they may be in an island situation, the idea being that you
can't perturb a true grid, but if the "grid" is an island with just
some other solar sources, you can and then other inverters will see
the deviation and shut down too.


My generator was pretty stable, looking at it on a scope and the
frequency doesn't drift that much when the engine grunts looking at a
frequency counter. An inverter generator should not change at all.
I think the author was just trying to dumb down his talk. When he says
"screw with the grid" what he really means is these things do not have
an internal clock and without a stable clock coming in they just go
nuts. It detects that condition and shuts down, probably in a cycle or
two.
..



  #57   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4,564
Default Sub Panel neutral bonding

On Wed, 12 Jun 2019 14:51:14 -0400, wrote:

On Wed, 12 Jun 2019 10:31:06 -0700 (PDT),
wrote:



I found this that explains a lot. We're on the right track of thinking
about what happens and that it's kind of a paradox as to how to detect
the loss of the "grid". They call this problem "islanding". This
talks about the ways they detect it, it's complicated and even includes
active action by inverters to deliberately try to destabilize the
grid so that it goes off kilter and all the other inverters can more
quickly detect it. It looks like they use voltage changes, freq changes
and power factor changes as possible parts of the algorithms and
that it's not a trivial problem. I think this gear is more for a larger
commercial array, but the same principles should apply to all inverters.


https://www.solectria.com/blog/anti-...-pv-inverters/

that is interesting

it is also what makes the frustrating situation for people that spent a lot of money for a solar system, and they still have no electricity when the grid is down, even when the sun is out.

m


Hence my question, could you disconnect from the grid and use a small
inverter or a little Honda to clock your solar inverter and rock on.
There is not much of an advantage with a construction generator but a
little inverter generator might be able to run at idle speed for days
on a tank of gas while the solar array does all of the heavy lifting,
Same with a 12v inverter, except you could use your solar power to
keep your 12v battery up.
I just have not found a guy with a grid tie system who was brave
enough to try it.
To really be effective you would need a 240v centertapped supply. That
might be as simple as a transformer tho.

The question is what dioes the generator/inverter think of having
power supplied to the output?? Now, if you could iso;ate the "clock" a
small inverter would do the job - all it would produce is the "sync"
signal. You could produce that from the sound output of a cell phone
or tablet - - -
  #58   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4,564
Default Sub Panel neutral bonding

On Wed, 12 Jun 2019 15:43:06 -0400, Tekkie®
wrote:

dpb posted for all of us...


Still have all the old mother-of-pearl
inlaid pushbutton light switches that are classic in looks but not up to
120 VAC, sadly.


Ahh, still remember them from my childhood.

Had them for 120 volt too - lots of old houses here had them. There
is at least one company producing them for use in modern electrical
systems for the "retro" look.
  #59   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,325
Default Sub Panel neutral bonding

On 6/12/2019 8:52 PM, Clare Snyder wrote:
On Wed, 12 Jun 2019 15:43:06 -0400, Tekkie®
wrote:

dpb posted for all of us...


Still have all the old mother-of-pearl
inlaid pushbutton light switches that are classic in looks but not up to
120 VAC, sadly.


Ahh, still remember them from my childhood.

Had them for 120 volt too - lots of old houses here had them. There
is at least one company producing them for use in modern electrical
systems for the "retro" look.


Yeah, I've not looked for a number of years now, though--last time I did
the only ones I found at the time were outrageously priced even for a
low volume specialty product...

I've thought one could replace the workings behind the buttons on the
plate w/ new mechanical pushbutton switches but never had sufficient
initiative to actually do so.

--





  #60   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4,564
Default Sub Panel neutral bonding

On Wed, 12 Jun 2019 21:25:43 -0500, dpb wrote:

On 6/12/2019 8:52 PM, Clare Snyder wrote:
On Wed, 12 Jun 2019 15:43:06 -0400, Tekkie®
wrote:

dpb posted for all of us...


Still have all the old mother-of-pearl
inlaid pushbutton light switches that are classic in looks but not up to
120 VAC, sadly.


Ahh, still remember them from my childhood.

Had them for 120 volt too - lots of old houses here had them. There
is at least one company producing them for use in modern electrical
systems for the "retro" look.


Yeah, I've not looked for a number of years now, though--last time I did
the only ones I found at the time were outrageously priced even for a
low volume specialty product...


Last one I saw was $37 us each plus shipping. That was a few years
ago.

They are about $15 now from house of antique hardware or Classic
Accents on Amazon.

I've thought one could replace the workings behind the buttons on the
plate w/ new mechanical pushbutton switches but never had sufficient
initiative to actually do so.



  #61   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 390
Default Sub Panel neutral bonding

On 6/10/2019 11:53 AM, wrote:
On Mon, 10 Jun 2019 09:09:50 -0700 (PDT), trader_4
wrote:

On Sunday, June 9, 2019 at 10:40:23 PM UTC-4, wrote:
On Sun, 9 Jun 2019 20:01:54 -0500, Terry Coombs
wrote:


Â* When is it necessary ? I've just replaced the panel out in the shop
(aluminum buss bars on the old one were giving problems) and I have a 3
wire service run out there . At this time the only place the neutral is
bonded to ground is in the meter box . It has been suggested to me to
bond them in the main panel too ... but that seems redundant to me ,
they're only the thickness of a piece of plywood apart . I have
considered installing a ground rod at the new panel but am concerned
about the potential for ground loop currents .

If you only have 3 wires in the feeder going to the shop you need to
bond the neutral and ground out there too or there is no path for
fault current. You also need a ground electrode out there. Current
code requires a 4 wire feeder and isolating neutral and ground in sub
panels but if the wire was already there when the 1996 code was
adopted the 3 wire feeder is grandfathered in.
Ground loops are not an issue but carrying circuit current in the
grounding conductor is, That is why you do need another ground
electrode. Essentially you are creating another service in the second
building and creating a new ground reference there.
In the electrical biz, you can't have too many ground electrodes but
they all need to be bonded together.


His main question appeared to be whether the neutral and ground need
to be bonded in the MAIN panel if they are already bonded at the meter
which is right next to it?


That is open to debate. A strict reading of the NEC says the PoCo
should not have bonded the neutral in their can but since they do not
have to follow the NEC, the language was tweaked a little (again 96 as
I recall) so it is all "service equipment" and you still rebond the
neutral in the service disconnect enclosure where the code says the
"Main Bonding Jumper" is supposed to be. That is usually just a green
screw on the neutral bus or a strap.
The hitch is that the MBJ "shall remain accessible" and inside the
meter can isn't. Sanity prevailed. Meter cans are usually made so the
can is bonded to the neutral anyway. There is no way to avoid it.

Some inspectors require that there be no metallic paths between the
meter can (a PVC sleeve) and that you only bring 3 wires in. Then we
did not care what they did in the can, the MBJ was clearly in the
service disconnect enclosure.

The grounding electrode conductor can land anywhere from the service
point (usually the mast head on an overhead drop) to the service
disconnect enclosure. That is how they can land it in the meter can.
If you have an underground service lateral, the service point is
usually the transformer connection at the street. Yes you usually own
that wire in the yard. You typically do not own an overhead drop.


A slightly broader view - the requirements for grounding-bonding on a
service entrance are much tougher than past the service. Assume an
overhead drop and EMT service entrance. The EMT from the meter can to
the service panel is likely to be connected through concentric/ecentric
knockouts at each end. That is not allowed for bonding and the meter can
and EMT section are then not "grounded". Around here the practice was
for the GEC exiting the panel to go through a ground clamp on the EMT
then to the electrodes. That bonded the EMT but left the meter can. The
bond between neutral and meter can is then critical. The EMT riser above
the meter is connected through a hub, which is good for bonding.

I am too lazy to look it up, but I think if the EMT between the meter
can and service panel does not have concentric/ecentric knockouts, an
EMT connector through the right sized hole is also not an approved bond
and a "grounding locknut" (not an ordinary locknut) or other means has
to be used.

The EMT between the meter can and service panel is in parallel with the
neutral wire but that was not considered a problem here.

If PVC conduit is used, more likely now, the bonding problems go away,
but bonding the neutral to the meter can is then also critical.

The way I read Terry's post there is a utility meter separated from the
panel by 1/4" of plywood. Sounds like a service panel, not a
feeder-subpanel. Or that discussion may be in addition to a "new panel"
at a separate shop building run off of a 3-wire feeder. Neutral-ground
bond and earthing electrode(s) apply to both. More stringent bonding
(above) only applies to a service.

I would want a Main Bonding Jumper in a service panel (is required in a
separate building 3-wire feed subpanel). For a service with no MBJ in
the service panel the bonding (as above) on the ?metal pipe? from the
meter can is a particular question.
  #62   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,526
Default Sub Panel neutral bonding

On Wednesday, June 12, 2019 at 3:43:07 PM UTC-4, Tekkie® wrote:
dpb posted for all of us...


Still have all the old mother-of-pearl
inlaid pushbutton light switches that are classic in looks but not up to
120 VAC, sadly.


Ahh, still remember them from my childhood.

--
Tekkie


We had them when I was a kid.

We had a visitor with an intention tremor. Watching him try to stab those buttons when his finger was shaking was painful.

  #63   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 15,279
Default Sub Panel neutral bonding

On Wednesday, June 12, 2019 at 8:43:28 PM UTC-4, wrote:
On Wed, 12 Jun 2019 12:17:50 -0700 (PDT), trader_4
wrote:

On Wednesday, June 12, 2019 at 2:51:36 PM UTC-4, wrote:
On Wed, 12 Jun 2019 10:31:06 -0700 (PDT), wrote:



I found this that explains a lot. We're on the right track of thinking
about what happens and that it's kind of a paradox as to how to detect
the loss of the "grid". They call this problem "islanding". This
talks about the ways they detect it, it's complicated and even includes
active action by inverters to deliberately try to destabilize the
grid so that it goes off kilter and all the other inverters can more
quickly detect it. It looks like they use voltage changes, freq changes
and power factor changes as possible parts of the algorithms and
that it's not a trivial problem. I think this gear is more for a larger
commercial array, but the same principles should apply to all inverters.


https://www.solectria.com/blog/anti-...-pv-inverters/

that is interesting

it is also what makes the frustrating situation for people that spent a lot of money for a solar system, and they still have no electricity when the grid is down, even when the sun is out.

m

Hence my question, could you disconnect from the grid and use a small
inverter or a little Honda to clock your solar inverter and rock on.


I think if you read that description I provided of how they detect
the loss of the grid, the answer is almost certainly not. They are
looking for stability in voltage, freq, power factor and it's
unlikely a typical home generator is going to fool it. Especially
with variable load, which you'd have when a fridge cycles on, etc.
Of course that description looks like it's for a bigger solar install than
a home one, but the home ones have to comply with regs and must use
similar techniques. Most interesting in that was that the inverters
described there actually deliberately screw with the grid when they
think they may be in an island situation, the idea being that you
can't perturb a true grid, but if the "grid" is an island with just
some other solar sources, you can and then other inverters will see
the deviation and shut down too.


My generator was pretty stable, looking at it on a scope and the
frequency doesn't drift that much when the engine grunts looking at a
frequency counter.



"That much", is likely a world of difference compared to the normal
grid and would be instantly detected.


An inverter generator should not change at all.


Maybe.


I think the author was just trying to dumb down his talk. When he says
"screw with the grid" what he really means is these things do not have
an internal clock and without a stable clock coming in they just go
nuts. It detects that condition and shuts down, probably in a cycle or
two.
.


He didn't say "screw with the grid" and he actually explained what he
meant.


"For the active anti-islanding function, we use a technique called Slip Mode Frequency Shift. This varies the reactive power output of the inverter. The goal of this protection method is to destabilize an islanded feeder by trying to influence the frequency. This diagram, from the IEEE 1547 testing procedure, shows how we test the anti-islanding function in the inverter.

We intentionally force the frequency out of spec and push against the grid, so we can properly detect and dissolve the island. We actually turn the anti-islanding function off, create an island, turn the anti-islanding function back on, and test the ability to disturb the island within two seconds. In our tests, we actually do it much faster."


You could try to fool a grid tie inverter with another inverter. You
don't even need a generator inverter, you could use a car battery and
an inverter. If it worked, you could keep the battery charged from
the solar power. I doubt it would work. It would depend on
the actual anti-islanding methods used in the particular solar inverter.
And then there is the problem of how does a typical battery inverter
or generator inverter react when the solar inverter is fooled into
thinking the grid is there, powers up, connects and tries to put power
into the "grid", which in this case is just a small inverter or generator?
I would think that would produce a condition that if it didn't blow up
the other inverter/generator, would result in conditions that the grid
tie inverter would recognize as not right and it would shut down.
  #64   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 14,141
Default Sub Panel neutral bonding

On Thu, 13 Jun 2019 07:55:03 -0600, bud-- wrote:

On 6/10/2019 11:53 AM, wrote:
On Mon, 10 Jun 2019 09:09:50 -0700 (PDT), trader_4
wrote:

On Sunday, June 9, 2019 at 10:40:23 PM UTC-4, wrote:
On Sun, 9 Jun 2019 20:01:54 -0500, Terry Coombs
wrote:


Â* When is it necessary ? I've just replaced the panel out in the shop
(aluminum buss bars on the old one were giving problems) and I have a 3
wire service run out there . At this time the only place the neutral is
bonded to ground is in the meter box . It has been suggested to me to
bond them in the main panel too ... but that seems redundant to me ,
they're only the thickness of a piece of plywood apart . I have
considered installing a ground rod at the new panel but am concerned
about the potential for ground loop currents .

If you only have 3 wires in the feeder going to the shop you need to
bond the neutral and ground out there too or there is no path for
fault current. You also need a ground electrode out there. Current
code requires a 4 wire feeder and isolating neutral and ground in sub
panels but if the wire was already there when the 1996 code was
adopted the 3 wire feeder is grandfathered in.
Ground loops are not an issue but carrying circuit current in the
grounding conductor is, That is why you do need another ground
electrode. Essentially you are creating another service in the second
building and creating a new ground reference there.
In the electrical biz, you can't have too many ground electrodes but
they all need to be bonded together.

His main question appeared to be whether the neutral and ground need
to be bonded in the MAIN panel if they are already bonded at the meter
which is right next to it?


That is open to debate. A strict reading of the NEC says the PoCo
should not have bonded the neutral in their can but since they do not
have to follow the NEC, the language was tweaked a little (again 96 as
I recall) so it is all "service equipment" and you still rebond the
neutral in the service disconnect enclosure where the code says the
"Main Bonding Jumper" is supposed to be. That is usually just a green
screw on the neutral bus or a strap.
The hitch is that the MBJ "shall remain accessible" and inside the
meter can isn't. Sanity prevailed. Meter cans are usually made so the
can is bonded to the neutral anyway. There is no way to avoid it.

Some inspectors require that there be no metallic paths between the
meter can (a PVC sleeve) and that you only bring 3 wires in. Then we
did not care what they did in the can, the MBJ was clearly in the
service disconnect enclosure.

The grounding electrode conductor can land anywhere from the service
point (usually the mast head on an overhead drop) to the service
disconnect enclosure. That is how they can land it in the meter can.
If you have an underground service lateral, the service point is
usually the transformer connection at the street. Yes you usually own
that wire in the yard. You typically do not own an overhead drop.


A slightly broader view - the requirements for grounding-bonding on a
service entrance are much tougher than past the service. Assume an
overhead drop and EMT service entrance. The EMT from the meter can to
the service panel is likely to be connected through concentric/ecentric
knockouts at each end. That is not allowed for bonding and the meter can
and EMT section are then not "grounded". Around here the practice was
for the GEC exiting the panel to go through a ground clamp on the EMT
then to the electrodes. That bonded the EMT but left the meter can. The
bond between neutral and meter can is then critical. The EMT riser above
the meter is connected through a hub, which is good for bonding.

I am too lazy to look it up, but I think if the EMT between the meter
can and service panel does not have concentric/ecentric knockouts, an
EMT connector through the right sized hole is also not an approved bond
and a "grounding locknut" (not an ordinary locknut) or other means has
to be used.

The EMT between the meter can and service panel is in parallel with the
neutral wire but that was not considered a problem here.

If PVC conduit is used, more likely now, the bonding problems go away,
but bonding the neutral to the meter can is then also critical.

The way I read Terry's post there is a utility meter separated from the
panel by 1/4" of plywood. Sounds like a service panel, not a
feeder-subpanel. Or that discussion may be in addition to a "new panel"
at a separate shop building run off of a 3-wire feeder. Neutral-ground
bond and earthing electrode(s) apply to both. More stringent bonding
(above) only applies to a service.

I would want a Main Bonding Jumper in a service panel (is required in a
separate building 3-wire feed subpanel). For a service with no MBJ in
the service panel the bonding (as above) on the ?metal pipe? from the
meter can is a particular question.


Raceways for service conductors get extra protection because there is
no real overcurrent protection on a service conductor.
Feeders are protected at their ampacity but service conductors are
not. . A bolted fault on a service conductor is as likely to burn out
the drop as it is to blow the primary fuse on the transformer. It will
certainly get hot enough to roast that squirrel running along it.
That is why your typical branch circuit breaker has a 10,000a AIC but
the service disconnect/main breaker will be 65ka AIC or more.
  #65   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 14,141
Default Sub Panel neutral bonding

On Thu, 13 Jun 2019 10:25:59 -0700 (PDT), trader_4
wrote:

On Wednesday, June 12, 2019 at 8:43:28 PM UTC-4, wrote:
On Wed, 12 Jun 2019 12:17:50 -0700 (PDT), trader_4
wrote:

On Wednesday, June 12, 2019 at 2:51:36 PM UTC-4, wrote:
On Wed, 12 Jun 2019 10:31:06 -0700 (PDT), wrote:



I found this that explains a lot. We're on the right track of thinking
about what happens and that it's kind of a paradox as to how to detect
the loss of the "grid". They call this problem "islanding". This
talks about the ways they detect it, it's complicated and even includes
active action by inverters to deliberately try to destabilize the
grid so that it goes off kilter and all the other inverters can more
quickly detect it. It looks like they use voltage changes, freq changes
and power factor changes as possible parts of the algorithms and
that it's not a trivial problem. I think this gear is more for a larger
commercial array, but the same principles should apply to all inverters.


https://www.solectria.com/blog/anti-...-pv-inverters/

that is interesting

it is also what makes the frustrating situation for people that spent a lot of money for a solar system, and they still have no electricity when the grid is down, even when the sun is out.

m

Hence my question, could you disconnect from the grid and use a small
inverter or a little Honda to clock your solar inverter and rock on.

I think if you read that description I provided of how they detect
the loss of the grid, the answer is almost certainly not. They are
looking for stability in voltage, freq, power factor and it's
unlikely a typical home generator is going to fool it. Especially
with variable load, which you'd have when a fridge cycles on, etc.
Of course that description looks like it's for a bigger solar install than
a home one, but the home ones have to comply with regs and must use
similar techniques. Most interesting in that was that the inverters
described there actually deliberately screw with the grid when they
think they may be in an island situation, the idea being that you
can't perturb a true grid, but if the "grid" is an island with just
some other solar sources, you can and then other inverters will see
the deviation and shut down too.


My generator was pretty stable, looking at it on a scope and the
frequency doesn't drift that much when the engine grunts looking at a
frequency counter.



"That much", is likely a world of difference compared to the normal
grid and would be instantly detected.


An inverter generator should not change at all.


Maybe.


I think the author was just trying to dumb down his talk. When he says
"screw with the grid" what he really means is these things do not have
an internal clock and without a stable clock coming in they just go
nuts. It detects that condition and shuts down, probably in a cycle or
two.
.


He didn't say "screw with the grid" and he actually explained what he
meant.


"For the active anti-islanding function, we use a technique called Slip Mode Frequency Shift. This varies the reactive power output of the inverter. The goal of this protection method is to destabilize an islanded feeder by trying to influence the frequency. This diagram, from the IEEE 1547 testing procedure, shows how we test the anti-islanding function in the inverter.

We intentionally force the frequency out of spec and push against the grid, so we can properly detect and dissolve the island. We actually turn the anti-islanding function off, create an island, turn the anti-islanding function back on, and test the ability to disturb the island within two seconds. In our tests, we actually do it much faster."


That is still flowery rhetoric for saying an unclocked inverter will
go nuts. I think if it got a stable clock it would run.





  #66   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,367
Default Sub Panel neutral bonding

Terry Coombs posted for all of us...



On 6/12/2019 2:44 PM, Tekkie® wrote:
Terry Coombs posted for all of us...


* Done is done , I have bonded the ground/neutral in the sub panel and
added a ground rod out in the shop . Doing without 240V is unacceptable
, I have 2 welders and an air compressor that all need 240V . And plans
are to install a 240V 3 phase motor with a VFD on the mill in the future
. Lightning is unlikely down in The Holler , but still possible . This
is a "hobby" shop , but is very well equipped - pretty much a full
machine and welding shop .

I have a couple of 'projects' for you


* Whatcha got ?


I will find the list, it is buried somewhere here.

I will need your personal advice as my schemes can be questionable when the
synapses' misfire.

--
Tekkie
  #67   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,367
Default Sub Panel neutral bonding

Clare Snyder posted for all of us...


Had them for 120 volt too - lots of old houses here had them. There
is at least one company producing them for use in modern electrical
systems for the "retro" look.


That is what you could classify me: the retro look.

--
Tekkie
  #68   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 3,115
Default Sub Panel neutral bonding

On 6/14/2019 2:39 PM, Tekkie® wrote:
Terry Coombs posted for all of us...


On 6/12/2019 2:44 PM, Tekkie® wrote:
Terry Coombs posted for all of us...


* Done is done , I have bonded the ground/neutral in the sub panel and
added a ground rod out in the shop . Doing without 240V is unacceptable
, I have 2 welders and an air compressor that all need 240V . And plans
are to install a 240V 3 phase motor with a VFD on the mill in the future
. Lightning is unlikely down in The Holler , but still possible . This
is a "hobby" shop , but is very well equipped - pretty much a full
machine and welding shop .

I have a couple of 'projects' for you

* Whatcha got ?

I will find the list, it is buried somewhere here.

I will need your personal advice as my schemes can be questionable when the
synapses' misfire.

* My reply-to is good . Hit me there and I'll give you my main email
address .

--
Snag
Yes , I'm old
and crochety - and armed .
Get outta my woods !

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Adding extra ground/neutral buss bar in electrical panel or add sub-panel? Mikepier Home Repair 84 April 4th 13 04:15 PM
Running a sub panel off of a sub panel stryped[_3_] Metalworking 5 October 14th 09 06:29 AM
Sub panel to a sub panel stryped[_3_] Metalworking 36 July 14th 09 07:51 AM
THANK YOU! Installing a sub panel from a sub panel rchtravel Home Repair 0 April 9th 04 04:47 PM
Installing a sub panel from a sub panel rchtravel Home Repair 6 April 9th 04 04:28 PM


All times are GMT +1. The time now is 10:07 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"